OT - Fitting RCD in household mains supply
"Michael Chare" wrote in message ...
[news:uk.d-i-y added and follow-up set to uk.d-i-y] | I am contemplating fitting an RCD (Residual Current Device / | Earth Leakage Relay ) in the power supply to my house between | the meter and the fuse box. Whole-house RCDs are deprecated and are contrary to the IEE wiring regulations. It is unacceptable to lose power to lighting and smoke alarm circuits in the event of an earth leakage on a power circuit. If you will google this subject on news:uk.d-i-y you will find anecdotal evidence that whole-house RCDs may cause more deaths through sudden lighting failure causing a person to fall, than are caused by electrocution annually. The only requirement for whole-house RCDs is in an installation with TT (earth electrode) earthing, when it should be a 100mA time-delay RCD and the power circuits should be protected by 30mA RCDs such that proper discrimination is obtained. RCD protection should be provided to power circuits either using a 'split load' Consumer Unit where the power circuits are run through a 30mA RCD but the lighting circuits are not, or through individual RCBOs for each circuit, which combine the functions of MCB and RCD. | The problem with doing this is that it could involve some hot wiring | which I dont much like. So I have some questions: | a) The safest procedure looks to be to pull out the Electricity Board | (or who ever they are now) Fuses but I would have to break the seals | and this might annoy them. I have never tried doing this, I just | assume that it is possible and reasonably easy. You should only have one service fuse, and the "board" don't usually mind too much if that is pulled. Ensure it is pulled and replaced when no current is flowing. | b) I could break the seals on the meter and disconnect the wires, | coming from it. Again this would no doubt annoy the Electricity Board, | but looks to be quite easy and would involve minimal hot wiring, and | I would not have to tamper with the fuses. This *will* annoy the electricity co and does not remove the need for hot wiring; you are still handling live terminals on the meter. If you were going to do this you should pull the main fuse, remove the meter tails from the existing CU and connect to the RCD supply terminals, and provide new meter tails from the RCD load terminals to the existing CU. You should not open the seals on the meter. | I would happily post in a more relevant news group if I could find one. copied to and follow-ups set to uk.d-i-y That ng has an extensive FAQ section at http://www.diyfaq.org.uk/ Owain |
#2
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Mon, 15 Dec 2003 20:21:16 UTC, "Owain"
wrote: You should only have one service fuse, and the "board" don't usually mind too much if that is pulled. Ensure it is pulled and replaced when no current is flowing. And cover up the exposed terminals while you're working - you do NOT want to touch the exposed supply-side one, nor drop anything into it.... -- Bob Eager rde at tavi.co.uk PC Server 325*4; PS/2s 9585, 8595, 9595*2, 8580*3, P70... |
#3
|
|||
|
|||
OT - Fitting RCD in household mains supply
Whole-house RCDs are deprecated and are contrary to the IEE wiring
regulations. It is unacceptable to lose power to lighting and smoke alarm circuits in the event of an earth leakage on a power circuit. If you will google this subject on news:uk.d-i-y you will find anecdotal evidence that whole-house RCDs may cause more deaths through sudden lighting failure causing a person to fall, than are caused by electrocution annually. Our CU is a split load, the sockets are run off a 100A/30mA RCD (Via MCB's) The lighting is run off a 40A/30mA RCD, again via MCB's This was apparently installed when it became apparent I was very interested in electricity at a very early age! Is this arrangement not allowed, as IMHO there is more risk of electrocution when some dopey tw*t tries to change the dead bulb with the switch still on than the same dopy tw*t unplugging something when it is switched on! If someone was up a ladder, using a power drill for example, and the drill caused an earth fault, the sockets RCD would trip, leaving the lights on in my setup. Just my thoughts here... Sparks... |
#4
|
|||
|
|||
OT - Fitting RCD in household mains supply
If someone was up a ladder, using a power drill for example, and the drill
caused an earth fault, the sockets RCD would trip, leaving the lights on in my setup. Personally, I'd remove the lighting RCD. Even with it on, you'll still get enough jolt to knock you off the ladder, and you are unlikely to electrocute yourself with a pendant fitting. Loss of a lighting circuit can be very dangerous, especially in a fire, or whilst in a dangerous position, such as up a ladder. Christian. |
#5
|
|||
|
|||
OT - Fitting RCD in household mains supply
| I am contemplating fitting an RCD (Residual Current Device /
| Earth Leakage Relay ) in the power supply to my house between | the meter and the fuse box. Often, the easiest way to add RCD protection to an existing installation (using DIN rail CU) is to replace socket circuit MCBs with single width RCBOs, if they are available. It isn't necessarily the cheapest way, although if there are only 1 or 2 circuits to be protected, it can still be cost effective. It is certainly the best way to do it, however many ways there are. Christian. |
#6
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 00:37:33 -0000, "Sparks"
wrote: Is this arrangement not allowed, as IMHO there is more risk of electrocution when some dopey tw*t tries to change the dead bulb with the switch still on than the same dopy tw*t unplugging something when it is switched on! It is a classic example of the original specifier not understanding risk at all and making things more dangerous by installing "safety" measures. Putting an RCD in stops you being electrocuted whilst changing a light bulb. As far as I can find out the number of people killed or admitted to hospital from domestic premises in the UK for this reason in the last 10 years is precisely zero. On the other hand in the same period hundreds have died and thousands been injured in fires at night. Many more have been killed or injured in falls down stairs at night. Lighting RCD's regularly trip if a bulb blows (especially on switch on) and trip very quickly in a fire as combustion products create leakage paths in wiring. Both circumstances create risks considerably greater than the trivial one of electrocution while changing a bulb. The last thing you want in a fire at night is the lights going out on you. -- Peter Parry. http://www.wpp.ltd.uk/ |
#7
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message ... Putting an RCD in stops you being electrocuted whilst changing a light bulb. As far as I can find out the number of people killed or admitted to hospital from domestic premises in the UK for this reason in the last 10 years is precisely zero. Well, the only person I know personally who's received a serious electric shock at home received it from a wall-mounted (i.e. fixed) light fitting, while she was changing a light bulb. On the other hand in the same period hundreds have died and thousands been injured in fires at night. Many more have been killed or injured in falls down stairs at night. Lighting RCD's regularly trip if a bulb blows (especially on switch on) No they don't, that's the MCBs which trip. And *their* installation is considered to be a good thing. and trip very quickly in a fire as combustion products create leakage paths in wiring. Both circumstances create risks considerably greater than the trivial one of electrocution while changing a bulb. The last thing you want in a fire at night is the lights going out on you. I think that to form a balanced opinion at this point, we also need to know what proportion of fires are caused by electrical faults which might have been detected by an RCD. I've just spent 9 years living in a house with a 30mA RCD covering the lot, with a 6A MCB on the lighting circuit. The former is frowned upon, the latter is supposed to be good. The former *never* tripped except when there was a fault on an appliance. The latter tripped on probably 60% of bulb failures, as often as not requiring a journey downstairs in the dark (have you seen the number of people that die in stair-falls) to reset the breaker. If suddenly plunging a house into darkness is a dangerous, then so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. You're very acurately restating uk.d-i-y received wisdom on the subject (as a grandee, perhaps you're the origin of it :-), but it doesn't match my experience. Will |
#8
|
|||
|
|||
OT - Fitting RCD in household mains supply
If suddenly plunging a house into darkness is a dangerous, then
so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. No, it is incandescent light bulbs which are dangerous and should be banned. Lighting circuits intended to have incandescent monstrosities may be better equiped with a 5A cartridge fuse holder (and supply of fuses). Christian. |
#9
|
|||
|
|||
OT - Fitting RCD in household mains supply
Putting an RCD in stops you being electrocuted whilst changing a
light bulb. As far as I can find out the number of people killed or admitted to hospital from domestic premises in the UK for this reason in the last 10 years is precisely zero. Well, the only person I know personally who's received a serious electric shock at home received it from a wall-mounted (i.e. fixed) light fitting, while she was changing a light bulb. I too know of someone who did the exact same thing - they were thrown across the room (No RCD) On the other hand in the same period hundreds have died and thousands been injured in fires at night. Many more have been killed or injured in falls down stairs at night. Lighting RCD's regularly trip if a bulb blows (especially on switch on) No they don't, that's the MCBs which trip. And *their* installation is considered to be a good thing. Same here, out RCD has never tripped when a bulb has popped - The MCB's do The blowing of the bulb causes over current, not leakage. and trip very quickly in a fire as combustion products create leakage paths in wiring. Both circumstances create risks considerably greater than the trivial one of electrocution while changing a bulb. The last thing you want in a fire at night is the lights going out on you. I think that to form a balanced opinion at this point, we also need to know what proportion of fires are caused by electrical faults which might have been detected by an RCD. I've just spent 9 years living in a house with a 30mA RCD covering the lot, with a 6A MCB on the lighting circuit. The former is frowned upon, the latter is supposed to be good. I would always have a seperate MCB on the lights, especially if there were inquisative kids about. Is it a requirement to have no RCD, or is it mearly a suggestion? (Not that it's getting changed anyway) I fell there is far more risk of someone poking their fingers in the fitting while it is on, then there is of a fire breaking out - how often are [regular GLS] bulbs changed compaired to how many times fires break out in a house? The former *never* tripped except when there was a fault on an appliance. The latter tripped on probably 60% of bulb failures, as often as not requiring a journey downstairs in the dark (have you seen the number of people that die in stair-falls) to reset the breaker. If suddenly plunging a house into darkness is a dangerous, then so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. I have installed an emergancy light in the cupboard where the breakers are, If the lighting trips (or there is a power cut) this illuminates Sparks... |
#10
|
|||
|
|||
OT - Fitting RCD in household mains supply
I fell there is far more risk of someone poking their fingers in
the fitting while it is on, then there is of a fire breaking out how often are [regular GLS] bulbs changed compaired to how many times fires break out in a house? Yes, but the shock is rarely fatal or injurous, just painful and embarassing. The nature of the fitting doesn't lend it to maintaining a solid grip on you long enough to cause electrocution. And quick frankly, if you electrocute yourself changing a bulb, you're probably capable of removing yourself from the gene pool in a much more spectacular fashion. The reason not to install an RCD is because lights failing is a demonstrable and measurable cause of death either during house fires, or from sudden darkness during a dangerous task (such as operating machinery, or balancing on ladders). Electrocution from changing light bulbs doesn't figure in the statistics. Christian. |
#11
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Christian McArdle" wrote in message
. net... I fell there is far more risk of someone poking their fingers in the fitting while it is on, then there is of a fire breaking out how often are [regular GLS] bulbs changed compaired to how many times fires break out in a house? Yes, but the shock is rarely fatal or injurous, just painful and embarassing. The nature of the fitting doesn't lend it to maintaining a solid grip on you long enough to cause electrocution. ....just imagining frail old lady holding [Earthed] wall light to steady herself with one hand, and attempting to get the new bulb in with the other, and decides as she cant see the hole (its above her head) she fells around for it with her hand. It must happen... And quick frankly, if you electrocute yourself changing a bulb, you're probably capable of removing yourself from the gene pool in a much more spectacular fashion. Well, it ain't always me that changes light bulbs, if you get my drift The reason not to install an RCD is because lights failing is a demonstrable and measurable cause of death either during house fires, or from sudden darkness during a dangerous task (such as operating machinery, or balancing on ladders). Electrocution from changing light bulbs doesn't figure in the statistics. That's why there are two RCD's - one for the lights, and a separate one for the sockets (and an emergency light above the CU!) Christian. |
#12
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 16:22:40 -0000, "Will Dean"
wrote: "Peter Parry" wrote Well, the only person I know personally who's received a serious electric shock at home received it from a wall-mounted (i.e. fixed) light fitting, while she was changing a light bulb. Basing a judgement of low probability events on personal experience is never wise. On the other hand in the same period hundreds have died and thousands been injured in fires at night. Many more have been killed or injured in falls down stairs at night. Lighting RCD's regularly trip if a bulb blows (especially on switch on) No they don't, that's the MCBs which trip. And *their* installation is considered to be a good thing. RCD's regularly trip when bulbs blow. I think that to form a balanced opinion at this point, we also need to know what proportion of fires are caused by electrical faults which might have been detected by an RCD. Not very many. About 20 deaths a year are caused by fires where the cause is known after proper investigation to be an electrical fault. This is about 4% of the total who die in house fires. The following are based on 1999 figures from the Home Office. The number of people killed or severely injured by electrocution in domestic accidents the UK each year is very small. Even if you include accidents which are not electrocution but attributable to it (such as falling off a ladder after touching a live cable) the numbers involved in domestic accidents are still small, about 25 deaths and 2000 injuries of all severities (compare this with 70 deaths and 40,000 injuries caused by general DIY activities). Those figures have not reduced since whole house RCD's started to be used although the number of electrocutions in the garden (listed separately in the figures) has fallen. The total number of people killed in accidents in the home each year is about 4,000, of this roughly half are due to falls and about 1,000 due to falls down stairs. The number of people killed or injured in house fires is also depressingly large, many times greater than those killed by electrocution. Typically 500 people die and 18,000 are seriously injured each year by fire in the home. Of these deaths about 20 are attributable to electrical fires some of which an RCD might have prevented. The remainder are caused by non-electrical ignition. Of the 4,000 people killed in both falls and fires each year there is no easily available breakdown of contributory factors. However some police and fire reports do give further information. Of these I have seen only a very small number from one area, however within these there were a significant minority, probably about 10-20 which mentioned that lights were out and could not be turned back on from the light switch when the emergency services arrived. Only one or two of these, usually fire service reports, specifically mention RCD's having tripped. Nonetheless it is reasonable to infer even from this imperfect data that the number of people killed in falls and fires in which tripped RCD's were the cause or a major contributory factor is significantly higher than the number of people protected by them _in the home_. In the garden or garage is quite another matter. I've just spent 9 years living in a house with a 30mA RCD covering the lot, with a 6A MCB on the lighting circuit. The former is frowned upon, the latter is supposed to be good. The former *never* tripped except when there was a fault on an appliance. Of the 20 odd houses I have lived in most had 30mA RCD's covering everything and the majority of those would quite consistently knock everything off at the slightest provocation and especially if bulbs failed. The latter tripped on probably 60% of bulb failures, as often as not requiring a journey downstairs in the dark (have you seen the number of people that die in stair-falls) to reset the breaker. If suddenly plunging a house into darkness is a dangerous, then so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. You're very acurately restating uk.d-i-y received wisdom on the subject (as a grandee, perhaps you're the origin of it :-), Indeed I suspect I am. but it doesn't match my experience. My experience is of lifting the burnt corpses of family out of the way of the locked front door they had died against while trying to break it down to escape the fire which killed them. The key was on the floor under the body of the youngest child, the door was covered in blood from their hands. By the time they were found there was no consumer unit remaining but the neighbours all said they had seen no lights on in the house as the fire developed. Did they die because of the fathers love of securely locking the doors or because they couldn't see where the key fell? I don't even know if the house was fitted with an RCD but in view of the date and the fact it was a renovated council property I suspect it had a single whole house 30mA RCD. However, as I said earlier, relying upon personal experience is unwise. The reason I won't have RCD's on lighting circuits in the house (now I have a choice) is based upon evidence, not experience. -- Peter Parry. http://www.wpp.ltd.uk/ |
#13
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003, Christian McArdle wrote:
Loss of a lighting circuit can be very dangerous, especially in a fire, or whilst in a dangerous position, such as up a ladder. Seems to me that the obvious solution is to have whole-house RCD protection and install battery-backed emergency luminaires at e.g. stair wells. The ultra-cautious could have 30mA RCBOs protecting each circuit separately. -- Alistair Riddell - BOFH Microsoft - because god hates us |
#14
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote RCD's regularly trip when bulbs blow. They shouldnt, as RCD's will trip only if there is an imbalance between the live and the nuterual, when a bulb blows, it causes an overcurrent, this is when the MCB's trip as there is no earth inside the bulb, there cant be an imbalance. Of the 20 odd houses I have lived in most had 30mA RCD's covering everything and the majority of those would quite consistently knock everything off at the slightest provocation and especially if bulbs failed. This is not good, as has been previously mentioned - I still cant understand why an RCD is tripping on a bulb failure..(maybe it is faulty, or is under rated?) The latter tripped on probably 60% of bulb failures, as often as not requiring a journey downstairs in the dark (have you seen the number of people that die in stair-falls) to reset the breaker. If suddenly plunging a house into darkness is a dangerous, then so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. Just out of interest, why not? Do you mean fir CFL's, or am i missing the point here! .. My experience is of lifting the burnt corpses of family out of the way of the locked front door they had died against while trying to break it down to escape the fire which killed them. The key was on the floor under the body of the youngest child, the door was covered in blood from their hands. By the time they were found there was no consumer unit remaining but the neighbours all said they had seen no lights on in the house as the fire developed. Did they die because of the fathers love of securely locking the doors or because they couldn't see where the key fell? I don't even know if the house was fitted with an RCD but in view of the date and the fact it was a renovated council property I suspect it had a single whole house 30mA RCD. We have already agreed that a whole house RCD is bad. This is NOT what I am suggesting here! Sparks... |
#15
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message
... RCD's regularly trip when bulbs blow. This is not my experience either. Can you propose a mechanism for this? The only one which comes to mind would be that you already had a neutral-earth leakage fault, and the rise in neutral current caused by the bulb-failure arc was sufficient to create a leak to earth. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. It wouldn't matter what kind of lamp illuminated the stairs if the lighting circuit had tripped. My experience is of lifting the burnt corpses of family out of the way of the locked front door they had died against while trying to break it down to escape the fire which killed them. The key was on the floor under the body of the youngest child, the door was covered in blood from their hands. By the time they were found there was no consumer unit remaining but the neighbours all said they had seen no lights on in the house as the fire developed. Did they die because of the fathers love of securely locking the doors or because they couldn't see where the key fell? I don't even know if the house was fitted with an RCD but in view of the date and the fact it was a renovated council property I suspect it had a single whole house 30mA RCD. Yes, but you're a (former?) member of the emergency services, aren't you? As such, I have every sympathy with the gruesome sights you might have had to deal with in your chosen profession, but I do believe that members of such services are uniquely *ill* placed to give general advice about risks to ordinary people. To a fireman, a horrible death in a house fire is a common occurence - to me, as a resident of a non-smoking household, it's extremely unlikely to be the cause of my, or my family's demise. Personally, if I'm doing the neurotic parent bit I worry about road safety a darn sight more. However, as I said earlier, relying upon personal experience is unwise. The reason I won't have RCD's on lighting circuits in the house (now I have a choice) is based upon evidence, not experience. TBH, if you know of a property that has an RCD which trips when light bulbs blow, then you ought to advice the occupants to get the wiring fixed. Will |
#16
|
|||
|
|||
OT - Fitting RCD in household mains supply
Well said Peter. You are probably a voice in the wilderness, like that
chief inspector who categorically stated that 'excess speed is the cause of less than 7% of accidents' and 'speed cameras do not (statistically) reduce road deaths'. I am definitely with you on this. My 30mA RCD tripped about 50% of the time when any bulb blew, with the MCB about 60%. Sometimes both. Its bloody dangerous feeling down te saircase to get to the consumer unit, especialy if you have left the casing off...:-) Peter Parry wrote: On Tue, 16 Dec 2003 16:22:40 -0000, "Will Dean" wrote: "Peter Parry" wrote Well, the only person I know personally who's received a serious electric shock at home received it from a wall-mounted (i.e. fixed) light fitting, while she was changing a light bulb. Basing a judgement of low probability events on personal experience is never wise. On the other hand in the same period hundreds have died and thousands been injured in fires at night. Many more have been killed or injured in falls down stairs at night. Lighting RCD's regularly trip if a bulb blows (especially on switch on) No they don't, that's the MCBs which trip. And *their* installation is considered to be a good thing. RCD's regularly trip when bulbs blow. I think that to form a balanced opinion at this point, we also need to know what proportion of fires are caused by electrical faults which might have been detected by an RCD. Not very many. About 20 deaths a year are caused by fires where the cause is known after proper investigation to be an electrical fault. This is about 4% of the total who die in house fires. The following are based on 1999 figures from the Home Office. The number of people killed or severely injured by electrocution in domestic accidents the UK each year is very small. Even if you include accidents which are not electrocution but attributable to it (such as falling off a ladder after touching a live cable) the numbers involved in domestic accidents are still small, about 25 deaths and 2000 injuries of all severities (compare this with 70 deaths and 40,000 injuries caused by general DIY activities). Those figures have not reduced since whole house RCD's started to be used although the number of electrocutions in the garden (listed separately in the figures) has fallen. The total number of people killed in accidents in the home each year is about 4,000, of this roughly half are due to falls and about 1,000 due to falls down stairs. The number of people killed or injured in house fires is also depressingly large, many times greater than those killed by electrocution. Typically 500 people die and 18,000 are seriously injured each year by fire in the home. Of these deaths about 20 are attributable to electrical fires some of which an RCD might have prevented. The remainder are caused by non-electrical ignition. Of the 4,000 people killed in both falls and fires each year there is no easily available breakdown of contributory factors. However some police and fire reports do give further information. Of these I have seen only a very small number from one area, however within these there were a significant minority, probably about 10-20 which mentioned that lights were out and could not be turned back on from the light switch when the emergency services arrived. Only one or two of these, usually fire service reports, specifically mention RCD's having tripped. Nonetheless it is reasonable to infer even from this imperfect data that the number of people killed in falls and fires in which tripped RCD's were the cause or a major contributory factor is significantly higher than the number of people protected by them _in the home_. In the garden or garage is quite another matter. I've just spent 9 years living in a house with a 30mA RCD covering the lot, with a 6A MCB on the lighting circuit. The former is frowned upon, the latter is supposed to be good. The former *never* tripped except when there was a fault on an appliance. Of the 20 odd houses I have lived in most had 30mA RCD's covering everything and the majority of those would quite consistently knock everything off at the slightest provocation and especially if bulbs failed. The latter tripped on probably 60% of bulb failures, as often as not requiring a journey downstairs in the dark (have you seen the number of people that die in stair-falls) to reset the breaker. If suddenly plunging a house into darkness is a dangerous, then so are typical 6A type-I (B, nowadays) MCBs on lighting circuits. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. You're very acurately restating uk.d-i-y received wisdom on the subject (as a grandee, perhaps you're the origin of it :-), Indeed I suspect I am. but it doesn't match my experience. My experience is of lifting the burnt corpses of family out of the way of the locked front door they had died against while trying to break it down to escape the fire which killed them. The key was on the floor under the body of the youngest child, the door was covered in blood from their hands. By the time they were found there was no consumer unit remaining but the neighbours all said they had seen no lights on in the house as the fire developed. Did they die because of the fathers love of securely locking the doors or because they couldn't see where the key fell? I don't even know if the house was fitted with an RCD but in view of the date and the fact it was a renovated council property I suspect it had a single whole house 30mA RCD. However, as I said earlier, relying upon personal experience is unwise. The reason I won't have RCD's on lighting circuits in the house (now I have a choice) is based upon evidence, not experience. |
#17
|
|||
|
|||
OT - Fitting RCD in household mains supply
Sparks wrote:
"Peter Parry" wrote RCD's regularly trip when bulbs blow. They shouldnt, as RCD's will trip only if there is an imbalance between the live and the nuterual, when a bulb blows, it causes an overcurrent, this is when the MCB's trip as there is no earth inside the bulb, there cant be an imbalance. You haven't thought it through. there is ALWAYS some neutral earth leakage. It occurs every time an oh so rigorously RFI suppressed switch mode power supply (TV, computer, monitor, LV lighting) or any suppresed motor is plugged into the circuits. Enough of these and the 30mA RCD is on a hair trigger. Any voltage surge and over she goes. Here it was a toss up whether the RCD. MCB, or both would go. Now with a 100mA RCD, its not gone since. Whether or not I install RCBO's in the few circuits the regs demand depends on the building inspector. Proper standrads of wiring and better plugs, sockets, and particularly the use of double insulation and plastic cases have done far far more to reduce shock hazard than RCD's. I can clearly remember getting shocks of metal fires, whose earthing wwas poor or nonexistent, and whose rubber coated wires frayed all too easily. Now we seldom have metal frames, and we don't have users installing their own plugs nuch either. Of the 20 odd houses I have lived in most had 30mA RCD's covering everything and the majority of those would quite consistently knock everything off at the slightest provocation and especially if bulbs failed. This is not good, as has been previously mentioned - I still cant understand why an RCD is tripping on a bulb failure..(maybe it is faulty, or is under rated?) I have just explained why. We have already agreed that a whole house RCD is bad. This is NOT what I am suggesting here! Actually, I think its quite good, provided it trips only when there is a significant dangerous fault. Its the nusiance tripping that is so serious. Sparks... |
#18
|
|||
|
|||
OT - Fitting RCD in household mains supply
Will Dean wrote:
"Peter Parry" wrote in message ... RCD's regularly trip when bulbs blow. This is not my experience either. Can you propose a mechanism for this? The only one which comes to mind would be that you already had a neutral-earth leakage fault, and the rise in neutral current caused by the bulb-failure arc was sufficient to create a leak to earth. There is always some leakage from both L & N to earth. If nothing else due to the capacitance between the miles of T & E laid over the house. And more especially in all the capacitors used to RFI filter electronic devices. There is always some inductance in the supply, due to cable lengths and transformer secondaries. High speed switching currents will work with the capacitances to flip RCDs |
#19
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 21:35:43 +0000, The Natural Philosopher
wrote: Well said Peter. You are probably a voice in the wilderness, like that chief inspector who categorically stated that 'excess speed is the cause of less than 7% of accidents' and 'speed cameras do not (statistically) reduce road deaths'. I am definitely with you on this. My 30mA RCD tripped about 50% of the time when any bulb blew, with the MCB about 60%. Sometimes both. Its bloody dangerous feeling down te saircase to get to the consumer unit, especialy if you have left the casing off...:-) Reading this, and especially the very sad ending to Peter's post makes me think that it would not be a bad idea to add emergency lighting as something that should be included in Building Regulations for new properties and incentivised for others in some way, especially for the elderly and others with mobility difficulties.. We already have mains powered smoke detectors as an addition, basically to get over people taking the batteries out or forgetting to replace them. Non-maintained small fluorescent lights are not very expensive, although the fittings are pretty ugly. Undoubtedly this could be improved if there were a consumer premises market for them. It would seem to me that the populace would be better served with a lighting measure like this rather than the mandatory low energy lamps stuff. In fact with a bit of creativity, both objectives could be met in a single package. I am not sure what sort of size and power level that they would need to be to provide sufficient light say at the top and bottom of a staircase in a fire, but to be able to see adequately during a power cut, then the little 8w ones are probably enough. I have my consumer unit at the back of a cupboard in the kitchen and it would not be easy to see in the dark. I fitted a small maintained fitting, run from a (non-RCD ptotected) lighting circuit and operated also by a plunger switch on the cupboard door. Thus I have a light over the CU for when I want to work on it with the power deliberately off and also to be able to see the breakers after a trip. ..andy To email, substitute .nospam with .gl |
#20
|
|||
|
|||
OT - Fitting RCD in household mains supply
RCD's regularly trip when bulbs blow.
They shouldnt, as RCD's will trip only if there is an imbalance between the live and the nuterual, when a bulb blows, it causes an overcurrent, this is when the MCB's trip as there is no earth inside the bulb, there cant be an imbalance. You haven't thought it through. there is ALWAYS some neutral earth leakage. It occurs every time an oh so rigorously RFI suppressed switch mode power supply (TV, computer, monitor, LV lighting) or any suppresed motor is plugged into the circuits. Enough of these and the 30mA RCD is on a hair trigger. Any voltage surge and over she goes. Where does this stray energy go? All LV Transformers I have seen only have L&N, no earth, so where does it go? Into capacitors?? Here it was a toss up whether the RCD. MCB, or both would go. Now with a 100mA RCD, its not gone since. What use is a 100mA RCD? You die with a 40mA shock, that's why they make them 30mA We have already agreed that a whole house RCD is bad. This is NOT what I am suggesting here! Actually, I think its quite good, provided it trips only when there is a significant dangerous fault. Just like a split load would, but it would only take out the faulty section, not the whole lot. (If it took out the lighing, then there are still table lamps!) Its the nusiance tripping that is so serious. Well I have NEVER had one single nuisance trip on my lighting RCD, and it has been in since the 1980's It has never tripped when a bulb has blown - the only time it did trip was when some dickhead drilled through a cable (A builder, NOT me!!) We did however have a fault develop with our "sockets" RCD, this was then tested (along with the lighting one) and it was found to be defective (over sensitive) Sparks... |
#21
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 17:53:52 -0000, "Sparks"
wrote: "Christian McArdle" wrote ...just imagining frail old lady holding [Earthed] wall light to steady herself with one hand, and attempting to get the new bulb in with the other, and decides as she cant see the hole (its above her head) she fells around for it with her hand. It must happen... Possibly it does, an insignificant number of times. Many more fall down the stairs or perish in fires. The reason not to install an RCD is because lights failing is a demonstrable and measurable cause of death either during house fires, or from sudden darkness during a dangerous task (such as operating machinery, or balancing on ladders). Electrocution from changing light bulbs doesn't figure in the statistics. That's why there are two RCD's - one for the lights, and a separate one for the sockets (and an emergency light above the CU!) How exactly does this stop the lights going out when you need them most? -- Peter Parry. http://www.wpp.ltd.uk/ |
#22
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 18:54:40 -0000, "Sparks"
wrote: "Peter Parry" wrote RCD's regularly trip when bulbs blow. They shouldnt, as RCD's will trip only if there is an imbalance between the live and the nuterual, when a bulb blows, it causes an overcurrent, this is when the MCB's trip as there is no earth inside the bulb, there cant be an imbalance. Of course there can be, and is. You are forgetting what happens when a bulb goes and the effects of inductance. You are also forgetting the effect of sensitisation by unbalanced noise filters. Indeed it is questionable if simple 30mA protected power circuits have any future because of this alone. Of the 20 odd houses I have lived in most had 30mA RCD's covering everything and the majority of those would quite consistently knock everything off at the slightest provocation and especially if bulbs failed. This is not good, as has been previously mentioned - I still cant understand why an RCD is tripping on a bulb failure..(maybe it is faulty, or is under rated?) Perfectly serviceable. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. Just out of interest, why not? Because their most common failure mode is fail on power on and they have poor reliability. Do you mean fir CFL's, or am i missing the point here! CFL, permanent low level lighting, whatever suits the need. We have already agreed that a whole house RCD is bad. This is NOT what I am suggesting here! Any RCD on the lighting circuit is bad, and it is that which you do appear to be suggesting. -- Peter Parry. http://www.wpp.ltd.uk/ |
#23
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 17:15:10 -0000, "Sparks"
wrote: I would always have a seperate MCB on the lights, especially if there were inquisative kids about. Unfortunate, they may figure in the Darwin awards one day. Is it a requirement to have no RCD, or is it mearly a suggestion? (Not that it's getting changed anyway) It is neither, the fitting of RCD's on lighting circuits is deprecated in the IEE regulations. There is no requirement to fit them on power circuits either - only on sockets which may be used by equipment used out of doors. Most electricians simply take the cheap and lazy way out. I fell there is far more risk of someone poking their fingers in the fitting while it is on, then there is of a fire breaking out - how often are [regular GLS] bulbs changed compaired to how many times fires break out in a house? The facts on deaths and injuries are plain and speak for themselves, I can't help it if you can't understand them. I have installed an emergancy light in the cupboard where the breakers are, If the lighting trips (or there is a power cut) this illuminates Oh good, that will be really useful in a fire. -- Peter Parry. http://www.wpp.ltd.uk/ |
#24
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 20:29:09 -0000, "Will Dean"
wrote: "Peter Parry" wrote in message .. . Can you propose a mechanism for this? The only one which comes to mind would be that you already had a neutral-earth leakage fault, and the rise in neutral current caused by the bulb-failure arc was sufficient to create a leak to earth. You don't need resistive leakage to trip an RCD and the problems of pre-sensitisation are become more acute as more equipment includes noise filters. As has been pointed out the danger is in using inappropriate lighting. If the design of the house or the condition of the occupants makes a fall likely don't fit incandescent bulbs in lights needed for safe navigation of stairs. It wouldn't matter what kind of lamp illuminated the stairs if the lighting circuit had tripped. Indeed not, that is why you chose a lighting type of high reliability whose failure mode is such that it would not trip protective circuits. Incandescent bulbs have poor reliability and less than optimal failure characteristics. My experience is of lifting the burnt corpses of family out of the way of the locked front door they had died against while trying to break it down to escape the fire which killed them. Yes, but you're a (former?) member of the emergency services, aren't you? No. As such, I have every sympathy with the gruesome sights you might have had to deal with in your chosen profession, but I do believe that members of such services are uniquely *ill* placed to give general advice about risks to ordinary people. Why? Because they understand the balance of risks better? To a fireman, a horrible death in a house fire is a common occurence Actually it isn't. - to me, as a resident of a non-smoking household, it's extremely unlikely to be the cause of my, or my family's demise. Personally, if I'm doing the neurotic parent bit I worry about road safety a darn sight more. Quite reasonable, but risk assessment is about how much work you have to put into circumventing a risk. Removing (or not fitting) an RCD on a lighting circuit is trivial and although the risk of fire is small the consequences are devastating and I suggest the minimal effort is worth it. TBH, if you know of a property that has an RCD which trips when light bulbs blow, then you ought to advice the occupants to get the wiring fixed. What's to fix? I can set up a demonstration to prove an RCD will trip on a bulb blowing on a perfectly serviceable circuit with ease. The point is that an RCD on a lighting circuit does no good at all but potentially may be very harmful, a situation recognised in the wiring regulations. What's the agrement for fitting them? -- Peter Parry. http://www.wpp.ltd.uk/ |
#25
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message ... That's why there are two RCD's - one for the lights, and a separate one for the sockets (and an emergency light above the CU!) How exactly does this stop the lights going out when you need them most? When are you specificlly talking about here? |
#26
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Tue, 16 Dec 2003 23:52:33 +0000, Peter Parry
wrote: It is neither, the fitting of RCD's on lighting circuits is deprecated in the IEE regulations. There is no requirement to fit them on power circuits either - only on sockets which may be used by equipment used out of doors. Most electricians simply take the cheap and lazy way out. I have seen this interpreted (annoyingly I can't remember where) as meaning that all ground floor sockets should be RCD protected. -- Niall |
#27
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message ... On Tue, 16 Dec 2003 20:29:09 -0000, "Will Dean" wrote: "Peter Parry" wrote in message .. . Can you propose a mechanism for this? The only one which comes to mind would be that you already had a neutral-earth leakage fault, and the rise in neutral current caused by the bulb-failure arc was sufficient to create a leak to earth. You don't need resistive leakage to trip an RCD and the problems of pre-sensitisation are become more acute as more equipment includes noise filters. I dont know enough about this to comment, only that as I have said before, in my installation (With incadecent, CFL and LV switchmodes) I have never had the RCD trip on a bulb failure (Including with 500w halogens) - So in my setup I really dont see the added risk. please explain why in my setup it wouldnt be... TBH, if you know of a property that has an RCD which trips when light bulbs blow, then you ought to advice the occupants to get the wiring fixed. What's to fix? I can set up a demonstration to prove an RCD will trip on a bulb blowing on a perfectly serviceable circuit with ease. The point is that an RCD on a lighting circuit does no good at all Sorry but I totally disagree with that statment. It will stop people getting killed by electrocution. but potentially may be very harmful, a situation recognised in the wiring regulations. What's the agrement for fitting them? Please explain, in a property where there are never any nucence tips, whay is it bad? Sparks... |
#28
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Andy Hall" wrote
| Non-maintained small fluorescent lights are not very expensive, | although the fittings are pretty ugly. Undoubtedly this could be | improved if there were a consumer premises market for them. Something like this: http://www.tlc-direct.co.uk/Products/HS724LE.html Smoke alarm, emergency light and Part L1 compliant. Owain |
#29
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Sparks" wrote in message .. . "Peter Parry" wrote in message ... On Tue, 16 Dec 2003 20:29:09 -0000, "Will Dean" wrote: "Peter Parry" wrote in message .. . Can you propose a mechanism for this? The only one which comes to mind would be that you already had a neutral-earth leakage fault, and the rise in neutral current caused by the bulb-failure arc was sufficient to create a leak to earth. You don't need resistive leakage to trip an RCD and the problems of pre-sensitisation are become more acute as more equipment includes noise filters. I dont know enough about this to comment, only that as I have said before, in my installation (With incadecent, CFL and LV switchmodes) I have never had the RCD trip on a bulb failure (Including with 500w halogens) - So in my setup I really dont see the added risk. please explain why in my setup it wouldnt be... TBH, if you know of a property that has an RCD which trips when light bulbs blow, then you ought to advice the occupants to get the wiring fixed. What's to fix? I can set up a demonstration to prove an RCD will trip on a bulb blowing on a perfectly serviceable circuit with ease. The point is that an RCD on a lighting circuit does no good at all Sorry but I totally disagree with that statment. It will stop people getting killed by electrocution. but potentially may be very harmful, a situation recognised in the wiring regulations. What's the agrement for fitting them? Please explain, in a property where there are never any nucence tips, whay is it bad? I'm quite prepared to be shot down in flames BUT I operate a wet area supplied via 30ma RCDs ...it has 3kw of halogen lighting - failure mode is water spray on tubes. it also has two water pumps many switchmodes many fractional HP motors a large compressor many incandescents several EMI filters many 240v 3 port valves which are damp and the only RCD trip we ever had was from a cable rupture in a pudle of water. MCBs pop often with incandescant failure but never the RCD (it's NICIEC tested regularly) |
#30
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Wed, 17 Dec 2003 01:07:44 -0000, "Owain"
wrote: "Andy Hall" wrote | Non-maintained small fluorescent lights are not very expensive, | although the fittings are pretty ugly. Undoubtedly this could be | improved if there were a consumer premises market for them. Something like this: http://www.tlc-direct.co.uk/Products/HS724LE.html Smoke alarm, emergency light and Part L1 compliant. Owain Hmm. Interesting pair of products. It would be good if one could have conventional lighting and switch in the fluorescent stuff when the power fails or the alarm goes off. The technical design seems well thought out though ..andy To email, substitute .nospam with .gl |
#31
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Wed, 17 Dec 2003 01:32:03 -0000, "Chris Oates" none wrote:
" I'm quite prepared to be shot down in flames BUT I operate a wet area supplied via 30ma RCDs ..it has 3kw of halogen lighting - failure mode is water spray on tubes. it also has two water pumps many switchmodes many fractional HP motors a large compressor many incandescents several EMI filters many 240v 3 port valves which are damp and the only RCD trip we ever had was from a cable rupture in a pudle of water. MCBs pop often with incandescant failure but never the RCD (it's NICIEC tested regularly) No shooting, but was is it? ..andy To email, substitute .nospam with .gl |
#32
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Christian McArdle" wrote in message . net... | I am contemplating fitting an RCD (Residual Current Device / | Earth Leakage Relay ) in the power supply to my house between | the meter and the fuse box. Often, the easiest way to add RCD protection to an existing installation (using DIN rail CU) is to replace socket circuit MCBs with single width RCBOs, if they are available. It isn't necessarily the cheapest way, although if there are only 1 or 2 circuits to be protected, it can still be cost effective. It is certainly the best way to do it, however many ways there are. cheapest way is to replace the CU switch with an RCD switch but then we don't want the light going out see separate thread for thaat |
#33
|
|||
|
|||
OT - Fitting RCD in household mains supply
Andy Hall wrote:
On Tue, 16 Dec 2003 21:35:43 +0000, The Natural Philosopher wrote: Well said Peter. You are probably a voice in the wilderness, like that chief inspector who categorically stated that 'excess speed is the cause of less than 7% of accidents' and 'speed cameras do not (statistically) reduce road deaths'. I am definitely with you on this. My 30mA RCD tripped about 50% of the time when any bulb blew, with the MCB about 60%. Sometimes both. Its bloody dangerous feeling down te saircase to get to the consumer unit, especialy if you have left the casing off...:-) Reading this, and especially the very sad ending to Peter's post makes me think that it would not be a bad idea to add emergency lighting as something that should be included in Building Regulations for new properties and incentivised for others in some way, especially for the elderly and others with mobility difficulties.. We already have mains powered smoke detectors as an addition, basically to get over people taking the batteries out or forgetting to replace them. Non-maintained small fluorescent lights are not very expensive, although the fittings are pretty ugly. Undoubtedly this could be improved if there were a consumer premises market for them. It would seem to me that the populace would be better served with a lighting measure like this rather than the mandatory low energy lamps stuff. In fact with a bit of creativity, both objectives could be met in a single package. I am not sure what sort of size and power level that they would need to be to provide sufficient light say at the top and bottom of a staircase in a fire, but to be able to see adequately during a power cut, then the little 8w ones are probably enough. I have my consumer unit at the back of a cupboard in the kitchen and it would not be easy to see in the dark. I fitted a small maintained fitting, run from a (non-RCD ptotected) lighting circuit and operated also by a plunger switch on the cupboard door. Thus I have a light over the CU for when I want to work on it with the power deliberately off and also to be able to see the breakers after a trip. Not a bad idea actually. However I am against having to add two provisions to fix what Peter has probably identified is a non existent problem. .andy To email, substitute .nospam with .gl |
#34
|
|||
|
|||
OT - Fitting RCD in household mains supply
Sparks wrote:
You haven't thought it through. there is ALWAYS some neutral earth leakage. It occurs every time an oh so rigorously RFI suppressed switch mode power supply (TV, computer, monitor, LV lighting) or any suppresed motor is plugged into the circuits. Enough of these and the 30mA RCD is on a hair trigger. Any voltage surge and over she goes. Where does this stray energy go? All LV Transformers I have seen only have L&N, no earth, so where does it go? Into capacitors?? Mmm. Ok, I'll take out the LV transformers. Bercause thinking about mine, they are alos two wrire devices. That is probably why they interfere so badly with radios. Here it was a toss up whether the RCD. MCB, or both would go. Now with a 100mA RCD, its not gone since. What use is a 100mA RCD? You die with a 40mA shock, that's why they make them 30mA Well it trips if you get a neutral ertha short, or some other appliance problem. Whether you die at 40mA is not an established yes and no type thing. Much less applied across the heart can stop it in a vulnerable subject: Much more applied across just a finger, will burn, but not kill. The problem with 30mA is its proneness to false triggering, especially applied to a whole house. The other issue is WHAT should be protected. Arguably the most dangerous circuit in the house is lighting, where you have potentially two user accesible terminals, and a (now rigorously earthed) metal housing in close proximity. Grab the housing with one hand, and stck yer other finger in the socket and Whazza! you are across the floor... We have already agreed that a whole house RCD is bad. This is NOT what I am suggesting here! Actually, I think its quite good, provided it trips only when there is a significant dangerous fault. Just like a split load would, but it would only take out the faulty section, not the whole lot. (If it took out the lighing, then there are still table lamps!) Not in my house. They have theor own lighting sockets on the relevant lighting circits. I like the idea of split loads, but Peter has made me rethink all of this. Frankly, I cannot see an ideal solution. I am very happy that the discussion continue - if a general consensus of best practice CAN be established, then a fait accompli could be presented to those who dream up building regs. Its the nusiance tripping that is so serious. Well I have NEVER had one single nuisance trip on my lighting RCD, and it has been in since the 1980's It has never tripped when a bulb has blown - the only time it did trip was when some dickhead drilled through a cable (A builder, NOT me!!) We did however have a fault develop with our "sockets" RCD, this was then tested (along with the lighting one) and it was found to be defective (over sensitive) Sparks... |
#35
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message
... It is neither, the fitting of RCD's on lighting circuits is deprecated in the IEE regulations. There is no requirement to fit them on power circuits either - only on sockets which may be used by equipment used out of doors. Most electricians simply take the cheap and lazy way out. There's often a requirement to fit one (a 100mA one) covering the whole of a TT installation. Will |
#36
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Wed, 17 Dec 2003 09:16:57 +0000, The Natural Philosopher
wrote: I am very happy that the discussion continue - if a general consensus of best practice CAN be established, then a fait accompli could be presented to those who dream up building regs. Like a few of us tried to do with proposed part P? Worth a try, I suppose, but the decision making is much more about politics and financial control than anything about technical merit. It kind of reminds me of the old joke were the boss is interviewing for a secretary, has three candidates with all kinds of skills but chooses the one with the biggest tits. ..andy To email, substitute .nospam with .gl |
#37
|
|||
|
|||
OT - Fitting RCD in household mains supply
"Peter Parry" wrote in message
... What's to fix? I can set up a demonstration to prove an RCD will trip on a bulb blowing on a perfectly serviceable circuit with ease. JOOI, can you describe the circuit? As I say, I have many years experience of non-nuisance-tripping 30mA whole-house RCDs, and always with a room full of computer equipment somewhere on the circit. The point is that an RCD on a lighting circuit does no good at all but potentially may be very harmful, a situation recognised in the wiring regulations. What's the agrement for fitting them? I'm not particularly arguing for the fitting of them against the regulations, only against the received wisdom that A. they'll give you lots of nuisance tripping, and B. that they're the major cause of nuisance tripping on lighting circuits. (Which we can all agree is a bad thing.) However, my experience of whole-house RCDs is that they've given warning of incipient problems, both with wiring and with appliances. For a start, they detect neutral-earth failures (which one would guess represent about 50% of insulation problems) which are not typically detected by overcurrent protection at all. They also give early warning of thinks like heater sheath failure in immersion heaters and electric showers - I don't consider myself odd in thinking that I'd like to know about an immersed heater failure while there's 50mA flowing to earth rather than 50A. And, like I say, I know someone personally who had a bad shock off a fixed light fitting, and a teenage girl in the village I went to school in was killed by an electric shock from a light fitting - her parents returned to the house after a holiday to find her dead on the living room floor. I'm afraid I interpret your gruesome anecdote as a warning about the way one locks ones house at night (not being clear that it has any link to lighting circuit RCDs, anyway), and mine as warnings about earth protection on wiring .. No doubt we both feel rather closer to our own cautionary tales. Will |
#38
|
|||
|
|||
OT - Fitting RCD in household mains supply
I have seen this interpreted (annoyingly I can't remember where)
as meaning that all ground floor sockets should be RCD protected. It is not explicitly stated as such. However, I think it is considered reasonable to assume that downstairs sockets can be used for outside equipment, unless specific alternative provision is made for outside equipment, such as a weatherproof RCD socket on each outside wall. However, you should protect all socket circuits. This isn't a requirement, but common sense. It is also common sense to ensure that it is on a different RCD to the outside sockets, as these are quite likely to trip in wet weather. Christian. |
#39
|
|||
|
|||
OT - Fitting RCD in household mains supply
What use is a 100mA RCD?
You die with a 40mA shock, that's why they make them 30mA Firstly, it usually takes about 200mA to be killed. Secondly, a 100mA RCD is not for supplementary direct protection. i.e. it is not intended to prevent electrocution when you touch the live. Its purpose is to rapidly disconnect the supply in the event of a minor earth fault, rather than relying on there being a massive earth fault. Circuits likely to require supplementary direct protection should use dedicated 30mA RCBOs for that circuit only. Whole house RCDs (except 100mA Type S) and even split load consumer units are a bodge. Christian. |
#40
|
|||
|
|||
OT - Fitting RCD in household mains supply
On Wed, 17 Dec 2003 01:06:06 -0000, "Sparks"
wrote: "Peter Parry" wrote What's to fix? I can set up a demonstration to prove an RCD will trip on a bulb blowing on a perfectly serviceable circuit with ease. The point is that an RCD on a lighting circuit does no good at all Sorry but I totally disagree with that statment. It will stop people getting killed by electrocution. People don't get killed by electrocution from lighting circuits. They may sometimes get a belt from them (which an RCD will reduce but won't prevent) but they do not cause death or injury. but potentially may be very harmful, a situation recognised in the wiring regulations. What's the agrement for fitting them? Please explain, in a property where there are never any nucence tips, whay is it bad? Because in a fire the lights all go out as the RCD trips. Electrocution in the home kills 25 people a year and causes 2000 minor and serious injuries. I only have access to detailed figures for 1998 and in that year none of the 23 deaths by electrocution involved lighting circuits - all bar 6 were people dismantling live equipment, the remaining 6 were handling faulty supply cords. In one year 500 people die and 18,000 are seriously injured in fires in the home. That's why the wiring regulations don't support fitting of RCDs to lighting circuits. -- Peter Parry. http://www.wpp.ltd.uk/ |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Generator Grounding | UK diy | |||
Earthing | UK diy | |||
Mains failure generator switching tips? | UK diy | |||
Old hot water tank fitting | UK diy |