Home |
Search |
Today's Posts |
![]() |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
|
#1
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
Take a 3 phase incoming supply to a main distribution DB with a C100A
rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
ARW Wrote in message:
Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) -- Jim K ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
Jim K wrote:
ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) Purely from domestic experience I reckon one or both B20 MCBs while the 13A fuses are in a brief molten/vaporised state. But also no expert. It may be possible to calculate whether the C63A should trip before the others have time to open. -- Roger Hayter |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 20:19, Jim K wrote:
ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) I did not know the answer to this one myself until someone actually tried it:-) And the answer is "that every fuse and MCB tripped/blew including the C100A main switch". Only the main incoming fuses did not blow and I have no idea what rating they are and I have no way of finding out even if I wanted to as someone has installed a steel pillar in front of the incomer. -- Adam |
#5
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
ARW wrote:
On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) I did not know the answer to this one myself until someone actually tried it:-) And the answer is "that every fuse and MCB tripped/blew including the C100A main switch". Only the main incoming fuses did not blow and I have no idea what rating they are and I have no way of finding out even if I wanted to as someone has installed a steel pillar in front of the incomer. Is that unsurprising? There may be a fault current high enough for the breakers to be disengaged before the springs have time to accelerate the contacts apart? -- Roger Hayter |
#6
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 06/03/2018 20:49, Roger Hayter wrote:
ARW wrote: On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) I did not know the answer to this one myself until someone actually tried it:-) And the answer is "that every fuse and MCB tripped/blew including the C100A main switch". Only the main incoming fuses did not blow and I have no idea what rating they are and I have no way of finding out even if I wanted to as someone has installed a steel pillar in front of the incomer. Is that unsurprising? There may be a fault current high enough for the breakers to be disengaged before the springs have time to accelerate the contacts apart? I would not have expected the C100A main switch to have blown due to the resistance of the 2.5. -- Adam |
#7
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
ARW wrote:
On 06/03/2018 20:49, Roger Hayter wrote: ARW wrote: On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) I did not know the answer to this one myself until someone actually tried it:-) And the answer is "that every fuse and MCB tripped/blew including the C100A main switch". Only the main incoming fuses did not blow and I have no idea what rating they are and I have no way of finding out even if I wanted to as someone has installed a steel pillar in front of the incomer. Is that unsurprising? There may be a fault current high enough for the breakers to be disengaged before the springs have time to accelerate the contacts apart? I would not have expected the C100A main switch to have blown due to the resistance of the 2.5. Quick back of envelope (but calculator aided) calculation gives total resistance between phases 540mOhm, current 740A, divided by 63 equals 11.8 so it is within spec for the C63 to trip as fast as it likes (no min time). So even if it's surprising it is within specs. BICBW -- Roger Hayter |
#8
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 06/03/2018 19:22, ARW wrote:
On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) I did not know the answer to this one myself until someone actually tried it:-) And the answer is "that every fuse and MCB tripped/blew including the C100A main switch". Only the main incoming fuses did not blow and I have no idea what rating they are and I have no way of finding out even if I wanted to as someone has installed a steel pillar in front of the incomer. My experience of a complete failure of discrimination was when a total idiot closed the three phase breaker to a test stand without checking with anyone or warning anyone. It was supplying a 3ph, 11kV, 2.5MW motor .... which had shorting bars connected across the phases. The local breaker shot straight back out, as did the one in the distribution room, plus the electricity company's breaker in their panels in the same room and the one in the substation supplying the factory, and the one supplying that and presumably even the one supplying that, as not only the factory and offices, but the whole of Wythenshawe was off for more than three hours! SteveW |
#9
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 20:19, Jim K wrote:
ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) And my second question is how many laptops fried? -- Adam |
#10
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Wed, 07 Mar 2018 18:11:36 +0000, ARW wrote:
On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) And my second question is how many laptops fried? None of them. However, I think you were really wondering how many plugged in laptop charging bricks (connected or not to their respective laptops) got fried, in which case, pretty well all of them. -- Johnny B Good |
#11
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 07/03/2018 19:14, Johnny B Good wrote:
On Wed, 07 Mar 2018 18:11:36 +0000, ARW wrote: On 05/03/2018 20:19, Jim K wrote: ARW Wrote in message: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam The 20A MCB? (uneducated in electricals) And my second question is how many laptops fried? None of them. However, I think you were really wondering how many plugged in laptop charging bricks (connected or not to their respective laptops) got fried, in which case, pretty well all of them. Actually my suggestion was that it was the chargers. But where there's blame there is a claim and this lot are making the most of it (but they do not know what actually happened). I am glad it was not my cock-up (and I have made plenty). -- Adam |
#12
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Monday, 5 March 2018 20:13:32 UTC, ARW wrote:
You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Join what to what? Phase to phase? I'll guess the 3PH MCB as it has overcurrent on two phases. Owain |
#13
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 20:13, ARW wrote:
Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. What was the PSSC at the supply end? (although I am guessing since you asked the question probably the 63A 3ph MCB ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#14
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 21:23, John Rumm wrote:
On 05/03/2018 20:13, ARW wrote: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. What was the PSSC at the supply end? Greater than 12KA according to my test meter. The same as my house supply! (although I am guessing since you asked the question probably the 63A 3ph MCB ;-) Not saying ATM :-) -- Adam |
#15
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 20:13, ARW wrote:
Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. The apprentice who joined them? -- Robin reply-to address is (intended to be) valid |
#16
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 05/03/2018 21:42, Robin wrote:
On 05/03/2018 20:13, ARW wrote: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. The apprentice who joined them? Only if he is connected to the company fuses. |
#17
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Monday, 5 March 2018 20:13:32 UTC, ARW wrote:
Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam What you are talking about is called "discrimination". Google electrical discrimination Eg https://news.voltilink.co.uk/article...discrimination A whole sub-subject of electrical distribution |
#18
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 06/03/2018 08:28, harry wrote:
On Monday, 5 March 2018 20:13:32 UTC, ARW wrote: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam What you are talking about is called "discrimination". That would be a woosh then from harry ;-) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#19
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 06/03/2018 16:52, John Rumm wrote:
On 06/03/2018 08:28, harry wrote: On Monday, 5 March 2018 20:13:32 UTC, ARWÂ* wrote: Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam What you are talking about is called "discrimination". That would be a woosh then from harry ;-) Probably got his phases mixed up:-) -- Adam |
#20
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
You trying to blow yourself up or what?
Brian -- ----- - This newsgroup posting comes to you directly from... The Sofa of Brian Gaff... Blind user, so no pictures please! "ARW" wrote in message ... Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam |
#21
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Monday, March 5, 2018 at 8:13:32 PM UTC, ARW wrote:
Take a 3 phase incoming supply to a main distribution DB with a C100A rated main switch. This DB has a C63A 3PH MCB to power DB1 that is about 15m away with some 16mm SWA. You then use different phases with B20 MCBs at DB1, feed them through 13A SFCUs with 2.5mmT&E and join them at the load side of the SFCUs about 30m away with some more 2.5mm T&E. Then you turn on the 20A MCBs? So which goes first? One of the 13A BS1362 fuses, both of the 13A BS1362 fuses, a B20A MCB etc............? Educated guesses welcome. -- Adam Whichever will be the biggest pain in the arse when it blows/trips. Philip |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
Conundrum.... which opens first, a 13A plug fuse or a 32A MCB duringa L-N short circuit? | UK diy | |||
Unexplained MCB trips on outbuilding feed | UK diy | |||
Unexplained MCB trips on outbuilding feed | UK diy | |||
Storage heater sometimes trips MCB - what to do? | UK diy | |||
MCB trips | UK diy |