Hi all,

What is the position with calculating grouping for cables at the consumer
unit?

In my proposed location, I would have a 50x50mm trunking over the top of the
CU, that then meets the same size trunking running from the floor to the
ceiling of the ground floor. (It's all going to end up in a corner cupboard,
so the trunking won't look as bad as it sounds it might!)

So all cables will be grouped together over about 50cm over the top of the
CU (Starting with one cable at the far end, gradually increasing over the
width of the CU)

Then the following cables that go upstairs, and are grouped for about
1.4m...
Upstairs rung (2x2.5mm T&E)
Upstairs lights (1x1.5mm T&E)
Downstairs lights (1x1.5mm T&E)
Outside lights (1x 1.5mm T&E)
Loft Power (1x2.5mm T&E)
Emergency lighting (1x1.5 T&E)

Then the following cables that go under the ground floor, and are grouped
for about 1m...
Kitchen ring
Downstairs ring 2x2.5mm
Alarm 1x1.5mm
Fridge 1x2.5mm
Hob 1 x 6mm
Oven 1x2.5mm
Microwave 1x2.5mm
Air Conditioning 1x2.5mm (20A radial)

There is also a separate SWA cable for the garage, but this is on its own.

Thanks for any pointers!

Toby...

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,683
Default Cable grouping at Consumer Unit

On Jun 28, 3:04*pm, "Toby" wrote:
What is the position with calculating grouping for cables at the consumer
unit?
In my proposed location, I would have a 50x50mm trunking

....
It's all going to end up in a corner cupboard,
so the trunking won't look as bad as it sounds it might!


Flat Twin & Earth is rated to Medium Impact Duty (AG2).
Domestic Environment is classed as Low Impact environment (AG1).

Since "it's all going to end up in a corner cupboard" I would dispense
with trunking, or at least use multiple 38x25mm trunking and run a
nominal number of cables through each.

As a guide cables loaded to 30% of their grouped rating can be
disregarded for grouping purposes. In practice this means that
lighting up, lighting down, smoke, outside socket, security light
supplying cables may be disregarded from grouping calculations (ie, a
1.5mm cable protected by 6A Overcurrent (OC) device).

Likewise if your main fuse is 60A and it is obvious from cable routing
that whilst some (cooker, shower) cables may be drawing 16A (cooker
diversity) & 45A (shower has no diversity) then other cables will
actually be essentially zero, then grouping can be disregarded. It is
common in domestic for cables to be grouped seemingly "against
regulations", however a proper consideration can show the decision is
quite sound.

Where you can not ignore grouping is where you (say) ran the cooker &
shower cable against one another, or through insulation.

For practical purposes I would not consider using 50x50mm trunking,
but instead 2-3 38x25mm - thereby automatically spreading cables out
between the 2-3 "ducts". Lighting cables are your friend in that they
can be disregarded.

I notice you have air conditioning in there, if it is wall mounted
(off the ground) it does not require bonding back to the MET, however
if it is sat on concrete it does - so consider that when routing
cables. I would leave one trunking almost empty in order to add future
circuits as necessary.

If this is "all new", fit a larger CU than you might consider
originally, and size the cupboard accordingly. If the shed has its own
sub-main CU, you may want to put the HVAC on that side of things - re
"outdoor stuff". Same goes for security lighting, so it does not trip
out the house lights or a ring with the fridge/freezer on it for
example.
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Cable grouping at Consumer Unit


"Toby" wrote in message
...
Hi all,

What is the position with calculating grouping for cables at the consumer
unit?

In my proposed location, I would have a 50x50mm trunking over the top of
the CU, that then meets the same size trunking running from the floor to
the ceiling of the ground floor. (It's all going to end up in a corner
cupboard, so the trunking won't look as bad as it sounds it might!)

So all cables will be grouped together over about 50cm over the top of the
CU (Starting with one cable at the far end, gradually increasing over the
width of the CU)

Then the following cables that go upstairs, and are grouped for about
1.4m...
Upstairs rung (2x2.5mm T&E)
Upstairs lights (1x1.5mm T&E)
Downstairs lights (1x1.5mm T&E)
Outside lights (1x 1.5mm T&E)
Loft Power (1x2.5mm T&E)
Emergency lighting (1x1.5 T&E)

Then the following cables that go under the ground floor, and are grouped
for about 1m...
Kitchen ring
Downstairs ring 2x2.5mm
Alarm 1x1.5mm
Fridge 1x2.5mm
Hob 1 x 6mm
Oven 1x2.5mm
Microwave 1x2.5mm
Air Conditioning 1x2.5mm (20A radial)

There is also a separate SWA cable for the garage, but this is on its own.

Thanks for any pointers!

Toby...


Start with

http://www.tlc-direct.co.uk/Book/4.3.5.htm

But with all the diversity that you have thrown in then there is little
chance of anything but the aircon running at or near full load for any
length of time.

Why does the emergency lighting have it's own supply?

Cheers

Adam


  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 298
Default Cable grouping at Consumer Unit

"ARWadsworth" wrote in message
news:IMjWn.58926$NW.40970@hurricane...

"Toby" wrote in message
...
Hi all,

What is the position with calculating grouping for cables at the consumer
unit?

In my proposed location, I would have a 50x50mm trunking over the top of
the CU, that then meets the same size trunking running from the floor to
the ceiling of the ground floor. (It's all going to end up in a corner
cupboard, so the trunking won't look as bad as it sounds it might!)

So all cables will be grouped together over about 50cm over the top of
the CU (Starting with one cable at the far end, gradually increasing over
the width of the CU)

Then the following cables that go upstairs, and are grouped for about
1.4m...
Upstairs rung (2x2.5mm T&E)
Upstairs lights (1x1.5mm T&E)
Downstairs lights (1x1.5mm T&E)
Outside lights (1x 1.5mm T&E)
Loft Power (1x2.5mm T&E)
Emergency lighting (1x1.5 T&E)

Then the following cables that go under the ground floor, and are grouped
for about 1m...
Kitchen ring
Downstairs ring 2x2.5mm
Alarm 1x1.5mm
Fridge 1x2.5mm
Hob 1 x 6mm
Oven 1x2.5mm
Microwave 1x2.5mm
Air Conditioning 1x2.5mm (20A radial)

There is also a separate SWA cable for the garage, but this is on its
own.

Thanks for any pointers!

Toby...


Start with

http://www.tlc-direct.co.uk/Book/4.3.5.htm

But with all the diversity that you have thrown in then there is little
chance of anything but the aircon running at or near full load for any
length of time.

Why does the emergency lighting have it's own supply?

Cheers

Adam


Thanks Adam - I did think with all the diversity it would be fine.
I can route the A/C separately easily too, as it needs to go straight
outside to an isolator near the external (wall mounted) unit before going
anywhere else.

This A/C is actually a three way split system with three seperate
compressors(9,9,18K BTU) and it is unlikley I would have all three units
running at the same time, as I have the two 9k units in bedroom 1 and 2 and
the 18k unit in the through lounge diner, as they are reversable, I can also
use them as a backup or addition to the gas fired boiler for space heating.

The upstairs EL is powered from the upstairs lighting RCBO, and the
downstairs for the downstairs RCBO, but I have installed two of the MK
secret key switches above the CU, plus two normal switches (all on a 4 way
MK Grid plate), so I can put them on test without taking out the lighting
circuits and so I can also switch them on if I want to just use them as a
light (They are flush fitting, maintained fittings, so don't look too bad in
a domestic setting IMO, although the hyper bright greed LED may be dimmed
later!). so it is actually three core and earth cable to them from the
switch plate above the CU.

Toby...


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Moving a Consumer Unit. Cable extension "best practice" question. [PING Andy Gabriel] Vortex4 UK diy 5 October 29th 09 01:11 PM
New consumer unit Terry D[_2_] UK diy 9 December 2nd 07 02:34 PM
Cable Grouping Factor Confusion TheScullster UK diy 2 October 16th 06 11:21 PM
Cable size for fused connection straight from consumer unit keith UK diy 3 November 6th 04 10:15 PM


All times are GMT +1. The time now is 05:01 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"