A discussion in a separate thread has prompted me to look further at the
set up of my gas boiler. I have a heating system designed & supplied by NuHeat ...... 17 zones, all underfloor heating - no rads. There is a thermal store (Energymaster) and if the stat on the store (fitted on lower 1/3)is lower than 65C .. it requires heat .. zone valve opens on primaries, pump starts and 220V sent to boiler. Boiler runs until stat reaches 65C and opens. The heating system us fed from a lower heat exchanger, and the DHW form an a upper heat exchanger via a thermostatic valve. There is no blending valve on loop circuit - design relies of store stat limiting temp. ( I intend fitting a blending valve - but that id not in current design) Sketch of set up he http://tinyurl.com/ngeqfsy Safety bypass and pressure vessels left out for clarity The initial advice was to set boiler temp to Maxm .... but appreciate this may not be optimum .... I went back to NuHeat .. they advise # Boiler stat should be set to 75C ..... # Diff between boiler F& return should not exceed 13C Any suggestions on how to set this up ....... I have only the pump speed and boiler temp setting to adjust. Do I turn down boiler setting until it is at 75, then adjust pump for 13C difference ........ just not sure how to approach this. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 11:52, rick wrote:
A discussion in a separate thread has prompted me to look further at the set up of my gas boiler. I have a heating system designed & supplied by NuHeat ...... 17 zones, all underfloor heating - no rads. There is a thermal store (Energymaster) and if the stat on the store (fitted on lower 1/3)is lower than 65C .. it requires heat .. zone valve opens on primaries, pump starts and 220V sent to boiler. Boiler runs until stat reaches 65C and opens. The heating system us fed from a lower heat exchanger, and the DHW form an a upper heat exchanger via a thermostatic valve. There is no blending valve on loop circuit - design relies of store stat limiting temp. ( I intend fitting a blending valve - but that id not in current design) Sketch of set up he http://tinyurl.com/ngeqfsy Safety bypass and pressure vessels left out for clarity The initial advice was to set boiler temp to Maxm .... but appreciate this may not be optimum .... I went back to NuHeat .. they advise # Boiler stat should be set to 75C ..... # Diff between boiler F& return should not exceed 13C Any suggestions on how to set this up ....... I have only the pump speed and boiler temp setting to adjust. Do I turn down boiler setting until it is at 75, then adjust pump for 13C difference ........ just not sure how to approach this. It seems like you have a system optimised to get the best efficiency possible from a conventional non condensing non modulating boiler. i.e. Running the boiler at high output temperatures on high load in measured bursts. Traditional boilers were not good at trickling heat into a system at part load to match the heat loss of the building, and so the thermal store made a good buffer. It is also a simple way of using stratification to get a variety of output flow temperatures to suit different applications such as DHW and UFH which have different requirements. So the first question is, what kind of boiler are you using? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#3
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 11:52, rick wrote:
A discussion in a separate thread has prompted me to look further at the set up of my gas boiler. I have a heating system designed & supplied by NuHeat ...... 17 zones, all underfloor heating - no rads. There is a thermal store (Energymaster) and if the stat on the store (fitted on lower 1/3)is lower than 65C .. it requires heat .. zone valve opens on primaries, pump starts and 220V sent to boiler. Boiler runs until stat reaches 65C and opens. The heating system us fed from a lower heat exchanger, and the DHW form an a upper heat exchanger via a thermostatic valve. There is no blending valve on loop circuit - design relies of store stat limiting temp. ( I intend fitting a blending valve - but that id not in current design) Sketch of set up he http://tinyurl.com/ngeqfsy Safety bypass and pressure vessels left out for clarity The initial advice was to set boiler temp to Maxm .... but appreciate this may not be optimum .... I went back to NuHeat .. they advise # Boiler stat should be set to 75C ..... # Diff between boiler F& return should not exceed 13C Any suggestions on how to set this up ....... I have only the pump speed and boiler temp setting to adjust. The simplest empirical way is to monitor gas usage and daily min/max outside temperature whilst making adjustments on a weekly basis. I doubt if the boiler stat gets much of a look in compared to the thermal store provided that the pump is actually running. Do I turn down boiler setting until it is at 75, then adjust pump for 13C difference ........ just not sure how to approach this. My instinct is that provided the pump is fast enough to avoid a 13C temperature drop on the loop the overall efficiency won't be all that much different. The only thing that might make a difference is if one of the burner controllers is smart enough to determine the system thermal inertia and loading to avoid overshooting the 65C target. -- Regards, Martin Brown |
#4
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 13:59, John Rumm wrote:
requirements. So the first question is, what kind of boiler are you using? Gas condensing - Baxi Barcelona set for 1000,000 Btu/h (sorry meant to add that in OP) it has been fully upgraded to 100HE spec |
#5
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 14:25, Martin Brown wrote:
My instinct is that provided the pump is fast enough to avoid a 13C temperature drop on the loop the overall efficiency won't be all that much different. The only thing that might make a difference is if one of the burner controllers is smart enough to determine the system thermal inertia and loading to avoid overshooting the 65C target. Just a little unsure of what I'm trying to set .... NuHeat say 75C .... Comments I have read elsewhere state that I have to get return no higher than 55C to remain condensing ... that would be 13C difference I can happily take temp readings - but not sure what I should be setting to. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 14:25, Martin Brown wrote:
My instinct is that provided the pump is fast enough to avoid a 13C temperature drop on the loop the overall efficiency won't be all that much different. The only thing that might make a difference is if one of the burner controllers is smart enough to determine the system thermal inertia and loading to avoid overshooting the 65C target. Can anyone explain to me why it is desirable to avoid a temperature difference of more than 13C ? That means when it starts up from cold, with the inflow around say 15C that the outflow should be no more than 28C - which means the pump must send the same water around several times before the outflow gets to 75C? I don't understand why a boiler with a flame at several hundred Celsius would be more efficient working like that than it it raised it right away from say 15 to 75C. -- Clive Page |
#7
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 14:49, rick wrote:
On 09/11/2016 14:25, Martin Brown wrote: My instinct is that provided the pump is fast enough to avoid a 13C temperature drop on the loop the overall efficiency won't be all that much different. The only thing that might make a difference is if one of the burner controllers is smart enough to determine the system thermal inertia and loading to avoid overshooting the 65C target. Just a little unsure of what I'm trying to set .... NuHeat say 75C .... Comments I have read elsewhere state that I have to get return no higher than 55C to remain condensing ... that would be 13C difference You have a conflict of interests here really... Thermal stores work well at high temperatures, and condensing boilers get bigger efficiency gains at lower temperatures. Even at return temps above 54 degrees (the dew point of the flue gasses) the modern boiler will be more efficient than an older style one as a result of its larger heat exchanger. The efficiency graph just gets a bit steeper at that point. With a condenser there is no real problem with a delta over 13 degrees - that used to be a limitation of older boilers where you wanted to prevent them from condensing (since there was no mechanism for collecting and disposing of the condensate, all it was going to do it accelerate corrosion in the boiler). Modern condensing systems are often run at 20 degree delta or more. I can happily take temp readings - but not sure what I should be setting to. I expect your best situation is to have the boiler flow temperature set so that it can just satisfy the store stat in the coldest of conditions. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#8
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 17:44, John Rumm wrote:
I expect your best situation is to have the boiler flow temperature set so that it can just satisfy the store stat in the coldest of conditions. Did have a follow up email form Nuheat .. they stated manual advice was based on old style boilers, not modern condensing .... but no other advice on setup. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 17:44, John Rumm wrote:
You have a conflict of interests here really... Thermal stores work well at high temperatures, and condensing boilers get bigger efficiency gains at lower temperatures. Even at return temps above 54 degrees (the dew point of the flue gasses) the modern boiler will be more efficient than an older style one as a result of its larger heat exchanger. The efficiency graph just gets a bit steeper at that point. Like this (reposted): http://www.maxwell.myzen.co.uk/uk.d-i-y/AM3_fig2.6.gif The design seems mad to me. Surely for optimum efficiency you want the UFH running straight off the boiler primary, at the lowest feasible temperature. Weather compensation would help here, by reducing the temperature further in mild weather. Then use the store for DHW only with appropriate controls to heat it to ~65 deg. a couple of times a day, or as required, by running the boiler flat out into it for short periods (i.e. HW priority control). -- Andy |
#10
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 23:46, Andy Wade wrote:
On 09/11/2016 17:44, John Rumm wrote: You have a conflict of interests here really... Thermal stores work well at high temperatures, and condensing boilers get bigger efficiency gains at lower temperatures. Even at return temps above 54 degrees (the dew point of the flue gasses) the modern boiler will be more efficient than an older style one as a result of its larger heat exchanger. The efficiency graph just gets a bit steeper at that point. Like this (reposted): http://www.maxwell.myzen.co.uk/uk.d-i-y/AM3_fig2.6.gif The design seems mad to me. Surely for optimum efficiency you want the Not mad - but possibly from a different age! Its the kind of setup that a previous regular of this group was fond of promoting. It made sense with old clunker boilers. UFH running straight off the boiler primary, at the lowest feasible temperature. Weather compensation would help here, by reducing the temperature further in mild weather. Then use the store for DHW only with appropriate controls to heat it to ~65 deg. a couple of times a day, or as required, by running the boiler flat out into it for short periods (i.e. HW priority control). Yup I think that is the way I would design it if given the same choice of components (assuming the boiler can modulate low enough to run the UFH directly - you may need a blending valve or two in there). The boiler would need to be capable of (or be fooled into) split temperature operation so that it could run an appropriate flow temp for heating, but then use a much higher temp for store recharge. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#11
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 09/11/2016 15:36, Clive Page wrote:
On 09/11/2016 14:25, Martin Brown wrote: My instinct is that provided the pump is fast enough to avoid a 13C temperature drop on the loop the overall efficiency won't be all that much different. The only thing that might make a difference is if one of the burner controllers is smart enough to determine the system thermal inertia and loading to avoid overshooting the 65C target. Can anyone explain to me why it is desirable to avoid a temperature difference of more than 13C ? Its advice that applied to old non modulating non condensing boilers. If you designed for a delta of about 12 degrees, then you could be safe in the knowledge that even if you dropped the flow temperature to 65, you would still keep the return temperature above the point at which you would get condensation of the flue gasses in the boiler (once it was all up to temperature of course - you would still get some condensation at startup - but that water could be boiled off soon after). This at the time was a good thing since it stopped the boiler with its cast iron lump HX from rusting away. That means when it starts up from cold, with the inflow around say 15C that the outflow should be no more than 28C - which means the pump must send the same water around several times before the outflow gets to 75C? With old boilers they just ran at a fixed output - the system balancing combined with the boiler's internal stat would set the parameters. So it would condense a bit at startup, and then run normally once up to temperature. I don't understand why a boiler with a flame at several hundred Celsius would be more efficient working like that than it it raised it right away from say 15 to 75C. They don't have the power to lift that quantity of water to 75 in one pass. The efficiency gain in the condenser comes from two factors. Firstly being able to extract more heat from the combustion in the first place (bigger more efficient HX), and secondly by condensing the water produced during the combustion process, you can claw back the energy tied up in the latent heat of vaporisation of the H2O manufactured when you burn a hydrocarbon fuel. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#12
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 10/11/2016 01:32, John Rumm wrote:
On 09/11/2016 15:36, Clive Page wrote: On 09/11/2016 14:25, Martin Brown wrote: A bit of pushing back at NuHeat and they admit the commissioning notes of setting to 75C and a 13c differential were actually based on old style non-condensing boilers. Even though my system was specifically to be used with a condensing boiler. When asked what to set it to all they will advise is Boiler must be set higher than store stat temp ... anything else is up to me. So back to question ... do I set the boiler to run the water at 75C, then what do I set the pump speed at.. on old system you would adjust pump speed to to get correct differential ... Or would I be better setting at lower temp ... boiler has option to limit flow temp to 63C by a control board jumper setting. This is what it is currently set to ... and pump is on max speed. (If any of you have knowledge of Baxi's .. I have posted separate Post on Baxi control board jumpers - welcome input) |
#13
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 10/11/2016 01:32, John Rumm wrote:
The efficiency gain in the condenser comes from two factors. Firstly being able to extract more heat from the combustion in the first place (bigger more efficient HX), and secondly by condensing the water produced during the combustion process, you can claw back the energy tied up in the latent heat of vaporisation of the H2O manufactured when you burn a hydrocarbon fuel. Thanks. I hadn't thought about the efficiency of the condensing stage. I guess that is a large part of the explanation. -- Clive Page |
#14
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 10/11/2016 01:22, John Rumm wrote:
[...] Yup I think that is the way I would design it if given the same choice of components (assuming the boiler can modulate low enough to run the UFH directly - you may need a blending valve or two in there). Er, if the heat demand is less than the minimum modulated output of the boiler the boiler will just cycle on and off (PWM). If you force it not to do that it will be delivering excess energy which has to go somewhere. Either the house will overheat, or a room 'stat will perform the PWM function instead. Unless weather compensation is employed that will be the main control mechanism in any case. [Re DHW:] The boiler would need to be capable of (or be fooled into) split temperature operation so that it could run an appropriate flow temp for heating, but then use a much higher temp for store recharge. True. Combis do this innately of course if you replace "store recharge" with "provide hot water, but I dont know if there are any system boilers that have two demand inputs like that. There should be though... -- Andy |
#15
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 10/11/2016 20:26, rick wrote:
On 10/11/2016 01:32, John Rumm wrote: So back to question ... do I set the boiler to run the water at 75C, then what do I set the pump speed at.. on old system you would adjust pump speed to to get correct differential If efficiency is your aim I'd ignore that and set to the lowest boiler temperature that gives you sufficiently hot water and adequate space heating, with your system as-is. (Min. 60 deg. for HW to kill Legionella of course.) Or would I be better setting at lower temp ... boiler has option to limit flow temp to 63C by a control board jumper setting. Yes, try it and see, .... and pump is on max speed. Temperature differential is generally not critical over quite a wide range. I'd aim for the lowest speed that gives adequate performance. Preferably keep the return temp down in the low 50s (or less) to keep the boiler in condensing mode. -- Andy |
#16
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 11/11/2016 00:25, Andy Wade wrote:
On 10/11/2016 01:22, John Rumm wrote: [...] Yup I think that is the way I would design it if given the same choice of components (assuming the boiler can modulate low enough to run the UFH directly - you may need a blending valve or two in there). Er, if the heat demand is less than the minimum modulated output of the boiler the boiler will just cycle on and off (PWM). If you force it not to do that it will be delivering excess energy which has to go somewhere. Either the house will overheat, or a room 'stat will perform the PWM function instead. Unless weather compensation is employed that will be the main control mechanism in any case. It will indeed. The purpose of the blending valve in this case is to control the maximum flow temperature into the UFH to prevent it being uncomfortably hot on the feet, or distorting floor coverings etc. The boiler will still need to cycle to only deliver the power level actually needed. [Re DHW:] The boiler would need to be capable of (or be fooled into) split temperature operation so that it could run an appropriate flow temp for heating, but then use a much higher temp for store recharge. True. Combis do this innately of course if you replace "store recharge" with "provide hot water, but I dont know if there are any system boilers that have two demand inputs like that. There should be though... There are a few - I spent some time researching when looking for a system boiler setup for my place. Some have it built in, others you can add it or get the same effect with the right control system. Anything that has weather compensation will normally include it. Most of the Vaillant models seem to include separate temperature controls on the boiler itself for the DHW and CH - even on the basic 400 series "heat only" vented range. The posher weather compensating controls allow for the CH flow temp to be slaved to the external temperature, modified via user selectable response curves to model the thermal properties of the building, and also to introduce an element of PID style control such that the current target temperature in the building will be taken into account (i.e. girl mode - if its well below the current set temperature it will turning it up more for faster warm up ;-). The DHW then runs at a separate preset maximum flow temp (with an optional weekly "anti legionella" cycle where it recharges the DHW at a higher temperature). Many weather compensators seem to use a NTC thermistor as their temperature sensor. So a control system could obviously switch in additional resistors to trick the system into running a different flow temperature. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#17
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 10/11/2016 20:26, rick wrote:
On 10/11/2016 01:32, John Rumm wrote: On 09/11/2016 15:36, Clive Page wrote: On 09/11/2016 14:25, Martin Brown wrote: A bit of pushing back at NuHeat and they admit the commissioning notes of setting to 75C and a 13c differential were actually based on old style non-condensing boilers. Even though my system was specifically to be used with a condensing boiler. When asked what to set it to all they will advise is Boiler must be set higher than store stat temp ... anything else is up to me. So long as the flow temp is higher than the set temp on the store you should be ok. So back to question ... do I set the boiler to run the water at 75C, then what do I set the pump speed at.. on old system you would adjust pump speed to to get correct differential ... With your boiler I would not worry about differentials particularly. Just go for the lowest setting that does the job adequately (less system pump noise that way) Or would I be better setting at lower temp ... boiler has option to limit flow temp to 63C by a control board jumper setting. This is what it is currently set to ... and pump is on max speed. The lower temp will give better efficiency but possibly at a slight price of longer re-heat times on the store. How is the store heated? (i.e. direct or indirect coil) If its an indirect coil, then it might be worth checking what the maximum transfer rate for the coil is specced at. If its an older diesgn it may limit the maximum power to somewhat less than the boiler's full output anyway. (stores used for system buffers like that are often "direct" - i.e. they are full of primary water heated by the boiler) (If any of you have knowledge of Baxi's .. I have posted separate Post on Baxi control board jumpers - welcome input) Nope, nothing specific, although I probably have collection of manuals for many of the older ones. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 11/11/2016 09:48, John Rumm wrote:
How is the store heated? (i.e. direct or indirect coil) Direct - whole contents of store circulated around boiler 2 heat exchangers - lower for UFH Upper for DHW (with Thermostatic mixing valve) as per: http://tinyurl.com/ngeqfsy The tank is set to 60 degrees .. to limit max temp of water that can get to UFH circuits. My plan is to install a Thermostatic Mixing Valve set to 50C and run tank at higher temp (probably 70) The store has a baffle - to help stratification, but as soon as you draw any hot water it energises the pimp on primaries to 'stir' the store and keep recharging heat exchanger. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 11/11/2016 13:05, rick wrote:
On 11/11/2016 09:48, John Rumm wrote: How is the store heated? (i.e. direct or indirect coil) Direct - whole contents of store circulated around boiler 2 heat exchangers - lower for UFH Upper for DHW (with Thermostatic mixing valve) ok, so it can take the full boiler output which makes it a bit simpler. as per: http://tinyurl.com/ngeqfsy Yup saw that, was just not sure if there was no coil or you had omitted it for simplicity. The tank is set to 60 degrees .. to limit max temp of water that can get to UFH circuits. My plan is to install a Thermostatic Mixing Valve set to 50C and run tank at higher temp (probably 70) It would store more energy in the tank, at a slight cost in boiler efficiency (but probably only for the last few degrees of the reheat). The store has a baffle - to help stratification, but as soon as you draw any hot water it energises the pimp on primaries to 'stir' the store and keep recharging heat exchanger. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 11/11/2016 23:46, John Rumm wrote:
ok, so it can take the full boiler output which makes it a bit simpler. It would store more energy in the tank, at a slight cost in boiler efficiency (but probably only for the last few degrees of the reheat). Not easy trying to get information on how to best set up ........ GasSafe servce guys have no clue at all about Thermal stores, in fact couldn't even advise on how to set up jumpers on control board. NuHeat who designed & sold system - admit their commissioning notes are based on non-condensing boilers - and when asked about what I should do for a condensing boiler - advise just make sure flow temp is higher than tank stat ... the greater the difference the quicker it will recover - but other than that they say to contact boiler manufacture. Baxi reply with "with the store needing to maintain a constant store temperature of 60 degrees. You will need to follow the manufacturers guidance, as it is their system that requires these temperatures to run correctly, and unfortunately achieving a target 55 degree return temperature doesn't sound possible." At the moment the boiler control board is set to 100,00BTU/h and 83C Turned down variable temp control (user front panel knob) to get 75C and reduced pump to speed II I'll try fitting a pair of thermometers and watch the F&R and see if I can reduce speed further. Maybe I can get a reasonable differential on F&R ... but Baxi don't think I will not get 55C |
#21
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
rick wrote:
Baxi reply with "with the store needing to maintain a constant store temperature of 60 degrees. You will need to follow the manufacturers guidance, as it is their system that requires these temperatures to run correctly, and unfortunately achieving a target 55 degree return temperature doesn't sound possible." Does the store really want to stay constant? I'd have thought with a non-modulating boiler, firing in frequent short bursts would not be the most efficient while the UFH is drawing out heat. |
#22
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 12/11/2016 10:56, rick wrote:
On 11/11/2016 23:46, John Rumm wrote: ok, so it can take the full boiler output which makes it a bit simpler. It would store more energy in the tank, at a slight cost in boiler efficiency (but probably only for the last few degrees of the reheat). Not easy trying to get information on how to best set up ........ GasSafe servce guys have no clue at all about Thermal stores, in fact couldn't even advise on how to set up jumpers on control board. NuHeat who designed & sold system - admit their commissioning notes are based on non-condensing boilers - and when asked about what I should do for a condensing boiler - advise just make sure flow temp is higher than tank stat ... the greater the difference the quicker it will recover - but other than that they say to contact boiler manufacture. Baxi reply with "with the store needing to maintain a constant store temperature of 60 degrees. You will need to follow the manufacturers guidance, as it is their system that requires these temperatures to run correctly, and unfortunately achieving a target 55 degree return temperature doesn't sound possible." I think there is a danger of over thinking this one! Beyond basic requirements like making sure the flow is hot enough to get the store to its set point, there are only a few variable to play with, and each has pros and cons - so pick whichever is most important to you. None are necessarily right or wrong. You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. At the moment the boiler control board is set to 100,00BTU/h and 83C Turned down variable temp control (user front panel knob) to get 75C and reduced pump to speed II I'll try fitting a pair of thermometers and watch the F&R and see if I can reduce speed further. Maybe I can get a reasonable differential on F&R ... but Baxi don't think I will not get 55C You will do if the store is nearly depleted, but obviously as it warms up that will get harder. All that means is you will get a reduction in boiler efficiency for the last phase of the reheat. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#23
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On Sat, 12 Nov 2016 13:00:32 +0000, John Rumm
wrote: You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. Not being much good at plumbing but having some experience of thermal stores: My first point is that it's far better to store the energy as natural gas and only convert it to heat as you need it. So the OP's system has a heat store for the two reasons John has discussed 1) to deliver more instantaneous hot water than the boiler can supply from the top part of the thermal store that, I assume this goes through a plate heat exchanger so returns to the bottom of the store at near ambient? Water from the main tends to be around 10C here. 2) To allow a blending valve to take water from the top of the thermal store but under the part reserved for DHW, mix it with water going around the under floor circuit and then return is at around 25C to the bottom of the tank. The need is always to return water below about 40C to the boiler to keep it in condensing mode? My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? The demand for underfloor heating then being sensed when the blender valve input from the thermal store falls below the set underfloor temperature it can maintain? The boiler then heats the whole of the tank until it starts drawing water above 40 C from the bottom of the tank? The system I used to service a pellet boiler on in a block of flats in Brixton failed to maintain stratification because the flows where so high they constantly mixed the store's contents. I advocated a possible solution but the german makers of the thermal store would not countenance it. AJH |
#24
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
wrote:
On Sat, 12 Nov 2016 13:00:32 +0000, John Rumm wrote: You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. Not being much good at plumbing but having some experience of thermal stores: My first point is that it's far better to store the energy as natural gas and only convert it to heat as you need it. So the OP's system has a heat store for the two reasons John has discussed 1) to deliver more instantaneous hot water than the boiler can supply from the top part of the thermal store that, I assume this goes through a plate heat exchanger so returns to the bottom of the store at near ambient? Water from the main tends to be around 10C here. 2) To allow a blending valve to take water from the top of the thermal store but under the part reserved for DHW, mix it with water going around the under floor circuit and then return is at around 25C to the bottom of the tank. The need is always to return water below about 40C to the boiler to keep it in condensing mode? My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? The demand for underfloor heating then being sensed when the blender valve input from the thermal store falls below the set underfloor temperature it can maintain? The boiler then heats the whole of the tank until it starts drawing water above 40 C from the bottom of the tank? The system I used to service a pellet boiler on in a block of flats in Brixton failed to maintain stratification because the flows where so high they constantly mixed the store's contents. I advocated a possible solution but the german makers of the thermal store would not countenance it. It seems an awfully complicated way of meeting two very different demands. Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? Tim -- Please don't feed the trolls |
#25
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On Sat, 12 Nov 2016 15:15:46 -0000 (UTC), Tim+
wrote: It seems an awfully complicated way of meeting two very different demands. Why it's just a matter of changing where the thermostats that trigger the burner are placed except on the underfloor system a different stat triggers on from the one that turns off the boiler? Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? At over £700 each? AJH |
#27
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 12/11/2016 15:15, Tim+ wrote:
wrote: On Sat, 12 Nov 2016 13:00:32 +0000, John Rumm wrote: You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. Not being much good at plumbing but having some experience of thermal stores: My first point is that it's far better to store the energy as natural gas and only convert it to heat as you need it. So the OP's system has a heat store for the two reasons John has discussed 1) to deliver more instantaneous hot water than the boiler can supply from the top part of the thermal store that, I assume this goes through a plate heat exchanger so returns to the bottom of the store at near ambient? Water from the main tends to be around 10C here. 2) To allow a blending valve to take water from the top of the thermal store but under the part reserved for DHW, mix it with water going around the under floor circuit and then return is at around 25C to the bottom of the tank. The need is always to return water below about 40C to the boiler to keep it in condensing mode? My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? The demand for underfloor heating then being sensed when the blender valve input from the thermal store falls below the set underfloor temperature it can maintain? The boiler then heats the whole of the tank until it starts drawing water above 40 C from the bottom of the tank? The system I used to service a pellet boiler on in a block of flats in Brixton failed to maintain stratification because the flows where so high they constantly mixed the store's contents. I advocated a possible solution but the german makers of the thermal store would not countenance it. It seems an awfully complicated way of meeting two very different demands. Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? Only if you like hot water dribbling from the taps ;-) An alternative would be to drive the UFH from a modern boiler directly with blending valves. The devote the store to just giving you DHW. No real advantages over a unvented hot water cylinder though it has to be said. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#28
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
John Rumm wrote:
On 12/11/2016 15:15, Tim+ wrote: wrote: On Sat, 12 Nov 2016 13:00:32 +0000, John Rumm wrote: You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. Not being much good at plumbing but having some experience of thermal stores: My first point is that it's far better to store the energy as natural gas and only convert it to heat as you need it. So the OP's system has a heat store for the two reasons John has discussed 1) to deliver more instantaneous hot water than the boiler can supply from the top part of the thermal store that, I assume this goes through a plate heat exchanger so returns to the bottom of the store at near ambient? Water from the main tends to be around 10C here. 2) To allow a blending valve to take water from the top of the thermal store but under the part reserved for DHW, mix it with water going around the under floor circuit and then return is at around 25C to the bottom of the tank. The need is always to return water below about 40C to the boiler to keep it in condensing mode? My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? The demand for underfloor heating then being sensed when the blender valve input from the thermal store falls below the set underfloor temperature it can maintain? The boiler then heats the whole of the tank until it starts drawing water above 40 C from the bottom of the tank? The system I used to service a pellet boiler on in a block of flats in Brixton failed to maintain stratification because the flows where so high they constantly mixed the store's contents. I advocated a possible solution but the german makers of the thermal store would not countenance it. It seems an awfully complicated way of meeting two very different demands. Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? Only if you like hot water dribbling from the taps ;-) A bit unfair on instantaneous water heaters. For sure not going to match the best output of a stored water solution but more than adequate for many folk who don't run a bath too often. Tim -- Please don't feed the trolls |
#29
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On Sat, 12 Nov 2016 19:20:14 +0000, John Rumm
wrote: What was your suggested solution? Return the cold water tangentially to prevent the mixing, the colder water then inducing a slight vortex and falling to the bottom, any warmer water at the same level would be less dense so would rise and not tend to move past the denser colder layer from centrifugal effects as long as there was little turbulence. Hot take offs were already from the centre of the 3000litre cylindrical tanks. AJH |
#30
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 12/11/2016 20:36, Tim+ wrote:
John Rumm wrote: On 12/11/2016 15:15, Tim+ wrote: wrote: On Sat, 12 Nov 2016 13:00:32 +0000, John Rumm wrote: You have a setup that was really conceived as a way of gaining efficiency on systems with a demand for low flow temps (i.e. UFH) and a fixed output non condensing boiler. As addition benefits it allows high delivery rates of mains pressure DHW without being limited to the instantaneous power available from your gas/oil supply, and makes it easy to incorporate multiple sources of heat into a system. Not being much good at plumbing but having some experience of thermal stores: My first point is that it's far better to store the energy as natural gas and only convert it to heat as you need it. So the OP's system has a heat store for the two reasons John has discussed 1) to deliver more instantaneous hot water than the boiler can supply from the top part of the thermal store that, I assume this goes through a plate heat exchanger so returns to the bottom of the store at near ambient? Water from the main tends to be around 10C here. 2) To allow a blending valve to take water from the top of the thermal store but under the part reserved for DHW, mix it with water going around the under floor circuit and then return is at around 25C to the bottom of the tank. The need is always to return water below about 40C to the boiler to keep it in condensing mode? My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? The demand for underfloor heating then being sensed when the blender valve input from the thermal store falls below the set underfloor temperature it can maintain? The boiler then heats the whole of the tank until it starts drawing water above 40 C from the bottom of the tank? The system I used to service a pellet boiler on in a block of flats in Brixton failed to maintain stratification because the flows where so high they constantly mixed the store's contents. I advocated a possible solution but the german makers of the thermal store would not countenance it. It seems an awfully complicated way of meeting two very different demands. Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? Only if you like hot water dribbling from the taps ;-) A bit unfair on instantaneous water heaters. For sure not going to match the best output of a stored water solution but more than adequate for many folk who don't run a bath too often. Yup fair point, It was intended more of a "in comparison to what the thermal store can deliver", rather than in absolute terms. Many multipoints are only about 24kW though - so 9 lpm of hot water. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#31
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
John Rumm wrote:
On 12/11/2016 20:36, Tim+ wrote: A bit unfair on instantaneous water heaters. For sure not going to match the best output of a stored water solution but more than adequate for many folk who don't run a bath too often. Yup fair point, It was intended more of a "in comparison to what the thermal store can deliver", rather than in absolute terms. Many multipoints are only about 24kW though - so 9 lpm of hot water. Okay, not a multipoint then, just a big combi. ;-) Tim -- Please don't feed the trolls |
#32
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 12/11/2016 15:15, Tim+ wrote:
It seems an awfully complicated way of meeting two very different demands. Wouldn't two boilers be simpler/cheaper? Condensing multipoint for HW and standard condensing boiler for CH? Tim Certianly not in may case Certainly not in may case as single boiler already installed... In general the store is not particularly expensive .. and in my case I also dump all spare electrically generated power form my Solar PV array .... very easy to mix any heat source as the store is just a storage battery. It also provides a very large buffer - so if tehre is demand for a lot of heat for heating or DHW .... don't have to wait ... it's there and immediate. |
#33
Posted to uk.d-i-y
|
|||
|
|||
Setting up boiler for optimum efficiency
On 12/11/2016 19:20, John Rumm wrote:
The need is always to return water below about 40C to the boiler to keep it in condensing mode? Below 54 is ideal... My thoughts are on how well the thermal store remains stratified or is the flow too great such that it induces a lot of turbulence? If it remains stratified then why can the boiler not be set to burn if the DHW reserve falls below a high set temperature, whilst still drawing cool water from the bottom of the tank? You can tweak these things by selecting where you sense the temperature of the store. You can also use two stats some distance apart to increase the hysteresis and hence boiler run time to get larger more efficient recharges. The issue is the stratification is there with the horizontal baffle in the store .. but once you start running DHW the pump on the primaries is operated to 'stir the store' ondoing any stratification. I have 'improved' things with a delay .. DHW has to be running for 45sec before pump will start ...... which prevent lots of small runs. |