Default installing downstairs wc - syphonage on soil stack consideration?

I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.

1. Or will it be ok re syphonage?

2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?

thanks
Tony
  #2   Report Post  
Posted to uk.d-i-y
Rod Rod is offline
external usenet poster
 
Posts: 2,892
Default installing downstairs wc - syphonage on soil stack consideration?

tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.

1. Or will it be ok re syphonage?

2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?

thanks
Tony


Provided that your stack pipe is properly installed, I would not expect
a problem with syphonage. (Our ground floor WC is not under the stairs
but does connect to the stack pipe which services the upstairs WC and
bathroom. No problems. Not even a trace of a ripple on the ground floor
WC when the upstairs one is flushed.)

I suggest you look at the archive if this group for general opinion of
Saniflo. (Summary: It will need unblocking. Unblocking is extremely
unpleasant.) I can't imagine a reason for installing one if a
conventional waste is possible.

--
Rod

Hypothyroidism is a seriously debilitating condition with an insidious
onset.
Although common it frequently goes undiagnosed.
www.thyromind.info www.thyroiduk.org www.altsupportthyroid.org
  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 305
Default installing downstairs wc - syphonage on soil stack consideration?

Rod wrote:
tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.

1. Or will it be ok re syphonage?

2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?

thanks
Tony


Provided that your stack pipe is properly installed, I would not expect
a problem with syphonage. (Our ground floor WC is not under the stairs
but does connect to the stack pipe which services the upstairs WC and
bathroom. No problems. Not even a trace of a ripple on the ground floor
WC when the upstairs one is flushed.)

I suggest you look at the archive if this group for general opinion of
Saniflo. (Summary: It will need unblocking. Unblocking is extremely
unpleasant.) I can't imagine a reason for installing one if a
conventional waste is possible.

same here downstairs loo is more or less directly below a bath shower
and two toilets with no problems what so ever, you can hear the water in
the stack pipe as its internal but you don't get any movement of water
in the downstairs loo

--
Kevin R
Reply address works
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default installing downstairs wc - syphonage on soil stack consideration?

The design of soil stacks is specified in the building regs:

http://www.planningportal.gov.uk/eng...000000382.html
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8,319
Default installing downstairs wc - syphonage on soil stack consideration?

Rod wrote:
tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the
lower section of the stack? I vaguely remember learning about this,
but have never seen it done. Perhaps it isn't necessary.

1. Or will it be ok re syphonage?

2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?

thanks
Tony


Provided that your stack pipe is properly installed, I would not
expect a problem with syphonage. (Our ground floor WC is not under
the stairs but does connect to the stack pipe which services the
upstairs WC and bathroom. No problems. Not even a trace of a ripple
on the ground floor WC when the upstairs one is flushed.)

I suggest you look at the archive if this group for general opinion of
Saniflo. (Summary: It will need unblocking. Unblocking is extremely
unpleasant.) I can't imagine a reason for installing one if a
conventional waste is possible.


Read this as Rod suggests http://www.diyfaq.org.uk/humour.html#saniflo


--
Dave - The Medway Handyman
www.medwayhandyman.co.uk




  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 91
Default installing downstairs wc - syphonage on soil stack consideration?

On Oct 12, 9:40*am, "The Medway Handyman"
wrote:
Rod wrote:
tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the
lower section of the stack? I vaguely remember learning about this,
but have never seen it done. Perhaps it isn't necessary.


1. Or will it be ok re syphonage?


2. Is a Saniflo macerator *a good idea, or is a conventional waste
outlet better?


thanks
Tony


Provided that your stack pipe is properly installed, I would not
expect a problem with syphonage. (Our ground floor WC is not under
the stairs but does connect to the stack pipe which services the
upstairs WC and bathroom. No problems. Not even a trace of a ripple
on the ground floor WC when the upstairs one is flushed.)


I suggest you look at the archive if this group for general opinion of
Saniflo. (Summary: It will need unblocking. Unblocking is extremely
unpleasant.) I can't imagine a reason for installing one if a
conventional waste is possible.


Read this as Rod suggestshttp://www.diyfaq.org.uk/humour.html#saniflo

--
Dave - The Medway Handymanwww.medwayhandyman.co.uk- Hide quoted text -

- Show quoted text -


I enjoyed reading 'bout saniflo :-)
I guess I'll give it a miss!!
Cheers

Tony
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 532
Default installing downstairs wc - syphonage on soil stack consideration?

tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?


Provided that a) the distance to the stack from your new toilet doesn't
exceed 6m (or less if there are a number of bends), or b) there is a
vent on the existing stack (which there should be anyway for a toilet
above the ground floor), then you shouldn't have a problem. Even if you
do, you could stick a 'Durgo' valve on the new branch.
--
Hugo Nebula
"If no-one on the internet wants a piece of this,
just how far from the pack have you strayed"?
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 112
Default installing downstairs wc - syphonage on soil stack consideration?

tonyjeffs wrote:

On Oct 12, 9:40�am, "The Medway Handyman"
wrote:
Rod wrote:
tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the
lower section of the stack? I vaguely remember learning about this,
but have never seen it done. Perhaps it isn't necessary.


1. Or will it be ok re syphonage?


2. Is a Saniflo macerator �a good idea, or is a conventional waste
outlet better?


thanks
Tony


Provided that your stack pipe is properly installed, I would not
expect a problem with syphonage. (Our ground floor WC is not under
the stairs but does connect to the stack pipe which services the
upstairs WC and bathroom. No problems. Not even a trace of a ripple
on the ground floor WC when the upstairs one is flushed.)


I suggest you look at the archive if this group for general opinion of
Saniflo. (Summary: It will need unblocking. Unblocking is extremely
unpleasant.) I can't imagine a reason for installing one if a
conventional waste is possible.


Read this as Rod suggestshttp://www.diyfaq.org.uk/humour.html#saniflo

--
Dave - The Medway Handymanwww.medwayhandyman.co.uk- Hide quoted text -

- Show quoted text -


I enjoyed reading 'bout saniflo :-)
I guess I'll give it a miss!!
Cheers

Tony


Surely Saniflo is a breach of Trades Descriptions: Sani == Sanitary
and Flo == Flow, both of which seem questionable.

Seriously though, provided your waste instalation complies with
Building Regs in respect to pipe sizes and open vents it will be
fine. In essence make sure it uses 110mm plastic pipe or if it's
older then the cast iron equivalent and that there is an open vent
within (IIRC) 6 instalations away and preferably on the last
installation of a run. In any normal setup these requirements are
already easily met and you'll probably find that your pipe to upstairs
goes on to roof level where it is open vented. In essence this open
venting provides an "easy" path for air to get in so that there is
never a negative pressure to induce siphonage. Even if you have an
automatic valve upstairs instead you'll probably be fine.

The only other thing you might need to look out for is wether other
wastes join the downpipe near your intended join. If so you have some
other requirements to meet to avoid backflow. Not hard usually but
you do need to meet them.
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 112
Default installing downstairs wc - syphonage on soil stack consideration?

Hugo Nebula wrote:

tonyjeffs wrote:
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?


Provided that a) the distance to the stack from your new toilet doesn't
exceed 6m (or less if there are a number of bends), or b) there is a
vent on the existing stack (which there should be anyway for a toilet
above the ground floor), then you shouldn't have a problem. Even if you
do, you could stick a 'Durgo' valve on the new branch.
--
Hugo Nebula
"If no-one on the internet wants a piece of this,
just how far from the pack have you strayed"?


From memory Hugo I think you couldn't fit a Durgo on the new branch as
to comply with regs these need to be installed above the flood level
of all fittings so it would need to be higher than the upstairs loo.
That's from memory though so the OP might like to check the regs
before dismissing the idea. Mind you I suspect it wouldn't be
neccessary anyway as I, like you, think he's probably compliant
anyway.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,356
Default installing downstairs wc - syphonage on soil stack consideration?

On Sat, 11 Oct 2008 20:32:16 -0700 (PDT) someone who may be
tonyjeffs wrote this:-

I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?


Not if you follow the regulations with regard to distances, falls
and the like. Make sure no other appliances join the pipe close to
the new connection.

should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.


Necessary in rare cases, which are extremely unlikely to be
encountered in a house. Even if it was necessary in a particular
installation there is a lot to be said for avoiding it by, for
example, adding another stack. It was done in the distant past when
they had less experience of the then fancy new concept of having
toilets and basins inside buildings. Toilet pans are unlikely to be
affected anyway, it is more likely to be basins.

2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?


If gravity drainage can be arranged then it is always better.
Simpler, uses no electricity and less likely to go wrong. However,
that doesn't mean one should pay much attention to the loud voices
of the trolls on the subject. Provided they are properly installed
and used macerators work fine. If they are abused they don't, but
that is true of many things (including gravity drainage).


--
David Hansen, Edinburgh
I will *always* explain revoked encryption keys, unless RIP prevents me
http://www.opsi.gov.uk/acts/acts2000/00023--e.htm#54


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,369
Default installing downstairs wc - syphonage on soil stack consideration?



"tonyjeffs" wrote in message
...
I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.

1. Or will it be ok re syphonage?


The stack is vented so there shouldn't be any siphon.


2. Is a Saniflo macerator a good idea, or is a conventional waste
outlet better?


If you can fit a normal waste it is better.
If you can't a Saniflow is better.



  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 91
Default installing downstairs wc - syphonage on soil stack consideration?

On Oct 12, 7:07*pm, "dennis@home"
wrote:
"tonyjeffs" wrote in message

...

I'm going to fit a wc below the stairs on the ground floor of our
semi, and attach to the same soil stack as the existing FF wc.
Is there likely to be a problem with syphonage - such that when I
flush the upstairs toilet, the ground floor toilet will gurgle?
should I consider putting some kind of vent bypass pipe from the lower
section of the stack? I vaguely remember learning about this, but have
never seen it done. Perhaps it isn't necessary.


1. Or will it be ok re syphonage?


The stack is vented so there shouldn't be any siphon.



2. Is a Saniflo macerator *a good idea, or is a conventional waste
outlet better?


If you can fit a normal waste it is better.
If you can't a Saniflow is better.


Thanks to everyone.
I'll do the drainage the conventional way, not worry about syphonage
and give Saniflo a miss.

To


  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 532
Default installing downstairs wc - syphonage on soil stack consideration?

Calvin wrote:

From memory Hugo I think you couldn't fit a Durgo on the new branch as
to comply with regs these need to be installed above the flood level
of all fittings so it would need to be higher than the upstairs loo.


No, it's above the flood level of any appliance _on that stack_ (in this
case the new ground floor one).
--
Hugo Nebula
"If no-one on the internet wants a piece of this,
just how far from the pack have you strayed"?
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help: Soil Connection Options for Under Stairs Macerator (Soil Stack/ Manhole) GC UK diy 0 March 23rd 08 12:32 PM
soil stack. [email protected] UK diy 6 August 30th 06 12:43 AM
Soil stack? Stinkoman UK diy 4 April 10th 05 01:45 PM
soil stack karla Home Repair 1 February 2nd 05 12:41 AM
Replacing downstairs bog - soil pipe problems Jon Taylor UK diy 12 April 12th 04 10:48 PM


All times are GMT +1. The time now is 10:19 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"