CU for HMO
Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this?
NT |
#2
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#4
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#5
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 25/06/18 07:50, Fredxx wrote:
On 25/06/2018 01:08, wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? I thought it was normal to use a 100mA time delay RCD at the 'main' CU? It does mean the wiring to each rented room would need to have mechanical protection or be surface wired, etc. That's for TT earthing. 100mA Type S RCD does *not* provide "personal protection" which is the factor here. |
#6
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 25/06/2018 13:32, Tim Watts wrote:
On 25/06/18 07:50, Fredxx wrote: On 25/06/2018 01:08, wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? I thought it was normal to use a 100mA time delay RCD at the 'main' CU? It does mean the wiring to each rented room would need to have mechanical protection or be surface wired, etc. That's for TT earthing. 100mA Type S RCD does *not* provide "personal protection" which is the factor here. I thought the 100mA was primarily for fire protection rather than just a requirement for TT earthing? In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. |
#7
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 25/06/2018 14:30, Fredxx wrote:
On 25/06/2018 13:32, Tim Watts wrote: On 25/06/18 07:50, Fredxx wrote: On 25/06/2018 01:08, wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? I thought it was normal to use a 100mA time delay RCD at the 'main' CU? It does mean the wiring to each rented room would need to have mechanical protection or be surface wired, etc. That's for TT earthing. 100mA Type S RCD does *not* provide "personal protection" which is the factor here. Not if there are downstream 30mA trip devices... I thought the 100mA was primarily for fire protection rather than just a requirement for TT earthing? Both - either for installation protection, or for circumstances where the earth loop impedance is too high to reliably trip a MCB under fault conditions. In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. If they are independent, (e.g. RCBOs) then you can skip the lighting unless you are doing something particularly risky in there... Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#8
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 25/06/2018 12:22, John Rumm wrote:
On 25/06/2018 01:08, wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. So not an acceptable solution... If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. If its clipped to the surface, then it does not require RCD protection. (assuming the earthing system is not TT) Neither of those options strike me as fully satisfactory. How's good to do this? If you need RCD protection for the submain, then use a type S device at the main CU. Just to add to that last bit. It depends on why you need the RCD protection. If you need RCD protection other than for a TT supply (ignoring stables etc) because the regs demand it due eg buried T&E then it must be 30mA non time delayed. -- Adam |
#9
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#10
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 25/06/2018 14:30, Fredxx wrote:
On 25/06/2018 13:32, Tim Watts wrote: On 25/06/18 07:50, Fredxx wrote: On 25/06/2018 01:08, wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? I thought it was normal to use a 100mA time delay RCD at the 'main' CU? It does mean the wiring to each rented room would need to have mechanical protection or be surface wired, etc. That's for TT earthing. 100mA Type S RCD does *not* provide "personal protection" which is the factor here. I thought the 100mA was primarily for fire protection rather than just a requirement for TT earthing? That would be 300mA RCD eg stables In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. That would be nice, but of no use if there is a 30mA RCD in series with it. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. Yes, if done properly. Certainly for the communal areas. I am not sure what the regs are for em lighting inside a HMO room. It certainly had non on the last one I worked in. -- Adam |
#11
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Monday, 25 June 2018 12:22:33 UTC+1, John Rumm wrote:
On 25/06/2018 01:08, tabbypurr wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. So not an acceptable solution... If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. If its clipped to the surface, then it does not require RCD protection. (assuming the earthing system is not TT) Neither of those options strike me as fully satisfactory. How's good to do this? If you need RCD protection for the submain, then use a type S device at the main CU. I didn't think to mention the earthing: it's TT. So everything must be RCDed. Leaving the lights out of the metering would make life a lot easier, presumably the secondary CUs could be dispensed with entirely. But it does create some problems down the line, so I'm not sure that'll be chosen. NT |
#12
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Monday, 25 June 2018 16:53:35 UTC+1, ARW wrote:
On 25/06/2018 14:30, Fredxx wrote: On 25/06/2018 13:32, Tim Watts wrote: On 25/06/18 07:50, Fredxx wrote: On 25/06/2018 01:08, tabbypurr wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? I thought it was normal to use a 100mA time delay RCD at the 'main' CU? It does mean the wiring to each rented room would need to have mechanical protection or be surface wired, etc. That's for TT earthing. 100mA Type S RCD does *not* provide "personal protection" which is the factor here. I thought the 100mA was primarily for fire protection rather than just a requirement for TT earthing? That would be 300mA RCD eg stables In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. That would be nice, but of no use if there is a 30mA RCD in series with it. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. Yes, if done properly. Certainly for the communal areas. I am not sure what the regs are for em lighting inside a HMO room. It certainly had non on the last one I worked in. The communal areas are unmetered. Is it acceptable to use just one CU, like so: Shared 300mA RCD feeds an MCB for each room. Each MCB output goes to a meter and back into the main CU, where it feeds 2x RCBOs for lighting & sockets. There are then no secondary CUs. NT |
#13
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 26/06/2018 10:47, wrote:
On Monday, 25 June 2018 16:53:35 UTC+1, ARW wrote: In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. That would be nice, but of no use if there is a 30mA RCD in series with it. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. Yes, if done properly. Certainly for the communal areas. I am not sure what the regs are for em lighting inside a HMO room. It certainly had non on the last one I worked in. The communal areas are unmetered. Is it acceptable to use just one CU, like so: Shared 300mA RCD feeds an MCB for each room. How many rooms? Each MCB output goes to a meter and back into the main CU, where it feeds 2x RCBOs for lighting & sockets. There are then no secondary CUs. You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. You may find some CUs designed for a 4 way split, Adam will probably be better able to advise. Since its TT and you need all circuits RCD protected, you will have to ensure any submains are routed in such a way that you don't trigger the requirement that they be protected by a 30mA RCD, else you lose discrimination. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#14
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#16
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#17
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Tuesday, 26 June 2018 11:42:01 UTC+1, John Rumm wrote:
On 26/06/2018 10:47, tabbypurr wrote: On Monday, 25 June 2018 16:53:35 UTC+1, ARW wrote: In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. That would be nice, but of no use if there is a 30mA RCD in series with it. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. Yes, if done properly. Certainly for the communal areas. I am not sure what the regs are for em lighting inside a HMO room. It certainly had non on the last one I worked in. The communal areas are unmetered. Is it acceptable to use just one CU, like so: Shared 300mA RCD feeds an MCB for each room. How many rooms? 4 Each MCB output goes to a meter and back into the main CU, where it feeds 2x RCBOs for lighting & sockets. There are then no secondary CUs. You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. why a main switch for each room? So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. RCBOs means each circuit neutral fed from its own RCBO You may find some CUs designed for a 4 way split, Adam will probably be better able to advise. Since its TT and you need all circuits RCD protected, you will have to ensure any submains are routed in such a way that you don't trigger the requirement that they be protected by a 30mA RCD, else you lose discrimination. they're surface wired, clipped direct NT |
#18
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 26/06/2018 22:19, ARW wrote:
On 26/06/2018 11:42, John Rumm wrote: You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. The 30mA RCBOs need to be DP switched. You need DP isolation for TT, but the switch at the head of each sub section would achieve that would it not? Or am I missing something? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#19
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 00:55, wrote:
On Tuesday, 26 June 2018 11:42:01 UTC+1, John Rumm wrote: On 26/06/2018 10:47, tabbypurr wrote: On Monday, 25 June 2018 16:53:35 UTC+1, ARW wrote: In this instance I had also assumed that each room would have its own CU with two RCDs or perhaps one with some form of emergency lighting. That would be nice, but of no use if there is a 30mA RCD in series with it. Its also not unknown for lighting to be on a permanent, separate circuit, such it is not powered through a coin slot meter. Yes, if done properly. Certainly for the communal areas. I am not sure what the regs are for em lighting inside a HMO room. It certainly had non on the last one I worked in. The communal areas are unmetered. Is it acceptable to use just one CU, like so: Shared 300mA RCD feeds an MCB for each room. How many rooms? 4 That's going to be pushing it a bit for one CU... Each MCB output goes to a meter and back into the main CU, where it feeds 2x RCBOs for lighting & sockets. There are then no secondary CUs. You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. why a main switch for each room? Its one way of getting round the limitations on the number of available neutral bus bars - you could return the circuit neutrals to the neutral pole of the switch (since there will only be two circuit). It also gives you a convenient method of isolation for the room. So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. RCBOs means each circuit neutral fed from its own RCBO and in turn those need to be fed from somewhere... [1] Adam makes a good point that I did overlook though. Using single pole RCBOs like this potentially causes a loss of discrimination if you were to ever get a neutral to earth short. It would trip the local RCBO, but that would not clear the actual fault which would still be visible to the head end RCD. Hence it would trip the whole installation. The only way round that would be using double pole RCBOs, or using another type S RCD in the place of each of the main switches. You may find some CUs designed for a 4 way split, Adam will probably be better able to advise. Since its TT and you need all circuits RCD protected, you will have to ensure any submains are routed in such a way that you don't trigger the requirement that they be protected by a 30mA RCD, else you lose discrimination. they're surface wired, clipped direct So at the moment, no need for a 30mA RCD on the submains. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/18 13:58, John Rumm wrote:
[1] Adam makes a good point that I did overlook though. Using single pole RCBOs like this potentially causes a loss of discrimination if you were to ever get a neutral to earth short. It would trip the local RCBO, but that would not clear the actual fault which would still be visible to the head end RCD. Hence it would trip the whole installation. The only way round that would be using double pole RCBOs, or using another type S RCD in the place of each of the main switches. And as a side note, Hager sell DP RCBOs (industrial range) but they are compatible with their consumer boards. |
#21
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 13:58, John Rumm wrote:
On 27/06/2018 00:55, wrote: On Tuesday, 26 June 2018 11:42:01 UTC+1, John RummÂ* wrote: On 26/06/2018 10:47, tabbypurr wrote: You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. why a main switch for each room? Its one way of getting round the limitations on the number of available neutral bus bars - you could return the circuit neutrals to the neutral pole of the switch (since there will only be two circuit). It also gives you a convenient method of isolation for the room. So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. RCBOs means each circuit neutral fed from its own RCBO and in turn those need to be fed from somewhere... [1] Adam makes a good point that I did overlook though. Using single pole RCBOs like this potentially causes a loss of discrimination if you were to ever get a neutral to earth short. It would trip the local RCBO, but that would not clear the actual fault which would still be visible to the head end RCD. Hence it would trip the whole installation. The only way round that would be using double pole RCBOs, or using another type S RCD in the place of each of the main switches. So if the main switch for each room is done away with because we are using DP 30mA RCBOs then that is 2 ways for the main 100mA switch and assuming that the DP RCBOs are double width then a 21 way module CU will work. Schneider do single module DP RCBOs if you want a smaller CU but only on a C curve. There is now need for extra bus bars as the RCBOs neutrals would be directly fed from the neutral bus bar on the outgoing side of the main switch. -- Adam |
#22
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 18:39, ARW wrote:
On 27/06/2018 13:58, John Rumm wrote: On 27/06/2018 00:55, wrote: On Tuesday, 26 June 2018 11:42:01 UTC+1, John RummÂ* wrote: On 26/06/2018 10:47, tabbypurr wrote: You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. why a main switch for each room? Its one way of getting round the limitations on the number of available neutral bus bars - you could return the circuit neutrals to the neutral pole of the switch (since there will only be two circuit). It also gives you a convenient method of isolation for the room. So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. RCBOs means each circuit neutral fed from its own RCBO and in turn those need to be fed from somewhere... [1] Adam makes a good point that I did overlook though. Using single pole RCBOs like this potentially causes a loss of discrimination if you were to ever get a neutral to earth short. It would trip the local RCBO, but that would not clear the actual fault which would still be visible to the head end RCD. Hence it would trip the whole installation. The only way round that would be using double pole RCBOs, or using another type S RCD in the place of each of the main switches. So if the main switch for each room is done away with because we are using DP 30mA RCBOs then that is 2 ways for the main 100mA switch and assuming that the DP RCBOs are double width then a 21 way module CU will work. Schneider do single module DP RCBOs if you want a smaller CU but only on a C curve. There is now need for extra bus bars as the RCBOs neutrals would be Sorry - NO need for extra bus bars -- Adam |
#23
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
Tim Watts wrote:
as a side note, Hager sell DP RCBOs List price is north of £135+VAT though ... |
#24
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 19:21, Andy Burns wrote:
Tim Watts wrote: as a side note, Hager sell DP RCBOs List price is north of £135+VAT though ... Cheap then? https://uk.rs-online.com/web/p/products/7909443 -- Adam |
#25
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 19:54, ARW wrote:
On 27/06/2018 19:21, Andy Burns wrote: Tim Watts wrote: as a side note, Hager sell DP RCBOs List price is north of £135+VAT though ... Cheap then? https://uk.rs-online.com/web/p/products/7909443 Just spotted these. https://www.tlc-direct.co.uk/Products/WYNHXS1B06.html https://www.electrium.co.uk/media/20...%20(We b).pdf Not sure if the second link will work. So Wylex are finally back in the game. -- Adam |
#26
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Wednesday, 27 June 2018 18:39:08 UTC+1, ARW wrote:
On 27/06/2018 13:58, John Rumm wrote: On 27/06/2018 00:55, tabbypurr wrote: On Tuesday, 26 June 2018 11:42:01 UTC+1, John RummÂ* wrote: On 26/06/2018 10:47, tabbypurr wrote: You would need a separate set of busbars for each room then, in addition to a set for the main feeds to the meters. That may prove tricky depending on how many rooms there are. So you would need a main switch position with your type S RCD, plus a MCB for each room's meter feed. You then need a main switch for each room plus 2 x RCBOs. why a main switch for each room? Its one way of getting round the limitations on the number of available neutral bus bars - you could return the circuit neutrals to the neutral pole of the switch (since there will only be two circuit). It also gives you a convenient method of isolation for the room. So if it were say three rooms, that would be 5 ways on the supply side, plus 3 x 4 ways on the secondary side. 17 ways in total and 4 discrete sets of neutral bars. RCBOs means each circuit neutral fed from its own RCBO and in turn those need to be fed from somewhere... [1] Adam makes a good point that I did overlook though. Using single pole RCBOs like this potentially causes a loss of discrimination if you were to ever get a neutral to earth short. It would trip the local RCBO, but that would not clear the actual fault which would still be visible to the head end RCD. Hence it would trip the whole installation. The only way round that would be using double pole RCBOs, or using another type S RCD in the place of each of the main switches. So if the main switch for each room is done away with because we are using DP 30mA RCBOs then that is 2 ways for the main 100mA switch and assuming that the DP RCBOs are double width then a 21 way module CU will work. each room would need 4 ways for itself, so the rooms alone would take up 16 ways, then there's the rest of the circuits. It would take more than a 21 way. Schneider do single module DP RCBOs if you want a smaller CU but only on a C curve. There is now need for extra bus bars as the RCBOs neutrals would be directly fed from the neutral bus bar on the outgoing side of the main switch. A bunch of Wylex RCBOs are available to use, the cost of all new DP RCBOs is not going down well. There are some things I'm not seeing here. Why would socket & lighting need separate RCD action when the norm is to fit a split CU where lots of circuits all share each RCD? NT |
#27
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/18 19:21, Andy Burns wrote:
Tim Watts wrote: as a side note, Hager sell DP RCBOs List price is north of £135+VAT though ... I have one and they're nothing like that in reality... |
#28
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 27/06/2018 18:39, ARW wrote:
There is now need for extra bus bars as the RCBOs neutrals would be directly fed from the neutral bus bar on the outgoing side of the main switch. That would mean that you are taking your live feed to the RCBO from the return submain from the external meter, and the neutral feed from the origin of the supply submain to the meter. Probably not a problem electrically (the neutral connections on the meter are likely just looped through anyway), but not quite as elegant as using the neutral return from the meter. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#29
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 28/06/2018 11:07, John Rumm wrote:
On 27/06/2018 18:39, ARW wrote: There is now need for extra bus bars as the RCBOs neutrals would be directly fed from the neutral bus bar on the outgoing side of the main switch. That would mean that you are taking your live feed to the RCBO from the return submain from the external meter, and the neutral feed from the origin of the supply submain to the meter. Probably not a problem electrically (the neutral connections on the meter are likely just looped through anyway), but not quite as elegant as using the neutral return from the meter. The neutral is only there to allow the meter to measure the live current. A meter will work without a neutral return. Safest way to bypass a meter? - remove the neutral. -- Adam |
#30
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 28/06/2018 19:02, ARW wrote:
On 28/06/2018 11:07, John Rumm wrote: On 27/06/2018 18:39, ARW wrote: There is now need for extra bus bars as the RCBOs neutrals would be directly fed from the neutral bus bar on the outgoing side of the main switch. That would mean that you are taking your live feed to the RCBO from the return submain from the external meter, and the neutral feed from the origin of the supply submain to the meter. Probably not a problem electrically (the neutral connections on the meter are likely just looped through anyway), but not quite as elegant as using the neutral return from the meter. The neutral is only there to allow the meter to measure the live current. Indeed, I realise it will work ok, it was more a case of my being wary of doing something unexpected for a future maintainer. A meter will work without a neutral return. Safest way to bypass a meter? - remove the neutral. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#31
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Monday, 25 June 2018 01:08:08 UTC+1, tabby wrote:
Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? I take it there's no regulatory problem with using one secondary CU for 4 circuits rather than 4 separate CUs. Thanks everyone, getting close to plan 2 I think. NT |
#32
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
|
#33
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 29/06/2018 00:19, wrote:
On Monday, 25 June 2018 01:08:08 UTC+1, tabby wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. The submain feeds then return to a *pair* of basic 17th edition bundle deal style CUs (i.e. split load type with two normal RCDs and a selection of MCBs). Feed two rooms from each of the secondary CUs. You will probably get a good enough selection of MCBs with the CUs to meet your needs. I take it there's no regulatory problem with using one secondary CU for 4 circuits rather than 4 separate CUs. That bit is ok. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#34
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Friday, 29 June 2018 18:32:50 UTC+1, ARW wrote:
On 29/06/2018 00:19, tabbypurr wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabby wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? They must be 30mA RCD. If the cables feeding the meters require 30mA RCDs I'm seeing a problem with that. Either a) there is no RCD further downline, and any current imabalnce causes both sockets & lights to go out in a room, or b) there is another RCD, but no discrimination, so luck of the draw which trips & still often both circuits go off on a leakage fault. I take it there's no regulatory problem with using one secondary CU for 4 circuits rather than 4 separate CUs. Thanks everyone, getting close to plan 2 I think. No problem other than inconvenience with a fault. The 4 feeds would be electrically unconnected to each other, wouldn't make any difference to fault behaviour. So the secondary CU would have 4 inputs, 1 from each landlord's meter, not the usual 1. You did make it sound like each meter was just supplying one room with just a light and socket circuit. So what are the 4 circuits? that's right, one return from the meter for each room. Each of which then feeds socket & light circuits. NT |
#35
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Friday, 29 June 2018 21:51:21 UTC+1, John Rumm wrote:
On 29/06/2018 00:19, tabbypurr wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabby wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes the question is really whether it's required or not. Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. I don't think I follow. The whole point of time delayed RCDs is to achieve discrimination. But if the 30mA RCDs are SP, of course there would be no discrimination on a N-E fault. I gather that's not permissible. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). those options look excessively expensive The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. we can put those in the main CU The submain feeds then return to a *pair* of basic 17th edition bundle deal style CUs (i.e. split load type with two normal RCDs and a selection of MCBs). Feed two rooms from each of the secondary CUs. You will probably get a good enough selection of MCBs with the CUs to meet your needs. IIUC you mean separate the 2 halves of the split CU so each RCD supplies one room. That brings me back to the question of whether lighting/socket discrimination within each room is a requirement. Life is easier if it isn't. I take it there's no regulatory problem with using one secondary CU for 4 circuits rather than 4 separate CUs. That bit is ok. thanks everyone, busy making progress on other work atm. NT |
#36
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 29/06/2018 21:51, John Rumm wrote:
On 29/06/2018 00:19, wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabbyÂ* wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. It would probably be a a lot cheaper and easier to use a hi integrity dual split load CU with a 100mA main switch, 4 MCBs for the rooms fed from the mains switch and to use the 30mA RCD supplies for the communal areas and just fit a 2 way garage CU in each room. -- Adam |
#37
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On Saturday, 30 June 2018 08:15:22 UTC+1, ARW wrote:
On 29/06/2018 21:51, John Rumm wrote: On 29/06/2018 00:19, tabbypurr wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabbyÂ* wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. It would probably be a a lot cheaper and easier to use a hi integrity dual split load CU with a 100mA main switch, 4 MCBs for the rooms fed from the mains switch and to use the 30mA RCD supplies for the communal areas and just fit a 2 way garage CU in each room. Unless I'm mistaken the surface wiring to & from the meters must be DP RCDed on this TT system, either at 30mA or 100mA time delayed. I think it would be ok to feed all 4 meters from the same RCD. I take it discrimination between lights & sockets in each room is not required, meaning both can run off the same RCD. That certainly simplifies things, as you say a garage CU would do the job. I was looking at a single larger secondary CU with SP RCBOs because that would be cheaper & neater, but if SP RCBOs are no good then so be it. If discrimination against N-E faults is required, why are single pole RCBOs sold? There's something I'm not clear on yet here. I've also been reading about the 18th edition, such as it is so far. Fixing of cables in escape routes has come up. I presume the usual plastic cable clips will no longer be permissible, are we going to go back to metal buckle clips? Is their lack of insulation ok today? NT |
#38
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 30/06/2018 08:15, ARW wrote:
On 29/06/2018 21:51, John Rumm wrote: On 29/06/2018 00:19, wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabbyÂ* wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. It would probably be a a lot cheaper and easier to use a hi integrity dual split load CU with a 100mA main switch, 4 MCBs for the rooms fed from the mains switch and to use the 30mA RCD supplies for the communal areas and just fit a 2 way garage CU in each room. Won't that mean the feeds to each room will not be 30mA RCD protected and will need to be surfaced wired, or in SWA. Do you need the lighting in a HMO room to be on a separate RCD to mains outlets, or is the light in the landing on a different RCD circuit sufficient? |
#39
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 30/06/2018 01:47, wrote:
On Friday, 29 June 2018 18:32:50 UTC+1, ARW wrote: On 29/06/2018 00:19, tabbypurr wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabby wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? They must be 30mA RCD. If the cables feeding the meters require 30mA RCDs I'm seeing a problem with that. Either A 30mA trip RCD (i.e. shock protection) would only be required for the feeds to and from the meters if the cables are both hidden, and do not had sufficient protection (either mechanically or by virtue of burial depth). If they are surface wired, then you can do without 30mA protection. They will need infrastructure / fire protection since its a TT install - but that can be via a type S RCD -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#40
Posted to uk.d-i-y
|
|||
|
|||
CU for HMO
On 30/06/2018 11:42, wrote:
On Saturday, 30 June 2018 08:15:22 UTC+1, ARW wrote: On 29/06/2018 21:51, John Rumm wrote: On 29/06/2018 00:19, tabbypurr wrote: On Monday, 25 June 2018 01:08:08 UTC+1, tabbyÂ* wrote: Current fusebox has several fuseways each feeding a meter then a 2 way fusebox which powers each rented room. Plan is a new CU & new secondary 2 way CUs, the meters will be retained. The question is how may RCD protection be implemented. If done in the main CU with an RCBO, a trip results in a room losing all power including lighting. If done in the secondary small CU, the cable from main CU to meter to secondary would not be RCD protected. This wiring is surface clipped direct. Neither of those options strike me as fully satisfactory. How's good to do this? NT OK, some questions. Does there need to be separate rcd protection for lights & sockets so lighting isn't lost when sockets trip? Ideally, yes Since SP RCBOs don't disconnect N-E faults, I presume the whole install still requires 2x DP RCDs. Can these be 300mA time delayed or must they be 30mA? If there are additional downstream 30mA trip devices, then they can in theory be 100mA type S devices. However you won't then be able to achieve discrimination with the RCD protecting the submain feeds to the meters. So you are no nearer a workable solution. So that leaves you needing either 2 DP RCBOs per room, or two conventional 30mA RCDs and two MCBs (likely 6 ways in total per room). The cheapest option may be a small CU for the head end - Type S RCD on its incomer, then 4 x regular MCBs for your submain feeds. It would probably be a a lot cheaper and easier to use a hi integrity dual split load CU with a 100mA main switch, 4 MCBs for the rooms fed from the mains switch and to use the 30mA RCD supplies for the communal areas and just fit a 2 way garage CU in each room. Unless I'm mistaken the surface wiring to & from the meters must be DP RCDed on this TT system, either at 30mA or 100mA time delayed. Yup, if you look carefully at what Adam wrote "100mA" main switch rather than the more common "100A" main switch, I think he was implying that the main switch would be a 100mA trip type S device. I think it would be ok to feed all 4 meters from the same RCD. I would be happy with that since the chances of a fault on the submains is likely to be rare enough for it to be an acceptable risk / inconvenience. I take it discrimination between lights & sockets in each room is not required, meaning both can run off the same RCD. That certainly simplifies things, as you say a garage CU would do the job. I was looking at a single larger secondary CU with SP RCBOs because that would be cheaper & neater, but if SP RCBOs are no good then so be it. This is one of the cases where the designer will need to make a judgement call based on the circumstances. No discrimination between circuits in the room is less than the perfect ideal, but may be acceptable since the risks are low - i.e. no stairs, no rotating machinery etc, and its only one room etc. A similar situation will exist with a 17th edition style split load unit - one RCD trip will affect several circuits (although you normally arrange them such that the power circuit would not cause a trip on the same lighting circuit that serves the power circuit) You could also mitigate with a £15 non maintained emergency light in the room if you wanted. If discrimination against N-E faults is required, why are single pole RCBOs sold? There's something I'm not clear on yet here. For TN-C-S installs there is unlikely to be any significant voltage difference between N & E at the origin of the installation (since they are joined there). So once the loads are disconnected there is unlikely to be any significant current flow in the CPC. What there is, will be conducted by the suppliers PEN conductor which is designed to be a current carrying conductor in normal operation (i.e. it is a "live" wire) With TT, the neutral at the point of supply could be at a different potential to that of the local earth spike. So a persistent N E fault could drive significant current through the local earth spike (which in turn could cause heating, loss of moisture and rising external earth impedance). So on balance a SP RCBO will still result in a significant reduction in serious injury risk for most installations - its just not as suitable for TT installs (although I would highlight that I have a 16th edition style TT system here, with 100mA trip type S incomer, and then a DP 30mA normal RCD for power circuits. I also have a SP RCBO on my kitchen circuit (since that was nuisance tripping the 30mA RCD). I decided it was preferable to accept that a N&E fault on that one circuit could result in tripping the incomer RCD as well, and be rid of the nuisance trip issue that was there before). (I do have several non maintained emergency lights as well though) I've also been reading about the 18th edition, such as it is so far. Fixing of cables in escape routes has come up. I presume the usual plastic cable clips will no longer be permissible, are we going to go back to metal buckle clips? Is their lack of insulation ok today? Yup this is a significant (and long overdue) change especially for commercial / office installs. (The main issue being that in many office / commercial fires things like suspended ceilings would be covered is a mass of wiring. The moment the flimsy ali frames fail in the heat, this is dropped onto the people below - typically fire fighters - where it will snag on their breathing apparatus and risks trapping them). For the commercial installs, better use of cable trays, metal trunking etc will solve most of the problems. For smaller installs and domestic situations, I would expect there will emerge a new range of non combustible cable restraint systems. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |