I have a 2-wire overhead sub-main to a large shed 40-45m away. The house
earthing is TN-C-S (with an earth rod, ref other append) and the shed
earth comes from a local earth rod; there's an RCD in the shed CU. I
plan to replace the overhead feed with 3 core SWA in the ground (0.5m
deep, with warning tape above it at 0.3m deep), terminating the SWA
internally in IP65 adaptable boxes at each end and running the final
couple of metres in T&E.

The feed will come from a non-RCD protected MCB in the house CU. From
the TLC cable size calculator it seems that buried 2.5 SWA is OK up to
about 3.6kW for non-lighting circuits (about 2.2kW for lighting
circuits). I plan to either feed the SWA from a 16A MCB in the house and
to use a 10A MCB in the shed or or to use a 16A type C MCB in the house
and a 16A type B MCB at the shed. Any comments?

I believe the correct earthing in this situation is to export the house
earth down the SWA (hence 3-core, the armour will only be earthed at the
house end) and to remove the shed earth rod. Once again, have I missed
anything?
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical question: cable size and earthing for outbuilding

On 30/09/2017 11:36, wrote:

I have a 2-wire overhead sub-main to a large shed 40-45m away. The house
earthing is TN-C-S (with an earth rod, ref other append) and the shed
earth comes from a local earth rod; there's an RCD in the shed CU. I
plan to replace the overhead feed with 3 core SWA in the ground (0.5m
deep, with warning tape above it at 0.3m deep), terminating the SWA
internally in IP65 adaptable boxes at each end and running the final
couple of metres in T&E.


ok. Although in reality with the current configuration, two core SWA
would be adequate in the circumstance.

The feed will come from a non-RCD protected MCB in the house CU. From
the TLC cable size calculator it seems that buried 2.5 SWA is OK up to
about 3.6kW for non-lighting circuits (about 2.2kW for lighting
circuits).


Your limitation here is down to voltage drop. 2.5mm^2 SWA gives around
18mV/m/A of voltage drop. So 45m of 2.5mm^2 is going to give 10.53V on a
13A load. i.e. Just out of spec for a supply that will run lights...
(how much you care again will depend on the use case for the building)

I plan to either feed the SWA from a 16A MCB in the house and
to use a 10A MCB in the shed or or to use a 16A type C MCB in the house
and a 16A type B MCB at the shed. Any comments?


At that distance I would run a larger CSA SWA - the difference in cost
of cable is small compared to the effort in laying it in. So allow for
some future proofing and expansion unless you are sure that the current
demands are unlikely to ever change.

As to MCB selection, that rather depends on what the power requirements
in the shed are going to be?

I believe the correct earthing in this situation is to export the house
earth down the SWA (hence 3-core, the armour will only be earthed at the
house end) and to remove the shed earth rod. Once again, have I missed
anything?


There is no "correct" answer as such, which option you choose will
depend a bit on circumstance. With a PME head end, if you elect to
export the earth, then you also need to export the main equipotential
zone. For that to make sense, the outbuilding should not have access to
any other sources of earth potential that can't readily be bonded into
the zone. (so for example, it would not be possible to extend the
equipotential zone into a greenhouse with a bare soil floor).

Also if extending the equipotential zone, the earth connection of your
submain will also need to function as a main bonding conductor and hence
meet the (copper equivalent) CSA requirements for that (typically 10mm^2
with PME - although that assumes size of the neutral of the supply is of
35mm^2 CSA or less, and where the supplier has not specified another
size be used).

If you are using 2.5mm^2 SWA, then its armour will typically be around
17mm^2 CSA. Divide that by 2.255 to get a copper equivalent of 7.55mm^2.
So if you add a 2.5mm^2 core to that, you just squeak in to meet the
minimum CSA for a PME main equipotential bond.




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 68
Default Electrical question: cable size and earthing for outbuilding

On 30/09/2017 13:25, John Rumm wrote:
On 30/09/2017 11:36, wrote:

I have a 2-wire overhead sub-main to a large shed 40-45m away. The house
earthing is TN-C-S (with an earth rod, ref other append) and the shed
earth comes from a local earth rod; there's an RCD in the shed CU. I
plan to replace the overhead feed with 3 core SWA in the ground (0.5m
deep, with warning tape above it at 0.3m deep), terminating the SWA
internally in IP65 adaptable boxes at each end and running the final
couple of metres in T&E.


ok. Although in reality with the current configuration, two core SWA
would be adequate in the circumstance.

The feed will come from a non-RCD protected MCB in the house CU. From
the TLC cable size calculator it seems that buried 2.5 SWA is OK up to
about 3.6kW for non-lighting circuits (about 2.2kW for lighting
circuits).


Your limitation here is down to voltage drop. 2.5mm^2 SWA gives around
18mV/m/A of voltage drop. So 45m of 2.5mm^2 is going to give 10.53V on a
13A load. i.e. Just out of spec for a supply that will run lights...
(how much you care again will depend on the use case for the building)


The building is mostly a store with a powered hacksaw, log splitter and
small welder. Electrical loads are modest and not going to exceed a
couple of kW.

I plan to either feed the SWA from a 16A MCB in the house and
to use a 10A MCB in the shed or or to use a 16A type C MCB in the house
and a 16A type B MCB at the shed. Any comments?


At that distance I would run a larger CSA SWA - the difference in cost
of cable is small compared to the effort in laying it in. So allow for
some future proofing and expansion unless you are sure that the current
demands are unlikely to ever change.

I've already got enough 2.5 SWA to do it.

As to MCB selection, that rather depends on what the power requirements
in the shed are going to be?

I chose 10A at the shed to ensure the installation stayed compliant and
16A at the head to protect the cable and avoid nuisance trips.

I believe the correct earthing in this situation is to export the house
earth down the SWA (hence 3-core, the armour will only be earthed at the
house end) and to remove the shed earth rod. Once again, have I missed
anything?


There is no "correct" answer as such, which option you choose will
depend a bit on circumstance. With a PME head end, if you elect to
export the earth, then you also need to export the main equipotential
zone. For that to make sense, the outbuilding should not have access to
any other sources of earth potential that can't readily be bonded into
the zone. (so for example, it would not be possible to extend the
equipotential zone into a greenhouse with a bare soil floor).

The point about the floor is new to me, and very relevant to another
task on the tuit list. I have a greenhouse with an overhead T&E feed
(without local earch rod) that was signed-off by someone before I bought
the house.
Is there really a difference between a soil floor and a concrete floor
that doesn't have a DPM? Where do I find the details?

Also if extending the equipotential zone, the earth connection of your
submain will also need to function as a main bonding conductor and hence
meet the (copper equivalent) CSA requirements for that (typically 10mm^2
with PME - although that assumes size of the neutral of the supply is of
35mm^2 CSA or less, and where the supplier has not specified another
size be used).
If you are using 2.5mm^2 SWA, then its armour will typically be around
17mm^2 CSA. Divide that by 2.255 to get a copper equivalent of 7.55mm^2.
So if you add a 2.5mm^2 core to that, you just squeak in to meet the
minimum CSA for a PME main equipotential bond.

Yes, and I would also need to add supplemental cable between the main
earth and the SWA termination.

It's starting to look like I'm better to keep the shed earth rod and not
to export the house earth.

Thanks for your comments.
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Electrical question: cable size and earthing for outbuilding

On 30/09/2017 14:23, wrote:
On 30/09/2017 13:25, John Rumm wrote:
On 30/09/2017 11:36,
wrote:

I have a 2-wire overhead sub-main to a large shed 40-45m away. The house
earthing is TN-C-S (with an earth rod, ref other append) and the shed
earth comes from a local earth rod; there's an RCD in the shed CU. I
plan to replace the overhead feed with 3 core SWA in the ground (0.5m
deep, with warning tape above it at 0.3m deep), terminating the SWA
internally in IP65 adaptable boxes at each end and running the final
couple of metres in T&E.


ok. Although in reality with the current configuration, two core SWA
would be adequate in the circumstance.

The feed will come from a non-RCD protected MCB in the house CU. From
the TLC cable size calculator it seems that buried 2.5 SWA is OK up to
about 3.6kW for non-lighting circuits (about 2.2kW for lighting
circuits).


Your limitation here is down to voltage drop. 2.5mm^2 SWA gives around
18mV/m/A of voltage drop. So 45m of 2.5mm^2 is going to give 10.53V on
a 13A load. i.e. Just out of spec for a supply that will run lights...
(how much you care again will depend on the use case for the building)


The building is mostly a store with a powered hacksaw, log splitter and
small welder. Electrical loads are modest and not going to exceed a
couple of kW.


Personally I would still design for at least 13A capacity at the socket,
then you know you can plug it most loads without any difficulty.

(things like a 110V 3KV site transformers may still cause problems
though - they will often trip 20A MCBs with inrush)

I plan to either feed the SWA from a 16A MCB in the house and
to use a 10A MCB in the shed or or to use a 16A type C MCB in the house
and a 16A type B MCB at the shed. Any comments?


At that distance I would run a larger CSA SWA - the difference in cost
of cable is small compared to the effort in laying it in. So allow for
some future proofing and expansion unless you are sure that the
current demands are unlikely to ever change.


I've already got enough 2.5 SWA to do it.


Well your call then ;-)

As to MCB selection, that rather depends on what the power
requirements in the shed are going to be?

I chose 10A at the shed to ensure the installation stayed compliant and
16A at the head to protect the cable and avoid nuisance trips.


The head end only really needs fault protection in this case - so the
protective device could be sized well above those in the shed. Even 32A
would probably still protect it...

I believe the correct earthing in this situation is to export the house
earth down the SWA (hence 3-core, the armour will only be earthed at the
house end) and to remove the shed earth rod. Once again, have I missed
anything?


There is no "correct" answer as such, which option you choose will
depend a bit on circumstance. With a PME head end, if you elect to
export the earth, then you also need to export the main equipotential
zone. For that to make sense, the outbuilding should not have access
to any other sources of earth potential that can't readily be bonded
into the zone. (so for example, it would not be possible to extend the
equipotential zone into a greenhouse with a bare soil floor).

The point about the floor is new to me, and very relevant to another
task on the tuit list. I have a greenhouse with an overhead T&E feed
(without local earch rod) that was signed-off by someone before I bought
the house.


Yup, that's a harder one with a PME supply. You can't realistically make
the greenhouse part of the equipotential zone, so in the event of a loss
of combined earth / neutral on the supply side, you would be at risk in
the greenhouse with your independent earth connections at very different
potentials.

Is there really a difference between a soil floor and a concrete floor
that doesn't have a DPM? Where do I find the details?


You would probably have to find a way of measuring the earth impedance
of the concrete to be sure. You could argue that if its 23K Ohms or
higher, then its not an extraneous conductive part that would otherwise
need to be included in the main bonding.

A variation on the test procedure here might work:

http://wiki.diyfaq.org.uk/index.php/...list_test_gear

(personally though, if there was any doubt, I would make the outbuilding
TT and be done with it)

Also if extending the equipotential zone, the earth connection of your
submain will also need to function as a main bonding conductor and
hence meet the (copper equivalent) CSA requirements for that
(typically 10mm^2 with PME - although that assumes size of the neutral
of the supply is of 35mm^2 CSA or less, and where the supplier has not
specified another size be used).
If you are using 2.5mm^2 SWA, then its armour will typically be around
17mm^2 CSA. Divide that by 2.255 to get a copper equivalent of
7.55mm^2. So if you add a 2.5mm^2 core to that, you just squeak in to
meet the minimum CSA for a PME main equipotential bond.


Yes, and I would also need to add supplemental cable between the main
earth and the SWA termination.


Yup, this is true if you are not running the SWA right to the CU.

It's starting to look like I'm better to keep the shed earth rod and not
to export the house earth.


Its what I normally do in most cases unless its a simple run close to
the main building.



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 10,998
Default Electrical question: cable size and earthing for outbuilding

Makes my brain hurt, For many years we got used to the lights dimming as a
fan heater cut in at our shed end. No people or animals came to any harm in
over 20 years.
grin.
Brian

--
Brian Gaff....Note, this account does not accept Bcc: email.
graphics are great, but the blind can't hear them
Email:
__________________________________________________ __________________________________________________ __________


"John Rumm" wrote in message
o.uk...
On 30/09/2017 11:36,
wrote:

I have a 2-wire overhead sub-main to a large shed 40-45m away. The house
earthing is TN-C-S (with an earth rod, ref other append) and the shed
earth comes from a local earth rod; there's an RCD in the shed CU. I
plan to replace the overhead feed with 3 core SWA in the ground (0.5m
deep, with warning tape above it at 0.3m deep), terminating the SWA
internally in IP65 adaptable boxes at each end and running the final
couple of metres in T&E.


ok. Although in reality with the current configuration, two core SWA would
be adequate in the circumstance.

The feed will come from a non-RCD protected MCB in the house CU. From
the TLC cable size calculator it seems that buried 2.5 SWA is OK up to
about 3.6kW for non-lighting circuits (about 2.2kW for lighting
circuits).


Your limitation here is down to voltage drop. 2.5mm^2 SWA gives around
18mV/m/A of voltage drop. So 45m of 2.5mm^2 is going to give 10.53V on a
13A load. i.e. Just out of spec for a supply that will run lights... (how
much you care again will depend on the use case for the building)

I plan to either feed the SWA from a 16A MCB in the house and
to use a 10A MCB in the shed or or to use a 16A type C MCB in the house
and a 16A type B MCB at the shed. Any comments?


At that distance I would run a larger CSA SWA - the difference in cost of
cable is small compared to the effort in laying it in. So allow for some
future proofing and expansion unless you are sure that the current demands
are unlikely to ever change.

As to MCB selection, that rather depends on what the power requirements in
the shed are going to be?

I believe the correct earthing in this situation is to export the house
earth down the SWA (hence 3-core, the armour will only be earthed at the
house end) and to remove the shed earth rod. Once again, have I missed
anything?


There is no "correct" answer as such, which option you choose will depend
a bit on circumstance. With a PME head end, if you elect to export the
earth, then you also need to export the main equipotential zone. For that
to make sense, the outbuilding should not have access to any other sources
of earth potential that can't readily be bonded into the zone. (so for
example, it would not be possible to extend the equipotential zone into a
greenhouse with a bare soil floor).

Also if extending the equipotential zone, the earth connection of your
submain will also need to function as a main bonding conductor and hence
meet the (copper equivalent) CSA requirements for that (typically 10mm^2
with PME - although that assumes size of the neutral of the supply is of
35mm^2 CSA or less, and where the supplier has not specified another size
be used).

If you are using 2.5mm^2 SWA, then its armour will typically be around
17mm^2 CSA. Divide that by 2.255 to get a copper equivalent of 7.55mm^2.
So if you add a 2.5mm^2 core to that, you just squeak in to meet the
minimum CSA for a PME main equipotential bond.




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd -
http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
DIY electrical repairs in outbuilding and part P Simon UK diy 11 December 12th 06 01:20 PM
outbuilding electrical disconnect [email protected] Home Repair 3 August 28th 06 02:58 AM
Earthing a kitchen sink - what size cable? Bert Coules UK diy 57 May 17th 05 09:48 PM
Earthing Conductor size (massive??) & new Consumer Unit jim_in_sussex UK diy 14 July 8th 04 01:51 PM
Earthing Conductor size (massive??) & new Consumer Unit jim_in_sussex UK diy 5 July 8th 04 01:14 PM


All times are GMT +1. The time now is 11:40 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"