I have moved into a house with a dog's breakfast of a CH system. The CH
system looks like it's been around a while, but fairly recently the hot
water tank has been replaced with a combi boiler. (Installed arse about
face as it happens - the TRVs on the (15) rads are all the older type that
are mono-directional - the combi had been connected into the existing
system the wrong way round.)

The towel rail in the bathroom has stopped heating up, but the other rads
are ok. There is no air in any of the rads. I think the system needs a
good clean and then some re-filled with some inhibitor.

The question: Is it a DIY job? None of my DIY books cover it and my
googling of the NG archives hasn't come up with anything definitive in the
Janet and John guide to flushing your system vein.

Dougie

  #2   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Mon, 20 Oct 2003 20:34:09 +0100, Dougie Nisbet
wrote:

I have moved into a house with a dog's breakfast of a CH system. The CH
system looks like it's been around a while, but fairly recently the hot
water tank has been replaced with a combi boiler. (Installed arse about
face as it happens - the TRVs on the (15) rads are all the older type that
are mono-directional - the combi had been connected into the existing
system the wrong way round.)

The towel rail in the bathroom has stopped heating up, but the other rads
are ok. There is no air in any of the rads. I think the system needs a
good clean and then some re-filled with some inhibitor.

The question: Is it a DIY job? None of my DIY books cover it and my
googling of the NG archives hasn't come up with anything definitive in the
Janet and John guide to flushing your system vein.

Dougie


Yes it is.

You can do a Google Groups search for a method that I have used to
clean and flush successfully, by removing each radiator and taking it
outside for flushing with a mains hose or pressure washer.

This method works especially well if you have a sealed system with a
filling loop connected to the mains water supply. You can flush the
crud out at each radiator valve and clear the pipes very effectively.

Do watch out for sludge and other iron compounds from the radiators.
They are an indellible dye on carpets and furnishings. I use a
plastic bag on each valve tail held on with a rubber band.

I use a pair of new cat litter trays to collect water etc. from each
radiator.

For the TRVs, if they are old enough to be unidirectional, then they
are probably beyond their useful life as well. While you are
cleaning the radiators, I would be inclined to replace them and also
the lockshields.

Once the system is flushed clean, it is a good idea to put in a
chemical flushing agent and running the system hot for a few days.
Then rinse and flush thoroughly.

Finally refill, adding inhibitor. You can add a filling point to do
this by creating a vertical short stub of pipe on the system, closed
off with a cap and then using a funnel to add liquid inhibitor.
Alternatively, you can use a gel inhibitor which comes in mastic gun
cartridges. It is a lot easier and cleaner if you put this stuff
in through a vent before finally filling the system, rather than doing
so against the pressure afterwards.




..andy

To email, substitute .nospam with .gl
  #3   Report Post  
M. Damerell
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system


With all due respect I dont think that removing the rads and carrying
them out is the easiest way to flush a sealed system. If the system
was properly designed, (yes I know the OP called it a dogs breakfast)
the fill point and drain point should be on opposite sides. (i.e. one
on the hot flow from boiler, one on cold return). Then you can

switch off, release pressure at the release point.

connect fill and drain hoses, open drain valve, close pressure
release valve.

Turn on supply. Then by opening and shutting valves round the house,
you can send a fast stream of water through each rad in turn. This
should remove a lot of the sludge except if a rad is solidly blocked;
if so, then you will have to remove that rad and flush it.

Refill as normal adding Fernox or similar sludge-remover. Repressurise,
run hot for a while as per instructions.

drain, flush, refill adding anti-rust.

If the drain point is on the wrong side of the system, you will need
to cut pipe and insert an extra drain point. You may prefer to remove
rads.

If you do decide to remove and flush out rads, note:
1. When you undo the joint, water will ooze out. When you definitely
separate the pipes, it will gush.
2. However carefully you tilt a rad to drain it, there is always a
little bit of mucky water lurking inside, waiting for a chance to run
out & ruin your carpet. Carry rads upside down, with ends plugged.

Making joints. I know that other posters use PTFE tape, I have had
better results with Fernox leak sealer (I have no connection with
Fernox). It comes in a toothpaste tube, you smear it onto the male
part of the joint, dont get it on your hands, bad for skin.




  #4   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 18:49:30 +0100, "M. Damerell"
wrote:


With all due respect I dont think that removing the rads and carrying
them out is the easiest way to flush a sealed system.


Well..... yes and no. I hadn't posted the full version of the
procedure this time because it is already in the Google archives, and
not all steps may be necessary.

If the system
was properly designed, (yes I know the OP called it a dogs breakfast)
the fill point and drain point should be on opposite sides. (i.e. one
on the hot flow from boiler, one on cold return). Then you can

switch off, release pressure at the release point.

connect fill and drain hoses, open drain valve, close pressure
release valve.

Turn on supply. Then by opening and shutting valves round the house,
you can send a fast stream of water through each rad in turn. This
should remove a lot of the sludge except if a rad is solidly blocked;
if so, then you will have to remove that rad and flush it.


I follow what you are saying and I did actually do this when
refurbishing my system with a new boiler. In principle it would work
well. However, there are a couple of points:

- If you have the filling point on one side of the boiler and the
drain close by on the other, then there is an easier flow path through
the boiler and you won't get that much water being forced through even
a single selected radiator. I fitted lever ball valves on each
side of the boiler - making sure a pressure relief valve was between
them. In any case this is a good plan because it avoids pushing crud
through the boiler. By adding another drain point I was able to
flush the boiler through independently as well. Then, as you say,
water can be forced through a single radiator to good effect. This
was my starting point, but I have to say that not a lot of material
came out or even much rusty water.

- I needed to replace the lockshield valves and TRVs on some of the
radiators (the lockshields were seeping and the TRVs had stopped
woring properly), and when I removed them I found quite a bit of old
copper swarf and a little sludge in the bottom of each radiator that I
investigated. It was really that which led me to systematically
take each radiator off and outside for a good flush through with a
pressure washer. This proved very effective at removing all of the
remaining crud.

I replaced the lockshield valves with Pegler Terrier types, which are
pretty good quality and there is a version with built in drain point
in the tail. Thus it's possible to drain a radiator before or
without undoing the unions.

With the radiator removed, the valves either side of the boiler can be
opened and mains pressure applied to the system. Each radiator
valve can be opened in turn at the location where the radiator is
removed and the pipework leading to it is flushed out rather than
anything being recirculated at all. I found that I got quite a bit
more copper swarf out this way and a small amount of iron crud as
well.

It's also worth mentioning that for a more complete job, fitting an
inline strainer on the boiler return is a good plan.


Refill as normal adding Fernox or similar sludge-remover. Repressurise,
run hot for a while as per instructions.


I found that this was worth doing as well.


drain, flush, refill adding anti-rust.


Very important and there is no harm in overdosing to some extent.


If the drain point is on the wrong side of the system, you will need
to cut pipe and insert an extra drain point. You may prefer to remove
rads.

If you do decide to remove and flush out rads, note:
1. When you undo the joint, water will ooze out. When you definitely
separate the pipes, it will gush.


That's true if they were full. Generally it is possible to drain
upstairs radiators through the pipework, although downstairs ones at
the unions. Hence the suggestion of using cat litter trays as they
will take the water from most sizes of radiator.


2. However carefully you tilt a rad to drain it, there is always a
little bit of mucky water lurking inside, waiting for a chance to run
out & ruin your carpet. Carry rads upside down, with ends plugged.


Yep. I used "condoms" made from small sandwich bags held on the
tails with rubber bands.



Making joints. I know that other posters use PTFE tape, I have had
better results with Fernox leak sealer (I have no connection with
Fernox). It comes in a toothpaste tube, you smear it onto the male
part of the joint, dont get it on your hands, bad for skin.


You can get PTFE liquid thread sealer which is also effective as a
substitute for the tape - probably similar stuff to the leak sealer.
Radiator tails often do seem to have looser threads than other
threaded joints. I've also found the thicker PTFE tape used for gas
(on yellow reels) to be good for this.


..andy

To email, substitute .nospam with .gl
  #5   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 18:49:30 +0100, M. Damerell wrote:


With all due respect I dont think that removing the rads and carrying
them out is the easiest way to flush a sealed system. If the system
was properly designed, (yes I know the OP called it a dogs breakfast)
the fill point and drain point should be on opposite sides. (i.e. one
on the hot flow from boiler, one on cold return). Then you can


Could you clarify exactly what you mean by 'fill point' and 'drain point'
- because I suspect I have neither. Oh, hang on - I'm wrong. Re-reading
the rather good http://www.makewrite.demon.co.uk/SealedCH.html I certainly
have a Fill point, but I can't see any sign of a drain point. Neither
could a plumber who replaced a radiator for me a couple of months ago. He
drained (more or less) the system by shoving a bit of hosepipe into the
rad in the kitchen. The fill hose is connected and has been much used
until the plumber replaced the faulty rad which was leaking and
de-pressurising the system.


switch off, release pressure at the release point.

connect fill and drain hoses, open drain valve, close pressure
release valve.

Turn on supply. Then by opening and shutting valves round the house,
you can send a fast stream of water through each rad in turn. This
should remove a lot of the sludge except if a rad is solidly blocked;
if so, then you will have to remove that rad and flush it.

I understand the fundamentals behind what you're saying but I'm struggling
with some terminology. 'pressure release valve' - is that the bypass valve
that connected CH flow and return just below the boiler?

Refill as normal adding Fernox or similar sludge-remover. Repressurise,
run hot for a while as per instructions.

drain, flush, refill adding anti-rust.

If the drain point is on the wrong side of the system, you will need to
cut pipe and insert an extra drain point. You may prefer to remove rads.


Will I definitely have a drain point and I just haven't found it yet? Or
could it be that the installers were too busy eating digestives to bother?

If you do decide to remove and flush out rads, note: 1. When you undo
the joint, water will ooze out. When you definitely separate the pipes,
it will gush.
2. However carefully you tilt a rad to drain it, there is always a
little bit of mucky water lurking inside, waiting for a chance to run
out & ruin your carpet. Carry rads upside down, with ends plugged.

Making joints. I know that other posters use PTFE tape, I have had
better results with Fernox leak sealer (I have no connection with
Fernox). It comes in a toothpaste tube, you smear it onto the male part
of the joint, dont get it on your hands, bad for skin.


Thanks for all the info - food for thought.

Dougie




  #6   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 22:09:02 +0100, Dougie Nisbet wrote:

[ ... ]

switch off, release pressure at the release point.

connect fill and drain hoses, open drain valve, close pressure
release valve.

Turn on supply. Then by opening and shutting valves round the house,
you can send a fast stream of water through each rad in turn. This
should remove a lot of the sludge except if a rad is solidly blocked;
if so, then you will have to remove that rad and flush it.

I understand the fundamentals behind what you're saying but I'm struggling
with some terminology. 'pressure release valve' - is that the bypass valve
that connected CH flow and return just below the boiler?


Nah - I'll answer my own question. I presume it's the 'pressure relief
system' mentioned in the manual for my boiler (a RAVENHEAT RSF 100ET). I
can't get access to it without taking the cover of the boiler.

  #7   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 23:14:21 +0100, Dougie Nisbet
wrote:



I understand the fundamentals behind what you're saying but I'm struggling
with some terminology. 'pressure release valve' - is that the bypass valve
that connected CH flow and return just below the boiler?


Nah - I'll answer my own question. I presume it's the 'pressure relief
system' mentioned in the manual for my boiler (a RAVENHEAT RSF 100ET). I
can't get access to it without taking the cover of the boiler.


Probably.

It isn't a good idea to use it deliberately to drain the system
anyway. See other post.


..andy

To email, substitute .nospam with .gl
  #8   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 22:09:02 +0100, Dougie Nisbet
wrote:



Could you clarify exactly what you mean by 'fill point' and 'drain point'
- because I suspect I have neither. Oh, hang on - I'm wrong. Re-reading
the rather good http://www.makewrite.demon.co.uk/SealedCH.html I certainly
have a Fill point, but I can't see any sign of a drain point. Neither
could a plumber who replaced a radiator for me a couple of months ago. He
drained (more or less) the system by shoving a bit of hosepipe into the
rad in the kitchen. The fill hose is connected and has been much used
until the plumber replaced the faulty rad which was leaking and
de-pressurising the system.


Look for something like

http://www.screwfix.com/app/sfd/cat/...12232&ts=73105

fitted at a low point normally near the boiler.

There should really be one at every low point.

Otherwise, after you have drained via a low radiator, you could fit
one using a push fit tee.

http://www.screwfix.com/app/sfd/cat/...73302&id=17972




switch off, release pressure at the release point.

connect fill and drain hoses, open drain valve, close pressure
release valve.

Turn on supply. Then by opening and shutting valves round the house,
you can send a fast stream of water through each rad in turn. This
should remove a lot of the sludge except if a rad is solidly blocked;
if so, then you will have to remove that rad and flush it.

I understand the fundamentals behind what you're saying but I'm struggling
with some terminology. 'pressure release valve' - is that the bypass valve
that connected CH flow and return just below the boiler?


No. Take a look at www.bes.ltd.uk and the section Plumbing-Central
Heating-Central Heating Sealed System Equipment.

You should find a valve somewhere (typically near the expansion
vessel) with a knurled knob. It could also be near the filling point.
It may well have a label with 3 bar on it and there should be an exit
pipe to a drain. However, since there are other questionnable
aspects of the system then it may not have that. There *must* be
one on the system somewhere though.
It is possible that it is inside the boiler, especially if the
expansion vessel is in there as well.

If you don't have a pressure relief valve, then it is probably time to
seek professional help because the system would be dangerous without
one. There is no reason why yoiu couldn't DIY the addition of such a
valve, but absence would be an indicator that there could be other
problems.

Assuming you can find the valve, it is not a good idea to use it to
drain or even depressurise the system. Pieces of crud or scale
could easily become caught in it and then the valve won't seal again
and a new one will be required.





Will I definitely have a drain point and I just haven't found it yet? Or
could it be that the installers were too busy eating digestives to bother?


Based on some of the oddities you've mentioned, this is entirely
possible. It's laziness at best and incompetence at worst.
If you have any doubts about the system, it's also possible that the
gas installation has not been done properly either.
I don't want to frighten you, but if you are not 100% certain, then a
prudent move would be to get a CORGI registered heating engineer to
look at it (not BG since they are generally expensive).




..andy

To email, substitute .nospam with .gl
  #9   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 23:14:31 +0100, Andy Hall wrote:

[ .. ]


Look for something like

http://www.screwfix.com/app/sfd/cat/...12232&ts=73105

fitted at a low point normally near the boiler.

There should really be one at every low point.


I suspect I won't find one. The reason I say that is that the house has a
raised floor and a lot of the CH pipework (22mm plastic) runs underneath
the floor. Now that I know what I'm looking for I'll go underground and
have another look - but presumably if there is one below the floor it'd
have limited effectiveness as the water would have to go uphill to get to
a drain. It was a factor in my thinking about trying to go down the route
of forcing water around the entire CH system as it's possible that a lot
of the 22 mm pipework under the floor will be acting as a sump and
collecting gunge.

Dougie


  #10   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Mon, 20 Oct 2003 21:59:06 +0100, Andy Hall wrote:

On Mon, 20 Oct 2003 20:34:09 +0100, Dougie Nisbet
wrote:

[ .. ]

The question: Is it a DIY job? None of my DIY books cover it and my
googling of the NG archives hasn't come up with anything definitive in the
Janet and John guide to flushing your system vein.

Dougie


Yes it is.

You can do a Google Groups search for a method that I have used to
clean and flush successfully, by removing each radiator and taking it
outside for flushing with a mains hose or pressure washer.

This method works especially well if you have a sealed system with a
filling loop connected to the mains water supply. You can flush the
crud out at each radiator valve and clear the pipes very effectively.

Do watch out for sludge and other iron compounds from the radiators.
They are an indellible dye on carpets and furnishings. I use a
plastic bag on each valve tail held on with a rubber band.

I use a pair of new cat litter trays to collect water etc. from each
radiator.

For the TRVs, if they are old enough to be unidirectional, then they
are probably beyond their useful life as well. While you are
cleaning the radiators, I would be inclined to replace them and also
the lockshields.

Once the system is flushed clean, it is a good idea to put in a
chemical flushing agent and running the system hot for a few days.
Then rinse and flush thoroughly.

Finally refill, adding inhibitor. You can add a filling point to do
this by creating a vertical short stub of pipe on the system, closed
off with a cap and then using a funnel to add liquid inhibitor.
Alternatively, you can use a gel inhibitor which comes in mastic gun
cartridges. It is a lot easier and cleaner if you put this stuff
in through a vent before finally filling the system, rather than doing
so against the pressure afterwards.


Thanks - that sounds rather encouraging. The towel rail in the bathroom
has capped tops (what are they called) which I need to investigate but
look very promising in the longer term for adding inhibiter. The bathroom
is on the ground floor so I guess I may have to more or less completely
drain the system when I decide to do this after cleaning.

I'm not sure I'll bother replacing the LSVs and TRVs at the time of
flushing. Partly because of cost although I've not investigated this) but
mostly because I'm not a wild fan of TRVs and recently wired in a Danfoss
TP5 room thermostat
http://www.screwfix.com/app/sfd/cat/...39276&ts=68941 into the
combi which I find much easier and useful. Almost all the rads have the
TRVs fully open and I control temperature and timer with the Danfoss.

I've already read the other posts in this thread and tracked down some of
the archived material and it's raised more questions. I'm not wild about
the idea of removing and flushing 16 rads, but certainly think that doing
the bathroom rail and using it as the access point for flushing the system
is the way for me to go, and I'll see how it goes from there. One problem
I may have of trying to flush water around the CH circuit as my mains
water pressure is pretty poor anyway (lead piping) and I'm not convinced
that it will suffice to give my rads the colonic irrigation they so much
desire. That's another thought - if I shove a hose up the backside of rad
at poor mains pressure, am I not contravening some law about risking
backflow of dirty water into the mains?

Dougie




  #11   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 21:52:03 +0100, Dougie Nisbet
wrote:




Thanks - that sounds rather encouraging. The towel rail in the bathroom
has capped tops (what are they called) which I need to investigate but
look very promising in the longer term for adding inhibiter. The bathroom
is on the ground floor so I guess I may have to more or less completely
drain the system when I decide to do this after cleaning.


I guess that you mean vents??



I'm not sure I'll bother replacing the LSVs and TRVs at the time of
flushing. Partly because of cost although I've not investigated this) but
mostly because I'm not a wild fan of TRVs and recently wired in a Danfoss
TP5 room thermostat


The reason that I replaced my lockshield valves was because the system
had previously been open vented and upon pressurisation there was
seepage from some of the valves. They were poor quality anyway, so
I decided to resolve by replacing them.




I've already read the other posts in this thread and tracked down some of
the archived material and it's raised more questions. I'm not wild about
the idea of removing and flushing 16 rads, but certainly think that doing
the bathroom rail and using it as the access point for flushing the system
is the way for me to go, and I'll see how it goes from there.


You could certain start this way. However, if the system is really
full of crud then you run the risk of pushing some into the boiler.
If that happens, you need to be very sure that it gets flushed
through.

You could certainly start with one radiator and see how bad it is.
If a lot of sludge comes through, then trying to clear them in situ is
probably not going to be effective and you will spend a lot of time
running round getting all the muck out.

I did about 15 radiators in a morning of removing, fliushing, swapping
valve and replacing. If you organise the procedure it is quite
quick.


One problem
I may have of trying to flush water around the CH circuit as my mains
water pressure is pretty poor anyway (lead piping) and I'm not convinced
that it will suffice to give my rads the colonic irrigation they so much
desire. That's another thought - if I shove a hose up the backside of rad
at poor mains pressure, am I not contravening some law about risking
backflow of dirty water into the mains?


If you put a double check valve on the hose connector at the tap, that
can't happen. The filling point also ha one of these (or should
do).



..andy

To email, substitute .nospam with .gl
  #12   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 23:24:06 +0100, Andy Hall wrote:

[ .. ]

I've already read the other posts in this thread and tracked down some
of the archived material and it's raised more questions. I'm not wild
about the idea of removing and flushing 16 rads, but certainly think
that doing the bathroom rail and using it as the access point for
flushing the system is the way for me to go, and I'll see how it goes
from there.


You could certain start this way. However, if the system is really
full of crud then you run the risk of pushing some into the boiler. If
that happens, you need to be very sure that it gets flushed through.


The Flow and Return pipes at the boiler both have isolating valves.
Perhaps I could protect the boiler by closing both valves, then fully
opening the by-pass valve - thus forming a closed circuit for the CH but
isolating the boiler. Might that work?

You could certainly start with one radiator and see how bad it is. If a
lot of sludge comes through, then trying to clear them in situ is
probably not going to be effective and you will spend a lot of time
running round getting all the muck out.

I did about 15 radiators in a morning of removing, fliushing, swapping
valve and replacing. If you organise the procedure it is quite quick.


In the end I think I probably shall do this. The 'thorougness' of the
procedure appeals to me. Although I'm a little concerned about getting the
upstairs rads down the narrow staircase to get to the garden to flush them
out. Presumably it helps to have a helper for this.

Dougie

  #13   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Wed, 22 Oct 2003 08:48:12 +0100, Dougie Nisbet
wrote:

On Tue, 21 Oct 2003 23:24:06 +0100, Andy Hall wrote:



The Flow and Return pipes at the boiler both have isolating valves.
Perhaps I could protect the boiler by closing both valves, then fully
opening the by-pass valve - thus forming a closed circuit for the CH but
isolating the boiler. Might that work?


Certainly protecting the boiler is a good idea.

You can then open the bypass fully as you say, but do make a note of
the setting position so that you can adjust it back afterwards.

In effect, this will allow you to inject water at the filling point
and then you can create an exit on either the flow or the return side
of a given radiator or radiators.

If you draw a sketch of the system (boiler, filling point, flow and
return pipes and a couple of radiators), it will become obvious where
the drain points should be to get the crud out. Remember that it's
useful to flush both flow and return pipework and that doing so away
form the boiler is a good idea.




In the end I think I probably shall do this. The 'thorougness' of the
procedure appeals to me.


Since you have plastic pipes, putting in drain cocks will be very easy
to do.


Although I'm a little concerned about getting the
upstairs rads down the narrow staircase to get to the garden to flush them
out. Presumably it helps to have a helper for this.


Smaller single panel radiators are easily manageable single handed,
but a larger or two panel one is better with two. Once you have
drained the bulk of the water out, if you tip the radiator in one
direction as you remove it from the wall, most of the rest will come
out. Then if you apply plastic bags to the tails and fix with rubber
bands, you won't drip water anywhere.
Also, you will need to have two wrenches. One for holding the valve
body and one for the union nut.




..andy

To email, substitute .nospam with .gl
  #14   Report Post  
Dougie Nisbet
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Mon, 20 Oct 2003 21:59:06 +0100, Andy Hall wrote:

[ .. ]

Finally refill, adding inhibitor. You can add a filling point to do
this by creating a vertical short stub of pipe on the system, closed
off with a cap and then using a funnel to add liquid inhibitor.
Alternatively, you can use a gel inhibitor which comes in mastic gun
cartridges. It is a lot easier and cleaner if you put this stuff
in through a vent before finally filling the system, rather than doing
so against the pressure afterwards.


I tried one of those mastic gun cartridge affairs a few months ago. I
bought it in B&Q and carefully read the instructions. I had high hopes for
improving the health of my CH system but it all ended in tears and neither
the CH system or I enjoyed the experience very much. Despite carefully
following the instructions the inevitable result was a lot of swearing and
sad little puddles of vulcan blood on the kitchen lino.

The thought of tipping a dose of cleaner or inhibitor at no pressure into
the bathroom rail cap (what's it called?) sounds far less stressful all
round.

Dougie

  #15   Report Post  
Andy Hall
 
Posts: n/a
Default Cleaning/Flushing a pressurise ad sealed CH system

On Tue, 21 Oct 2003 21:56:45 +0100, Dougie Nisbet
wrote:



I tried one of those mastic gun cartridge affairs a few months ago. I
bought it in B&Q and carefully read the instructions. I had high hopes for
improving the health of my CH system but it all ended in tears and neither
the CH system or I enjoyed the experience very much. Despite carefully
following the instructions the inevitable result was a lot of swearing and
sad little puddles of vulcan blood on the kitchen lino.



The thought of tipping a dose of cleaner or inhibitor at no pressure into
the bathroom rail cap (what's it called?) sounds far less stressful all
round.



It's a lot easier to inject into an empty radiator rather than trying
to do so against the pressure.
There are only a few hundred ml. of paste in a mastic cartridge and
that can be squirted into any empty radiator.
You could try adding the liquid (e.g. Fernox MB-1) via an upstairs
radiator using a fine plastic tube. Bear in mind that there is 5l of
it, so the system would need to be as empty as possible.









Dougie


..andy

To email, substitute .nospam with .gl


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Getting Inhibiter into a sealed heating system Rich UK diy 2 September 9th 03 09:59 PM
Filling sealed heating system. Do I need a flexi pipe? Rob UK diy 3 September 3rd 03 09:12 AM
Repairing leaks and adding a radiator in a CH sealed system. Paulo UK diy 1 August 18th 03 10:00 PM
mains Hot water, and do I convert open heating to a closed heating system Ian Tracey UK diy 5 July 18th 03 09:55 AM


All times are GMT +1. The time now is 05:47 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"