Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.
About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.
I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal? Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?
Without a working expansion vessel, would the hot pressure be more than
2 bar?
Ta.
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default Combi boiler pressure

On 18/03/2017 14:07, Grumps wrote:
Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.
About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.
I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal? Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?
Without a working expansion vessel, would the hot pressure be more than
2 bar?
Ta.


Without a working expansion vessel the pressure would go way over 2 bar
when the system is hot, causing the pressure relief valve to open and
discharge water to the outside world. Then, when it cooled, the pressure
would fall to zero. Very unlikely that this is happening.

Much more likely that there was dissolved air in the water when the
system was initially filled, and this collected in the towel rail.
Hopefully you've now got rid of it all, and shouldn't have any further
problems.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Combi boiler pressure

On 18/03/2017 14:07, Grumps wrote:
Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.


Yup that's not surprising, there is a fair amount of dissolved air in
the water that will come out over time.

About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.


Every time you bleed the air out you reduce the overall system volume a
bit. Eventually the pressure will be too low for the boiler to operate.

I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal?


Yup that perfectly normal.

Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?


Not on an 8 month old boiler. I expect you have just seen the system
water loosing its dissolved air. There may also be a tiny weep / leak
that (in a hard water area anyway) will tend to self seal.

Make sure you add some inhibitor about once a year - that prevents any
corrosion and generation of gas in the system from that.

Without a working expansion vessel, would the hot pressure be more than
2 bar?


Yes - massively... The pressure would exceed that of the safety release
valve (usually about 3.5 bar) and that would vent water outside. Once
the boiler cools you would have low pressure. So the loss of pressure
would be a daily (or more frequent) cycle.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 121
Default Combi boiler pressure

On 18/03/2017 16:17, John Rumm wrote:
On 18/03/2017 14:07, Grumps wrote:
Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.


Yup that's not surprising, there is a fair amount of dissolved air in
the water that will come out over time.

About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.


Every time you bleed the air out you reduce the overall system volume a
bit. Eventually the pressure will be too low for the boiler to operate.

I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal?


Yup that perfectly normal.

Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?


Not on an 8 month old boiler. I expect you have just seen the system
water loosing its dissolved air. There may also be a tiny weep / leak
that (in a hard water area anyway) will tend to self seal.

Make sure you add some inhibitor about once a year - that prevents any
corrosion and generation of gas in the system from that.

Without a working expansion vessel, would the hot pressure be more than
2 bar?


Yes - massively... The pressure would exceed that of the safety release
valve (usually about 3.5 bar) and that would vent water outside. Once
the boiler cools you would have low pressure. So the loss of pressure
would be a daily (or more frequent) cycle.


Thanks both. I'm reassured that all is OK now.

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,766
Default Combi boiler pressure

Grumps formulated on Saturday :
Thanks both. I'm reassured that all is OK now.


If you think the pressure release valve might be opening or leaking, a
simple way to check, is to add a plastic sandwich bag over the outlet
fixed with a rubber band. It will catch any released water.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default Combi boiler pressure

On 18/03/17 15:42, Roger Mills wrote:
On 18/03/2017 14:07, Grumps wrote:
Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.
About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.
I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal? Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?
Without a working expansion vessel, would the hot pressure be more than
2 bar?
Ta.


Without a working expansion vessel the pressure would go way over 2 bar
when the system is hot, causing the pressure relief valve to open and
discharge water to the outside world. Then, when it cooled, the pressure
would fall to zero. Very unlikely that this is happening.


However a pressure vessel that hasn't *failed*, but has lost a lot of
its pressure, behaves exactly like the OP describes. Essentially it
needs pumping up with a car or bike tyre inflator.


Much more likely that there was dissolved air in the water when the
system was initially filled, and this collected in the towel rail.
Hopefully you've now got rid of it all, and shouldn't have any further
problems


Pressure should not vary between 1 and 2 bar. That's a fpressure
vessel that is barely working.


--
All political activity makes complete sense once the proposition that
all government is basically a self-legalising protection racket, is
fully understood.

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,120
Default Combi boiler pressure

On 19/03/2017 09:17, The Natural Philosopher wrote:
On 18/03/17 15:42, Roger Mills wrote:
On 18/03/2017 14:07, Grumps wrote:
Hi
I'm slowly renovating a house and had a new combi central heating system
installed about 8 months ago.
Every week when I visit the property, the towel rad (highest point in
the system) needed a little bleeding.
About 4 weeks ago, the boiler's display said "bleed radiators". So I
did. Then the display read "call engineer" and the pressure was 0.
I called the installer and he said to top it up. I did this to a
pressure of 1 bar.
The pressure varies between 1 and 2 bar when cold and hot. Is this
normal? Since topping up the system hasn't need bleeding.
In my uneducated state, I'm thinking that maybe the expansion vessel had
a leak and was letting its air into the system. This being the air that
needed to be bled every week. And now the vessel is just full of water.
What's the likelihood of that being an explanation for the requirement
for frequent bleeding?
Without a working expansion vessel, would the hot pressure be more than
2 bar?
Ta.


Without a working expansion vessel the pressure would go way over 2 bar
when the system is hot, causing the pressure relief valve to open and
discharge water to the outside world. Then, when it cooled, the pressure
would fall to zero. Very unlikely that this is happening.


However a pressure vessel that hasn't *failed*, but has lost a lot of
its pressure, behaves exactly like the OP describes. Essentially it
needs pumping up with a car or bike tyre inflator.


You can indeed revive a pressure vessel in that way if it has simply
lost its charge pressure and not failed completely.

But the OP's symptoms didn't indicate a pressure vessel problem, anyway!


Much more likely that there was dissolved air in the water when the
system was initially filled, and this collected in the towel rail.
Hopefully you've now got rid of it all, and shouldn't have any further
problems


Pressure should not vary between 1 and 2 bar. That's a fpressure vessel
that is barely working.


Not at all! It depends on the volume of water in the system vs the size
of the pressure vessel. A cold/hot rise from 1 bar to 2 bar is perfectly
acceptable. It's still a long way from it's blow-off pressure of 3.5 bar.
--
Cheers,
Roger
____________
Please reply to Newsgroup. Whilst email address is valid, it is seldom
checked.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,034
Default Combi boiler pressure

On 19/03/2017 09:17, The Natural Philosopher wrote:



Much more likely that there was dissolved air in the water when the
system was initially filled, and this collected in the towel rail.
Hopefully you've now got rid of it all, and shouldn't have any further
problems


Pressure should not vary between 1 and 2 bar. That's a fpressure vessel
that is barely working.


How often would you expect to have to top up a sealed system?

(or what rate of loss would you consider normal?)


--
Michael Chare

---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
combi boiler - pressure increases then boiler shuts down peri UK diy 1 July 10th 06 09:50 PM
Combi boiler too much pressure [email protected] UK diy 5 November 20th 05 02:37 PM
Low pressure in combi boiler Andy UK diy 8 October 11th 05 12:39 AM
Fault in combi boiler's pressure guage, and/or pressure-relief valve? DaveŁ UK diy 14 October 19th 04 08:29 PM
combi boiler pressure down - help please One Man Show UK diy 3 July 23rd 03 07:30 PM


All times are GMT +1. The time now is 10:17 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"