Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on ground under plants
b) surface clipped run to lighting, some lengths under plants some not.


NT

ARW January 25th 20 03:12 AM

Which cable outdoors?
 
On 25/01/2020 00:25, wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.




--
Adam

Jeff Layman[_2_] January 25th 20 08:34 AM

Which cable outdoors?
 
On 25/01/20 03:12, ARW wrote:
On 25/01/2020 00:25, wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.


If it's buried under plants, doesn't it have to be in conduit or
trunking to avoid damage from spades and forks?

Seems to me that "some laid on ground under plants" is a little unclear.
Does it mean only on the surface under the top growth of a plant?
Trouble is, it wouldn't take long to get hidden by fallen leaves and
other stuff, perhaps making it vulnerable to a spade.

--

Jeff

[email protected] January 25th 20 08:58 AM

Which cable outdoors?
 
On Saturday, 25 January 2020 08:34:59 UTC, Jeff Layman wrote:
On 25/01/20 03:12, ARW wrote:
On 25/01/2020 00:25, tabbypurr wrote:


Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.


If it's buried under plants, doesn't it have to be in conduit or
trunking to avoid damage from spades and forks?

Seems to me that "some laid on ground under plants" is a little unclear.
Does it mean only on the surface under the top growth of a plant?
Trouble is, it wouldn't take long to get hidden by fallen leaves and
other stuff, perhaps making it vulnerable to a spade.


I thought SWA was specifically for that. I just wondered if anything was also acceptable but of course it's not.

I see a fair bit of controversy over SY. This job has to be 100% to all standards, so looks like the non-plant on-wall areas will be NYY-J, and the under bushes one SWA.

Thanks folks


NT

[email protected] January 25th 20 09:37 AM

Which cable outdoors?
 
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25, wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


T i m January 25th 20 09:57 AM

Which cable outdoors?
 
On Sat, 25 Jan 2020 08:34:56 +0000, Jeff Layman
wrote:

On 25/01/20 03:12, ARW wrote:
On 25/01/2020 00:25, wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on ground under plants
b) surface clipped run to lighting, some lengths under plants some not.

snip

Seems to me that "some laid on ground under plants" is a little unclear.
Does it mean only on the surface under the top growth of a plant?


I read that as *on* the ground (as most of the options were 'surface
runs') under plants (in pots / planters)?

Otherwise wouldn't / shouldn't it have read '*In* ground under
plants'?

Cheers, T i m

Cynic[_2_] January 25th 20 10:38 AM

Which cable outdoors?
 
Heavy micc with pvc oversheath (provided you have the skill to correctly terminate it)

T i m January 25th 20 10:38 AM

Which cable outdoors?
 
On Sat, 25 Jan 2020 09:37:05 +0000, wrote:

snip


I hadn't heard of NYY-J until now, why would you use it rather than SWA?


Easier to cut / terminate than SWA but when I looked at it previously
I would have still needed to protect it so was back to SWA?

Cheers, T i m

Tricky Dicky[_4_] January 25th 20 10:42 AM

Which cable outdoors?
 
Depending on the length of cable run it might not be worth using two types, eg the difference in price according to CEF between 3 core 2.5mm2 SWA and the equivalent Tufsheath is 12p per metre if you have to use additional glands then you may not save much plus one less joint box and a potential point of water ingress.

Richard

Brian Gaff \(Sofa 2\) January 25th 20 11:33 AM

Which cable outdoors?
 
Well my armoured cable to the shed and when the garage greenouse and shed
were there is still in good nick, but was attached to the fence, most of it
still is. I'd not want to bury any kind of cable under a garden myself. The
old overhead links were ordinary pvc double insulated for a time but we soon
discovered that the sun and the cold did not make it last very long. The
plastic shroud of the armoured cable seemms to be a completely different
type of plastic that feels a bit like Teflon to the touch, and has lasted
well over 15 years. I think, was I doing it again, I'd use a bigger capacity
one though, since you could see lights dim when you put on a3kw fan heater.
grin.
Brian

--
----- --
This newsgroup posting comes to you directly from...
The Sofa of Brian Gaff...

Blind user, so no pictures please
Note this Signature is meaningless.!
"Jeff Layman" wrote in message
...
On 25/01/20 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.


If it's buried under plants, doesn't it have to be in conduit or trunking
to avoid damage from spades and forks?

Seems to me that "some laid on ground under plants" is a little unclear.
Does it mean only on the surface under the top growth of a plant? Trouble
is, it wouldn't take long to get hidden by fallen leaves and other stuff,
perhaps making it vulnerable to a spade.

--

Jeff




ARW January 25th 20 11:38 AM

Which cable outdoors?
 
On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.



--
Adam

ARW January 25th 20 11:39 AM

Which cable outdoors?
 
On 25/01/2020 10:42, Tricky Dicky wrote:
Depending on the length of cable run it might not be worth using two types, eg the difference in price according to CEF between 3 core 2.5mm2 SWA and the equivalent Tufsheath is 12p per metre if you have to use additional glands then you may not save much plus one less joint box and a potential point of water ingress.


And the time to make the joints.


--
Adam

Tim Lamb[_2_] January 25th 20 01:44 PM

Which cable outdoors?
 
In message , ARW
writes
On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.


He could shove it down a length of galvanised pipe for the ground level
bit. Or is that an offence nowadays?

--
Tim Lamb

ARW January 25th 20 02:47 PM

Which cable outdoors?
 
On 25/01/2020 13:44, Tim Lamb wrote:
In message , ARW
writes
On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some
not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount
jobs. It is not suitable for direct burial in the ground unlike SWA.


He could shove it down a length of galvanised pipe for the ground level
bit. Or is that an offence nowadays?


That would probably be OK.

--
Adam

Rod Speed January 25th 20 04:19 PM

Which cable outdoors?
 
Brian Gaff (Sofa 2) wrote

Well my armoured cable to the shed and when the garage greenouse and shed
were there is still in good nick, but was attached to the fence, most of
it still is. I'd not want to bury any kind of cable under a garden myself.


You don’t have any choice here, its all underground supply now.

The old overhead links were ordinary pvc double insulated for a time but
we soon discovered that the sun and the cold did not make it last very
long. The plastic shroud of the armoured cable seemms to be a completely
different type of plastic that feels a bit like Teflon to the touch, and
has lasted well over 15 years.


My overhead link to power lines down the street have
done fine for 45 years, single insulated twisted cable.


"Jeff Layman" wrote in message
...
On 25/01/20 03:12, ARW wrote:
On 25/01/2020 00:25, wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you need
a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.


If it's buried under plants, doesn't it have to be in conduit or trunking
to avoid damage from spades and forks?

Seems to me that "some laid on ground under plants" is a little unclear.
Does it mean only on the surface under the top growth of a plant? Trouble
is, it wouldn't take long to get hidden by fallen leaves and other stuff,
perhaps making it vulnerable to a spade.

--

Jeff




Peeler[_4_] January 25th 20 06:13 PM

UNBELIEVABLE: It's 03:19 am in Australia and the Senile Ozzietard has been out of Bed and TROLLING for OVER HALF AN HOUR already!!!! LOL
 
On Sun, 26 Jan 2020 03:19:18 +1100, cantankerous trolling geezer Rodent
Speed, the auto-contradicting senile sociopath, blabbered, again:

FLUSH senile troll's troll****

03:19? So, when's bedtime for you this night? Or rather day, you abnormal
sleepless senile pest?

--
Website (from 2007) dedicated to the 85-year-old trolling senile
cretin from Oz:
https://www.pcreview.co.uk/threads/r...d-faq.2973853/

[email protected] January 27th 20 02:30 AM

Which cable outdoors?
 
On 25/01/2020 11:38, ARW wrote:
On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.



Thanks. I hadn't realised it was another name for Hi-Tuff

Adam Funk[_3_] January 27th 20 04:05 PM

Which cable outdoors?
 
On 2020-01-25, ARW wrote:

On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.


The description I found on-line says:

Indoor use where mechanical damages are not to be expected.

Outdoors, Underground, in Brickwork, Concrete with the exception of
cabling in shaken, vibrated or compressed concrete. and in Water.

The UV-resistance allows for outdoor use.

https://www.tlc-direct.co.uk/Main_Index/Cable_Index/NYY/index.html

Doesn't using it where garden tools might hit it count as risk of
mechanical damage? (That's why I used SWA clipped to a garden fence
to my shed.)

ARW January 27th 20 05:18 PM

Which cable outdoors?
 
On 27/01/2020 16:05, Adam Funk wrote:
On 2020-01-25, ARW wrote:

On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.


The description I found on-line says:

Indoor use where mechanical damages are not to be expected.

Outdoors, Underground, in Brickwork, Concrete with the exception of
cabling in shaken, vibrated or compressed concrete. and in Water.

The UV-resistance allows for outdoor use.

https://www.tlc-direct.co.uk/Main_Index/Cable_Index/NYY/index.html

Doesn't using it where garden tools might hit it count as risk of
mechanical damage? (That's why I used SWA clipped to a garden fence
to my shed.)


Strictly speaking SWA should be protected from damage:-)

Assuming you are talking about a plastic strimmer wire then I doubt it
would damage either cable unless it was a sustained and violent attack
of the strimmer. A spade will damage both. I did like Tim Lambs idea of
running the cable through galv conduit. You cannot get a spade through that.

It's down to the installer to decide which they are going to fit. I just
gave an option to SWA.

I probably should have called it Hi-tuff but ISTR the trade name went
out of business.

--
Adam

Adam Funk[_3_] January 28th 20 03:23 PM

Which cable outdoors?
 
On 2020-01-27, ARW wrote:

On 27/01/2020 16:05, Adam Funk wrote:
On 2020-01-25, ARW wrote:

On 25/01/2020 09:37, wrote:
On 25/01/2020 03:12, ARW wrote:
On 25/01/2020 00:25,
wrote:
Which cable types are now required for:

a) nonburied run to shed, some attached to brickwork, some laid on
ground under plants
b) surface clipped run to lighting, some lengths under plants some not.



If there is a risk of damage due to strimmers/ cutters etc then you
need a cable with an outer earth sheath. So that's SWA or SY.

If not then use NYY-J cable.

I hadn't heard of NYY-J until now, why would you use it rather than SWA?


NYY-J used to be sold under the name Hi-Tuff. It's cheaper than SWA,
does not need glanding off and is ideal for outdoor surface mount jobs.
It is not suitable for direct burial in the ground unlike SWA.


The description I found on-line says:

Indoor use where mechanical damages are not to be expected.

Outdoors, Underground, in Brickwork, Concrete with the exception of
cabling in shaken, vibrated or compressed concrete. and in Water.

The UV-resistance allows for outdoor use.

https://www.tlc-direct.co.uk/Main_Index/Cable_Index/NYY/index.html

Doesn't using it where garden tools might hit it count as risk of
mechanical damage? (That's why I used SWA clipped to a garden fence
to my shed.)


Strictly speaking SWA should be protected from damage:-)


Hmm!

Assuming you are talking about a plastic strimmer wire then I doubt it
would damage either cable unless it was a sustained and violent attack
of the strimmer. A spade will damage both. I did like Tim Lambs idea of
running the cable through galv conduit. You cannot get a spade through that.

It's down to the installer to decide which they are going to fit. I just
gave an option to SWA.

I probably should have called it Hi-tuff but ISTR the trade name went
out of business.



All times are GMT +1. The time now is 01:47 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter