UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,688
Default size SWA to garage 30m away

I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,853
Default size SWA to garage 30m away

On 14/02/2019 14:43, sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?


It's a garage.

One day you may want to charge an electric car...

Andy
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default size SWA to garage 30m away

On 14/02/2019 14:43, sm_jamieson wrote:

I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?


So are we assuming the design load is 32A?

Current capacity for either are fine (the current carrying capacity
"clipped direct" for PVC clad [1] SWA would be 38A/49A (4mm^2/6mm^2))

So we can check voltage drop. Since you have lighting, that ought to be
a 3% or 6.9V. At 11mV/A/m 32A load would give ~ 10.5V, so 4mm^2 cable
will not meet the spec.

Going to 6mm^2, that would be 7.3mV/A/m or ~7V

So you could easily argue that 6mm^2 will get you close enough -
especially as it does not sound like the circuit will likely have
anything near that load on it normally. (you could also argue that the
effects of small voltage drops with modern low energy lighting are
overstated anyway).

You have not said what the earthing system is at the head end, but we
can make a crude disconnection time check: If you are using 2 core 6mm^2
SWA, the core resistance will be about 3 mOhms/m, and the armour
7mOhms/m for a total of about 10 mOhms/m round trip. That gives us 0.3
Ohms. If it were a TN-S head end you could add on 0.8 for Ze, so 1.1 Ohm
total. Low enough to meet then 1.37 Ohms min for a B32 MCB [3].

Prospective fault current = 230/1.1 = 253A, enough to be in the magnetic
part of the trip response.

Adiabatic check, sqrt( 253^2 x 0.1 ) / 115 [4] = 0.7mm^2 minimum CSA
wire required. The copper equivalent 7mm^2 of armour being 3mm^2 if we
use the 2.255 conversion factor. So plenty good enough.



[1] Much SWA will be the 90 deg C XLPE style sheathed stuff anyway,
which has higher limits)

[2]
http://wiki.diyfaq.org.uk/index.php/...our_as_a_C PC

[3]
http://wiki.diyfaq.org.uk/index.php/...g_Voltage_Drop

[4] Appropriate k factor for a PVC cable - but low for a XLPE one - see
[1] above.




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default size SWA to garage 30m away

On 14/02/2019 21:39, John Rumm wrote:

Going to 6mm^2, that would be 7.3mV/A/m or ~7V

So you could easily argue that 6mm^2 will get you close enough -
especially as it does not sound like the circuit will likely have
anything near that load on it normally. (you could also argue that the
effects of small voltage drops with modern low energy lighting are
overstated anyway).



This is where the tightening up of lighting circuits to a 3% voltage
drop in the regs may need to change.

The 3% voltage drop for lighting became a reg before the use of LED
lighting became mainstream.

The use of a deviation from the regs is a useful tool. If the OP fits
LED lighting that works from 80 to 250V (most of it does) then you can
ignore the 3% voltage drop and calculate for a 5% drop.

There are other reasons not to design the circuit to the absolute
minimum allowed.

The three most obvious ones are

1. Most of the cost is actually the labour to fit the supply cable. You
only have to do the job once.

2. If running at near max allowed current for long periods you get
wasted power in the cable.


3. Future expansion of the system (if 2 does not apply)

--


Adam
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 148
Default size SWA to garage 30m away

Point 3 is very important for garages used to park daily cars in.

Eventually


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 148
Default size SWA to garage 30m away

Point 3 is important particularly for detached garages used for storing daily use vehicles overnight.

Eventually we will all be driving electric vehicles which will need charging overnight....

I have been informed that my 80a cutout is only sufficient for charging 1 vehicle. If I want to charge two vehicles overnight, I have to have the cutout upgraded to 100a and possibly the service Cable to the cutout.....

So a detached garage having a 3 core 25mm2 SWA cable does not now seem excessive to put in while the trench is still open instead of that 6mm2 or 10mm2 SWA cable.....
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,853
Default size SWA to garage 30m away

On 17/02/2019 14:59, ARW wrote:

As for upgrading your cut out to 100A. If you have to do this then so
would most the people on your street. The infra stucture of the grid
cannot not cope with this.


I have 63A out here (the SWA cable predates the building!) but even if I
wanted I couldn't go all the way to 100A. That's the house main fuse limit.

Andy
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 148
Default size SWA to garage 30m away

Regarding your point about the infrastructure being unable to cope....

I reckon that electric car owners will sign up to economy 7 electric which means their cars will be charged between midnight and seven am where the majority of people will be in bed.

The infrastructure is clearly able to cope with peak load during the morning get up, shower and have beakfast run and again for when people get home, shower cook and watch tav, surf internet and then go to bed.

So instead of two peak time periods every day we could see three peak periods every day.

When you consider all the kettles, electric showers, toasters, electric cookers etc during day time Vs battery Chargers during the night....

Having said that, houses with night storage heating systema may struggle to charge cars without having a 250 amp cutout supply!
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 40,893
Default size SWA to garage 30m away



wrote

Point 3 is important particularly for detached garages used for storing
daily use vehicles overnight.


Eventually we will all be driving electric vehicles which will need
charging overnight....


Dont believe that, particularly with most in here, they'll be dead first.

I have been informed that my 80a cutout is only sufficient for charging
1 vehicle. If I want to charge two vehicles overnight, I have to have the
cutout upgraded to 100a and possibly the service Cable to the cutout.....


So a detached garage having a 3 core 25mm2 SWA cable
does not now seem excessive to put in while the trench is
still open instead of that 6mm2 or 10mm2 SWA cable.....




  #11   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default size SWA to garage 30m away

On 17/02/2019 16:54, Rod Speed wrote:


wrote

Point 3 is important particularly for detached garages used for
storing daily use vehicles overnight.


Eventually we will all be driving electric vehicles which will need
charging overnight....


Dont believe that, particularly with most in here, they'll be dead first.


Care to lead by example and show us how it is done?

--
Adam
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,153
Default Lonely Psychotic Senile Ozzie Troll Alert! LOL

On Mon, 18 Feb 2019 03:54:53 +1100, cantankerous trolling senile geezer Rot
Speed blabbered, again:


Eventually we will all be driving electric vehicles which will need
charging overnight....


Don¢t believe that, particularly with most in here, they'll be dead first.


Not with most, but with you certainly, you 85-year-old senile Ozzie cretin!

--
Sqwertz to Rot Speed:
"This is just a hunch, but I'm betting you're kinda an argumentative
asshole.
MID:
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default size SWA to garage 30m away

On Sunday, 17 February 2019 16:55:02 UTC, Rod Speed wrote:
wrote

Point 3 is important particularly for detached garages used for storing
daily use vehicles overnight.


Eventually we will all be driving electric vehicles which will need
charging overnight....


Dont believe that, particularly with most in here, they'll be dead first.



I have had an electric car for seven years.
The charge leads supplied with electric cars range from 10 to 13 amps.
They go into a domestic socket.
  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,066
Default size SWA to garage 30m away

On Sunday, 17 February 2019 11:44:34 UTC, wrote:
Point 3 is important particularly for detached garages used for storing daily use vehicles overnight.

Eventually we will all be driving electric vehicles which will need charging overnight....

I have been informed that my 80a cutout is only sufficient for charging 1 vehicle. If I want to charge two vehicles overnight, I have to have the cutout upgraded to 100a and possibly the service Cable to the cutout.....

So a detached garage having a 3 core 25mm2 SWA cable does not now seem excessive to put in while the trench is still open instead of that 6mm2 or 10mm2 SWA cable.....


Overnight EV charging is very low current.
My EV charger is only 10 Amps.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default size SWA to garage 30m away

On 07/03/2019 19:04, harry wrote:
On Sunday, 17 February 2019 11:44:34 UTC, wrote:
Point 3 is important particularly for detached garages used for storing daily use vehicles overnight.

Eventually we will all be driving electric vehicles which will need charging overnight....

I have been informed that my 80a cutout is only sufficient for charging 1 vehicle. If I want to charge two vehicles overnight, I have to have the cutout upgraded to 100a and possibly the service Cable to the cutout.....

So a detached garage having a 3 core 25mm2 SWA cable does not now seem excessive to put in while the trench is still open instead of that 6mm2 or 10mm2 SWA cable.....


Overnight EV charging is very low current.
My EV charger is only 10 Amps.


That's because you have car with the battery capacity comparable to a
bulk pack of AAs from Poundland.

Most dedicated chargers (i.e. hard wired rather than plug in) will draw 6kW.

A Tesla with its more practical 130kWh battery would take more than two
and a half full days to charge at the charge rate delivered with your
charger.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/


  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 684
Default size SWA to garage 30m away

sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.


6 or 10 for me
  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,688
Default size SWA to garage 30m away

On Friday, February 15, 2019 at 3:40:34 AM UTC, FMurtz wrote:
sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.


6 or 10 for me


I suspected 4mm would be iffy. Load will be lowish (def. no electric cars !)
Thanks for John's calcs.
I will use 6mm.
Most of my neighbours have a string of 2.5mm nailed to the fence.

Simon.
  #18   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default size SWA to garage 30m away

On 15/02/2019 11:58, sm_jamieson wrote:
On Friday, February 15, 2019 at 3:40:34 AM UTC, FMurtz wrote:
sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.


6 or 10 for me


I suspected 4mm would be iffy. Load will be lowish (def. no electric cars !)
Thanks for John's calcs.
I will use 6mm.
Most of my neighbours have a string of 2.5mm nailed to the fence.


6mm minimum.

No electric cars ATM:-) What would be the extra cost to put 10mm cable in?


--
Adam
  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 148
Default size SWA to garage 30m away

Well last July I bought 20 m of 10mm2 three phase SWA cable for 70 quid from denmans so I would expect 30 m of 10mm2 to be around 105 quid....

My SWA cable is awaiting connection at both ends with suitable coloured sleeving to mark it has single phase, neutral and earth.

one is at the garage end and the other is for the wood shed and greenhouse
  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,564
Default size SWA to garage 30m away

On Friday, 15 February 2019 11:58:13 UTC, sm_jamieson wrote:
Most of my neighbours have a string of 2.5mm nailed to the fence.


That's probably okay in winter.

Owain

  #24   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,688
Default size SWA to garage 30m away

On Thursday, February 14, 2019 at 2:43:17 PM UTC, sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.


OK thanks all.
I've ordered 30m of 10mm 3-core SWA even though its way over for current usage.
If I ever needed to make use of its capacity I'd have to upgrade some internal wiring, but hey ho as they say.
And it will certainly sort out the earthing requirements.

Simon.
  #25   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default size SWA to garage 30m away

On 07/03/2019 14:00, sm_jamieson wrote:
On Thursday, February 14, 2019 at 2:43:17 PM UTC, sm_jamieson wrote:
I am putting in SWA cable to the garage, total length max 30 metres,
load just a few sockets for low powered tools, and lights, connected to 32A RCBO in the house CU. Should I use 4mm or 6mm SWA ?

Cheers,
Simon.


OK thanks all.
I've ordered 30m of 10mm 3-core SWA even though its way over for current usage.
If I ever needed to make use of its capacity I'd have to upgrade some internal wiring, but hey ho as they say.
And it will certainly sort out the earthing requirements.


You will not regret it. Just another small point in oversizing the cable
means a smaller voltage drop and so less losses in the cable. So even a
13A sustained load (future small EV charging point) will make savings
over time.

--
Adam


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Conductor size for earthing SWA shield to TT system? [email protected] UK diy 6 July 4th 18 11:24 PM
SWA calculation size ARWadsworth UK diy 11 March 31st 11 02:14 PM
SWA Size question Toby UK diy 12 May 13th 10 03:05 PM
What size SWA? r.p.mcmurphy UK diy 16 March 21st 05 08:57 PM
How much current safe for 30m extension? Ian Stirling UK diy 80 February 24th 05 06:26 PM


All times are GMT +1. The time now is 02:59 AM.

Powered by vBulletin® Copyright ©2000 - 2025, Jelsoft Enterprises Ltd.
Copyright ©2004-2025 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"