Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on. When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!

What is the most common/likely cause of this symptom?

Thanks
Biggles
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Biasi 24S Boiler Problem

On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on.


Had he run the heating ok before the rad move?

When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.


So have you checked that the call for heat from the stat is actually
getting to the boiler?

Does the boiler attempt to light (i.e. you hear the fan spin up, perhaps
clicks from the igniter?)

Does it still produce hot water on demand ok?

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!


Broken lights don't usually work so good ;-)

What is the most common/likely cause of this symptom?


I think we need a bit more diagnostic info first.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 81
Default Biasi 24S Boiler Problem

On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on.


Had he run the heating ok before the rad move?


No but the hot water ran OK, now it doesn't, or rather the pump comes on
but the boiler doesn't fire up.

When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.


So have you checked that the call for heat from the stat is actually
getting to the boiler?

Not exactly but as the pump comes on it suggests the call for heat is
getting there.

Does the boiler attempt to light (i.e. you hear the fan spin up, perhaps
clicks from the igniter?)

My son says not, it doesn't appear to do anything, just starts the pump.

Does it still produce hot water on demand ok?

No, doesn't produce hot water or heating.

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!


Broken lights don't usually work so good ;-)

What is the most common/likely cause of this symptom?


I think we need a bit more diagnostic info first.

Fair comment, I'm 150 miles away and although he is a qualified
Mechanical Engineer he has no experience of domestic heating systems.

It seems somewhat of a coincidence that the hot water has become faulty
about the same time as he removed the radiator, but it may be unrelated.

I'm wondering whether a full service might sort it out - dirty sensors
etc? Puzzled as to why resetting the boiler makes the system work OK for
a while though.
--
Biggles
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Biasi 24S Boiler Problem

On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on.


Had he run the heating ok before the rad move?


No but the hot water ran OK, now it doesn't, or rather the pump comes on
but the boiler doesn't fire up.

When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.


So have you checked that the call for heat from the stat is actually
getting to the boiler?

Not exactly but as the pump comes on it suggests the call for heat is
getting there.

Does the boiler attempt to light (i.e. you hear the fan spin up, perhaps
clicks from the igniter?)

My son says not, it doesn't appear to do anything, just starts the pump.


The boiler will go through an ignition sequence with a number of proving
steps. Running the pump will be one. But others like detecting adequate
airflow from the fan, adequate primary system pressure etc will also
need to be proved before it gets as far as attempting ignition. Even
when it it will need to prove the flame, and then check the overheat
stats etc.

Does it still produce hot water on demand ok?

No, doesn't produce hot water or heating.

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!


Broken lights don't usually work so good ;-)

What is the most common/likely cause of this symptom?


I think we need a bit more diagnostic info first.

Fair comment, I'm 150 miles away and although he is a qualified
Mechanical Engineer he has no experience of domestic heating systems.

It seems somewhat of a coincidence that the hot water has become faulty
about the same time as he removed the radiator, but it may be unrelated.


The obvious one to check is there is enough primary system pressure...

I'm wondering whether a full service might sort it out - dirty sensors
etc? Puzzled as to why resetting the boiler makes the system work OK for
a while though.



--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,213
Default Biasi 24S Boiler Problem

On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002

I think we need a bit more diagnostic info first.

I'm wondering whether a full service might sort it out - dirty sensors
--
Biggles


Full service on a 14 year old Biasi (probably bought in B&Q with
unknown installation history) will probably result in much
sucking of teeth and mumbling about a replacement.


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 81
Default Biasi 24S Boiler Problem

John Rumm Wrote in message:
On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on.

Had he run the heating ok before the rad move?


No but the hot water ran OK, now it doesn't, or rather the pump comes on
but the boiler doesn't fire up.

When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.

So have you checked that the call for heat from the stat is actually
getting to the boiler?

Not exactly but as the pump comes on it suggests the call for heat is
getting there.

Does the boiler attempt to light (i.e. you hear the fan spin up, perhaps
clicks from the igniter?)

My son says not, it doesn't appear to do anything, just starts the pump.


The boiler will go through an ignition sequence with a number of proving
steps. Running the pump will be one. But others like detecting adequate
airflow from the fan, adequate primary system pressure etc will also
need to be proved before it gets as far as attempting ignition. Even
when it it will need to prove the flame, and then check the overheat
stats etc.

Does it still produce hot water on demand ok?

No, doesn't produce hot water or heating.

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!

Broken lights don't usually work so good ;-)

What is the most common/likely cause of this symptom?

I think we need a bit more diagnostic info first.

Fair comment, I'm 150 miles away and although he is a qualified
Mechanical Engineer he has no experience of domestic heating systems.

It seems somewhat of a coincidence that the hot water has become faulty
about the same time as he removed the radiator, but it may be unrelated.


The obvious one to check is there is enough primary system pressure...

As mentioned in my original post, system was re-pressurised to 1.2
bar after the rad was removed. It is still showing that pressure
when the boiler is failing to start. I assume thats what you mean
by "primary system pressure"?

--
Biggles


----Android NewsGroup Reader----
http://usenet.sinaapp.com/
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 81
Default Biasi 24S Boiler Problem

Andrew Wrote in message:
On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
I think we need a bit more diagnostic info first.

I'm wondering whether a full service might sort it out - dirty sensors
--
Biggles


Full service on a 14 year old Biasi (probably bought in B&Q with
unknown installation history) will probably result in much
sucking of teeth and mumbling about a replacement.


Are Biasi boilers crap then? Must admit I had never heard of
them.I think you may be on the right lines though, I'm not
getting a warm feeling about this (pun intended).
--
Biggles


----Android NewsGroup Reader----
http://usenet.sinaapp.com/
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Biasi 24S Boiler Problem

On 10/11/2016 23:42, Biggles wrote:
John Rumm Wrote in message:
On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
vintage.

For the first few days he only had the hot water switched on and it
seemed to work fine - plenty of really hot water.

Since then he has removed one of the radiators for decoration, then
repressurised the system (to 1.2 bar cold). Now with the heating
switched on, the boiler frequently fails to come on.

Had he run the heating ok before the rad move?

No but the hot water ran OK, now it doesn't, or rather the pump comes on
but the boiler doesn't fire up.

When this happens,
pressing the boiler reset button resolves the problem temporarily. He
has to reset the boiler about once or twice a day.

The red lockout lamp does not come on and he says he can hear the pump
running when the boiler fails to come on.

So have you checked that the call for heat from the stat is actually
getting to the boiler?
Not exactly but as the pump comes on it suggests the call for heat is
getting there.

Does the boiler attempt to light (i.e. you hear the fan spin up, perhaps
clicks from the igniter?)
My son says not, it doesn't appear to do anything, just starts the pump.


The boiler will go through an ignition sequence with a number of proving
steps. Running the pump will be one. But others like detecting adequate
airflow from the fan, adequate primary system pressure etc will also
need to be proved before it gets as far as attempting ignition. Even
when it it will need to prove the flame, and then check the overheat
stats etc.

Does it still produce hot water on demand ok?
No, doesn't produce hot water or heating.

We've had a look at the fault finding section of the service manual but
nothing really matches this set of symptoms - all of the fault
conditions which are resolved by resetting the boiler cause the red
fault light to come on. I guess it's just possible that the red fault
light is broken!

Broken lights don't usually work so good ;-)

What is the most common/likely cause of this symptom?

I think we need a bit more diagnostic info first.
Fair comment, I'm 150 miles away and although he is a qualified
Mechanical Engineer he has no experience of domestic heating systems.

It seems somewhat of a coincidence that the hot water has become faulty
about the same time as he removed the radiator, but it may be unrelated.


The obvious one to check is there is enough primary system pressure...

As mentioned in my original post, system was re-pressurised to 1.2
bar after the rad was removed. It is still showing that pressure
when the boiler is failing to start. I assume thats what you mean
by "primary system pressure"?


Yup... what does the manual say is the required pressure? Also are you
sure the pressure gauge is showing the right value?


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 25,191
Default Biasi 24S Boiler Problem

On 10/11/2016 23:45, Biggles wrote:
Andrew Wrote in message:
On 09/11/2016 18:32, Biggles wrote:
On 09/11/2016 11:34, John Rumm wrote:
On 09/11/2016 01:30, Biggles wrote:
Biasi 24S Combi Boiler

My son has just moved into his house which has a Biasi 24S boiler, 2002
I think we need a bit more diagnostic info first.
I'm wondering whether a full service might sort it out - dirty sensors
--
Biggles


Full service on a 14 year old Biasi (probably bought in B&Q with
unknown installation history) will probably result in much
sucking of teeth and mumbling about a replacement.


Are Biasi boilers crap then? Must admit I had never heard of
them.


They are at the cheap end of the market, and (last time I looked at one)
were still using quite old designs (with a secondary bolt on additional
heat exchanger on the condensing models). Having said that some of them
seem to last well enough, and the economics of "half the life", a "third
or quarter of the price" can still make sense.

I think you may be on the right lines though, I'm not
getting a warm feeling about this (pun intended).




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Biasi 24S Combi - Hot Water problem Keith UK diy 7 January 6th 18 04:44 PM
Biasi Boiler No DHW [email protected] UK diy 3 January 11th 07 09:46 PM
Biasi 24HE combi boiler any good? Chris Tomlinson UK diy 3 August 3rd 06 01:42 PM
DHW problem on a BIASI boiler [email protected] UK diy 2 November 22nd 05 11:24 AM
boiler fires on and off constantly - Biasi Riva Jon UK diy 4 July 18th 04 11:17 AM


All times are GMT +1. The time now is 06:13 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"