Failed central heating valve?
Let me start by saying that central heating systems are a black art to me. Ours is a conventional oil fired boiler supplying DHW and three traditional wet radiator zones. Two zones are working, but the third is not, and has not been used for two or possibly three years. The zone valves are Honeywell, with a silver box on top, and having read that the protruding lever should have resistance when the heating is off, and no resistance when on, I have found the offending valve. There are three valves in total, presumably one for each zone. Just one pump, too. I've taken the top off the silver box (one screw) and can see the actuator, but beyond that? Will tapping the actuator or the valve or anything else release it? I guess it is stuck because it hasn't been used. Can the actuator be changed without water pouring out? -- Graeme |
#2
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
If you select "images" after typing honeywell 3 port actuator into
Yahoo, it should make things fairly clear. I believe the synchronous motor holds the valve position against the stop by means of a constant "stall current" which affects the reliability of the motor. The motor is available as a seperate item. AB On Sun, 11 Sep 2016 13:43:49 +0100, Graeme wrote: Let me start by saying that central heating systems are a black art to me. Ours is a conventional oil fired boiler supplying DHW and three traditional wet radiator zones. Two zones are working, but the third is not, and has not been used for two or possibly three years. The zone valves are Honeywell, with a silver box on top, and having read that the protruding lever should have resistance when the heating is off, and no resistance when on, I have found the offending valve. There are three valves in total, presumably one for each zone. Just one pump, too. I've taken the top off the silver box (one screw) and can see the actuator, but beyond that? Will tapping the actuator or the valve or anything else release it? I guess it is stuck because it hasn't been used. Can the actuator be changed without water pouring out? |
#3
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Archibald
Tarquin Blenkinsopp writes If you select "images" after typing honeywell 3 port actuator into Yahoo, it should make things fairly clear. My valves are 2 port not 3 port, but I see what you mean. Thank you. Thinking about it, just changing the actuator is not going to help if the valve itself has stuck. Bugger. -- Graeme |
#4
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
"Graeme" wrote in message
... In message , Archibald Tarquin Blenkinsopp writes If you select "images" after typing honeywell 3 port actuator into Yahoo, it should make things fairly clear. My valves are 2 port not 3 port, but I see what you mean. Thank you. Thinking about it, just changing the actuator is not going to help if the valve itself has stuck. Bugger. Well if you cannot open it manually then it is buggered. I assume that the programmer and stat are calling for heat. -- Adam |
#5
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 11-Sep-16 1:43 PM, Graeme wrote:
Let me start by saying that central heating systems are a black art to me. Ours is a conventional oil fired boiler supplying DHW and three traditional wet radiator zones. Two zones are working, but the third is not, and has not been used for two or possibly three years. The zone valves are Honeywell, with a silver box on top, and having read that the protruding lever should have resistance when the heating is off, and no resistance when on, I have found the offending valve. There are three valves in total, presumably one for each zone. Just one pump, too. I've taken the top off the silver box (one screw) and can see the actuator, but beyond that? Will tapping the actuator or the valve or anything else release it? I guess it is stuck because it hasn't been used. Can the actuator be changed without water pouring out? If you unclip the silver box (probably twist it) you will see the top of the valve. There's probably a prong sticking up. You should be able to free it up. It may well stay free until next summer. You can get kits to change the innards of the valve, but it does require draining down the system. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , ARW
writes "Graeme" wrote in message ... Thinking about it, just changing the actuator is not going to help if the valve itself has stuck. Bugger. Well if you cannot open it manually then it is buggered. But which part? The actuator or the valve? I assume that the programmer and stat are calling for heat. Yes. -- Graeme |
#7
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 14:02:31 +0100
Graeme wrote: In message , Archibald Tarquin Blenkinsopp writes If you select "images" after typing honeywell 3 port actuator into Yahoo, it should make things fairly clear. My valves are 2 port not 3 port, but I see what you mean. Thank you. Thinking about it, just changing the actuator is not going to help if the valve itself has stuck. Bugger. Let's go back to basics. You say that you have identified the offending valve. Do you mean that it should be powered, therefore open, and so should have no resistance on the manual lever, but that it does have resistance, indicating that it is still closed? If so, can you move the lever against the resistance, thereby opening the valve? There should be a little catch so that you can lock it in the open position. Does doing this allow hot water through the zone? If not, why do you think this is the defective valve? Approaching this logically should give us the answer. Do you have a voltmeter, and the ability to use it safely? I am not being funny, I don't want you to electrocute yourself. -- Davey. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
"Graeme" wrote in message
... In message , ARW writes "Graeme" wrote in message ... Thinking about it, just changing the actuator is not going to help if the valve itself has stuck. Bugger. Well if you cannot open it manually then it is buggered. But which part? The actuator or the valve? I assume that the programmer and stat are calling for heat. Yes. Well the simple test is to try the actuator whilst it is removed from the valve and see what happens. TBH if after removing the actuator, the valve spindle will not turn with the help of a pair of pliers then that is your answer. -- Adam |
#9
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Davey
writes Let's go back to basics. Excellent. You say that you have identified the offending valve. Do you mean that it should be powered, therefore open, and so should have no resistance on the manual lever, but that it does have resistance, indicating that it is still closed? It does have resistance whether or not the system is calling for heat. If so, can you move the lever against the resistance, thereby opening the valve? There should be a little catch so that you can lock it in the open position. Does doing this allow hot water through the zone? Yes! Why didn't I realise that? Anyway, yes, little catch locked, and rads heating. I could live with that, at least for a while. This zone heats four rads in what was our shop, attached to the side of our house. The shop is closed and the space will be my 'hobby room', so remembering to use that little catch to heat the place is acceptable if not perfect. Do you have a voltmeter, and the ability to use it safely? I am not being funny, I don't want you to electrocute yourself. grin I'm no electrician but yes, I have a small multimeter, and can use it for fairly straightforward stuff. -- Graeme |
#10
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 14:53:23 +0100
Graeme wrote: You say that you have identified the offending valve. Do you mean that it should be powered, therefore open, and so should have no resistance on the manual lever, but that it does have resistance, indicating that it is still closed? It does have resistance whether or not the system is calling for heat. Which indicates that the actuator is not functioning, for whatever reason, but the valve should be ok. If so, can you move the lever against the resistance, thereby opening the valve? There should be a little catch so that you can lock it in the open position. Does doing this allow hot water through the zone? Yes! Why didn't I realise that? Anyway, yes, little catch locked, and rads heating. I could live with that, at least for a while. This zone heats four rads in what was our shop, attached to the side of our house. The shop is closed and the space will be my 'hobby room', so remembering to use that little catch to heat the place is acceptable if not perfect. Good so far! Now we need to find out why the actuator is not working. Do you have a voltmeter, and the ability to use it safely? I am not being funny, I don't want you to electrocute yourself. grin I'm no electrician but yes, I have a small multimeter, and can use it for fairly straightforward stuff. You will really need a wiring diagram at this point. I expect that the valve and wiring look something like the one shown in the 'S' Plan: http://www.honeywelluk.com/documents/All/pdf/974.pdf This shows that the Brown and Blue wires are the power for the valve, so IF you can get the probes for the meter to these terminals, you should see 240 V AC across them. If they are unreachable, then find where the wires go to, there will most likely be a junction box of some kind within a few feet. Try there for the same thing, and report back. http://www.honeywelluk.com/documents...Issue%2016.pdf shows various Plans. -- Davey. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 15:30:40 +0100, Davey
wrote: On Sun, 11 Sep 2016 14:53:23 +0100 Graeme wrote: You say that you have identified the offending valve. Do you mean that it should be powered, therefore open, and so should have no resistance on the manual lever, but that it does have resistance, indicating that it is still closed? It does have resistance whether or not the system is calling for heat. Which indicates that the actuator is not functioning, for whatever reason, but the valve should be ok. If so, can you move the lever against the resistance, thereby opening the valve? There should be a little catch so that you can lock it in the open position. Does doing this allow hot water through the zone? Yes! Why didn't I realise that? Anyway, yes, little catch locked, and rads heating. I could live with that, at least for a while. This zone heats four rads in what was our shop, attached to the side of our house. The shop is closed and the space will be my 'hobby room', so remembering to use that little catch to heat the place is acceptable if not perfect. Good so far! Now we need to find out why the actuator is not working. Do you have a voltmeter, and the ability to use it safely? I am not being funny, I don't want you to electrocute yourself. grin I'm no electrician but yes, I have a small multimeter, and can use it for fairly straightforward stuff. You will really need a wiring diagram at this point. I expect that the valve and wiring look something like the one shown in the 'S' Plan: http://www.honeywelluk.com/documents/All/pdf/974.pdf This shows that the Brown and Blue wires are the power for the valve, so IF you can get the probes for the meter to these terminals, you should see 240 V AC across them. If they are unreachable, then find where the wires go to, there will most likely be a junction box of some kind within a few feet. Try there for the same thing, and report back. http://www.honeywelluk.com/documents...Issue%2016.pdf shows various Plans. Exactly right. If the lever moves back very slowly when released then the wet part of the valve is OK If there is 240vAC across the motor when the system is calling for heat on that zone then the motor is shagged. Does your valve have a removable head? The early ones didn't. In either case I wouldn't buy a replacement head or valve, as the synchronous motor is obtainable by itself. Generic ones should be under £10 delivered, I think I got my last ones from BES. If there isn't 240vAC across the motor then you need to look at the thermostat and switches that are dedicated to that zone only. -- Graham. %Profound_observation% |
#12
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 16:17:54 +0100
Graham. wrote: If there isn't 240vAC across the motor then you need to look at the thermostat and switches that are dedicated to that zone only. And that's where a correct wiring diagram will make all the difference. Remember that not all setups are wired correctly, though, as I found out earlier this year. Good luck. -- Davey. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 11/09/16 13:43, Graeme wrote:
Let me start by saying that central heating systems are a black art to me. Ours is a conventional oil fired boiler supplying DHW and three traditional wet radiator zones. Two zones are working, but the third is not, and has not been used for two or possibly three years. The zone valves are Honeywell, with a silver box on top, and having read that the protruding lever should have resistance when the heating is off, and no resistance when on, I have found the offending valve. There are three valves in total, presumably one for each zone. Just one pump, too. I've taken the top off the silver box (one screw) and can see the actuator, but beyond that? Will tapping the actuator or the valve or anything else release it? I guess it is stuck because it hasn't been used. Can the actuator be changed without water pouring out? Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it If not its drain down and replace the lot time :-( -- Ideas are more powerful than guns. We would not let our enemies have guns, why should we let them have ideas? Josef Stalin |
#14
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 11/09/16 14:53, Graeme wrote:
Anyway, yes, little catch locked, and rads heating. Ok actuator is ****ed, get a new one and fit. No need to drain -- Gun Control: The law that ensures that only criminals have guns. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 23:25:28 +0100
The Natural Philosopher wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. -- Davey. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 11 Sep 2016 23:27:20 +0100
The Natural Philosopher wrote: On 11/09/16 14:53, Graeme wrote: Anyway, yes, little catch locked, and rads heating. Ok actuator is ****ed, get a new one and fit. No need to drain Or there is no power getting to the actuator, in which case a new one won't work either. -- Davey. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
Graeme Wrote in message:
In message , Davey writes Let's go back to basics. Excellent. You say that you have identified the offending valve. Do you mean that it should be powered, therefore open, and so should have no resistance on the manual lever, but that it does have resistance, indicating that it is still closed? It does have resistance whether or not the system is calling for heat. If so, can you move the lever against the resistance, thereby opening the valve? There should be a little catch so that you can lock it in the open position. Does doing this allow hot water through the zone? Yes! Why didn't I realise that? Anyway, yes, little catch locked, and rads heating. I could live with that, at least for a while. This zone heats four rads in what was our shop, attached to the side of our house. The shop is closed and the space will be my 'hobby room', so remembering to use that little catch to heat the place is acceptable if not perfect. Just remember that when latched like that the internal microswitch won't be closed so it will rely on one of the other zones (or the DHW) to be calling for heat for the boiler & pump to run. -- %Profound_observation% ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Graham.
writes Just remember that when latched like that the internal microswitch won't be closed so it will rely on one of the other zones (or the DHW) to be calling for heat for the boiler & pump to run. I realised that, backwards :-) When I had finished fiddling yesterday, I forgot to unlatch the little lever and realised later that the heating for that zone had come on, with the DHW. Doh. -- Graeme |
#19
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
Graeme Wrote in message:
In message , Graham. writes Just remember that when latched like that the internal microswitch won't be closed so it will rely on one of the other zones (or the DHW) to be calling for heat for the boiler & pump to run. I realised that, backwards :-) When I had finished fiddling yesterday, I forgot to unlatch the little lever and realised later that the heating for that zone had come on, with the DHW. Doh. -- Graeme Is there a separate thermostat, timer, or programmer for the shop zone? -- %Profound_observation% ----Android NewsGroup Reader---- http://usenet.sinaapp.com/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 11/09/2016 23:48, Davey wrote:
On Sun, 11 Sep 2016 23:25:28 +0100 The Natural wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. Not necessarily. If the wet part is stiff, the actuator may not have enough grunt to shift it - even though you can do it with the manual lever. The OP needs to remover the actuator, see whether it moves when it's not on the valve, and make sure that the valve's spindle is free to turn. Chances are that the actuator's motor has died, but it *could* just be a partially seized valve. If so, rotating it to and fro a few times with pliers may well free it up. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#21
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Mon, 12 Sep 2016 11:18:31 +0100
Roger Mills wrote: On 11/09/2016 23:48, Davey wrote: On Sun, 11 Sep 2016 23:25:28 +0100 The Natural wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. Not necessarily. If the wet part is stiff, the actuator may not have enough grunt to shift it - even though you can do it with the manual lever. The OP needs to remover the actuator, see whether it moves when it's not on the valve, and make sure that the valve's spindle is free to turn. Chances are that the actuator's motor has died, but it *could* just be a partially seized valve. If so, rotating it to and fro a few times with pliers may well free it up. Before that, he needs to check that the actuator is actually getting power. -- Davey. |
#22
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Graham.
writes Graeme Wrote in message: In message , Graham. writes Just remember that when latched like that the internal microswitch won't be closed so it will rely on one of the other zones (or the DHW) to be calling for heat for the boiler & pump to run. I realised that, backwards :-) When I had finished fiddling yesterday, I forgot to unlatch the little lever and realised later that the heating for that zone had come on, with the DHW. Doh. Is there a separate thermostat, timer, or programmer for the shop zone? There is a separate timer/programmer for each zone, but not thermostat. I turned the shop zone programmer off and, there being no other call for heat, the boiler stopped. What I said above is not quite true - it was the downstairs heating coming on which caused the shop heating to also come on. -- Graeme |
#23
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 12/09/2016 12:12, Davey wrote:
On Mon, 12 Sep 2016 11:18:31 +0100 Roger wrote: On 11/09/2016 23:48, Davey wrote: On Sun, 11 Sep 2016 23:25:28 +0100 The Natural wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. Not necessarily. If the wet part is stiff, the actuator may not have enough grunt to shift it - even though you can do it with the manual lever. The OP needs to remover the actuator, see whether it moves when it's not on the valve, and make sure that the valve's spindle is free to turn. Chances are that the actuator's motor has died, but it *could* just be a partially seized valve. If so, rotating it to and fro a few times with pliers may well free it up. Before that, he needs to check that the actuator is actually getting power. ICBW but I thought he'd already confirmed that. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Mon, 12 Sep 2016 22:52:04 +0100
Roger Mills wrote: On 12/09/2016 12:12, Davey wrote: On Mon, 12 Sep 2016 11:18:31 +0100 Roger wrote: On 11/09/2016 23:48, Davey wrote: On Sun, 11 Sep 2016 23:25:28 +0100 The Natural wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. Not necessarily. If the wet part is stiff, the actuator may not have enough grunt to shift it - even though you can do it with the manual lever. The OP needs to remover the actuator, see whether it moves when it's not on the valve, and make sure that the valve's spindle is free to turn. Chances are that the actuator's motor has died, but it *could* just be a partially seized valve. If so, rotating it to and fro a few times with pliers may well free it up. Before that, he needs to check that the actuator is actually getting power. ICBW but I thought he'd already confirmed that. Which post? I missed it if he did. I saw that he said he had a meter available. -- Davey. |
#25
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Davey
writes And that's where a correct wiring diagram will make all the difference. Remember that not all setups are wired correctly, though, as I found out earlier this year. Thanks for all the advice guys. I'm not ignoring you, just waiting for the weather to turn. Seems a pity to be doing indoor stuff on days like today. -- Graeme |
#26
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Roger Mills
writes On 12/09/2016 12:12, Davey wrote: Before that, he needs to check that the actuator is actually getting power. ICBW but I thought he'd already confirmed that. Not yet, but will do. -- Graeme |
#27
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 13/09/2016 00:21, Davey wrote:
On Mon, 12 Sep 2016 22:52:04 +0100 Roger wrote: On 12/09/2016 12:12, Davey wrote: On Mon, 12 Sep 2016 11:18:31 +0100 Roger wrote: On 11/09/2016 23:48, Davey wrote: On Sun, 11 Sep 2016 23:25:28 +0100 The Natural wrote: Remove the silver box off teh actual valve and you should expose a shaft that should turn., Often it doesnt till some serious plier work has been done on it, by which time the actuator may have enough guts to turn it But he has already said that it works fine when using the manual lever to operate it, so the actuator should also be able to turn it. Not necessarily. If the wet part is stiff, the actuator may not have enough grunt to shift it - even though you can do it with the manual lever. The OP needs to remover the actuator, see whether it moves when it's not on the valve, and make sure that the valve's spindle is free to turn. Chances are that the actuator's motor has died, but it *could* just be a partially seized valve. If so, rotating it to and fro a few times with pliers may well free it up. Before that, he needs to check that the actuator is actually getting power. ICBW but I thought he'd already confirmed that. Which post? I missed it if he did. I saw that he said he had a meter available. He's now saying he didn't - so I must have imagined it. I did say ICBW . . . -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
"Graeme" wrote in message
... In message , Davey writes And that's where a correct wiring diagram will make all the difference. Remember that not all setups are wired correctly, though, as I found out earlier this year. Thanks for all the advice guys. I'm not ignoring you, just waiting for the weather to turn. Seems a pity to be doing indoor stuff on days like today. Normally the sort of job you can do in August:-) We hit 30 deg today Linconshire -- Adam |
#29
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , ARW
writes "Graeme" wrote in message ... Thanks for all the advice guys. I'm not ignoring you, just waiting for the weather to turn. Seems a pity to be doing indoor stuff on days like today. Normally the sort of job you can do in August:-) We hit 30 deg today Linconshire Even up here in Aberdeenshire we hit 26 which is good for mid summer! -- Graeme |
#30
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Davey
writes This shows that the Brown and Blue wires are the power for the valve, so IF you can get the probes for the meter to these terminals, you should see 240 V AC across them. If they are unreachable, then find where the wires go to, there will most likely be a junction box of some kind within a few feet. Try there for the same thing, and report back. Right. Removed the whole actuator assembly from the valve, and the valve spindle turns easily. Held the actuator and applied power - I'm assuming the actuator should actuate, but it didn't so either the actuator is dead or there is a wiring problem. There is indeed a nearby junction box and, within, the four wires from the actuator are connected to a four wire cable which runs to the programmer. The wires within the junction box are all neatly connected and insulated, so cannot get probes in, to test. Would it be OK to cut the wires, remove the four connectors and replace with a chocolate block, which will fit within the junction box? -- Graeme |
#31
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Sun, 18 Sep 2016 11:36:59 +0100
Graeme wrote: In message , Davey writes This shows that the Brown and Blue wires are the power for the valve, so IF you can get the probes for the meter to these terminals, you should see 240 V AC across them. If they are unreachable, then find where the wires go to, there will most likely be a junction box of some kind within a few feet. Try there for the same thing, and report back. Right. Removed the whole actuator assembly from the valve, and the valve spindle turns easily. Held the actuator and applied power - I'm assuming the actuator should actuate, but it didn't so either the actuator is dead or there is a wiring problem. There is indeed a nearby junction box and, within, the four wires from the actuator are connected to a four wire cable which runs to the programmer. The wires within the junction box are all neatly connected and insulated, so cannot get probes in, to test. Would it be OK to cut the wires, remove the four connectors and replace with a chocolate block, which will fit within the junction box? Personally, I see no problem, but I'm not a qualified electrician! What you describe is how mine is done. Can you find the other ends of the wires that feed the junction box, at the programmer end, and check the wires for power there? That might find a problem, closer to its actual location. Or maybe test the wires at the actuator? I reckon at this point that the actuator is probably dead, but it's worth checking as far as possible first, just in case it's not that. -- Davey. |
#32
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 18/09/2016 11:36, Graeme wrote:
In message , Davey writes This shows that the Brown and Blue wires are the power for the valve, so IF you can get the probes for the meter to these terminals, you should see 240 V AC across them. If they are unreachable, then find where the wires go to, there will most likely be a junction box of some kind within a few feet. Try there for the same thing, and report back. Right. Removed the whole actuator assembly from the valve, and the valve spindle turns easily. Held the actuator and applied power - I'm assuming the actuator should actuate, but it didn't so either the actuator is dead or there is a wiring problem. There is indeed a nearby junction box and, within, the four wires from the actuator are connected to a four wire cable which runs to the programmer. The wires within the junction box are all neatly connected and insulated, so cannot get probes in, to test. Would it be OK to cut the wires, remove the four connectors and replace with a chocolate block, which will fit within the junction box? Don't see why not. If - as seems likely - you end up needing to replace the actuator, you'll need to break those connections anyway. -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#33
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Davey
writes Personally, I see no problem, but I'm not a qualified electrician! What you describe is how mine is done. I went ahead without waiting for a reply. Five wires, not four, one being earth. Anyway, now joined via a choc block and 240v indeed across the brown and blue wires. Tried applying power whilst the actuator was off the valve, and nothing, so looks like a new actuator. Oh well, at least the wiring connections will be easy, now. Will report back when actuator purchased and fitted. -- Graeme |
#34
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 18/09/2016 13:20, Graeme wrote:
In message , Davey writes Personally, I see no problem, but I'm not a qualified electrician! What you describe is how mine is done. I went ahead without waiting for a reply. Five wires, not four, one being earth. Anyway, now joined via a choc block and 240v indeed across the brown and blue wires. Tried applying power whilst the actuator was off the valve, and nothing, so looks like a new actuator. Oh well, at least the wiring connections will be easy, now. Will report back when actuator purchased and fitted. If you fancy taking it apart you may find that you only need to replace the motor - obtainable from the likes of Screwfix for about 16 quid. http://www.screwfix.com/p/drayton-sy...questid=290766 [Read the reviews for further info.] -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#35
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Roger Mills
writes On 18/09/2016 13:20, Graeme wrote: Will report back when actuator purchased and fitted. If you fancy taking it apart you may find that you only need to replace the motor - obtainable from the likes of Screwfix for about 16 quid. http://www.screwfix.com/p/drayton-sy...questid=290766 [Read the reviews for further info.] Yes, I had thought about that, but the area just below the motor itself seems stuffed full of little parts ready to ping around the room, never to be seen again. I'll have another look, though. Having got this far .... -- Graeme |
#36
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 18/09/2016 17:44, Graeme wrote:
In message , Roger Mills writes On 18/09/2016 13:20, Graeme wrote: Will report back when actuator purchased and fitted. If you fancy taking it apart you may find that you only need to replace the motor - obtainable from the likes of Screwfix for about 16 quid. http://www.screwfix.com/p/drayton-sy...questid=290766 [Read the reviews for further info.] Yes, I had thought about that, but the area just below the motor itself seems stuffed full of little parts ready to ping around the room, never to be seen again. I'll have another look, though. Having got this far ... I don't think you've got a lot to lose! If you can't mend it, you'll have to buy another actuator anyway, so you may as well see whether you can get the motor out without everything flying apart. [The motor itself comes with a reduction gearbox whose output shaft rotates very slowly - so that will all get replaced. Is that what you mean by little parts?] Once you've got the motor out, test it by applying power directly to it before buying a new one - in case the fault isn't the motor itself (but it almost certainly is). -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#37
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On Tue, 13 Sep 2016 09:39:06 +0100
Graeme wrote: In message , Davey writes And that's where a correct wiring diagram will make all the difference. Remember that not all setups are wired correctly, though, as I found out earlier this year. Thanks for all the advice guys. I'm not ignoring you, just waiting for the weather to turn. Seems a pity to be doing indoor stuff on days like today. Coincidentally, my boiler started to run yesterday, but stopped after a few seconds. It did not run again all evening or night. Today, I started by checking that it did indeed run of the CH was turned on, which it did, so the boiler is ok. Proceeded to do electrical checks, and eventually found that the cylinder 'stat was stuck Off, I had to turn it all the way to max. to make it work. It's now working, but I'll get a replacement. It's now working, but I'll get a replacement, it's clearly not happy any more. It's not always the valve! -- Davey. |
#38
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Roger Mills
writes On 18/09/2016 17:44, Graeme wrote: Yes, I had thought about that, but the area just below the motor itself seems stuffed full of little parts ready to ping around the room, never to be seen again. I'll have another look, though. Having got this far ... I don't think you've got a lot to lose! Interesting. Just removed the motor, and wired it to a 13 amp plug, and it works. Huge torque and slow final output. I couldn't stall it with my fingers. So, replaced motor and tried again, still with just the motor attached to a plug, but not attached to the valve itself. It works. Put the complete actuator back on the valve, and nothing, yet 240v registered by meter, which tells me something is broken in the electrical 'gubbins' mounted above the valve but below the motor. I imagine there is some sort of micro switch within, which is buggered? Time to replace? -- Graeme |
#39
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
On 24/09/2016 17:45, Graeme wrote:
In message , Roger Mills writes On 18/09/2016 17:44, Graeme wrote: Yes, I had thought about that, but the area just below the motor itself seems stuffed full of little parts ready to ping around the room, never to be seen again. I'll have another look, though. Having got this far ... I don't think you've got a lot to lose! Interesting. Just removed the motor, and wired it to a 13 amp plug, and it works. Huge torque and slow final output. I couldn't stall it with my fingers. So, replaced motor and tried again, still with just the motor attached to a plug, but not attached to the valve itself. It works. Put the complete actuator back on the valve, and nothing, yet 240v registered by meter, which tells me something is broken in the electrical 'gubbins' mounted above the valve but below the motor. I imagine there is some sort of micro switch within, which is buggered? Time to replace? If it's a 2-port valve - which I believe it is - the only micro-switch should be the one which closes when the valve is fully open. There's not one in the motor circuit - the motor is connected directly to the brown and blue external wires. [You should be able to verify that from the internal connections, having removed and replaced the motor]. So the motor works when you connect the mains directly to it. What I'm not clear about is how you tested it having re-installed the motor. With the motor installed and connected internally, and with the actuator OFF the valve, the motor should run when you connect mains across the brown and blue external wires and should rotate the internals against the return spring to the 'valve open' position, and the motor should then stall. What actually happens when you do that? Are the internals free to move? If, with no power applied, you move the manual lever to the 'open' position, can you feel some resistance, and hear the gears whirling? When you let go of the lever, does the spring move it all back to the closed position? -- Cheers, Roger ____________ Please reply to Newsgroup. Whilst email address is valid, it is seldom checked. |
#40
Posted to uk.d-i-y
|
|||
|
|||
Failed central heating valve?
In message , Roger Mills
writes Are the internals free to move? If, with no power applied, you move the manual lever to the 'open' position, can you feel some resistance, and hear the gears whirling? When you let go of the lever, does the spring move it all back to the closed position? Back to basics. The motor, when removed from the actuator assembly, works perfectly when connected to an ordinary domestic 13 amp plug. Plenty of torque - I cannot stop it turning, with my fingers. The valve stem, with actuator assembly removed, turns easily with fingers. The radiators then work with another zone calling for heat. Looking at another zone valve, the wiring is correct. There is a five core cable (including earth) from the programmer to the zone valve. Using a meter, there is 240v across the brown/blue, whether or not the programmer is on (calling for heat) or not BUT the motor, hanging loose from the actuator head, does not turn whether or not the programmer is on. There is a little micro switch within the actuator - pressing that in with a screwdriver blade causes the oil fired non combi boiler to fire, even if the programmer is off. However, clicking the micro switch in does not power the motor, whether or not the programmer is on or off. Ignoring the earth, the wiring is thus : Four cores from the programmer to the junction box. Blue, brown, black and second black. Another four cores from the junction box to the actuator. Blue, brown, grey and orange. They are connected at the junction box : From To programmer Actuator Black Brown Black Orange Brown Grey Blue Blue The brown and blue wires on the actuator side connect to the motor, so not connected directly to the incoming 240v (brown/blue) from the programmer. However, there is something else odd. Looking at another actuator, when the motor runs, a little tab moves and presses the micro switch to fire the boiler, but on the defective actuator, the tab does not move far enough to press the micro switch, when using the manual lever. Something has 'slipped'? I suppose next stage should be to swap actuators. -- Graeme |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Central heating bypass valve | UK diy | |||
central heating 3 way valve problem? | UK diy | |||
Central Heating Valve can I just remove it? | UK diy | |||
central heating 3 port/way valve | About this forum | |||
Central Heating valve problem. | UK diy |