I'm contemplating a serious rewire/CU replacement and had a few questions:


- I'll be using SWA to feed the CU some distance from the incoming
supply. I've read the excellent terminating SWA article on the wiki,
but it is unclear about exactly what size SWA can be cut using bolt
croppers. I'll probably be using 10mm2 or 16mm2 SWA - is it reasonable
to expect bolt croppers to be fine for cutting these sizes?


- Is my supply TN-S or TN-C-S?

While I have seperate PE and N entering my building, the PE and N are
connect together on my property. I have two wires (11kV?) coming onto
my property, which terminate on a larger transformer on a telegraph
pole. I can see the PE is provided from underground at the pole, and
is connected to the N supply from the transformer. So my thinking is
that I'm TN-S if the transformer is considered the power source, but
TN-C-S otherwise. Thoughts?

(Yes, I have asked my electricity supplier, but they have suggested
that I contact the DNO. I haven't yet summoned up the energy to do
this.)


- I'm considering using a metal CU. From doing a bit of research
online it may be a requirement that the supply to this CU is protected
by a 100mA time delayed RCD. However, I'm unclear as to whether this
is only a requirement for TT systems or whether it's applicable to my
scenario. I'll be digging out my 17th ed regs later, but can anyone
let me know whether the RCD is a requirement here?


- I'm considering a three phase CU, and using this as a single phase
CU. I'm unfamiliar with the internal construction of these CUs - is
there generally any problems with using a TP CU as a single phase one?
(The main obvious issue I've seen is that for the model I'm looking at
a DP incoming switch is not available - so I'd have to use a TP one and
leave one pole unused.


- Finally, any recommendations or brands to steer clear of? I've been
looking at the Hager Invicta 3.


Thanks,
Piers

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions

On 2010-02-28 19:25:04 +0000, John Rumm said:


- Is my supply TN-S or TN-C-S?

While I have seperate PE and N entering my building, the PE and N are
connect together on my property. I have two wires (11kV?) coming onto
my property, which terminate on a larger transformer on a telegraph

pole. I can see the PE is provided from underground at the pole, and
is connected to the N supply from the transformer. So my thinking is
that I'm TN-S if the transformer is considered the power source, but
TN-C-S otherwise. Thoughts?


Its not uncommon for TN-C-S to be provided on overhead supplies these
days. The fact that there is a join inside your property would suggest
TN-C-S. Are there no PME stickers on your head end gear?


Nope.


(Yes, I have asked my electricity supplier, but they have suggested
that I contact the DNO. I haven't yet summoned up the energy to do
this.)



- I'm considering using a metal CU. From doing a bit of research
online it may be a requirement that the supply to this CU is protected
by a 100mA time delayed RCD. However, I'm unclear as to whether this

is only a requirement for TT systems or whether it's applicable to my
scenario. I'll be digging out my 17th ed regs later, but can anyone

let me know whether the RCD is a requirement here?


The RCD protection of all circuits is nominally only for TT type
systems (although the 17th edition nudges you closer to that anyway for
all systems)

The fundamental question to answer is your earth loop impedance at the
supply adequate to clear a line to earth fault in the CU. If it is then
a metal CU is fine, and TT style protection is not required.


OK, thanks. I'll be asking the DNO for max Ze as well as supply type,
but I'm guessing it's worth me measuring myself as well?


- I'm considering a three phase CU, and using this as a single phase
CU. I'm unfamiliar with the internal construction of these CUs - is
there generally any problems with using a TP CU as a single phase one?

They tend to be of higher quality construction than the domestic ones.
The main objections to using one would be cost and size. Do you
anticipate having three phase supplied to it in the future then?


I see a number of benefits:
- Better quality construction.
- Better looks - more industrial and less cheap white plastic (the new
CU will be fairly exposed, both due to the convenient location and also
to ensure accessibility).
- More space inside for wiring (I hate fiddling around inside normal CUs).
- Many way - I've identified the need for at least 18 circuits and
want to leave room for expansion. I've got my eyes on either an 8 way
or 12 way TP CU.


(The main obvious issue I've seen is that for the model I'm looking at
a DP incoming switch is not available - so I'd have to use a TP one
and leave one pole unused.


I would expect the incomer to have 4 poles - one for each phase and
neutral. The CUs would normally supply a good number of single phase
circuits.


You're right - most of them are 4 pole (but there are a few 3 pole ones).


- Finally, any recommendations or brands to steer clear of? I've been
looking at the Hager Invicta 3.


In my limited experience of the three phase kit, the Memshield II stuff
was nice with a very good range of MCBs (including some high breaking
capacity ones as well (10kA)).


Thanks - I'll take a look at these.

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 548
Default Various electrial questions

On 28/02/2010 18:16, Piers Finlayson wrote:

- I'm considering a three phase CU, and using this as a single phase CU.
I'm unfamiliar with the internal construction of these CUs - is there
generally any problems with using a TP CU as a single phase one? (The
main obvious issue I've seen is that for the model I'm looking at a DP
incoming switch is not available - so I'd have to use a TP one and leave
one pole unused.


Assuming you are planning to use a type B distribution board (with two
columns of MCBs mounted vertically) then you will need a piece of MCB
busbar to short out the three phases on the output side of the (4-pole)
incomer. You may be able to buy this as a single pole conversion kit.


- Finally, any recommendations or brands to steer clear of? I've been
looking at the Hager Invicta 3.



Hager single phasing kit JK125BSP on page 12 he

http://download.hager.com/hager.uk/f..._catalogue.pdf


Also, there is a limit on the length of meter tails of 2m and the DNO
will probably insist on 25mm2 meter tails.

If there isn't already one, you will undoubtedly need to install a a
consumer unit within 2m tails-length of the meter and make your SWA a
sub-main. You will probably need to make this sub-main 25mm2 as well to
make the DNO happy (whether you can prove you need it to be 25mm2 or not).
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions




(Yes, I have asked my electricity supplier, but they have suggested
that I contact the DNO. I haven't yet summoned up the energy to do
this.)



- I'm considering using a metal CU. From doing a bit of research
online it may be a requirement that the supply to this CU is protected
by a 100mA time delayed RCD. However, I'm unclear as to whether
this is only a requirement for TT systems or whether it's
applicable to my scenario. I'll be digging out my 17th ed regs
later, but can anyone let me know whether the RCD is a requirement
here?


The RCD protection of all circuits is nominally only for TT type
systems (although the 17th edition nudges you closer to that anyway for
all systems)


The fundamental question to answer is your earth loop impedance at the
supply adequate to clear a line to earth fault in the CU. If it is

then a metal CU is fine, and TT style protection is not required.


OK, thanks. I'll be asking the DNO for max Ze as well as supply type,
but I'm guessing it's worth me measuring myself as well?


Actually, one other complexity here is that I'll be installing a
incoming feed from my generator behind a break before make switch,
before the SWA to the CU. In the event of a power cut I can't rely on
the earth from the supply being present, so I will be providing my own
via earth spike. In this case I'll be TT and Ze will be much larger,
so even if I don't need to protect the mains supply to the metal CU via
an RCD I will need to protect the feed from the genny supply. But
then, I may also need to protect the feed from the genny to the house
anyway (I haven't figured out how I'm going to run this yet).


  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions

On 2010-02-28 19:45:43 +0000, Dave Osborne said:



- Finally, any recommendations or brands to steer clear of? I've been
looking at the Hager Invicta 3.



Hager single phasing kit JK125BSP on page 12 he

http://download.hager.com/hager.uk/f..._catalogue.pdf


Excellent,

thanks - I hadn't spotted this kit.



Also, there is a limit on the length of meter tails of 2m and the DNO
will probably insist on 25mm2 meter tails.


Yes, I was aware of this.


If there isn't already one, you will undoubtedly need to install a a
consumer unit within 2m tails-length of the meter and make your SWA a
sub-main. You will probably need to make this sub-main 25mm2 as well to
make the DNO happy (whether you can prove you need it to be 25mm2 or
not).


Hmm, I wasn't aware of this :-(.




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Various electrial questions


"Piers Finlayson" wrote in message
...
On 2010-02-28 19:25:04 +0000, John Rumm said:


- Is my supply TN-S or TN-C-S?

While I have seperate PE and N entering my building, the PE and N are
connect together on my property. I have two wires (11kV?) coming onto
my property, which terminate on a larger transformer on a telegraph
pole. I can see the PE is provided from underground at the pole, and is
connected to the N supply from the transformer. So my thinking is
that I'm TN-S if the transformer is considered the power source, but
TN-C-S otherwise. Thoughts?


Its not uncommon for TN-C-S to be provided on overhead supplies these
days. The fact that there is a join inside your property would suggest
TN-C-S. Are there no PME stickers on your head end gear?


Nope.


(Yes, I have asked my electricity supplier, but they have suggested that
I contact the DNO. I haven't yet summoned up the energy to do this.)



- I'm considering using a metal CU. From doing a bit of research
online it may be a requirement that the supply to this CU is protected
by a 100mA time delayed RCD. However, I'm unclear as to whether this
is only a requirement for TT systems or whether it's applicable to my
scenario. I'll be digging out my 17th ed regs later, but can anyone
let me know whether the RCD is a requirement here?


The RCD protection of all circuits is nominally only for TT type systems
(although the 17th edition nudges you closer to that anyway for all
systems)

The fundamental question to answer is your earth loop impedance at the
supply adequate to clear a line to earth fault in the CU. If it is then a
metal CU is fine, and TT style protection is not required.


OK, thanks. I'll be asking the DNO for max Ze as well as supply type, but
I'm guessing it's worth me measuring myself as well?



Once the DNO gives you the supply type then the max Ze is defined by type of
supply.


- I'm considering a three phase CU, and using this as a single phase
CU.



OKAY. That is most unusual but there is nothing wrong with it if you use a
conversion kit. How many circuits do you want or need?

You can buy very good single phase CUs.

Adam

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 87
Default Various electrial questions

Piers Finlayson wrote:
On 2010-02-28 19:45:43 +0000, Dave Osborne said:



- Finally, any recommendations or brands to steer clear of? I've been
looking at the Hager Invicta 3.



Hager single phasing kit JK125BSP on page 12 he

http://download.hager.com/hager.uk/f..._catalogue.pdf


Excellent,

thanks - I hadn't spotted this kit.



Also, there is a limit on the length of meter tails of 2m and the DNO
will probably insist on 25mm2 meter tails.


Yes, I was aware of this.


If there isn't already one, you will undoubtedly need to install a a
consumer unit within 2m tails-length of the meter and make your SWA a
sub-main. You will probably need to make this sub-main 25mm2 as well
to make the DNO happy (whether you can prove you need it to be 25mm2
or not).


Hmm, I wasn't aware of this :-(.



Hi,
Merlin Gerlin do some big 23 way industrial single phase units
http://tobinternational.co.uk/acatalog/MM.html

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 548
Default Various electrial questions

On 28/02/2010 19:58, Piers Finlayson wrote:
On 2010-02-28 19:45:43 +0000, Dave Osborne said:



If there isn't already one, you will undoubtedly need to install a a
consumer unit within 2m tails-length of the meter and make your SWA a
sub-main. You will probably need to make this sub-main 25mm2 as well
to make the DNO happy (whether you can prove you need it to be 25mm2
or not).


Hmm, I wasn't aware of this :-(.



Well, I'm being pessimistic. It's not something I've personally
experienced, but it's come up before on this n.g.

I guess It largely depends on whether you are going to get the DNO in to
disconnect/reconnect your tails. If you are, then they can refuse to
re-connect if they don't like the look of your arrangement. If you
aren't, then they'll in all likelihood never know.

I'm pretty sure they won't like it if you don't have a CU of some sort
at the point of supply. As a minimum, you should have a 1-way metalclad
CU like this:

http://download.hager.com/hager.uk/f...umer_units.pdf
Page 1.23 (page 29 in pdf reader)

IU4-16 or
IU44-11 or
IU44-18 as appropriate.

As to whether you need 25mm2 SWA for your sub-main, I couldn't say, but
be aware that it *might* be a problem.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 11,175
Default Various electrial questions

In article ,
"ARWadsworth" writes:

"Piers Finlayson" wrote in message
- I'm considering a three phase CU, and using this as a single phase
CU.



OKAY. That is most unusual but there is nothing wrong with it if you use a
conversion kit. How many circuits do you want or need?


There is one gotcha which catches out electricians with this...
If it's rated at, say, 3 x 100A, then as a single phase CU, it's
going to be 1 x 100A, and not 1 x 300A. This is because the
neutral bus bar will only be rated for 100A.

--
Andrew Gabriel
[email address is not usable -- followup in the newsgroup]
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,285
Default Various electrial questions

John Rumm wrote:

A switchfuse would be ok rather than a CU as such:
[...]
(can't say I like the look of the price of the mem ones though! ;-)


For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK
and won't break the bank:

http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html
http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html

--
Andy


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions




- I'm considering a three phase CU, and using this as a single phase CU.



OKAY. That is most unusual but there is nothing wrong with it if you
use a conversion kit. How many circuits do you want or need?

You can buy very good single phase CUs.


I've identified the need for 18 circuits, but want room for expansion -
so at least an additional 5 circuits.

  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions

On 2010-02-28 23:52:21 +0000, Andrew Gabriel said:

In article ,
"ARWadsworth" writes:

"Piers Finlayson" wrote in message
- I'm considering a three phase CU, and using this as a single phase
CU.



OKAY. That is most unusual but there is nothing wrong with it if you use a
conversion kit. How many circuits do you want or need?


There is one gotcha which catches out electricians with this...
If it's rated at, say, 3 x 100A, then as a single phase CU, it's
going to be 1 x 100A, and not 1 x 300A. This is because the
neutral bus bar will only be rated for 100A.


Thanks for pointing that out - but that's fine because I won't be
needing more than 100A.

  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions

On 2010-02-28 20:46:41 +0000, Dave Osborne said:


I'm pretty sure they won't like it if you don't have a CU of some sort
at the point of supply. As a minimum, you should have a 1-way metalclad
CU like this:


Why metal? (I don't have any requirement for it to look good in this
location, and this may require an RCD depending on my earth type/Ze.)

I actually already have a Proteus (nasty stuff) 1-way CU with a 63A
fuse which will be surplus to requirements and I can reuse.

  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 272
Default Various electrial questions

On Sun, 28 Feb 2010 19:45:58 +0000, Piers Finlayson wrote:


snip

Actually, one other complexity here is that I'll be installing a
incoming feed from my generator behind a break before make switch,
before the SWA to the CU.

snip


Remember that your generator switch has to have a suitable load-make
rating unless there is some other method of protecting the operator (like
a suitable contactor circuit) if it is closed onto full load. It will
also have to switch Neutral so that you can work on the genny with the
mains live (unless you have a separate means of isolation). Ideally (and
*always* on 3-phase systems) the Neutral pole should make first, break
last.

--
Mick (Working in a M$-free zone!)
Web: http://www.nascom.info
Filtering everything posted from googlegroups to kill spam.
  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Various electrial questions


"Piers Finlayson" wrote in message
...



- I'm considering a three phase CU, and using this as a single phase
CU.



OKAY. That is most unusual but there is nothing wrong with it if you use
a conversion kit. How many circuits do you want or need?

You can buy very good single phase CUs.


I've identified the need for 18 circuits, but want room for expansion - so
at least an additional 5 circuits.


There is a 28 way A board on the Hager webside.

Adam



  #16   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 548
Default Various electrial questions

On 01/03/2010 09:02, Piers Finlayson wrote:
On 2010-02-28 20:46:41 +0000, Dave Osborne said:


I'm pretty sure they won't like it if you don't have a CU of some sort
at the point of supply. As a minimum, you should have a 1-way
metalclad CU like this:


Why metal?


Only because you can make off the swa directly to it. Saves time, which
may not be an issue for you ;-)


  #17   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Various electrial questions


"John Rumm" wrote in message
o.uk...
Andy Wade wrote:
John Rumm wrote:

A switchfuse would be ok rather than a CU as such:
[...]
(can't say I like the look of the price of the mem ones though! ;-)


For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK
and won't break the bank:

http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html
http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html


Still surprisingly expensive for something that can be assembled with a
DIN enclosure and off the shelf parts. Still I suppose you do get plenty
of wiring room in the pre built versions.

--
Cheers,

John.



I have been fitting these

http://cgi.ebay.co.uk/3-x-CLICK-80-amp-Fuse-Main-Switch-new-in-box_W0QQitemZ200444697921QQcmdZViewItemQQptZUK_BOI _Electrical_Components_Supplies_ET?hash=item2eab6f 5d41

when needed. I pay around £20 from my wholesalers inc VAT. The 25mm tails go
straight into the terminals with no bending required. I have found on line
suppliers wanting £50+ for the same item.

Adam

  #18   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 264
Default Various electrial questions

On 2010-03-01 12:04:15 +0000, Dave Osborne said:

On 01/03/2010 09:02, Piers Finlayson wrote:
On 2010-02-28 20:46:41 +0000, Dave Osborne said:


I'm pretty sure they won't like it if you don't have a CU of some sort
at the point of supply. As a minimum, you should have a 1-way
metalclad CU like this:


Why metal?


Only because you can make off the swa directly to it. Saves time, which
may not be an issue for you ;-)


Ah, OK. The SWA will be after the break before make switch for the
genny, which in turn will be after this CU.

  #19   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,360
Default Various electrial questions

John Rumm
wibbled on Monday 01 March 2010 22:05


What sort of fuse do they take? Are the boxes available in other ratings?


Often BS88, at least the ones I've come across. Not sure about that specific
one but it's likely.

100A, 80A and 60A seem to be the standard ratings.

--
Tim Watts

Managers, politicians and environmentalists: Nature's carbon buffer.

  #20   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Various electrial questions


"John Rumm" wrote in message
o.uk...
ARWadsworth wrote:

"John Rumm" wrote in message
o.uk...
Andy Wade wrote:
John Rumm wrote:

A switchfuse would be ok rather than a CU as such:
[...]
(can't say I like the look of the price of the mem ones though! ;-)

For single-phase the Wylex 110M (or 108 / 108M if 60 A is enough) is OK
and won't break the bank:

http://www.tlc-direct.co.uk/Main_Ind...d_N/index.html
http://www.tlc-direct.co.uk/Main_Ind...P_1/index.html

Still surprisingly expensive for something that can be assembled with a
DIN enclosure and off the shelf parts. Still I suppose you do get plenty
of wiring room in the pre built versions.

--
Cheers,

John.



I have been fitting these

http://cgi.ebay.co.uk/3-x-CLICK-80-amp-Fuse-Main-Switch-new-in-box_W0QQitemZ200444697921QQcmdZViewItemQQptZUK_BOI _Electrical_Components_Supplies_ET?hash=item2eab6f 5d41
when needed. I pay around £20 from my wholesalers inc VAT. The 25mm tails
go straight into the terminals with no bending required. I have found on
line suppliers wanting £50+ for the same item.


What sort of fuse do they take? Are the boxes available in other ratings?

--
Cheers,

John.



It comes with a HRC fuse. They do a 100A switch but it comes with an 80A
fuse! I assume that it is to allow some diversity against a 100A supply
fuse.

See page 4 of

http://www.scolmore.com/documents/ci...protection.pdf

Cheers

Adam



  #21   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 7,688
Default Various electrial questions


"ARWadsworth" wrote in message
om...


It comes with a HRC fuse. They do a 100A switch but it comes with an 80A
fuse! I assume that it is to allow some diversity against a 100A supply
fuse.

See page 4 of

http://www.scolmore.com/documents/ci...protection.pdf

Cheers

Adam


Additional info

It uses these fuses

http://www.gil-lec.co.uk/products/2262066219

Adam

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Getting An Enclosed Trailer...Questions, Questions, Questions Too_Many_Tools Metalworking 30 December 30th 07 06:19 PM
3 way electrial wall switch question [email protected] Home Repair 9 January 27th 06 02:01 PM
Electrial Question Bill Davis Jr Home Repair 11 June 28th 05 07:41 PM
New Electrial outlets in barry martin Home Repair 2 February 17th 04 12:41 AM
New Electrial outlets in Basement Wade Eyre Home Repair 9 February 16th 04 05:45 AM


All times are GMT +1. The time now is 06:22 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"