Home |
Search |
Today's Posts |
![]() |
|
UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions. |
Reply |
|
LinkBack | Thread Tools | Display Modes |
#1
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
Got very useful input from here last week - thanks again.
My home electric circuits were tested as ok some weeks ago, including adequate earthing, when a survey was done for a new combi boiler. When they came to fit boiler, this was abandoned when initial tests showed earthing inadequate - nearly 5 ohms instead og 1. In the interim new street mains and house supply gas pipes were replaced with plastic and one possibility is that my equipotential bonding to old iron gas pipes was helping earth my system, instead of gas pipes being earthed to my system. Impedance of about 5 ohms was measured at earth connection on sockets. Same was measured at what was supposed to be the actual main earth; an earth wire from the consumer unit - what I call the fuse box!! - to an ordinary earth clamp (http://www.ultimatehandyman.co.uk/ earth_clamp.htm) round the pipe containing the incoming mains electricity supply. The theory, by both British Gas (boiler fitters) and Scottish Power (DNO for my area) is that the earthing supplied by this pipe is inadequate or has become compromised. One electrician did try scraping the pipe a bit at this earth connection to get a better connection, without success. However, I've since noticed that what looks like copper is more like some ancient gunge/paint/corrosion which I've scraped down to a shiny metal surface and re-attached the earth. I'd like to now measure the earthing impedance at this earth connection down the pipe and, if possible, at the sockets. After initial crude tests with 'socket and see', I think electricians previously tested it with multimeter. I know enough about volts amps and ohms to know what they are, but don't usually touch electrics - but I do enough about electrics to know what not to try!! What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. I'm not measuring the resistance across something but down something where I dont have access to the other end. Do I attach attach one probe to something non-conductive and the other to the pipe to get the resistance to leakage in one direction, and how do I safely get a reading at socket (and no, I do know enough not to poke into the live supply). There is a delay in the DNO attending - I'd be interested to know whether things are safer meantime and to what extent what one electrician saw as the possible problem, might have been corrected. Regards Toom |
#2
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article
, Toom Tabard wrote: What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. In practice, you can't. You need a proper tester which just looks a bit like a multi-meter. It puts a very large load to earth on the circuit for a fraction of a second and measures the current flow, and from that calculates the impedance. They are quite expensive devices and need regular calibration. -- *What happens when none of your bees wax? * Dave Plowman London SW To e-mail, change noise into sound. |
#3
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
"Toom Tabard" wrote in message
... Got very useful input from here last week - thanks again. My home electric circuits were tested as ok some weeks ago, including adequate earthing, when a survey was done for a new combi boiler. When they came to fit boiler, this was abandoned when initial tests showed earthing inadequate - nearly 5 ohms instead og 1. In the interim new street mains and house supply gas pipes were replaced with plastic and one possibility is that my equipotential bonding to old iron gas pipes was helping earth my system, instead of gas pipes being earthed to my system. Impedance of about 5 ohms was measured at earth connection on sockets. Same was measured at what was supposed to be the actual main earth; an earth wire from the consumer unit - what I call the fuse box!! - to an ordinary earth clamp (http://www.ultimatehandyman.co.uk/ earth_clamp.htm) round the pipe containing the incoming mains electricity supply. The theory, by both British Gas (boiler fitters) and Scottish Power (DNO for my area) is that the earthing supplied by this pipe is inadequate or has become compromised. One electrician did try scraping the pipe a bit at this earth connection to get a better connection, without success. However, I've since noticed that what looks like copper is more like some ancient gunge/paint/corrosion which I've scraped down to a shiny metal surface and re-attached the earth. I'd like to now measure the earthing impedance at this earth connection down the pipe and, if possible, at the sockets. After initial crude tests with 'socket and see', I think electricians previously tested it with multimeter. I know enough about volts amps and ohms to know what they are, but don't usually touch electrics - but I do enough about electrics to know what not to try!! What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. I'm not measuring the resistance across something but down something where I dont have access to the other end. Do I attach attach one probe to something non-conductive and the other to the pipe to get the resistance to leakage in one direction, and how do I safely get a reading at socket (and no, I do know enough not to poke into the live supply). There is a delay in the DNO attending - I'd be interested to know whether things are safer meantime and to what extent what one electrician saw as the possible problem, might have been corrected. Regards Toom Put a photo up on photobucket so we can have a look. -- Adam |
#4
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]() "Dave Plowman (News)" wrote in message ... In article , Toom Tabard wrote: What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. In practice, you can't. You need a proper tester which just looks a bit like a multi-meter. It puts a very large load to earth on the circuit for a fraction of a second and measures the current flow, and from that calculates the impedance. They are quite expensive devices and need regular calibration. Wouldn't a 3 bar electric fire between live and earth do the job? Where you measure the voltage (change) between earth and neutral? Resistance = voltage / current through fire? |
#5
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 2 Sep, 16:32, Toom Tabard wrote:
Got very useful input from here last week - thanks again. My home electric circuits were tested as ok some weeks ago, including adequate earthing, when a survey was done for a new combi boiler. When they came to fit boiler, this was abandoned when initial tests showed earthing inadequate - nearly 5 ohms instead og 1. In the interim new street mains and house supply gas pipes were replaced with plastic and one possibility is that my equipotential bonding to old iron gas pipes was helping earth my system, instead of gas pipes being earthed to my system. Impedance of about 5 ohms was measured at earth connection on sockets. Same was measured at what was supposed to be the actual main earth; an earth wire from the consumer unit - what I call the fuse box!! - to an ordinary earth clamp (http://www.ultimatehandyman.co.uk/ earth_clamp.htm) round the pipe containing the incoming mains electricity supply. The theory, by both British Gas (boiler fitters) and Scottish Power (DNO for my area) is that the earthing supplied by this pipe is inadequate or has become compromised. One electrician did try scraping the pipe a bit at this earth connection to get a better connection, without success. However, I've since noticed that what looks like copper is more like some ancient gunge/paint/corrosion which I've scraped down to a shiny metal surface and re-attached the earth. I'd like to now measure the earthing impedance at this earth connection down the pipe and, if possible, at the sockets. After initial crude tests with 'socket and see', I think electricians previously tested it with multimeter. I know enough about volts amps and ohms to know what they are, but don't usually touch electrics - but I do enough about electrics to know what not to try!! What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. I'm not measuring the resistance across something but down something where I dont have access to the other end. Do I attach attach one probe to something non-conductive and the other to the pipe to get the resistance to leakage in one direction, and how do I safely get a reading at socket (and no, I do know enough not to poke into the live supply). There is a delay in the DNO attending - I'd be interested to know whether things are safer meantime and to what extent what one electrician saw as the possible problem, might have been corrected. Regards Toom You probably need to get yourself a new earth spike or maybe more than one. If your house is built one sand or one high ground there is sometimes a problem getting a good earth especially in dry weather. There's usually no problem in clay soils. In a worst case scenario, you may have to excavate a trench and lay copper tape in it, even import some clay. I was traditional to cover the tape in charcoal/coke in the past before burying(Conducts electrcity.) Dunno if that's still done. Soil in trench has to be well compacted and wetted down to ensure intimate contact. Lots of problems arose when gas and water pipes became plastic instead of metal. If you have metal gas or water pipes coming into the house, you can get an indication of what's going on by measuring resistance between them and your earth spike. (Before you connect it on to anything.) It should be virtually zero. This however is NOT a proper test but you can find out if your new earth spike is likely to have a good effect or not. |
#6
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 2 Sep, 19:22, harry wrote:
On 2 Sep, 16:32, Toom Tabard wrote: Got very useful input from here last week - thanks again. My home electric circuits were tested as ok some weeks ago, including adequate earthing, when a survey was done for a new combi boiler. When they came to fit boiler, this was abandoned when initial tests showed earthing inadequate - nearly 5 ohms instead og 1. In the interim new street mains and house supply gas pipes were replaced with plastic and one possibility is that my equipotential bonding to old iron gas pipes was helping earth my system, instead of gas pipes being earthed to my system. Impedance of about 5 ohms was measured at earth connection on sockets. Same was measured at what was supposed to be the actual main earth; an earth wire from the consumer unit - what I call the fuse box!! - to an ordinary earth clamp (http://www.ultimatehandyman.co.uk/ earth_clamp.htm) round the pipe containing the incoming mains electricity supply. The theory, by both British Gas (boiler fitters) and Scottish Power (DNO for my area) is that the earthing supplied by this pipe is inadequate or has become compromised. One electrician did try scraping the pipe a bit at this earth connection to get a better connection, without success. However, I've since noticed that what looks like copper is more like some ancient gunge/paint/corrosion which I've scraped down to a shiny metal surface and re-attached the earth. I'd like to now measure the earthing impedance at this earth connection down the pipe and, if possible, at the sockets. After initial crude tests with 'socket and see', I think electricians previously tested it with multimeter. I know enough about volts amps and ohms to know what they are, but don't usually touch electrics - but I do enough about electrics to know what not to try!! What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. I'm not measuring the resistance across something but down something where I dont have access to the other end. Do I attach attach one probe to something non-conductive and the other to the pipe to get the resistance to leakage in one direction, and how do I safely get a reading at socket (and no, I do know enough not to poke into the live supply). There is a delay in the DNO attending - I'd be interested to know whether things are safer meantime and to what extent what one electrician saw as the possible problem, might have been corrected. Regards Toom You probably need to get yourself a new earth spike or maybe more than one. If your house is built one sand or one high ground there is sometimes a problem getting a good earth especially in dry weather. *There's usually no problem in clay soils. *In a worst case scenario, you may have to excavate a trench and lay copper tape in it, even import some clay. *I was traditional to cover the tape in charcoal/coke in the past before burying(Conducts electrcity.) Dunno if that's still done. Soil in trench has to be well compacted and wetted down to ensure intimate contact. *Lots of problems arose when gas and water pipes became plastic instead of metal. If you have metal gas or water pipes coming into the house, you can get an indication of what's going on by measuring resistance between them and your earth spike. (Before you connect it on to anything.) It should be virtually zero. This however is NOT a proper test but you can find out if your new earth spike is likely to have a good effect or not.- Hide quoted text - - Show quoted text - I'd say your assessment of the earth being supported by the old metal underground pipes is correct. Forget all the above comments about using ground spikes on their own and get a pro with an earth fault loop impedance tester to check it correctly. Its very unlikely that an earth spike or multiple earth spikes will be adequate to solve your problem in most parts of the uk as you will typically have ground loop resistances in excess of 15 ohms and maybe as high as the hundreds. Unless the supply undertaking are willing to provide you with a low impedance earth terminal you should change to a TT system with RCD protection. |
#7
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 2 Sep, 20:44, John Rumm wrote:
Careful there - it sounds like the OP has what is intended to be a TN-S supply where the earth is provided by the supplier. That last thing he wants to do is start messing about providing his own earth connection when that is the supplier's responsibility. It would also potentially mean changing the whole installation to make it suitable for TT rather than TN-S. John, Many thanks for your input - and thanks to all others for information and comment. My understanding is my present situation is an earthing through an available pipe (the one containing the incoming supply), but that both British Gas (boiler electrician) and DNO electrian are saying I need a DNO-provided connection to the incoming cabling rather than being earthed through the pipe. I assume that would then give me the TN-S you refer to. They gave the impression it should be straightforward and I just request it from DNO. My concerns are the vintage looks of the DNO supply to the house and whether it's as straightforward as that (much like the vintage gas supply pipes that have just been replaced). I take the point from others that an amateur can't easily accurately measure the earth resistance at main connector or sockets. All the cheap socket testers just seem to distinguish between some level of earth and no earth and the more expensive (sok34) type only give three levels of LCD display of qualitative earthing effectiveness. I've contacted the DNO again to try and speed up the initial assessment - I think they should be the first option. I'm in a residential area of a large city but mainly older property (1930s) and, understandably, the public supply water, gas and electricity pipes/cables are/were somewhat elderly. I can't be the only one who has needed new earthing and I'm hoping DNO provide a viable solution. Otherwise, if I understand the electrician, I think some sort of front- end RCD to the whole system was what he was suggesting as a possible option. Thanks again Regards, Toom |
#8
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
John Rumm wrote:
The way in which an earth loop impedance meter will test, is to apply a known voltage to the earth, and measure the current that flows down it. ... The theory: ... Nice explanation. But for the process to work, there is an underlying assumption that there is a practically zero ohm connection between N and E somewhere out there (i.e. that N and E are well bonded together at the substation or wherever the supply is coming from). That being the case, why would it not suffice simply to measure the DC resistance between N and E directly with an ordinary multimeter? Another question is how nearly zero "practically zero" really is. Where highish currents are involved, there will be a voltage drop in the mains cable supplying the house, i.e. across the cable impedances Zl and Zn in the diagram below. Zl L ----------------/\/\/\/\/\----------------- L House N ----------------/\/\/\/\/\--------------+-- N Substation Zn | E ----/\/\/\/\--+ +--/\/\/\/\--+ Zeh | | Zes | Zee | +--/\/\/\/\--+ Zes is the earth impedance at the substation end which is presumed to be of very high quality (of the order of milliohms I guess), and Zeh is the earth impedance at the house end which is under test. Zee is the "real" (non-cable) earth path impedance which is presumed (isn't it?) also to be virtually zero. Now when you connect your shunt in the first instance between L and N for calibration purposes, and subsequently move it to between L and E, what you are calculating from your measurements isn't Zeh, but it is the amount by which Zeh+Zee+Zes exceeds Zn. Zee+Zes can be disregarded as being of a lower order of magnitude, but I wouldn't expect Zn to be small enough to ignore when we're expecting Zeh to be less than 0.3 ohm. Is it normal practice to measure Zn (actually to measure Zl+Zn and to assume Zn is half that) by measuring the voltage between L and N under no-load and known high-load conditions, and to take this into account when calculating Zeh? |
#9
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Fri, 03 Sep 2010 01:33:49 -0700, Toom Tabard wrote:
My understanding is my present situation is an earthing through an available pipe (the one containing the incoming supply), but that both British Gas (boiler electrician) and DNO electrian are saying I need a DNO-provided connection to the incoming cabling rather than being earthed through the pipe. I assume that would then give me the TN-S you refer to. They gave the impression it should be straightforward and I just request it from DNO. My concerns are the vintage looks of the DNO supply to the house and whether it's as straightforward as that (much like the vintage gas supply pipes that have just been replaced). We have an incomer that dates back to the 1920s (still has a tag saying "Herne Bay Electricity Supply Company". The conversion to TN-S took very little time - minutes. I take the point from others that an amateur can't easily accurately measure the earth resistance at main connector or sockets. All the cheap socket testers just seem to distinguish between some level of earth and no earth and the more expensive (sok34) type only give three levels of LCD display of qualitative earthing effectiveness. That's right....and they don't do that under the same conditions, either. Bear in mind that with TN-S you need to be careful with appliances used outside the house - an RCD on them, at minimum, is a must - even if you don't immediately have RCDs elsewhere. -- Use the BIG mirror service in the UK: http://www.mirrorservice.org *lightning protection* - a w_tom conductor |
#10
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 02/09/2010 19:16, Fredxx wrote:
"Dave Plowman wrote in message ... In article , Toom wrote: What I don't understand is how to find impedance down earth pipe and at socket with a multimeter. In practice, you can't. You need a proper tester which just looks a bit like a multi-meter. It puts a very large load to earth on the circuit for a fraction of a second and measures the current flow, and from that calculates the impedance. They are quite expensive devices and need regular calibration. Wouldn't a 3 bar electric fire between live and earth do the job? Where you measure the voltage (change) between earth and neutral? Resistance = voltage / current through fire? That would work well, I think, in the absence of more sophisticated equipment. Many years ago I was having problems with hum in a particular piece of equipment. The problem only occurred first thing in the morning, so I swapped out the obvious part for further examination. When I'd done so, every thing was perfect, as anticipated. Until the following morning! I missed that day's display but turned up bright and early the following day to witness the problem at its most severe. It defied all logic and I was desparate but luck was on my side. It was an office in old building and the corner I was working in wasn't very well lit - it was mid winter and natural light was virtually non-existent. As I disconnected an earthed cable I saw a minute spark between the connector and the earthed chassis. I plugged it back in again and, almost immediately, I noticed the fault condition sharply reduce in intensity - and realised that a girl was just returning to her desk after turning down the fan heater they were using to supplement the central heating ... I immediately realised that earth and neutral must be reversed somewhere along the line and connected a meter between the 'earthed' chassis and the cable that I knew was most definitely earthed down in the basement. Each kilowatt step on the fan heater produced a voltage drop of 500mV or so and the hum was obviously being injected by the hefty AC current passing through the screen of the cable. I was deceived on my first visit, of course, because, by the time I'd got the kit going again, the temperature had risen sufficiently for the temporary fan heater to be switched off completely for the rest of the day ... -- Terry |
#11
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 3 Sep, 09:51, Bob Eager wrote:
On Fri, 03 Sep 2010 01:33:49 -0700, Toom Tabard wrote: My understanding is my present situation is an earthing through an available pipe (the one containing the incoming supply), but that both British Gas (boiler electrician) and DNO electrian are saying I need a DNO-provided connection to the incoming cabling rather than being earthed through the pipe. I assume that would then give me the TN-S you refer to. They gave the impression it should be straightforward and I just request it from DNO. My concerns are the vintage looks of the DNO supply to the house and whether it's as straightforward as that (much like the vintage gas supply pipes that have just been replaced). We have an incomer that dates back to the 1920s (still has a tag saying "Herne Bay Electricity Supply Company". The conversion to TN-S took very little time - minutes. Thanks for that - gives me some hope that it's easy. DNO emergency electrician didn't comment on obvious vintage and seemed to think it would about an hour's work for their connections division. Suppose I'm just a bit jaded after doing so much recent refurbishment of my 1930's house, where you start something, and uncover another problem, and when you start to fix that .... - the new McCarthy and Stone retirement apartments across the road are almost starting to look like an attractive option for me. Toom |
#12
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article , John
Rumm writes Not all multimeters take kindly to being placed across a live circuit on their ohms range. ![]() an unguarded moment! -- (\__/) (='.'=) (")_(") |
#13
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
In article ,
Mike Tomlinson wrote: In article , John Rumm writes Not all multimeters take kindly to being placed across a live circuit on their ohms range. ![]() an unguarded moment! I had the magic smoke from a well used Maplin Gold DVM when measuring mains voltage - and it was on the correct setting. Investigation showed brass dust from the switch tracks has caused it to flash over. Managed to fix it, though. -- *Consciousness: That annoying time between naps. Dave Plowman London SW To e-mail, change noise into sound. |
#14
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
John Rumm wrote:
On 04/09/2010 05:17, Mike Tomlinson wrote: In articleC9udna_20fKfpBzRnZ2dnUVZ8q2dnZ2d@brightvie w.co.uk, John writes Not all multimeters take kindly to being placed across a live circuit on their ohms range. o) I think we've all tried to measure the resistance of the mains in an unguarded moment! Yup, I still have most of the probe left to prove it ;-) (amazingly the meter survived (an ICE Multitest 80), although that ohms range was always a bit suspect after) I like the fuse in my 17th edition tester. -- Adam |
#15
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 4 Sep, 15:18, "ARWadsworth" wrote:
ohms range was always a bit suspect after) I like the fuse in my 17th edition tester. -- Adam The definition of a semiconductor is an expensive fast acting device to open circuit in time to protect a cheap fuse |
#16
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
cynic wrote:
The definition of a semiconductor is an expensive fast acting device to open circuit in time to protect a cheap fuse You want to see the price of the fast acting fuses recommended to protect the solid state relays controlling dad's kiln, I think he has given up on the fuses as the relays are cheaper to replace. |
#17
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
cynic wrote:
On 4 Sep, 15:18, "ARWadsworth" wrote: ohms range was always a bit suspect after) I like the fuse in my 17th edition tester. -- Adam The definition of a semiconductor is an expensive fast acting device to open circuit in time to protect a cheap fuse Not so expensive these days. Compare the cost of a diode and a fuse.. |
#18
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 4 Sep,
Andy Burns wrote: You want to see the price of the fast acting fuses recommended to protect the solid state relays controlling dad's kiln, I think he has given up on the fuses as the relays are cheaper to replace. I came across that in a 110 volt 3 phase to DC transformer many years ago. The fast acting fuses were failing frequently costing about £3 to replace. The diodes they were protecting were about 80p each. After replacing the fuses with cheaper ones fast enough to protect for overload, neither the fuses or the diodes failed. -- B Thumbs Change lycos to yahoo to reply |
#19
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]() |
#20
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On Sat, 04 Sep 2010 17:10:33 +0100, Andy Burns
wrote: cynic wrote: The definition of a semiconductor is an expensive fast acting device to open circuit in time to protect a cheap fuse You want to see the price of the fast acting fuses recommended to protect the solid state relays controlling dad's kiln, I think he has given up on the fuses as the relays are cheaper to replace. It's the same with a stage lighting dimmer pack we had at a local theatre. However it was much quicker to replace the very fast-acting fuse than the triac. -- Frank Erskine |
#21
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
wrote:
I came across that in a 110 volt 3 phase to DC transformer many years ago. The fast acting fuses were failing frequently costing about £3 to replace. The diodes they were protecting were about 80p each. After replacing the fuses with cheaper ones fast enough to protect for overload, neither the fuses or the diodes failed. On a rather larger scale, the substantial semiconductors used in the Traction Convertor in APT-P had pretty large (1) and expensive fuses which appeared to be blowing spuriously. Upon opening them up for investigation, the internal structure was of multiple parallel thin copper strips, with sections punched out to create lots of necking points in series. Close examination showed that the necking points which had shared the arcing when it blew all had little blobs of fused sand (with which the fuse cartridge was filled). However, there were also a fair number of clean breaks, and it was eventually determined that they were failing mechanically due to vibration, and thus as the number of parallel paths reduced, the current capacity slowly degraded. (1) In the region of 1000 V, several hundred amps. Chris -- Chris J Dixon Nottingham UK Have dancing shoes, will ceilidh. |
#22
![]()
Posted to uk.d-i-y
|
|||
|
|||
![]()
On 3 Sep, 19:25, John Rumm wrote:
.......... Yup TT would be one option. Note also though that in many cases the supplier can upgrade an installation to TN-C-S these days. Perhaps a first step is finding out what earthing they think you have! John, many thanks again for so much clear and useful info Two weeks after their quick initial safety check, Scottish Power project manager (seemed to be purely administrative) turned up at door and simply looked at installation. Couldn't tell what they can do because incoming cable is completely sheathed in pipe!! Situation is, they'll send me a quote for what standard earthing will cost. I prepay and send signed acceptance, then job goes into queue - so it could be six weeks before they can tell me if they can do it in which case they'll do it then!!!! No option for sending someone qualified and equipped now. Seems another case where company procedures trounce customer requirements. Meantime, I think I'd better enquire about options in case I'm left high and dry. Before calling in commercial contractors, I've been trying to find some local (Edinburgh) independent electrical installation inspector or consultant to give impartial advice for a fee, but can't locate even one. Thanks for explaining what the options are and pointing to other info. Regards Norman |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
![]() |
||||
Thread | Forum | |||
A collection of electrical earthing questions | UK diy | |||
Electrical earthing | UK diy |