Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
Just for reference, in case anyone has the same problem, my Vaillant non-condensing Turbomax 628 or is it 828 ? combi, now 9 years old, has been a little intermittent lately, with hot water sometimes not coming through. However, it always fixed itself quickly. Not today.
The diagnostic code was S.33 wich points to the fan/pressure switch. Indeed I couldn't pick up any voltage to the fan at the circuit board connector when I turned the hot water on or tried the CH. The pump ran, the diverter valve diverted etc. The diagnostic booklet flow chart simply tells you to change the pcb at this point. I prised the plastic back covers off the pcb had a look. The central (mains voltage) area smelt of ozone. Ozone meant sparking, but I couldn't figure out what might be sparking. Well a few attempts at turning a hot tap on and tapping things soon provided an explanation - greenish-blue arcing inside one of three large relays (transparent cover). Prising the transparent cover off allowed access and bit of a scrape of the changeover contacts later (using wet and dry) and the relay closed without continual fizzing and arcing (a slight spark but that's normal for an inductive load like a motor). However, still no 240V at the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. A word of warning - to gain access to the relays you have to take a second protective cover off the pcb, the high voltage bit. There are plenty of terminals at mains voltage including the mains transformer terminals which are very in-the-way. Don't work on live mains equipment unless you know what you are about. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Tuesday, 28 August 2012 17:28:24 UTC+1, (unknown) wrote:
Just for reference, in case anyone has the same problem, my Vaillant non-condensing Turbomax 628 or is it 828 ? combi, now 9 years old, has been a little intermittent lately, with hot water sometimes not coming through. However, it always fixed itself quickly. Not today. The diagnostic code was S.33 wich points to the fan/pressure switch. Indeed I couldn't pick up any voltage to the fan at the circuit board connector when I turned the hot water on or tried the CH. The pump ran, the diverter valve diverted etc. The diagnostic booklet flow chart simply tells you to change the pcb at this point. I prised the plastic back covers off the pcb had a look. The central (mains voltage) area smelt of ozone. Ozone meant sparking, but I couldn't figure out what might be sparking. Well a few attempts at turning a hot tap on and tapping things soon provided an explanation - greenish-blue arcing inside one of three large relays (transparent cover). By the way I isolated the mains before I started to poke around inside the relay! Prising the transparent cover off allowed access and bit of a scrape of the changeover contacts later (using wet and dry) and the relay closed without continual fizzing and arcing (a slight spark but that's normal for an inductive load like a motor). However, still no 240V at the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. A word of warning - to gain access to the relays you have to take a second protective cover off the pcb, the high voltage bit. There are plenty of terminals at mains voltage including the mains transformer terminals which are very in-the-way. Don't work on live mains equipment unless you know what you are about. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed -for reference
|
#4
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
|
#5
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
|
#6
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 28, 7:43*pm, geoff wrote:
In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. MBQ |
#7
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 28, 7:58*pm, "ARWadsworth"
wrote: geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil You should consider this sort of thing for a living geoff. Given that comment, I would not employ him. MBQ |
#8
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes On Aug 28, 7:43*pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. regards -- Tim Lamb |
#9
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes On Aug 28, 7:58*pm, "ARWadsworth" wrote: geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil You should consider this sort of thing for a living geoff. Given that comment, I would not employ him. I was using noddy language in a noddy thread (a bit like people who misuse the term "dry joint") Its actually the energy stored in the fan coil when the relay contacts open arcing across the contacts that knackers the relay Would I want you as an employer - I think not -- geoff |
#10
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes On Aug 28, 7:43*pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Oh do **** off -- geoff |
#11
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
Man at B&Q wrote:
On Aug 28, 7:58 pm, "ARWadsworth" wrote: geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil You should consider this sort of thing for a living geoff. Given that comment, I would not employ him. Why? -- Adam |
#12
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 29, 9:20*am, Tim Lamb wrote:
In message , Man at B&Q writes On Aug 28, 7:43*pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. MBQ |
#13
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 29, 8:10*pm, "ARWadsworth"
wrote: Man at B&Q wrote: On Aug 28, 7:58 pm, "ARWadsworth" wrote: geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil You should consider this sort of thing for a living geoff. Given that comment, I would not employ him. Why? Either he doesn't understand back EMF or he can't explain himself clearly. In this case the latter. If he'd said "fan coil" (a strange term in itself) then it would hev been clearer. MBQ |
#14
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes On Aug 29, 9:20*am, Tim Lamb wrote: In message , Man at B&Q writes On Aug 28, 7:43*pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. Hmm.. I think you know what was meant:-) regards -- Tim Lamb |
#15
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. No it doesn't you retard I admit that I could have actually stated which coil I was on about, but I expected people to have a bit more of a clue than yourself and understand that I was on about the fan coil, as that is what the contacts of the relay are switching People like you are the reason that manufacturers of toasters have to put warnings on them stating that it gets hot ... Get back under your bridge -- geoff |
#16
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 30, 8:09*pm, geoff wrote:
In message , Man at B&Q writes I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. No it doesn't you retard I admit that I could have actually stated which coil I was on about, but I expected people to have a bit more of a clue than yourself and understand that I was on about the fan coil Relays have coils. Motors have rotor or stator windings (maybe even both). Learn to use the correct terminolgy and we might get on. MBQ |
#17
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 30, 12:16*pm, Tim Lamb wrote:
In message , Man at B&Q writes On Aug 29, 9:20*am, Tim Lamb wrote: In message , Man at B&Q writes On Aug 28, 7:43*pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. Hmm.. I think you know what was meant:-) No, using the words "relay" and "coil" in the same sentence is very easily construed as referring only to the relay. MBQ |
#18
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
"Man at B&Q" wrote:
On Aug 30, 12:16 pm, Tim Lamb wrote: In message , Man at B&Q writes On Aug 29, 9:20 am, Tim Lamb wrote: In message , Man at B&Q writes On Aug 28, 7:43 pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. Hmm.. I think you know what was meant:-) No, using the words "relay" and "coil" in the same sentence is very easily construed as referring only to the relay. MBQ ********. We (and you) knew that he was talking about an inductive load. Tim |
#19
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
In message
, Man at B&Q writes On Aug 30, 8:09*pm, geoff wrote: In message , Man at B&Q writes I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. No it doesn't you retard I admit that I could have actually stated which coil I was on about, but I expected people to have a bit more of a clue than yourself and understand that I was on about the fan coil Relays have coils. Motors have rotor or stator windings (maybe even both). Learn to use the correct terminolgy and we might get on. Not sure I really want to Pedants who are stupid for the sake of it are not the sort of person I can be arsed with I have better things to do with my time, like running a business which repairs boiler pcbs, for example -- geoff |
#20
Posted to uk.d-i-y
|
|||
|
|||
Vaillant Turbomax 828 (628?) combi - fault found and fixed - for reference
On Aug 30, 8:27*pm, Tim+ wrote:
"Man at B&Q" wrote: On Aug 30, 12:16 pm, Tim Lamb wrote: In message , Man at B&Q writes On Aug 29, 9:20 am, Tim Lamb wrote: In message , Man at B&Q writes On Aug 28, 7:43 pm, geoff wrote: In message , writes the fan motor connector! I isolated the mains and set to buzzing out the route between line at the mains LIVE input screw terminal, the relay contacts and the brown wire (live) on the fan connector (WITH A dvm SET TO AUDIO BUZZER) revealed that the contacts were now making too light a contact to work. A bit of adjustment with a fine blade on the live fixed relay contact soon brought the clearances back into kilter and I now have hot water again. I may have to replace that relay in future but I'll see how it goes. Fan control relay - back EMF of the coil Doesn't affect the contacts. Yes it does. Maintains the arc for longer than for a resistive load would. Well, "Fan control relay - back EMF of the coil" implies the back EMF of the relay coil is somehow causing the isue with the contacts. It dosn't. Hmm.. I think you know what was meant:-) No, using the words "relay" and "coil" in the same sentence is very easily construed as referring only to the relay. MBQ ********. We (and you) knew that he was talking about an inductive load. ******** to that. MBQ |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Vaillant Turbomax VUW combi boiler | UK diy | |||
Pressure loss on Vaillant Turbomax combi. | UK diy | |||
Pressure loss on Vaillant Turbomax combi. | UK diy | |||
Vaillant TurboMax Combi problems | UK diy | |||
vaillant Turbomax 824/828 combi boilers | UK diy |