My electric wiring was done 25+ years ago, professionally, has given
no problems, and is still in good nick. Earthing, not now compliant, is by bonding to the incoming pipe containing power supply cable and that seemed to work. British Gas heating advisor came to estimate for new boiler 2 weeks ago, tested my power sockets with 'socket and see' device and everything ok including earthing. Engineer came to install boiler yesterday and his 'socket and see' showed earthing totally inadequate. Electrician then did more detailed measurement and got earth reading of 5ohms (should be under 1). Boiler installation now postponed, and can't really expect anyone to work on faults on existing boiler The one possibly relevant thing in the two weeks has been gas mains in street and up to house renewed with plastic pipes. Meter is now outside with no earthing. Equipotential bonding is on copper pipe pipe from meter just after it enters house. It used to be on consumer side of internal meter. Could it be that the iron supply pipe (now disconnected) on other (supply) side of the meter was providing some of the earthing for my electricity circuits through the equipotential bonding? Power distribution is responsibilty of Scottish Power who are coming to look at fitting fused cut out and mains earthing terminal at consumer supply point. Apparently so many people are finding their houses non-compliant for various reasons that I may join a 6-8 week queue. Anyone know of any other compliant answer to getting earthing to required level? Thanks Toom |
#2
Posted to uk.d-i-y
|
|||
|
|||
Earthing
On 26 Aug, 18:26, Toom Tabard wrote:
My electric wiring was done 25+ years ago, professionally, has given no problems, and is still in good nick. Earthing, not now compliant, is by bonding to the incoming pipe containing power supply cable and that seemed to work. British Gas heating advisor came to estimate for new boiler 2 weeks ago, tested my power sockets with 'socket and see' device and everything ok including earthing. Engineer came to install boiler yesterday and his 'socket and see' showed earthing totally inadequate. Electrician then did more detailed measurement and got earth reading of 5ohms (should be under 1). Boiler installation now postponed, and can't really expect anyone to work on faults on existing boiler The one possibly relevant thing in the two weeks has been gas mains in street and up to house renewed with plastic pipes. Meter is now outside with no earthing. Equipotential bonding is on copper pipe pipe from meter just after it enters house. It used to be on consumer side of internal meter. Could it be that the iron supply pipe (now disconnected) on other (supply) side of the meter was providing some of the earthing for my electricity circuits through the equipotential bonding? Power distribution is responsibilty of Scottish Power who are coming to look at fitting fused cut out and mains earthing terminal at consumer supply point. Apparently so many people are finding their houses non-compliant for various reasons that I may join a 6-8 week queue. Anyone know of any other compliant answer to getting earthing to required level? Thanks Toom Convert the installation to TT. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Earthing
On 26/08/2010 19:08, cynic wrote:
On 26 Aug, 18:26, Toom wrote: My electric wiring was done 25+ years ago, professionally, has given no problems, and is still in good nick. Earthing, not now compliant, is by bonding to the incoming pipe containing power supply cable and that seemed to work. British Gas heating advisor came to estimate for new boiler 2 weeks ago, tested my power sockets with 'socket and see' device and everything ok including earthing. Engineer came to install boiler yesterday and his 'socket and see' showed earthing totally inadequate. Electrician then did more detailed measurement and got earth reading of 5ohms (should be under 1). Boiler installation now postponed, and can't really expect anyone to work on faults on existing boiler The one possibly relevant thing in the two weeks has been gas mains in street and up to house renewed with plastic pipes. Meter is now outside with no earthing. Equipotential bonding is on copper pipe pipe from meter just after it enters house. It used to be on consumer side of internal meter. Could it be that the iron supply pipe (now disconnected) on other (supply) side of the meter was providing some of the earthing for my electricity circuits through the equipotential bonding? Power distribution is responsibilty of Scottish Power who are coming to look at fitting fused cut out and mains earthing terminal at consumer supply point. Apparently so many people are finding their houses non-compliant for various reasons that I may join a 6-8 week queue. Anyone know of any other compliant answer to getting earthing to required level? Thanks Toom Convert the installation to TT. Which will mean RCD protection and an earth spike. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Earthing
"Toom Tabard" wrote in message
... My electric wiring was done 25+ years ago, professionally, has given no problems, and is still in good nick. Earthing, not now compliant, is by bonding to the incoming pipe containing power supply cable and that seemed to work. British Gas heating advisor came to estimate for new boiler 2 weeks ago, tested my power sockets with 'socket and see' device and everything ok including earthing. Engineer came to install boiler yesterday and his 'socket and see' showed earthing totally inadequate. Electrician then did more detailed measurement and got earth reading of 5ohms (should be under 1). Boiler installation now postponed, and can't really expect anyone to work on faults on existing boiler The one possibly relevant thing in the two weeks has been gas mains in street and up to house renewed with plastic pipes. Meter is now outside with no earthing. Equipotential bonding is on copper pipe pipe from meter just after it enters house. It used to be on consumer side of internal meter. Could it be that the iron supply pipe (now disconnected) on other (supply) side of the meter was providing some of the earthing for my electricity circuits through the equipotential bonding? Power distribution is responsibilty of Scottish Power who are coming to look at fitting fused cut out and mains earthing terminal at consumer supply point. Apparently so many people are finding their houses non-compliant for various reasons that I may join a 6-8 week queue. Anyone know of any other compliant answer to getting earthing to required level? After 25 years you should seriously consider getting the entire wring system checked by NICEIC qualified electrician. Peter Crosland |
#5
Posted to uk.d-i-y
|
|||
|
|||
Earthing
After 25 years you should seriously consider getting the entire wring
system checked by NICEIC qualified electrician. NICEIC are not the only game in town (albeit they try to give the impression people they are). Other "competent persons schemes" for installers who can do all electrical installation work are BSI, EC Certification Limited / ELECSA and NAPIT (And yes, I dislike monopolies and wannabe monopolies.) -- Robin PM may be sent to rbw0{at}hotmail{dot}com |
#6
Posted to uk.d-i-y
|
|||
|
|||
Earthing
On Aug 26, 8:41*pm, "Peter Crosland" wrote:
After 25 years you should seriously consider getting the entire wring system checked Conflict of interest between those doing the PIR and those wanting to do remedials :-) It sounds like the OP has 2 issues. #1 - Supplier earth is not up to specification. A DNO provided earth must be maintained once provided. If the supply is TN-C-S (PME) or TN-S the Ze figure should be 0.35ohm or 0.80ohm respectively. If the figure is 5ohms then it sounds like the old metal gas pipe was contributing to the earth. An out of spec earth is an emergency callout if it is sufficiently out of spec, 5ohms will mean no more than 50 Amps will flow to earth which will either result in a delayed fault disconnect (seconds to minutes) or no fault disconnect (40A shower). Worse 5ohms may be at "15mA earth fault loop impedance (EFLI) tester current" and I would much rather know a 25Amp high current EFLI test result - which might potentially be substantially worse. #2 - Main Equipotential Bonding is not current. I suspect the cold water pipe if metal is providing some or all of the earth, it comes down to what supply type the OP has. At present I would want... 1 - an electrician to check a) what supply type you have b) whether the cold water main is providing the earth b) whether MEB is correct (mainly re in-place and sized correctly). 2 - a conversion to a "TT supply" temporarily or permanently, that is where you have individual RCBO or a front-end RCD to the whole house temporarily until the DNO can get their bods on your doorstep. If you have an electrical fault with a 5ohm Ze then insufficient current may flow to blow a fuse or trip a circuit breaker, either in a timely manner (0.4-4sec disconnect depending on appliance type/risk) or without overheating wiring sufficiently to cause permanent damage or fire. Personally I would have a spark check and convert to TT as mentioned. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Earthing
On 26 Aug, 22:08, "js.b1" wrote:
On Aug 26, 8:41*pm, "Peter Crosland" wrote: After 25 years you should seriously consider getting the entire wring system checked Conflict of interest between those doing the PIR and those wanting to do remedials :-) It sounds like the OP has 2 issues. #1 - Supplier earth is not up to specification. A DNO provided earth must be maintained once provided. If the supply is TN-C-S (PME) or TN-S the Ze figure should be 0.35ohm or 0.80ohm respectively. If the figure is 5ohms then it sounds like the old metal gas pipe was contributing to the earth. An out of spec earth is an emergency callout if it is sufficiently out of spec, 5ohms will mean no more than 50 Amps will flow to earth which will either result in a delayed fault disconnect (seconds to minutes) or no fault disconnect (40A shower). Worse 5ohms may be at "15mA earth fault loop impedance (EFLI) tester current" and I would much rather know a 25Amp high current EFLI test result - which might potentially be substantially worse. #2 - Main Equipotential Bonding is not current. I suspect the cold water pipe if metal is providing some or all of the earth, it comes down to what supply type the OP has. At present I would want... 1 - an electrician to check a) what supply type you have b) whether the cold water main is providing the earth b) whether MEB is correct (mainly re in-place and sized correctly). 2 - a conversion to a "TT supply" temporarily or permanently, that is where you have individual RCBO or a front-end RCD to the whole house temporarily until the DNO can get their bods on your doorstep. If you have an electrical fault with a 5ohm Ze then insufficient current may flow to blow a fuse or trip a circuit breaker, either in a timely manner (0.4-4sec disconnect depending on appliance type/risk) or without overheating wiring sufficiently to cause permanent damage or fire. Personally I would have a spark check and convert to TT as mentioned. Thanks to all who replied - that info is very helpful. I'm not an electrician and don't understand all the terminology used. But, if a gas meter can allow a continuous circuit - can it? - metal pipe to metal chassis to metal pipe? - then that might explain the earth working the other way into the iron supply pipe and maybe helping earth the whole house, and why the change to unearthed external meter/ box with plastic supply pipe has made a difference. I called in a senior technician from the gas supply renewal company, who are still working in the area - he seemed unaware that that could happen and is interested to find out if it is the cause - I suppose few folk happen to have their earthing tested just before and then just after gas supply replacement. The distribution company - Scottish power - did send someone within hours. They checked it out, but merely said I should phone their installation dept and arrange for them to come fit their standard earthing. He did mention the possibility of getting an electrician to fit a front end RCD meantime but said they'd need to check if that was regs 17? compliant - he wasn't sure. Neither boiler company nor distribution company electrician gave any indication of it being an emergency situation, and there is this mention of 6 - 8 week queue for rectification of many similar situations - mainly where water mains and water supply pipes have been replaced with plastic. Scottish Power are sending someone to look at rectification in detail - but not for several days. I'll look into it further, since a more urgent temporary or permanent fix seems needed, both for safety and to get boiler installation moving. Thanks again to all Toom |
#8
Posted to uk.d-i-y
|
|||
|
|||
Earthing
"Toom Tabard" wrote in message ... On 26 Aug, 22:08, "js.b1" wrote: On Aug 26, 8:41 pm, "Peter Crosland" wrote: I called in a senior technician from the gas supply renewal company, who are still working in the area - he seemed unaware that that could happen and is interested to find out if it is the cause - I suppose few folk happen to have their earthing tested just before and then just after gas supply replacement. The distribution company - Scottish power - did send someone within hours. They checked it out, but merely said I should phone their installation dept and arrange for them to come fit their standard earthing. He did mention the possibility of getting an electrician to fit a front end RCD meantime but said they'd need to check if that was regs 17? compliant - he wasn't sure. The senior technician is just being dozy, either deliberately or otherwise. In other areas, where utility companies work on gas or water mains replacing metal with plastic they send postcards out to affected consumers warning them of the possible effect on earthing and that it is the customer's responsibility to sort out. You have done well to get the supplier to do something about it, particularly if they will sort out the earthing for free. In many areas, DNOs seem to try to deny they provided the original earth and so it becomes the consumer's problem via his electrician. Regards Bruce |
#9
Posted to uk.d-i-y
|
|||
|
|||
Earthing
On 27 Aug, 13:56, "BruceB" wrote:
"Toom Tabard" wrote in message ... On 26 Aug, 22:08, "js.b1" wrote: On Aug 26, 8:41 pm, "Peter Crosland" wrote: I called in a senior technician from the gas supply renewal company, who are still working in the area - he seemed unaware that that could happen and is interested to find out if it is the cause - I suppose few folk happen to have their earthing tested just before and then just after gas supply replacement. The distribution company - Scottish power - did send someone within hours. They checked it out, but merely said I should phone their installation dept and arrange for them to come fit their standard earthing. He did mention the possibility of getting an electrician to fit a front end RCD meantime but said they'd need to check if that was regs 17? compliant - he wasn't sure. The senior technician is just being dozy, either deliberately or otherwise. In other areas, where utility companies work on gas or water mains replacing metal with plastic they send postcards out to affected consumers warning them of the possible effect on earthing and that it is the customer's responsibility to sort out. Electricians and Scottish Power have both mentioned the problems when earthing is to water pipes and these are replaced with plastic. Senior technician for gas pipe replacement said they leave cards when they notice the equipotential bonding on internal gas pipes isn't there, or isn't correctly positioned. Position of mine isn't quite correct but that wasn't mentioned at the time or by card. It does seem they could be a bit more consumer friendly about it, but general approach seems to be they do their bit and don't want to get involved in the complexities which exist or which they cause in individual houses. In my case, if equipotential bonding was incidentally giving earthing to my electrics through old metal gas pipe, then that seemed something technician didn't know about, but wanted to find out more. Said he knew all about equipotential bonding for gas regulations, but did know domestics electrics. You have done well to get the supplier to do something about it, particularly if they will sort out the earthing for free. *In many areas, DNOs seem to try to deny they provided the original earth and so it becomes the consumer's problem via his electrician. I gather from engineer that what is supplied and fitted at consumer unit is at customers expense and it's a good earner for the company. Any problem with earthing from there to distribution system is company's problem/expense. Regards Toom |
#10
Posted to uk.d-i-y
|
|||
|
|||
Earthing
Peter Crosland wrote:
"Toom Tabard" wrote in message ... After 25 years you should seriously consider getting the entire wring system checked by NICEIC qualified electrician. I disagree. Provided that the circuits have not been modified in the time being, there is no need to have it checked. Be aware, the Elfins are about. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Earthing Again | UK diy | |||
Yet more earthing.... | UK diy | |||
Earthing | UK diy | |||
Earthing | UK diy |