I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 40
Default 1 to 3 phase inverter


"robgraham" wrote in message
...
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob


I probably have this wrong but IIRC, for 240v 3 phase, if you had a neutral
you would measure 240 between any phase and neutral, but ~350 between
phases.


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 3,703
Default 1 to 3 phase inverter

In article , fred
writes

"robgraham" wrote in message
...
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob


I probably have this wrong but IIRC, for 240v 3 phase, if you had a neutral
you would measure 240 between any phase and neutral, but ~350 between
phases.

240V phase to neutral is 415V between phases, sqrt3 being the
multiplying factor.
--
fred
BBC3, ITV2/3/4, channels going to the DOGs
  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

robgraham wrote:
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob

Rob, You should have no need to be concerned. The inverter you have does
not put out any higher voltage than you put into it.
I rectifies the mains directly to peak mains voltage and uses this to
synthesize three phase waveforms by pulse modulation. The resultant
waveform is tolerably smoothed to be sinusoidal using the inductance of
the motor.
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.
Most DVM/DMMs work much the same. Top of the range models claim to offer
true RMS via signal processing. I suspect they could also get it a bit
wrong when pulses are present.

Out of curiosity, I have just made some quick measurements on a Siemens
inverter running a 3HP motor in my workshop.
Nominal single phase mains in and delta connected motor on the output.
Voltages measured from phase to phase.
My cheapy DMM max range 700 vac indicates off scale.
My Avo 8 indicated about 700 v on 1000vac range
My Tektronix true RMS DMM reads between 235 and 240 vac

I have run many motors on these converters with no signs of insulation
breakdown or inverter failure. The worst problem was a stress fracture
in the lead of the crystal on a control micro. Even that failed safe and
a replacement part rendered the unit working again.

HTH

Bob
  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

fred wrote:
In article , fred
writes

"robgraham" wrote in message
...
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob


I probably have this wrong but IIRC, for 240v 3 phase, if you had a
neutral
you would measure 240 between any phase and neutral, but ~350 between
phases.

240V phase to neutral is 415V between phases, sqrt3 being the
multiplying factor.

True but inverters like this produce 240 phase to phase. Equivalent to
about 140v phase to neutral if there was such a thing.

Bob


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,730
Default 1 to 3 phase inverter

On 29 Aug, 23:08, Bob Minchin wrote:
robgraham wrote:
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).


I am looking for some input from someone who has used one of these
before and done some measurements.


I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. *I put the
'extra' volts down to DVM anomaly ! *Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.


This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.


Thanks
Rob


Rob, You should have no need to be concerned. The inverter you have does
not put out any higher voltage than you put into it.
I rectifies the mains directly to peak mains voltage and uses this to
synthesize three phase waveforms by pulse modulation. The resultant
waveform is tolerably smoothed to be sinusoidal using the inductance of
the motor.
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.
Most DVM/DMMs work much the same. Top of the range models claim to offer
true RMS via signal processing. I suspect they could also get it a bit
wrong when pulses are present.

Out of curiosity, I have just made some quick measurements on a Siemens
inverter running a 3HP motor in my workshop.
Nominal single phase mains in and delta connected motor on the output.
Voltages measured from phase to phase.
My cheapy DMM max range 700 vac indicates off scale.
My Avo 8 indicated about 700 v on 1000vac range
My Tektronix true RMS DMM reads between 235 and 240 vac

I have run many motors on these converters with no signs of insulation
breakdown or inverter failure. The worst problem was a stress fracture
in the lead of the crystal on a control micro. Even that failed safe and
a replacement part rendered the unit working again.

HTH

Bob


Many thanks, Bob - that was the answer I was hoping someone would come
up with. Taking your point about peak rectification, that would give
340v pk, so although the logic isn't perfect, that makes 320v on my
meters understandable.

Rob
  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

dave wrote:
On Fri, 29 Aug 2008 23:13:20 +0100, Bob Minchin
wrote:

fred wrote:
In article , fred
writes
"robgraham" wrote in message
...
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).

I am looking for some input from someone who has used one of these
before and done some measurements.

I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.

This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.

Thanks
Rob
I probably have this wrong but IIRC, for 240v 3 phase, if you had a
neutral
you would measure 240 between any phase and neutral, but ~350 between
phases.

240V phase to neutral is 415V between phases, sqrt3 being the
multiplying factor.

True but inverters like this produce 240 phase to phase. Equivalent to
about 140v phase to neutral if there was such a thing.

Bob

I don't pretend to know what one of these beasties is, but are we
talking sine waves here? If not then sqrt3 does prob not apply. ie
waveshape accounts for the difference?

Yes. The waveform is the core of the perceived problem.
All Ac voltmeters aim to give correct readings for sinusoidal waveforms
at typical mains frequencies but use differing methods to achieve this.
These methods lead to errors when the waveform is non sinusoidal or has
a higher frequency.

Bob
  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

robgraham wrote:
On 29 Aug, 23:08, Bob Minchin wrote:
robgraham wrote:
I bought one of these some time back for a project which never
materialised, but am now experimenting with it to drive a 3 phase
powered wood turning lathe (ex school hence the 3 ph motor probably
connected in star).
I am looking for some input from someone who has used one of these
before and done some measurements.
I didn't realise to begin with that it converted 240v single phase to
240v 3 phase and that the motor should be connected in delta format to
get full power - I thought it would have been 440V 3 ph and continued
to think so as my DVM was registering 600v ph tp ph. I put the
'extra' volts down to DVM anomaly ! Anyhow a bit more reading and
then experimenting with an old AVO and a more up to date DVM gave 320v
ph to ph.
This is a bit nearer 240v but far enough off to puzzle me somewhat -
the fact that both the AVO and the modern DVM read the same would
suggest that this is a true RMS reading but at some 30% above 240v,
that does seem a bit odd, and should I be concerned about it with
respect to the winding insulation.
Thanks
Rob

Rob, You should have no need to be concerned. The inverter you have does
not put out any higher voltage than you put into it.
I rectifies the mains directly to peak mains voltage and uses this to
synthesize three phase waveforms by pulse modulation. The resultant
waveform is tolerably smoothed to be sinusoidal using the inductance of
the motor.
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.
Most DVM/DMMs work much the same. Top of the range models claim to offer
true RMS via signal processing. I suspect they could also get it a bit
wrong when pulses are present.

Out of curiosity, I have just made some quick measurements on a Siemens
inverter running a 3HP motor in my workshop.
Nominal single phase mains in and delta connected motor on the output.
Voltages measured from phase to phase.
My cheapy DMM max range 700 vac indicates off scale.
My Avo 8 indicated about 700 v on 1000vac range
My Tektronix true RMS DMM reads between 235 and 240 vac

I have run many motors on these converters with no signs of insulation
breakdown or inverter failure. The worst problem was a stress fracture
in the lead of the crystal on a control micro. Even that failed safe and
a replacement part rendered the unit working again.

HTH

Bob


Many thanks, Bob - that was the answer I was hoping someone would come
up with. Taking your point about peak rectification, that would give
340v pk, so although the logic isn't perfect, that makes 320v on my
meters understandable.

Rob

Rob,
My point on p-p rectification was that with internal supply rails no
greater than input mains p-p values, the inverter could only generate
voltage pulse magnitudes up to the supply rails. These pulses are quite
likely to upset readings on many meters however which is probably what
you have found.
I suspect that my cheapy DMM gets it so wrong because the high frequency
components of the waveform is not being attenuated in the meter due to
stray capacitance in its input circuitry. To be fair it was free
promotion with an order from Rapid a few years back.
Bob
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 26
Default 1 to 3 phase inverter


Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.



The moving coil AVO is an Average reading device, not peak.
  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

John Evans wrote:
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.



The moving coil AVO is an Average reading device, not peak.

I'm not totally sure but, I suspect it is a mix of the two actually.
Peak detecting due to the diode and averaged/integrated by the inertia
of the mechanics of the movement.
It certainly does not like the pulse output of my inverter.

Bob


  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 26
Default 1 to 3 phase inverter

On Sat, 30 Aug 2008 21:47:11 +0100, Bob Minchin
wrote:

John Evans wrote:
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.



The moving coil AVO is an Average reading device, not peak.

I'm not totally sure but, I suspect it is a mix of the two actually.
Peak detecting due to the diode and averaged/integrated by the inertia
of the mechanics of the movement.
It certainly does not like the pulse output of my inverter.

Bob



The diode(s) conduct when the input is the appropiate polarity
presenting half of the waveform to the meter movement. If it is a full
wave - or bridge - circuit then both halves of the waveform are
presented. There is no peak action as there is nothing stopping the
diode(s) conducting for the full half cycle - ignoring the small
offset. The mechanical inertia then averages out the pulse levels.

John
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 400
Default 1 to 3 phase inverter

John Evans wrote:
On Sat, 30 Aug 2008 21:47:11 +0100, Bob Minchin
wrote:

John Evans wrote:
Your Avo is a peak reading device with a weighting factor to read RMS
assuming a sine wave. Any other waveform will give erroneous readings.

The moving coil AVO is an Average reading device, not peak.

I'm not totally sure but, I suspect it is a mix of the two actually.
Peak detecting due to the diode and averaged/integrated by the inertia
of the mechanics of the movement.
It certainly does not like the pulse output of my inverter.

Bob



The diode(s) conduct when the input is the appropiate polarity
presenting half of the waveform to the meter movement. If it is a full
wave - or bridge - circuit then both halves of the waveform are
presented. There is no peak action as there is nothing stopping the
diode(s) conducting for the full half cycle - ignoring the small
offset. The mechanical inertia then averages out the pulse levels.

John

John, I don't disagreed with the intended operation but something,
presumably the waveform or possibly high frequency components present,
causes my avo to read too high on an inverter. It could even be due to
capacitance which is irrelevant at 50hz but no so at inverter pulse
frequencies. One day I'll get a scope out into the workshop to try and
understand more fully what is going on. Fortunately my true RMS Tek DMM
seems to be telling the the truth.
Regards
Bob
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
profit-motive question: single phase adapter for 3-phase motor drives gwes Metalworking 8 October 5th 07 08:33 PM
3-phase used for 1-phase (split-phase) power SRK Home Repair 9 July 22nd 06 11:01 AM
VFD used with either a 3~ Rotary Converter or Phase Inverter Mark Main Metalworking 13 January 24th 06 08:36 PM


All times are GMT +1. The time now is 12:12 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"