I'm contemplating a serious rewire/CU replacement and had a few questions:
- I'll be using SWA to feed the CU some distance from the incoming supply. I've read the excellent terminating SWA article on the wiki, but it is unclear about exactly what size SWA can be cut using bolt croppers. I'll probably be using 10mm2 or 16mm2 SWA - is it reasonable to expect bolt croppers to be fine for cutting these sizes? - Is my supply TN-S or TN-C-S? While I have seperate PE and N entering my building, the PE and N are connect together on my property. I have two wires (11kV?) coming onto my property, which terminate on a larger transformer on a telegraph pole. I can see the PE is provided from underground at the pole, and is connected to the N supply from the transformer. So my thinking is that I'm TN-S if the transformer is considered the power source, but TN-C-S otherwise. Thoughts? (Yes, I have asked my electricity supplier, but they have suggested that I contact the DNO. I haven't yet summoned up the energy to do this.) - I'm considering using a metal CU. From doing a bit of research online it may be a requirement that the supply to this CU is protected by a 100mA time delayed RCD. However, I'm unclear as to whether this is only a requirement for TT systems or whether it's applicable to my scenario. I'll be digging out my 17th ed regs later, but can anyone let me know whether the RCD is a requirement here? - I'm considering a three phase CU, and using this as a single phase CU. I'm unfamiliar with the internal construction of these CUs - is there generally any problems with using a TP CU as a single phase one? (The main obvious issue I've seen is that for the model I'm looking at a DP incoming switch is not available - so I'd have to use a TP one and leave one pole unused. - Finally, any recommendations or brands to steer clear of? I've been looking at the Hager Invicta 3. Thanks, Piers |
#2
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 2010-02-28 19:25:04 +0000, John Rumm said:
- Is my supply TN-S or TN-C-S? While I have seperate PE and N entering my building, the PE and N are connect together on my property. I have two wires (11kV?) coming onto my property, which terminate on a larger transformer on a telegraph pole. I can see the PE is provided from underground at the pole, and is connected to the N supply from the transformer. So my thinking is that I'm TN-S if the transformer is considered the power source, but TN-C-S otherwise. Thoughts? Its not uncommon for TN-C-S to be provided on overhead supplies these days. The fact that there is a join inside your property would suggest TN-C-S. Are there no PME stickers on your head end gear? Nope. (Yes, I have asked my electricity supplier, but they have suggested that I contact the DNO. I haven't yet summoned up the energy to do this.) - I'm considering using a metal CU. From doing a bit of research online it may be a requirement that the supply to this CU is protected by a 100mA time delayed RCD. However, I'm unclear as to whether this is only a requirement for TT systems or whether it's applicable to my scenario. I'll be digging out my 17th ed regs later, but can anyone let me know whether the RCD is a requirement here? The RCD protection of all circuits is nominally only for TT type systems (although the 17th edition nudges you closer to that anyway for all systems) The fundamental question to answer is your earth loop impedance at the supply adequate to clear a line to earth fault in the CU. If it is then a metal CU is fine, and TT style protection is not required. OK, thanks. I'll be asking the DNO for max Ze as well as supply type, but I'm guessing it's worth me measuring myself as well? - I'm considering a three phase CU, and using this as a single phase CU. I'm unfamiliar with the internal construction of these CUs - is there generally any problems with using a TP CU as a single phase one? They tend to be of higher quality construction than the domestic ones. The main objections to using one would be cost and size. Do you anticipate having three phase supplied to it in the future then? I see a number of benefits: - Better quality construction. - Better looks - more industrial and less cheap white plastic (the new CU will be fairly exposed, both due to the convenient location and also to ensure accessibility). - More space inside for wiring (I hate fiddling around inside normal CUs). - Many way - I've identified the need for at least 18 circuits and want to leave room for expansion. I've got my eyes on either an 8 way or 12 way TP CU. (The main obvious issue I've seen is that for the model I'm looking at a DP incoming switch is not available - so I'd have to use a TP one and leave one pole unused. I would expect the incomer to have 4 poles - one for each phase and neutral. The CUs would normally supply a good number of single phase circuits. You're right - most of them are 4 pole (but there are a few 3 pole ones). - Finally, any recommendations or brands to steer clear of? I've been looking at the Hager Invicta 3. In my limited experience of the three phase kit, the Memshield II stuff was nice with a very good range of MCBs (including some high breaking capacity ones as well (10kA)). Thanks - I'll take a look at these. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 28/02/2010 18:16, Piers Finlayson wrote:
- I'm considering a three phase CU, and using this as a single phase CU. I'm unfamiliar with the internal construction of these CUs - is there generally any problems with using a TP CU as a single phase one? (The main obvious issue I've seen is that for the model I'm looking at a DP incoming switch is not available - so I'd have to use a TP one and leave one pole unused. Assuming you are planning to use a type B distribution board (with two columns of MCBs mounted vertically) then you will need a piece of MCB busbar to short out the three phases on the output side of the (4-pole) incomer. You may be able to buy this as a single pole conversion kit. - Finally, any recommendations or brands to steer clear of? I've been looking at the Hager Invicta 3. Hager single phasing kit JK125BSP on page 12 he http://download.hager.com/hager.uk/f..._catalogue.pdf Also, there is a limit on the length of meter tails of 2m and the DNO will probably insist on 25mm2 meter tails. If there isn't already one, you will undoubtedly need to install a a consumer unit within 2m tails-length of the meter and make your SWA a sub-main. You will probably need to make this sub-main 25mm2 as well to make the DNO happy (whether you can prove you need it to be 25mm2 or not). |
#4
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
(Yes, I have asked my electricity supplier, but they have suggested that I contact the DNO. I haven't yet summoned up the energy to do this.) - I'm considering using a metal CU. From doing a bit of research online it may be a requirement that the supply to this CU is protected by a 100mA time delayed RCD. However, I'm unclear as to whether this is only a requirement for TT systems or whether it's applicable to my scenario. I'll be digging out my 17th ed regs later, but can anyone let me know whether the RCD is a requirement here? The RCD protection of all circuits is nominally only for TT type systems (although the 17th edition nudges you closer to that anyway for all systems) The fundamental question to answer is your earth loop impedance at the supply adequate to clear a line to earth fault in the CU. If it is then a metal CU is fine, and TT style protection is not required. OK, thanks. I'll be asking the DNO for max Ze as well as supply type, but I'm guessing it's worth me measuring myself as well? Actually, one other complexity here is that I'll be installing a incoming feed from my generator behind a break before make switch, before the SWA to the CU. In the event of a power cut I can't rely on the earth from the supply being present, so I will be providing my own via earth spike. In this case I'll be TT and Ze will be much larger, so even if I don't need to protect the mains supply to the metal CU via an RCD I will need to protect the feed from the genny supply. But then, I may also need to protect the feed from the genny to the house anyway (I haven't figured out how I'm going to run this yet). |
#5
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 2010-02-28 19:45:43 +0000, Dave Osborne said:
- Finally, any recommendations or brands to steer clear of? I've been looking at the Hager Invicta 3. Hager single phasing kit JK125BSP on page 12 he http://download.hager.com/hager.uk/f..._catalogue.pdf Excellent, thanks - I hadn't spotted this kit. Also, there is a limit on the length of meter tails of 2m and the DNO will probably insist on 25mm2 meter tails. Yes, I was aware of this. If there isn't already one, you will undoubtedly need to install a a consumer unit within 2m tails-length of the meter and make your SWA a sub-main. You will probably need to make this sub-main 25mm2 as well to make the DNO happy (whether you can prove you need it to be 25mm2 or not). Hmm, I wasn't aware of this :-(. |
#6
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
"Piers Finlayson" wrote in message ... On 2010-02-28 19:25:04 +0000, John Rumm said: - Is my supply TN-S or TN-C-S? While I have seperate PE and N entering my building, the PE and N are connect together on my property. I have two wires (11kV?) coming onto my property, which terminate on a larger transformer on a telegraph pole. I can see the PE is provided from underground at the pole, and is connected to the N supply from the transformer. So my thinking is that I'm TN-S if the transformer is considered the power source, but TN-C-S otherwise. Thoughts? Its not uncommon for TN-C-S to be provided on overhead supplies these days. The fact that there is a join inside your property would suggest TN-C-S. Are there no PME stickers on your head end gear? Nope. (Yes, I have asked my electricity supplier, but they have suggested that I contact the DNO. I haven't yet summoned up the energy to do this.) - I'm considering using a metal CU. From doing a bit of research online it may be a requirement that the supply to this CU is protected by a 100mA time delayed RCD. However, I'm unclear as to whether this is only a requirement for TT systems or whether it's applicable to my scenario. I'll be digging out my 17th ed regs later, but can anyone let me know whether the RCD is a requirement here? The RCD protection of all circuits is nominally only for TT type systems (although the 17th edition nudges you closer to that anyway for all systems) The fundamental question to answer is your earth loop impedance at the supply adequate to clear a line to earth fault in the CU. If it is then a metal CU is fine, and TT style protection is not required. OK, thanks. I'll be asking the DNO for max Ze as well as supply type, but I'm guessing it's worth me measuring myself as well? Once the DNO gives you the supply type then the max Ze is defined by type of supply. - I'm considering a three phase CU, and using this as a single phase CU. OKAY. That is most unusual but there is nothing wrong with it if you use a conversion kit. How many circuits do you want or need? You can buy very good single phase CUs. Adam |
#7
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
Piers Finlayson wrote:
On 2010-02-28 19:45:43 +0000, Dave Osborne said: - Finally, any recommendations or brands to steer clear of? I've been looking at the Hager Invicta 3. Hager single phasing kit JK125BSP on page 12 he http://download.hager.com/hager.uk/f..._catalogue.pdf Excellent, thanks - I hadn't spotted this kit. Also, there is a limit on the length of meter tails of 2m and the DNO will probably insist on 25mm2 meter tails. Yes, I was aware of this. If there isn't already one, you will undoubtedly need to install a a consumer unit within 2m tails-length of the meter and make your SWA a sub-main. You will probably need to make this sub-main 25mm2 as well to make the DNO happy (whether you can prove you need it to be 25mm2 or not). Hmm, I wasn't aware of this :-(. Hi, Merlin Gerlin do some big 23 way industrial single phase units http://tobinternational.co.uk/acatalog/MM.html |
#8
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 28/02/2010 19:58, Piers Finlayson wrote:
On 2010-02-28 19:45:43 +0000, Dave Osborne said: If there isn't already one, you will undoubtedly need to install a a consumer unit within 2m tails-length of the meter and make your SWA a sub-main. You will probably need to make this sub-main 25mm2 as well to make the DNO happy (whether you can prove you need it to be 25mm2 or not). Hmm, I wasn't aware of this :-(. Well, I'm being pessimistic. It's not something I've personally experienced, but it's come up before on this n.g. I guess It largely depends on whether you are going to get the DNO in to disconnect/reconnect your tails. If you are, then they can refuse to re-connect if they don't like the look of your arrangement. If you aren't, then they'll in all likelihood never know. I'm pretty sure they won't like it if you don't have a CU of some sort at the point of supply. As a minimum, you should have a 1-way metalclad CU like this: http://download.hager.com/hager.uk/f...umer_units.pdf Page 1.23 (page 29 in pdf reader) IU4-16 or IU44-11 or IU44-18 as appropriate. As to whether you need 25mm2 SWA for your sub-main, I couldn't say, but be aware that it *might* be a problem. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
In article ,
"ARWadsworth" writes: "Piers Finlayson" wrote in message - I'm considering a three phase CU, and using this as a single phase CU. OKAY. That is most unusual but there is nothing wrong with it if you use a conversion kit. How many circuits do you want or need? There is one gotcha which catches out electricians with this... If it's rated at, say, 3 x 100A, then as a single phase CU, it's going to be 1 x 100A, and not 1 x 300A. This is because the neutral bus bar will only be rated for 100A. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#10
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
John Rumm wrote:
A switchfuse would be ok rather than a CU as such: [...] (can't say I like the look of the price of the mem ones though! ;-) For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK and won't break the bank: http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html -- Andy |
#11
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
- I'm considering a three phase CU, and using this as a single phase CU. OKAY. That is most unusual but there is nothing wrong with it if you use a conversion kit. How many circuits do you want or need? You can buy very good single phase CUs. I've identified the need for 18 circuits, but want room for expansion - so at least an additional 5 circuits. |
#12
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 2010-02-28 23:52:21 +0000, Andrew Gabriel said:
In article , "ARWadsworth" writes: "Piers Finlayson" wrote in message - I'm considering a three phase CU, and using this as a single phase CU. OKAY. That is most unusual but there is nothing wrong with it if you use a conversion kit. How many circuits do you want or need? There is one gotcha which catches out electricians with this... If it's rated at, say, 3 x 100A, then as a single phase CU, it's going to be 1 x 100A, and not 1 x 300A. This is because the neutral bus bar will only be rated for 100A. Thanks for pointing that out - but that's fine because I won't be needing more than 100A. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 2010-02-28 20:46:41 +0000, Dave Osborne said:
I'm pretty sure they won't like it if you don't have a CU of some sort at the point of supply. As a minimum, you should have a 1-way metalclad CU like this: Why metal? (I don't have any requirement for it to look good in this location, and this may require an RCD depending on my earth type/Ze.) I actually already have a Proteus (nasty stuff) 1-way CU with a 63A fuse which will be surplus to requirements and I can reuse. |
#14
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On Sun, 28 Feb 2010 19:45:58 +0000, Piers Finlayson wrote:
snip Actually, one other complexity here is that I'll be installing a incoming feed from my generator behind a break before make switch, before the SWA to the CU. snip Remember that your generator switch has to have a suitable load-make rating unless there is some other method of protecting the operator (like a suitable contactor circuit) if it is closed onto full load. It will also have to switch Neutral so that you can work on the genny with the mains live (unless you have a separate means of isolation). Ideally (and *always* on 3-phase systems) the Neutral pole should make first, break last. -- Mick (Working in a M$-free zone!) Web: http://www.nascom.info Filtering everything posted from googlegroups to kill spam. |
#15
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
"Piers Finlayson" wrote in message ... - I'm considering a three phase CU, and using this as a single phase CU. OKAY. That is most unusual but there is nothing wrong with it if you use a conversion kit. How many circuits do you want or need? You can buy very good single phase CUs. I've identified the need for 18 circuits, but want room for expansion - so at least an additional 5 circuits. There is a 28 way A board on the Hager webside. Adam |
#16
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 01/03/2010 09:02, Piers Finlayson wrote:
On 2010-02-28 20:46:41 +0000, Dave Osborne said: I'm pretty sure they won't like it if you don't have a CU of some sort at the point of supply. As a minimum, you should have a 1-way metalclad CU like this: Why metal? Only because you can make off the swa directly to it. Saves time, which may not be an issue for you ;-) |
#17
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
"John Rumm" wrote in message o.uk... Andy Wade wrote: John Rumm wrote: A switchfuse would be ok rather than a CU as such: [...] (can't say I like the look of the price of the mem ones though! ;-) For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK and won't break the bank: http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html Still surprisingly expensive for something that can be assembled with a DIN enclosure and off the shelf parts. Still I suppose you do get plenty of wiring room in the pre built versions. -- Cheers, John. I have been fitting these http://cgi.ebay.co.uk/3-x-CLICK-80-amp-Fuse-Main-Switch-new-in-box_W0QQitemZ200444697921QQcmdZViewItemQQptZUK_BOI _Electrical_Components_Supplies_ET?hash=item2eab6f 5d41 when needed. I pay around £20 from my wholesalers inc VAT. The 25mm tails go straight into the terminals with no bending required. I have found on line suppliers wanting £50+ for the same item. Adam |
#18
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
On 2010-03-01 12:04:15 +0000, Dave Osborne said:
On 01/03/2010 09:02, Piers Finlayson wrote: On 2010-02-28 20:46:41 +0000, Dave Osborne said: I'm pretty sure they won't like it if you don't have a CU of some sort at the point of supply. As a minimum, you should have a 1-way metalclad CU like this: Why metal? Only because you can make off the swa directly to it. Saves time, which may not be an issue for you ;-) Ah, OK. The SWA will be after the break before make switch for the genny, which in turn will be after this CU. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
John Rumm
wibbled on Monday 01 March 2010 22:05 What sort of fuse do they take? Are the boxes available in other ratings? Often BS88, at least the ones I've come across. Not sure about that specific one but it's likely. 100A, 80A and 60A seem to be the standard ratings. -- Tim Watts Managers, politicians and environmentalists: Nature's carbon buffer. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
"John Rumm" wrote in message o.uk... ARWadsworth wrote: "John Rumm" wrote in message o.uk... Andy Wade wrote: John Rumm wrote: A switchfuse would be ok rather than a CU as such: [...] (can't say I like the look of the price of the mem ones though! ;-) For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK and won't break the bank: http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html Still surprisingly expensive for something that can be assembled with a DIN enclosure and off the shelf parts. Still I suppose you do get plenty of wiring room in the pre built versions. -- Cheers, John. I have been fitting these http://cgi.ebay.co.uk/3-x-CLICK-80-amp-Fuse-Main-Switch-new-in-box_W0QQitemZ200444697921QQcmdZViewItemQQptZUK_BOI _Electrical_Components_Supplies_ET?hash=item2eab6f 5d41 when needed. I pay around £20 from my wholesalers inc VAT. The 25mm tails go straight into the terminals with no bending required. I have found on line suppliers wanting £50+ for the same item. What sort of fuse do they take? Are the boxes available in other ratings? -- Cheers, John. It comes with a HRC fuse. They do a 100A switch but it comes with an 80A fuse! I assume that it is to allow some diversity against a 100A supply fuse. See page 4 of http://www.scolmore.com/documents/ci...protection.pdf Cheers Adam |
#21
Posted to uk.d-i-y
|
|||
|
|||
Various electrial questions
"ARWadsworth" wrote in message om... It comes with a HRC fuse. They do a 100A switch but it comes with an 80A fuse! I assume that it is to allow some diversity against a 100A supply fuse. See page 4 of http://www.scolmore.com/documents/ci...protection.pdf Cheers Adam Additional info It uses these fuses http://www.gil-lec.co.uk/products/2262066219 Adam |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Getting An Enclosed Trailer...Questions, Questions, Questions | Metalworking | |||
3 way electrial wall switch question | Home Repair | |||
Electrial Question | Home Repair | |||
New Electrial outlets in | Home Repair | |||
New Electrial outlets in Basement | Home Repair |