Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?

Thanks

Phil
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,254
Default OT - Server Power Summary

thescullster wrote:

The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).


In normal running it will take 50% from each PSU, if one fails 100% from
the remaining PSU, is it just a single server? Is it a room or a broom
cupboard?


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 6,896
Default OT - Server Power Summary

In article , Andy
Burns scribeth thus
thescullster wrote:

The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).


In normal running it will take 50% from each PSU, if one fails 100% from
the remaining PSU, is it just a single server? Is it a room or a broom
cupboard?



Yeabut these places seem to grow stuff, least all the one I've been
into!
--
Tony Sayer



  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,069
Default OT - Server Power Summary

En el artículo , tony sayer
escribió:

Yeabut these places seem to grow stuff, least all the one I've been
into!


+1, in spades.

I've specified, designed and had built two server rooms for university
departments. It's always cheaper and easier to over-specify the aircon
in the first place, rather than try and retrofit additional cooling
later. (ps. Do the same for the power feed!)

You can be sure some git will wander along and say, "uh, I've got a
little rack mount server, it's too noisy for my office, can you install
it in one of your racks? It won't take up much power or heat" and it'll
turn out to be some 4U monster containing three dozen Xeons running full
pelt 24/7 doing astrophysical number crunching.

In the case of the second room, for server plant with an estimated
maximum heat output of 30kW, two 33kW floor standing aircon units were
installed in such a way that they circulated cool air around the five
fully-populated full-height (42u) racks. Most of those contained HP
Proliant DL360G3/4/5 servers, plus disk arrays of various makes and
vintages. The target temperature of the room was 19C.

That was ok, but I neglected to allow for that fact that the room gained
a lot of solar heat via sunlight in the summer with a large bank of
floor-to-ceiling southwest-facing windows. One day, despite the aircon,
the room temperature reached 39C and stuff began shutting itself down.
We had to have reflective tinted window film and roller blinds installed
to deal with that and even then it was touch and go.

--
(\_/) Tyson Fury: #homophobe #bigot #throwback #missinglink
(='.'=) #neanderthal #misogynist #redneck #dickhead
(")_(")
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,853
Default OT - Server Power Summary

On 15/12/2015 19:50, Mike Tomlinson wrote:
That was ok, but I neglected to allow for that fact that the room gained
a lot of solar heat via sunlight in the summer with a large bank of
floor-to-ceiling southwest-facing windows.


We had the reverse - an aircon unit blew, and it turned out we hadn't
allowed enough slack. Luckily it was a cold dry day, and we had windows
we could open. As the OPs is small you might be able to get away with
"in case of emergency open the door and station a guard".

Andy


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default OT - Server Power Summary

On 15/12/15 16:59, thescullster wrote:
Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?

Thanks

Phil



Having had real experience of medium computer rooms - you *must* have
n+1 redundancy at the minimu unless you are willing to shut machines
down (and air con repairs are often not fast, even on contract).

So you need 2 air con units of the rating that one alone can do the job.
Or 3 with 2 able. If you choose n+2 or a higher redundancy you can do
that, if you want extra protection against failure, but IME it tends to
be one unit will fail.

And yes, you are right - you need to size for actual consumption - but
peak consumption, not idling. If you cannot measure that, sizing by
plate rating is safer.

BUT you are right - if the server runs on 1 PSU of 800W, you size for
800W of cooling not 1600W. The server does not decrease its load to
match failed PSUs. But watch out for 3/2 PSUs (runs on 3 or 2 but not 1
- eg some big disk arrays or network switch stacks).


Other comments:


Will you cooling be on UPS? If not, things get warm real fast when the
mains fails - been there with about 40kW of UPS protected servers and no
air con and no windows! if not, automatic orderly shutdown of machines
would be advisable - perhaps with a whole room temperature logger/sensor
like computer rooms used to have.

And water - air con units are prone to spilling water (condensate) when
their drain gets blocked or something else happens. It can be a very
good idea to have some leak alarm around the units or secondary
containment under them (big tray).
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 748
Default OT - Server Power Summary

On 15/12/15 17:33, Tim Watts wrote:
On 15/12/15 16:59, thescullster wrote:
Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?

Thanks

Phil



Having had real experience of medium computer rooms - you *must* have
n+1 redundancy at the minimu unless you are willing to shut machines
down (and air con repairs are often not fast, even on contract).

So you need 2 air con units of the rating that one alone can do the job.
Or 3 with 2 able. If you choose n+2 or a higher



redundancy you can do
that, if you want extra protection against failure, but IME it tends to
be one unit will fail.

And yes, you are right - you need to size for actual consumption - but
peak consumption, not idling. If you cannot measure that, sizing by
plate rating is safer.

BUT you are right - if the server runs on 1 PSU of 800W, you size for
800W of cooling not 1600W. The server does not decrease its load to
match failed PSUs. But watch out for 3/2 PSUs (runs on 3 or 2 but not 1
- eg some big disk arrays or network switch stacks).


Other comments:


Will you cooling be on UPS? If not, things get warm real fast when the
mains fails - been there with about 40kW of UPS protected servers and no
air con and no windows! if not, automatic orderly shutdown of machines
would be advisable - perhaps with a whole room temperature logger/sensor
like computer rooms used to have.

And water - air con units are prone to spilling water (condensate) when
their drain gets blocked or something else happens. It can be a very
good idea to have some leak alarm around the units or secondary
containment under them (big tray).

I'd agree with all that, and add that for the monitoring, have a look he

http://www.openxtra.co.uk/environment-monitor

I installed a 4-channel SNMP temperature monitor, and there's a Linux
box with an old Nokia mobile attached for SMS alerts, and it's worth
noting that many UPSs have an SNMP card you can use as a sensor.
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 39,563
Default OT - Server Power Summary

On 15/12/15 16:59, thescullster wrote:
Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?


Yours, for the average case, theirs, for a possible peak case.

Thanks

Phil



--
the biggest threat to humanity comes from socialism, which has utterly
diverted our attention away from what really matters to our existential
survival, to indulging in navel gazing and faux moral investigations
into what the world ought to be, whilst we fail utterly to deal with
what it actually is.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default OT - Server Power Summary

In article ,
thescullster writes:
Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?


You use the Watts figure for aircon, and the VA figure for sizing
the power circuits.

Buy a watt meter or two for dual supply systems (around £10).
Check the power consumption of each system.
Allow for growth (both extra disks and cards in systems, and extra
systems and storage arrays - consider how much spare rack space
you have and space for more racks).
Add power consumption of lighting and any other electrical equipment,
unless it will normally be off and controlled by occupancy sensors.
If the room contains electrical switchgear and distribution boards,
allow for heat given off by those.
If you expect people to work in there for extended periods, add 100W
per person for non-physical activity, or 200W for people doing things
like assembling/racking servers.
If the room has windows, calculate the solar gain (this can be very
considerable).
Calculate heat leakage into the room from non-airconed adjacent areas
(including any room below and the outdoors) at a 10C temperature
differential.
Computer rooms are usually made airtight for effectiveness of automatic
fire extinguising systems, but if yours isn't and it's large, you might
want to allow for 2 air changes/hour (again at 10C temperature
differential), or more if people will be frequently opening the door.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,434
Default OT - Server Power Summary

On 15/12/15 23:16, Andrew Gabriel wrote:

You use the Watts figure for aircon, and the VA figure for sizing
the power circuits.


Power factor of about 0.9 is a pretty good worst case estimate. I had to
take a power and mass inventory of a small but extremely dense computer
room a few years back (for floor loading and aircon). The main power
distribution panel had a power/VA/PF meter built in. This was mostly HP
and Viglen gear IIRC, total power in the few 10's of kW.

Buy a watt meter or two for dual supply systems (around £10).
Check the power consumption of each system.
Allow for growth (both extra disks and cards in systems, and extra
systems and storage arrays - consider how much spare rack space
you have and space for more racks).
Add power consumption of lighting and any other electrical equipment,
unless it will normally be off and controlled by occupancy sensors.
If the room contains electrical switchgear and distribution boards,
allow for heat given off by those.
If you expect people to work in there for extended periods, add 100W
per person for non-physical activity, or 200W for people doing things
like assembling/racking servers.
If the room has windows, calculate the solar gain (this can be very
considerable).
Calculate heat leakage into the room from non-airconed adjacent areas
(including any room below and the outdoors) at a 10C temperature
differential.
Computer rooms are usually made airtight for effectiveness of automatic
fire extinguising systems, but if yours isn't and it's large, you might
want to allow for 2 air changes/hour (again at 10C temperature
differential), or more if people will be frequently opening the door.




  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 167
Default OT - Server Power Summary

On 15/12/2015 16:59, thescullster wrote:
Hi guys

I am looking again at air conditioning for a proposed server room.

While I don't mind over-egging it, I would like to know how much custard
I'm throwing around here.

The servers in question are HP DL360 Gen 9s which are each fitted with 2
800w powers supplies.
My understanding is that one of these will be a redundant standby supply
which means the server should run happily on just one 800w supply.

However, there are figures quoted at the bottom of the parts
specification for the server which state:



Power Summary (based on 100% utilization)

Total system VA rating 343.35 Total system BTU/hr 1154.31
Total input system current 1.56 Total wattage 338.51
Power supply efficiency (0.93) Power factor (0.99)
Inrush current (30) Leakage current (0.75)



The company group IT dept seem to be suggesting that we should be
providing 1.6Kw of cooling for each server (for the two 800w supplies).
My understanding would be that the server power consumption and
therefore ability to generate heat would be limited to the 343.35VA.
Not sure what the difference is between VA and watts to be fair, but
this gives a factor of 5 between the two figures.
Anyone able to clarify whether either approach is correct please?

Thanks

Phil


Thanks to all

In answer to the questions raised:

It is a large 2.4m square cupboard without windows.
There will be a number of devices including servers, switches, storage
and related IT stuff.

Phil
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power to server & machine and headend room from CU.... Stephen H UK diy 5 December 6th 12 08:16 PM
Server room rack power [email protected] UK diy 20 January 13th 09 02:15 PM
Tardis News Web Server inside Server Defies Laws of Nature [email protected] UK diy 1 March 3rd 08 08:38 PM
Power For Server Room AJ UK diy 11 March 17th 07 06:16 PM
Server Room Power Supply Richard UK diy 2 March 16th 07 03:06 PM


All times are GMT +1. The time now is 01:42 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"