UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Single circuit CU

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB. But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.






[1] It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.

--

Roger Hayter
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Single circuit CU

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.


Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.


Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.

[1] It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.


If the branch was at the CU that would actually be acceptable anyway.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Single circuit CU

John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.


Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.


Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.


It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.



[1] It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.


If the branch was at the CU that would actually be acceptable anyway.


That's because of the limited current demand from one socket outlet? I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.

--

Roger Hayter
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Single circuit CU

On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.


Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.


Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.


It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


ok, in which case all you can do is check the height of the available
single module RCBOs, and if not swap the box.

[1] It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.


If the branch was at the CU that would actually be acceptable anyway.


That's because of the limited current demand from one socket outlet?


Yup - you are in reality just talking about a spur - just one where its
taken from origin. So the MCB will still provide fault protection for
the single 2.5mm^2 T&E, and the limitation of a single socket will
provide the overload protection. (overload protection does not *have* to
be at the origin of the circuit (although often it is)).

I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,213
Default Single circuit CU

On 11/07/2018 12:02, John Rumm wrote:
On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1].
Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.

Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch?Â* Space is not very ample.

Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.


It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


ok, in which case all you can do is check the height of the available
single module RCBOs, and if not swap the box.

[1]Â* It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.

If the branch was at the CU that would actually be acceptable anyway.


That's because of the limited current demand from one socket outlet?


Yup - you are in reality just talking about a spur - just one where its
taken from origin. So the MCB will still provide fault protection for
the single 2.5mm^2 T&E, and the limitation of a single socket will
provide the overload protection. (overload protection does not *have* to
be at the origin of the circuit (although often it is)).

Â*I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


Since most of these off-peak installations had surface mounted
cables anyway, so surely RCD protection is not needed ?.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,554
Default Single circuit CU

On 12/07/2018 14:35, Andrew wrote:
On 11/07/2018 12:02, John Rumm wrote:
On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just
substitute
this for the MCB.

Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch?Â* Space is not very ample.

Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.

It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


ok, in which case all you can do is check the height of the available
single module RCBOs, and if not swap the box.

[1]Â* It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.

If the branch was at the CU that would actually be acceptable anyway.

That's because of the limited current demand from one socket outlet?


Yup - you are in reality just talking about a spur - just one where
its taken from origin. So the MCB will still provide fault protection
for the single 2.5mm^2 T&E, and the limitation of a single socket will
provide the overload protection. (overload protection does not *have*
to be at the origin of the circuit (although often it is)).

Â*I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


Since most of these off-peak installations had surface mounted
cables anyway, so surely RCD protection is not needed ?.


The man wants RCD protection, otherwise he wouldn't be changing it.

A nice shower/shed consumer unit sounds about right if it fits.

  #7   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Single circuit CU

On 12/07/2018 14:35, Andrew wrote:
On 11/07/2018 12:02, John Rumm wrote:
On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just
substitute
this for the MCB.

Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch?Â* Space is not very ample.

Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.

It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


ok, in which case all you can do is check the height of the available
single module RCBOs, and if not swap the box.

[1]Â* It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.

If the branch was at the CU that would actually be acceptable anyway.

That's because of the limited current demand from one socket outlet?


Yup - you are in reality just talking about a spur - just one where
its taken from origin. So the MCB will still provide fault protection
for the single 2.5mm^2 T&E, and the limitation of a single socket will
provide the overload protection. (overload protection does not *have*
to be at the origin of the circuit (although often it is)).

Â*I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


Since most of these off-peak installations had surface mounted
cables anyway, so surely RCD protection is not needed ?.



But socket outlets are now required to have RCD protection even if the
cable is surface mounted. So the OP would have to install RCD sockets.

--
Adam
  #8   Report Post  
Posted to uk.d-i-y
ARW ARW is offline
external usenet poster
 
Posts: 10,161
Default Single circuit CU

On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.


Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.


Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.


It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


A photo of the enclose would be nice. I might know of an RCBO that will
fit after looking.

But your suggestion of a double pole RCBO in an enclosure is fine. If
space is tight you may struggle


--
Adam
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Single circuit CU

On 12/07/2018 14:35, Andrew wrote:
On 11/07/2018 12:02, John Rumm wrote:
On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:



Â*I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


Since most of these off-peak installations had surface mounted
cables anyway, so surely RCD protection is not needed ?.


It sounds as if the circuit is now supplying sockets and not just fixed
heating equipment. So they would require RCD protection anyway.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,237
Default Single circuit CU

John Rumm wrote:

On 11/07/2018 10:23, Roger Hayter wrote:
John Rumm wrote:

On 10/07/2018 22:35, Roger Hayter wrote:

The Economy 7 supply to our house goes through a small box with a
built-in isolating switch and space for a single MCB[1]. Presumably if
I can find a 20A RCBO of the same width and shape I can just substitute
this for the MCB.

Such things exist - however they are taller, so not all CUs will have
space.

But if such a thing does not exist, would it be OK to
use a two pole RCBO mounted alone in a small box with no separate
isolating switch? Space is not very ample.

Yup that would be fine. Just blank the spare way, or leave the MCB in
place and label it as "spare" or similar.


It would have to be a new enclosure as the existing one has an integral,
non-modular switch and only space for one MCB.


ok, in which case all you can do is check the height of the available
single module RCBOs, and if not swap the box.

[1] It is probably a bit dubious now as it serves a single 'radial'
circuit which branches to two sockets (that I have found) and is wired
in 2.5mm^2 cable bundled with other cables and supplied through a 32A
MCB.

If the branch was at the CU that would actually be acceptable anyway.


That's because of the limited current demand from one socket outlet?


Yup - you are in reality just talking about a spur - just one where its
taken from origin. So the MCB will still provide fault protection for
the single 2.5mm^2 T&E, and the limitation of a single socket will
provide the overload protection. (overload protection does not *have* to
be at the origin of the circuit (although often it is)).

I
haven't actually checked where they branch because we only use one
socket anyway and the other one has duct tape to avoid confusion.


In reality, (and depending a bit on the installation method for the
cable) you would be hard pushed to do much damage with just a pair of
sockets even if the branch was elsewhere.


Thanks for the advice. I'll put it at the bottom of my list of jobs
that need doing. I'm only thinking of interfering with it because it is
the only non-RCD protected circuit in the house.


--

Roger Hayter
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wiring a 480V Single Phase Circuit Joshua Home Repair 58 June 8th 20 02:39 PM
Single axis stepper controller w/single programmable relay output? Jon Anderson Metalworking 44 July 23rd 11 06:15 PM
When you are shopping on an online auction or consignment site, usedjeans are often sold in "Lots". Lots are groupings of like items that are soldas a single unit. The advantages of lots are that you get a large selection ina single purchas [email protected] UK diy 0 April 19th 08 11:04 AM
Ring circuit form a single cable? Sparks UK diy 35 March 31st 05 09:18 AM
Powering two cookers off single radial electrical circuit Michael Brewer UK diy 20 January 27th 04 03:33 PM


All times are GMT +1. The time now is 06:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us