More Electrical/Kitchen Qs
Hi all
More of this electrickery stuff I'm afraid! Looking on the TLC web site, there is text that states that an outdoor socket must be on a dedicated 30mA RCD. If this was fed from an existing kitchen ring, wouldn't there be a problem with discrimination between the local socket protection and the circuit protection at the CU? Is there an outdoor socket with integral RCD and can I back-to-back this through an external wall with a kitchen socket IYSWIM? Any comments on height of sockets above worktops? Googling suggests that opinions are split either centering the sockets between worktop and underside of wall cupboards or specifically not centering or doing something that will marry with the tiles being used. As we aren't at tile choosing stage, I don't want to hold things up waiting for that decision. Similar with worktop thickness (still TBA), so approximate vertical centering is all that is really possible. One group member has suggested that, if I don't move the cooker point, then I don't need to RCD it to bring it up to 17th edition spec. - any other comments from the floor? I am working on the assumption that the install will be inspected by BC appointed sparks, so these issues need to be correct and Part P compliant. Where I have cables through a cavity wall, I understand that a pipe or conduit is required to protect these. What is recommended and is there a split version that I can fit retrospectively (rather than disconnecting and reconnecting exisiting equipment)? I'm sure there were other points, but if I could remember them, the length of the post would probably scare off the regulars! TIA Phil |
#2
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
"John Rumm" wrote in message o.uk... On 17/05/2010 09:18, TheScullster wrote: Hi all More of this electrickery stuff I'm afraid! Looking on the TLC web site, there is text that states that an outdoor socket must be on a dedicated 30mA RCD. It needs to be 30mA - not sure it has to be dedicated. However... If this was fed from an existing kitchen ring, wouldn't there be a problem with discrimination between the local socket protection and the circuit protection at the CU? Is there an outdoor socket with integral RCD and can I back-to-back this through an external wall with a kitchen socket IYSWIM? There is a good case for not having outdoor sockets etc not sharing a RCD with inside ones. Since it increases the liklihood of getting nuisance trips on your house circuits. Where possible it is best practice to try and put the outside sockets on their own RCBO. If that is not possible then I try to power them via a double pole switch so that if they do let water in then they can be isolated without causing any problems. There is no requirement for them to have their own dedicated RCD. Any comments on height of sockets above worktops? Googling suggests that opinions are split either centering the sockets between worktop and underside of wall cupboards or specifically not centering or doing something that will marry with the tiles being used. As we aren't at tile choosing stage, I don't want to hold things up waiting for that decision. Similar with worktop thickness (still TBA), so approximate vertical centering is all that is really possible. Roughly centre works for me, but go with whatever the management deems most desirable ;-) I still put them 6 inchs above the worktop unless otherwise instructed. If it don't line up with the tiles, then that's just an excuse to get a nice lekky tile cutter! vbg. One group member has suggested that, if I don't move the cooker point, then I don't need to RCD it to bring it up to 17th edition spec. - any other comments from the floor? I am working on the assumption that the install A bit more detail would help... i.e. what is there now, do you need it at all? Does it need moving etc. will be inspected by BC appointed sparks, so these issues need to be correct and Part P compliant. Might be worth clarifying with BC what they are anticipating. Technically speaking a part P sparks can only do the work and self certify - they can't certify someone else's work. (However BC may be happy with a sparks just testing / inspecting and reporting on someone else's work - or they may even be happy with accepting your test results if they get the impression you know what you are doing). Where I have cables through a cavity wall, I understand that a pipe or conduit is required to protect these. What is recommended and is there a Not necessarily. Cables should be either: I assumed that Phil was talking about passing a cable through a cavity for the outside socket! If so then use a bit of plastic pipe if you want to. Personally I just pass the cable through the hole. Cheers Adam |
#3
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
"ARWadsworth" wrote in message ... Any comments on height of sockets above worktops? Googling suggests that opinions are split either centering the sockets between worktop and underside of wall cupboards or specifically not centering or doing something that will marry with the tiles being used. As we aren't at tile choosing stage, I don't want to hold things up waiting for that decision. Similar with worktop thickness (still TBA), so approximate vertical centering is all that is really possible. Roughly centre works for me, but go with whatever the management deems most desirable ;-) I still put them 6 inchs above the worktop unless otherwise instructed. That's 6 inches from the worktop to the bottom of the back box. Adam |
#4
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
"John Rumm" wrote in message o.uk... On 17/05/2010 09:18, TheScullster wrote: Hi all More of this electrickery stuff I'm afraid! Looking on the TLC web site, there is text that states that an outdoor socket must be on a dedicated 30mA RCD. It needs to be 30mA - not sure it has to be dedicated. However... I'm struggling to refind the link now If this was fed from an existing kitchen ring, wouldn't there be a problem with discrimination between the local socket protection and the circuit protection at the CU? Is there an outdoor socket with integral RCD and can I back-to-back this through an external wall with a kitchen socket IYSWIM? There is a good case for not having outdoor sockets etc not sharing a RCD with inside ones. Since it increases the liklihood of getting nuisance trips on your house circuits. That I can see, but unfortunately I'm not in a position to route another dedicated feed through. There is no point in having cascaded RCDs though[1], since as you rightly suspect you can't predict whether one or both will trip, and if its one, then which. [1] The exception being when the upstream one is a type S device with a time delay. Any comments on height of sockets above worktops? Googling suggests that opinions are split either centering the sockets between worktop and underside of wall cupboards or specifically not centering or doing something that will marry with the tiles being used. As we aren't at tile choosing stage, I don't want to hold things up waiting for that decision. Similar with worktop thickness (still TBA), so approximate vertical centering is all that is really possible. Roughly centre works for me, but go with whatever the management deems most desirable ;-) Yes I always ask the questions in advance, but it doesn't necessarly absolve me of responsibility unfortunately. If it don't line up with the tiles, then that's just an excuse to get a nice lekky tile cutter! Hmm yes I have been pondering that idea! One group member has suggested that, if I don't move the cooker point, then I don't need to RCD it to bring it up to 17th edition spec. - any other comments from the floor? I am working on the assumption that the install A bit more detail would help... i.e. what is there now, do you need it at all? Does it need moving etc. Yes I need it exactly where it is now. will be inspected by BC appointed sparks, so these issues need to be correct and Part P compliant. Might be worth clarifying with BC what they are anticipating. Technically speaking a part P sparks can only do the work and self certify - they can't certify someone else's work. (However BC may be happy with a sparks just testing / inspecting and reporting on someone else's work - or they may even be happy with accepting your test results if they get the impression you know what you are doing). BC are supposed to inspect at first fix and then test on completion as part of the building notice AIUI - unless the goal posts have moved (again) of course. Where I have cables through a cavity wall, I understand that a pipe or conduit is required to protect these. What is recommended and is there a Not necessarily. Cables should be either: Buried = 50mm from the surface, or Protected by an earthed screen of some form (i.e. earthshild, SWA, MICC, Steel conduit etc), or protected by a 30mA trip RCD. split version that I can fit retrospectively (rather than disconnecting and reconnecting exisiting equipment)? Adding RCD protection is the easiest retrofit in most cases. Had intended fitting RCBOs to the affected circuits but they won't fit in my Clipsal box I'm sure there were other points, but if I could remember them, the length of the post would probably scare off the regulars! Do we look like the type to be scared by a few words ;-) On the strength of your previous posts I would say you were the most unlikely. Thanks John Phil |
#5
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
On Mon, 17 May 2010 17:35:27 +0100 someone who may be Dave Osborne
wrote this:- When the regs (for supplementary bonding) first came out, they were either a bit wishy washy or all-encompassing (I forget which), so in a belt-and-braces, cover-your-arse kind of knee-jerk response, it became the done thing to supplementary bond every little piece of extraneous metal in any location with running water. They were gold plated by some/many. It was always clear that if some metalwork could introduce a potential in a location then its resistance to earth should be measured and it should only be bonded if necessary. -- David Hansen, Edinburgh I will *always* explain revoked encryption keys, unless RIP prevents me http://www.opsi.gov.uk/acts/acts2000...#pt3-pb3-l1g54 |
#6
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
In article ,
"TheScullster" writes: "John Rumm" wrote in message o.uk... On 17/05/2010 09:18, TheScullster wrote: Hi all More of this electrickery stuff I'm afraid! Looking on the TLC web site, there is text that states that an outdoor socket must be on a dedicated 30mA RCD. It needs to be 30mA - not sure it has to be dedicated. However... I'm struggling to refind the link now It can be less than 30mA too. My outdoor socket circuit has a 10mA RCBO. If this was fed from an existing kitchen ring, wouldn't there be a problem with discrimination between the local socket protection and the circuit protection at the CU? Is there an outdoor socket with integral RCD and can I back-to-back this through an external wall with a kitchen socket IYSWIM? There is a good case for not having outdoor sockets etc not sharing a RCD with inside ones. Since it increases the liklihood of getting nuisance trips on your house circuits. That I can see, but unfortunately I'm not in a position to route another dedicated feed through. Include a double pole switch so you can isolate the outdoor circuit from indoors, in the event it gets wet and stops you keeping the indoor circuit on. You might also leave it switched off to stop someone else connecting appliances to it (which is why I have one even though it's a dedicated circuit). Actually, what works well for me is a cooker switch with integral socket in the garage, the cooker switch controlling the outdoor sockets (suitably relabeled). Might be worth clarifying with BC what they are anticipating. Technically speaking a part P sparks can only do the work and self certify - they can't certify someone else's work. (However BC may be happy with a sparks just testing / inspecting and reporting on someone else's work - or they may even be happy with accepting your test results if they get the impression you know what you are doing). BC are supposed to inspect at first fix and then test on completion as part of the building notice AIUI - unless the goal posts have moved (again) of course. That's entirely up to them. There's no requirement for them to test anything in Part P - that's just them gold plating the rules. It was originally envisaged that it would be a simple visual check by the BCO, not requiring specifically qualified electricians. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#7
Posted to uk.d-i-y
|
|||
|
|||
More Electrical/Kitchen Qs
TheScullster wrote:
"John Rumm" wrote in message o.uk... On 17/05/2010 09:18, TheScullster wrote: Any comments on height of sockets above worktops? Googling suggests that opinions are split either centering the sockets between worktop and underside of wall cupboards or specifically not centering or doing something that will marry with the tiles being used. As we aren't at tile choosing stage, I don't want to hold things up waiting for that decision. Similar with worktop thickness (still TBA), so approximate vertical centering is all that is really possible. Roughly centre works for me, but go with whatever the management deems most desirable ;-) Yes I always ask the questions in advance, but it doesn't necessarly absolve me of responsibility unfortunately. If it don't line up with the tiles, then that's just an excuse to get a nice lekky tile cutter! Hmm yes I have been pondering that idea! I think the main issue to consider when setting the socket position is what size tiles you'll be using... if you get it wrong you can end up with just a sliver of tile at the edge of the socket, which looks really ****e. Same issue applies to the horizontal position of the sockets, although bad tile cuts are usually easier to circumvent then. David |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Kitchen Sinks and Electrical Outlets | UK diy | |||
Electrical Outlet and Kitchen sink | Home Repair | |||
kitchen electrical work | UK diy | |||
kitchen electrical questions | Home Repair | |||
Kitchen electrical outlet | UK diy |