Electrical Installation Q
Adding a new out-building to my house and just pondering the
electricity supply to it. (ignoring issue of whether I am allowed to do this) Only need a couple of lights and a couple of sockets (ad hoc use only) Intend fitting a Garage CU ,,, 40A 30mA RCD – 1 x 16A for sockets 1 x 6A for lights Current house install is Supply authority cabinet .. cabled with 32mm tails to a 100A switch fuse which in turn goes to a Henley block and feeds 2 x CU's. (wanted plenty of circuit granularity) Be interested in knowing which option to follow… Opt A … put a DP switch alongside the switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed to outbuilding and it's CU. Does not allow full `isolation' but mcb would allow power interruption of that feed. Be interested in views … and whether Regs call for Opt A .. i.e. local isolation. |
#2
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Osprey wrote:
Adding a new out-building to my house and just pondering the electricity supply to it. (ignoring issue of whether I am allowed to do this) Only need a couple of lights and a couple of sockets (ad hoc use only) Intend fitting a Garage CU ,,, 40A 30mA RCD – 1 x 16A for sockets 1 x 6A for lights I would use a 20A MCB for the sockets, as per a normal radial circuit, assuming you are wiring it in 2.5mm cable. Current house install is Supply authority cabinet .. cabled with 32mm tails to a 100A switch fuse which in turn goes to a Henley block and feeds 2 x CU's. (wanted plenty of circuit granularity) Be interested in knowing which option to follow… Opt A … put a DP switch alongside the switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. If this new switch is just going to be a switch, then your run to the out-building is going to need a HUGE cable as it will be fused at 100A You would need to install a switch fuse with an appropriate fuse if you want to use a sensible sized cable. Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed to outbuilding and it's CU. Does not allow full `isolation' but mcb would allow power interruption of that feed. This is what I have done, but I used a 32A MCB, and made sure it was connected to the non RCD consumer unit. Be interested in views … and whether Regs call for Opt A .. i.e. local isolation. The main switch in the CU will act as local isolation, and as you will put it on a non RCD side, you wont have any problems with RCD's tripping because there is a neutral problem. More information is needed really.. How long is the cable run between the house CU and the outbuilding CU What cable are you planning on using (Have you installed this already?) What is the out-building made of? Are there any other services to this out-building (Water/Gas/etc.) Toby... |
#3
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Osprey wrote:
Current house install is Supply authority cabinet .. cabled with 32mm tails to a 100A switch fuse which in turn goes to a Henley block and feeds 2 x CU's. (wanted plenty of circuit granularity) Be interested in knowing which option to follow… Opt A … put a DP switch alongside the switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. You would need a fuse/mcb at the head end to protect the submain from overcurrent or fault currents, unless it is of sufficient size that the main 100A cutout can perform this task (which seems a bit excessive for a few sockets and a light) Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed to outbuilding and it's CU. Does not allow full `isolation' but mcb would allow power interruption of that feed. Full isolation would come via turning off the CU its fed from, not its MCB How about: Opt 3 - install third mini CU at the head end, fed via additional set of tails from the Henley. This could have a single fuse or MCB of appropriate size, and a master switch. Hence protecting the submain, and providing ready isolation discrete from any other circuits. More detail he http://wiki.diyfaq.org.uk/index.php?...ricity_outside -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#4
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
More detail he http://wiki.diyfaq.org.uk/index.php?...ricity_outside My description may not have been that clear … though both comments are useful. Current house install is Supply authority cabinet .. cabled with 32mm tails to a 100A switch fuse which in turn goes to a Henley block and feeds 2 x CU's. (wanted plenty of circuit granularity) I want to supply a feed to an outbuilding (new garage) … intend putting a small Cu in garage consisting of 40A 30mA RCD plus 16A & 6A mcb for limited light & power. Something like .. http://tinyurl.com/6rozky No other services - & this is a permanent building. Dug a trench last night, The run to this from house is 10m long and will be in 3core armoured, not checked but assuming it will be 2.5mm2 It would seem to make sense to have this capable of isolation from house … Opt A … put a 40A DP switch fuse alongside the existing switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. 40A fuse limits fault current to sub cct. Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed from this to outbuilding and it's CU. Does not allow full `isolation' without affecting house CU. If I do use Opt B … then guess I would have to terminate SWA cable in box of some sort alongside CU to allow a gland and correct earthing & termination of armour wires etc. I have sketched out the existing installation and 2 options … http://tinyurl.com/5ddcun |
#5
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"Rick Hughes" wrote in message ... More detail he http://wiki.diyfaq.org.uk/index.php?...ricity_outside My description may not have been that clear … though both comments are useful. Current house install is Supply authority cabinet .. cabled with 32mm tails to a 100A switch fuse which in turn goes to a Henley block and feeds 2 x CU's. (wanted plenty of circuit granularity) I want to supply a feed to an outbuilding (new garage) … intend putting a small Cu in garage consisting of 40A 30mA RCD plus 16A & 6A mcb for limited light & power. Something like .. http://tinyurl.com/6rozky No other services - & this is a permanent building. Dug a trench last night, The run to this from house is 10m long and will be in 3core armoured, not checked but assuming it will be 2.5mm2 It would seem to make sense to have this capable of isolation from house … Opt A … put a 40A DP switch fuse alongside the existing switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. 40A fuse limits fault current to sub cct. Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed from this to outbuilding and it's CU. Does not allow full `isolation' without affecting house CU. If I do use Opt B … then guess I would have to terminate SWA cable in box of some sort alongside CU to allow a gland and correct earthing & termination of armour wires etc. I have sketched out the existing installation and 2 options … http://tinyurl.com/5ddcun If you use option B then terminate the armoured into a metal clad 45Amp switch. (eg http://www.sparksdirect.co.uk/metal-clad-1-gang-45-amp-dp-red-rocker-switch-with-neon-p-13999.html ) Not only will this allow a good strong point for the armoured to terminate you will then have your double pole isolation in the house. There is little to chose beween options A and B. With option A you will still have to find a 40A DP switched fuse or a 2 way CU that will take your armoured. Personally I would also look up the difference in cost between 2.5mm and 4mm armoured. I suspect 10m of 2.5 armoured plus the wiring in the outbuilding will be big enough the expected voltage drop. Adam |
#6
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"ARWadworth" wrote in message m... If you use option B then terminate the armoured into a metal clad 45Amp switch. (eg http://www.sparksdirect.co.uk/metal-clad-1-gang-45-amp-dp-red-rocker-switch-with-neon-p-13999.html ) Not only will this allow a good strong point for the armoured to terminate you will then have your double pole isolation in the house. That is simpler (and presumably cheaper) than a switch fuse :-) not thought of that. There is little to chose beween options A and B. With option A you will still have to find a 40A DP switched fuse or a 2 way CU that will take your armoured. Personally I would also look up the difference in cost between 2.5mm and 4mm armoured. I suspect 10m of 2.5 armoured plus the wiring in the outbuilding will be big enough the expected voltage drop. Yep - not done the math's yet, but 4mm2 will be about 30% higher in cost .. plus not as easy to route, but I'll have to check the voltage drop. |
#7
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Rick Hughes wrote:
It would seem to make sense to have this capable of isolation from house … Opt A … put a 40A DP switch fuse alongside the existing switch fuse (downstream of the fuse) and feed that via armoured cable to the outbuilding, and install the garage CU … i.e. the DP sw allows complete isolation of outbuilding without impacting house. 40A fuse limits fault current to sub cct. Yup, that is fine, so long as you have the spare terminal capacity on the output of the existing switch fuse to get the new cable in. (this is essentially what I was suggesting as my option 3 - although taking the feed from the existing Henly. Obviously go with whichever is easiest and in the best location. Opt B .. add a 40A mcb into one of the existing house CU's, and then run feed from this to outbuilding and it's CU. Does not allow full `isolation' without affecting house CU. If I do use Opt B … then guess I would have to terminate SWA cable in box of some sort alongside CU to allow a gland and correct earthing & termination of armour wires etc. Yup, as Adam said, stick a small metal clad enclosure in somewhere with a DP switch and you have another workable solution. I have sketched out the existing installation and 2 options … http://tinyurl.com/5ddcun I would be tempted to up the size of the SWA a bit (using two core with armour for earth would keep the overall size about the same). If you max design load in the garage is 26A then your voltage drop on 2.5mm^2 SWA is well in spec, but it limits your future options a bit. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#8
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
I would be tempted to up the size of the SWA a bit (using two core with armour for earth would keep the overall size about the same). If you max design load in the garage is 26A then your voltage drop on 2.5mm^2 SWA is well in spec, but it limits your future options a bit. -- Cheers, John. John ... What is the 'current considered view on using SWA as earth ? .... When I last asked on this site why someone was running in a separate earth, was told that it is not acceptable good wiring practise to rely on SWA for earth fault protection on consumer side of installation ? The c/s area of armour is less than any one of the cores, and thus it is not suitable to be used as a bonding conductor. It therefore cannot be used as as a sub-main, but it can be used as a final sub-circuit. I am not sure what my use would be classed as. ? I have 2 garages as part of the house ... and have multiple outlets there including 32A industrial ones .. the new outbuildings do not need much in way of power ... Estimating total cable run (excluding wiring in outbuilding) as 15m and max current load as 22A (16 + 6), then using 18mV/A/M would give me 5.94V on 2.5mm2 (well under permitted 9.2V) and 3.63V on 4mm2 ... That makes 2.5mm2 more than man enough for the job ... However I would consider going to 4mm2 if dropping off the earth is allowable for this installation. (as per above comment) ... any comments ? |
#9
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Osprey wrote:
What is the 'current considered view on using SWA as earth ? ... Same as it's always been, it's allowable, desirable and from the point of view of saving valuable copper it's best practice. For cables of sizes likely to be used for DIY it will rarely if ever be necessary to use a separate circuit protective conductor (CPC). Even if a separate CPC is used it's still necessary to earth the armour. When I last asked on this site why someone was running in a separate earth, was told that it is not acceptable good wiring practise to rely on SWA for earth fault protection on consumer side of installation ? This is quite untrue. Good practice does of course mean using the correct size and type of glands. The c/s area of armour is less than any one of the cores, That's not true for any 2-core SWA size up to and including 120 mm^2 (XLPE cables to BS 5467). For the small sizes the armour CSA is much larger than the cores - e.g. 6 mm^2 2-core has 22 mm^2 of steel armour. Moreover the _copper_equivalent_ size of the armour (obtained by dividing the steel area by 2.255) complies with the tabulated requirements for use as a CPC without further calculation for all SWA sizes up to and including 95 mm^2. [Ref. Table 54G in BS 7671 (Table 54.7 in the 17th ed.)] The only thing that you have to watch is that the resistance per metre of the armour may be higher than for the line and neutral conductors, and you need to take this into account when evaluating the earth fault loop impedance (Zs). and thus it is not suitable to be used as a bonding conductor. If the armour has to act as a main bonding conductor as well as a CPC (e.g. for a submain to an outbuilding with services that need main bonding) then you'll usually need 10 mm^2 copper equivalent (for PME supplies). This, by coincidence, means using at least 10 mm^2 2-core SWA. Estimating total cable run (excluding wiring in outbuilding) as 15m and max current load as 22A (16 + 6), then using 18mV/A/M would give me 5.94V on 2.5mm2 (well under permitted 9.2V) As an aside, the voltage drop limits (guidance) have changed in the 17th ed. and are now 3% for lighting and 5% for all other uses. Also you must allow for drop in the outbuilding's wiring in addition to the submain. That makes 2.5mm2 more than man enough for the job ... Check the Zs though. The armour resistance of 2.5 SWA is 8.8 milliohm/m at 20 deg. so applying the usual rule of thumb for heating under fault conditions it will contribute about 0.18 ohm to Zs. What's the protection on the supply side? - if you have a 30 A fuse and a TN-S supply you might be getting near the limit... However I would consider going to 4mm2 if dropping off the earth is allowable for this installation. (as per above comment) ... any comments ? I'd go for at least 4, and possibly 6 for this. Incremental cost is small and extra capacity always useful in the future. And as I said, if you're exporting a PME earth and anything needs main bonding at the far end you must use 10, or run a separate bonding conductor. See also John Peckham's article here http://www.gadsolutions.biz/electric...wa-as-cpc.html -- Andy |
#10
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"Andy Wade" wrote in message ... Osprey wrote: The c/s area of armour is less than any one of the cores, That's not true for any 2-core SWA size up to and including 120 mm^2 (XLPE cables to BS 5467). For the small sizes the armour CSA is much larger than the cores - e.g. 6 mm^2 2-core has 22 mm^2 of steel armour. If the armour has to act as a main bonding conductor as well as a CPC (e.g. for a submain to an outbuilding with services that need main bonding) then you'll usually need 10 mm^2 copper equivalent (for PME supplies). This, by coincidence, means using at least 10 mm^2 2-core SWA. Estimating total cable run (excluding wiring in outbuilding) as 15m and max current load as 22A (16 + 6), then using 18mV/A/M would give See also John Peckham's article here http://www.gadsolutions.biz/electric...wa-as-cpc.html Andy as usual - many thanks I looked back at original comments here regarding not using earth wires .. and it was threaded to bonding conductor requirements. So 4mm2 it is, off to TLC this morning then. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"Andy Wade" wrote in message ... Osprey wrote: What is the 'current considered view on using SWA as earth ? ... I'd go for at least 4, and possibly 6 for this. Incremental cost is small and extra capacity always useful in the future. And as I said, if you're exporting a PME earth and anything needs main bonding at the far end you must use 10, or run a separate bonding conductor. See also John Peckham's article here http://www.gadsolutions.biz/electric...wa-as-cpc.html On further Q ... if you could help Existing house installation is on a PME (TN-C-S), but still classed as temporary supply (in final permanent location) and therefore using my own supplied earth rod. (been on this supply for 8 years ) Should I be exporting this earth to the outbuildings .. or should I insulate armour wires at outbuilding end and install a local earth rod ? At some point in future house will have it's acceptance certificate and I will request Supply Authority change supply over to a permanent one, at which point they will switch me to their earth. If I do use a local earth rod at out buildings do I then disconnect this when I go on permanent supply, or is it just left in place as another 'multiple earth point' There are no other services in the outbuildings. |
#12
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Rick Hughes wrote:
Existing house installation is on a PME (TN-C-S), but still classed as temporary supply (in final permanent location) and therefore using my own supplied earth rod. (been on this supply for 8 years ) With everything on one 30 mA RCD too, I guess... Should I be exporting this earth to the outbuildings .. or should I insulate armour wires at outbuilding end and install a local earth rod ? At some point in future house will have it's acceptance certificate and I will request Supply Authority change supply over to a permanent one, at which point they will switch me to their earth. In which case you should design the outbuilding installation on the assumption that the house will eventually be PME. The first decision is will the outbuilding use the exported house earth or be a separate TT installation. The basic question is "are you likely to come into simultaneous contact with the exported 'earth' (which will rise in potential during a fault) and the local ground, or metal things in contact with the local ground". Don't export PME if you're likely to use Class 1 (earthed) equipment outdoors, or to a workshop with a bare concrete floor, or to a metal greenhouse, and certainly not to a caravan or boat (the last two being illegal under the ESQC regs). TT is the safer option, provided your earth electrode remains in good condition (and remains connected!) and provided you test the RCDs regularly. For (eventual) exported PME option connect the armour solidly at both ends. Under the temporary arrangements this will give you TT throughout. There's no need for a separate earth rod at the outbuilding end, although you can add one if you like belt and braces. Assuming the plan is eventually to feed the submain via a fuse or MCB as a non-RCD-protected distribution circuit, you'll need one or more RCDs in the outbuilding (probably just a single 30 mA RCD if it's only a a few lights and sockets as described). Under the temporary arrangement you'll have two RCDs in cascade - so no discrimination - but this will eventually resolve itself. If the outbuilding is to be separately TT-earthed then, as you say, earth the armour at the house end only. Isolate and insulate it at the far end using an insulating gland (expensive) or use a big plastic stuffing gland and heatshrink sleeving. Earth the installation to a decent earth rod, preferably two 4ft. sections to get down to a good depth below any likely frost. The earthing conductor (rod to disboard), if normal 6491X green/yellow wire without mechanical protection, should be 16 mm^2 to comply with regs. RCD(s) as above are required and the discrimination issue remains until the house is converted to PME. [Exported PME) If I do use a local earth rod at out buildings do I then disconnect this when I go on permanent supply, or is it just left in place as another 'multiple earth point' Since you're using a fairly small cable I'd disconnect it. If the cable were big enough to satisfy the 10 mm^2 copper equivalent requirement for a main bonding conductor it would be safe to leave it in place. -- Andy |
#13
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"Andy Wade" wrote in message ... Rick Hughes wrote: Existing house installation is on a PME (TN-C-S), but still classed as temporary supply (in final permanent location) and therefore using my own supplied earth rod. (been on this supply for 8 years ) With everything on one 30 mA RCD too, I guess... Andy ,, Seems to be raising more questions than I thought. Some answers to questions raised. With everything on one 30 mA RCD too, I guess.. No, the existing house install has 2 CU's ... One of which is 30mA RCD protected ... ring mains & radials The other a Split load .. providing some non-protected (freezer, alarm, smk detectors etc.) and the rest via a 100mA RCD for lighting circuits. Don't export PME ... to a workshop with a bare concrete floor Outbuilding has a bare concrete floor but wooden fame, tiled roof .. no other services ... just a couple of sockets & lights. So will be running as advised 2C SWA cable out to the building ... If I fed this via 30mA RCD protection form the house .. (either existing CU or a new feed to a new small RCD CU off the 100A switch fuse) ... then am I Ok to export the earth to the garage ? Under fault conditions the SWA cable is RCD protected .. not just outbuilding wiring. I could then just use a small CU in the garage with no local RCD. Although I can happily install a local earth rod & cable at outbuilding ... I have a roll of 16mm2 earth cable spare. I have put what I think are the 2 options on this sketch http://tinyurl.com/59pw8h .... is either wrong or either preferred ? |
#14
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Andy Wade wrote:
If the outbuilding is to be separately TT-earthed then, as you say, earth the armour at the house end only. Isolate and insulate it at the far end using an insulating gland (expensive) or use a big plastic stuffing gland and heatshrink sleeving. Earth the installation to a How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#15
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Rick Hughes wrote:
Don't export PME ... to a workshop with a bare concrete floor Outbuilding has a bare concrete floor but wooden fame, tiled roof .. no other services ... just a couple of sockets & lights. So will be running as advised 2C SWA cable out to the building ... If I fed this via 30mA RCD protection form the house .. (either existing CU or a new feed to a new small RCD CU off the 100A switch fuse) ... then am I Ok to export the earth to the garage ? The RCD does not really have any bearing on the risk in this case - since under fault conditions it will not open the earth connection. The concern with PME is that in the event of a fault such as a disconnected PEN conductor (i.e. combined earth and neutral) provided by your supplier, your earthed metalwork could rise in voltage. This in itself is accceptable if you can maintain an equipotential bonded zone such that you can't expose yourself to a dangerous potential differences between the elevated earth and some external earth reference. If your outbuilding allows easy access to an independent earth reference, then you either have to include that in your equipotential bonding (back to separate protective conductor or large SWA again), or switch to TT for the outbuilding. The other consideration is the one Andy mentioned about use of class 1 appliances outside. With a garage there is always the danger that someone will plug in such a device - say a vacuum cleaner to take out to a car etc. So no matter how carefully you have preserved the equipotential zone in the garage, you can't stop someone exporting the earth to somewhere outside that zone via an appliance. Under fault conditions the SWA cable is RCD protected .. not just outbuilding wiring. I could then just use a small CU in the garage with no local RCD. You lose the discrimination in the garage (which may or may not be an issue), but more to the point you don't add much protection to the submain since it will have adequate earth fault protection by virtue of its PME head end. Although I can happily install a local earth rod & cable at outbuilding ... I have a roll of 16mm2 earth cable spare. I have put what I think are the 2 options on this sketch http://tinyurl.com/59pw8h ... is either wrong or either preferred ? First one has the problem described wrt to the exported earth and maintaining equipotential zones. The second would be my preferred of the two... (if you want to get posh, you could skip the RCD in the garage CU and use two RCBOs instead). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#16
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
John Rumm wrote:
[Big snip - all agreed] The other consideration is the one Andy mentioned about use of class 1 appliances outside. With a garage there is always the danger that someone will plug in such a device - say a vacuum cleaner [...] Don't think I've ever seen a Class 1 vacuum cleaner. Most portable appliances you'd want to use outside are Class 2 in fact, so this consideration is perhaps a bit theoretical. Nevertheless it is a consideration. First one has the problem described wrt to the exported earth and maintaining equipotential zones. Which may or may not be significant, depending on circumstances. The bare concrete floor though inclines me to prefer the second (TT) option. There's also the disadvantage that an RCD trip in the garage means a walk back to the house to reset it. The second would be my preferred of the two... Yes _BUT_ as drawn it's not acceptable with the house on a temporary TT supply. An earth fault on the submain cable is unprotected (Zs much to high to blow the 32 A fuse) and if it occurred all the earthing would sit up at 230 V waiting to bite you. There needs to be a temporary RCD at the house end (ideally a 100 mA delayed action one). -- Andy |
#17
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
John Rumm wrote:
How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? That's what I meant really - where the waterproof gland is an all plastic one, something like http://www.lapplimited.com/14/en/bra...opR/index.html. And I'd still put some heatshrink over the cable to dress the end where the armour has been cut off flush with the sheath (this is inside the CU, of course). A brass SWA gland wouldn't be acceptable since it's quite easy to pull the PVC sleeve down and make contact with the metal body which is connected to the armour. -- Andy |
#18
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Andy Wade wrote:
John Rumm wrote: [Big snip - all agreed] The other consideration is the one Andy mentioned about use of class 1 appliances outside. With a garage there is always the danger that someone will plug in such a device - say a vacuum cleaner [...] Don't think I've ever seen a Class 1 vacuum cleaner. Most portable appliances you'd want to use outside are Class 2 in fact, so this consideration is perhaps a bit theoretical. Nevertheless it is a consideration. Was about to say "I have", but that was a Hoover Senior about 20 years ago... and it was not exactly new then! ;-) First one has the problem described wrt to the exported earth and maintaining equipotential zones. Which may or may not be significant, depending on circumstances. The bare concrete floor though inclines me to prefer the second (TT) option. There's also the disadvantage that an RCD trip in the garage means a walk back to the house to reset it. Yes good point. I used to have an outbuilding supply like that (well I suppose I have again now - having fixed it once at the old house, I get to do it all over at the new one) and it was a PITA if you did get a trip. The second would be my preferred of the two... Yes _BUT_ as drawn it's not acceptable with the house on a temporary TT supply. An earth fault on the submain cable is unprotected (Zs much to high to blow the 32 A fuse) and if it occurred all the earthing would sit up at 230 V waiting to bite you. There needs to be a temporary RCD at the house end (ideally a 100 mA delayed action one). Yes well spotted - I was forgetting we were describing the future supply rather than the current situation. (I would still go TT on the outbuilding, and if need be run from a non time delayed RCD at the head end and just accept the lack of discrimination while the supply is still "temporary". Assuming the switch at the head end is in a normal DIN enclosure then swapping the switch for a RCD would probably be simplest) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#19
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Andy Wade wrote:
John Rumm wrote: How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? That's what I meant really - where the waterproof gland is an all plastic one, something like http://www.lapplimited.com/14/en/bra...opR/index.html. And I'd still put some heatshrink over the cable to dress the end where the armour has been cut off flush with the sheath (this is inside the CU, of course). Those are cheap enough at TLC IIRC... A brass SWA gland wouldn't be acceptable since it's quite easy to pull the PVC sleeve down and make contact with the metal body which is connected to the armour. You could substitute heatshrink for (or place under) the PVC boot - then it won't be sliding anywhere in a hurry! -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#20
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"John Rumm" wrote in message news:taWdnbH82MqiM5fVnZ2dnUVZ8vGdnZ2d@plusnet... Andy Wade wrote: John Rumm wrote: How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? That's what I meant really - where the waterproof gland is an all plastic one, something like http://www.lapplimited.com/14/en/bra...opR/index.html. And I'd still put some heatshrink over the cable to dress the end where the armour has been cut off flush with the sheath (this is inside the CU, of course). Those are cheap enough at TLC IIRC... A brass SWA gland wouldn't be acceptable since it's quite easy to pull the PVC sleeve down and make contact with the metal body which is connected to the armour. You could substitute heatshrink for (or place under) the PVC boot - then it won't be sliding anywhere in a hurry! Guys appreciate your help (and patience) ... let's see if I have understood. I earth the armour wires of cable at house end, and totally insulated armour wires at outbuilding (plastic gland) Install an earth rod and use that to supply earth to the out building. (making that a TT installation) I fit a 30mA RCD in outbuilding to protect all circuits there (or at least AC outlets) I then feed the cable at house end via a new sw fuse and 100mA RCD .. to provide fault current protection of the cable itself. or I could use an RCBO to combine fuse & RCD protection. http://tinyurl.com/5zd73z When Leccy board do finally change me to PME proper, I am assuming I can leave the install as is ? Just for a further option could I take the feed at house from a spare 30mA protected way in consumer unit .... and avoid need for the 100mA RCD. .... if this is OK (and can't see a reason why not) ... do I still need a separte RCD in outbuilding ? I can live without the discrimination. http://tinyurl.com/5kcsjc ... on the this option I have drawn a DP sw ... this is to give me a place to easily isolate the 'cable' and also easily terminate the armour wires, I would use the suggested option of.... http://tinyurl.com/57jmud In both cases am I right that I still need the RCD in the outbuilding to provide local protection to sockets ? I had some problem with eSnips .. so also uploaded a combined sketch ... http://tinyurl.com/6ovfum |
#21
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
On Apr 19, 9:16*pm, John Rumm wrote:
How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? Comment about using non swa glands with swa. - NICEIC fail such installations (then or later PIR) - BCO visual inspection check for non swa glands (perhaps new spies :-) Argument being swa bs type approval requires bs type approved glands for swa. For pme-to-tt swa perhaps consider swa glands into plastic box; type-approval of swa maintained, but house earth is not exported. Just a comment. |
#22
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
On 20 Apr, 16:37, wrote:
On Apr 19, 9:16*pm, John Rumm wrote: How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? Comment about using non swa glands with swa. - NICEIC fail such installations (then or later PIR) - BCO visual inspection check for non swa glands (perhaps new spies :-) Argument being swa bs type approval requires bs type approved glands for swa. For pme-to-tt swa perhaps consider swa glands into plastic box; type-approval of swa maintained, but house earth is not exported. Just a comment. Fair comment ... good to know I'll terminate using standard brass glands, in a plastic box in the outbuilding ... and insulate the gland, probably with industrial heatshrink over the normal plastic shround. |
#23
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Rick Hughes wrote:
Guys appreciate your help (and patience) ... let's see if I have understood. I earth the armour wires of cable at house end, and totally insulated armour wires at outbuilding (plastic gland) yup Install an earth rod and use that to supply earth to the out building. (making that a TT installation) yup I fit a 30mA RCD in outbuilding to protect all circuits there (or at least AC outlets) You will need RCD protection for all circuits - including lights - since the earth fault loop impedance may be too high to open a MCB on an earth fault in the garage. You could do this with one 30mA one if the loss of lights on a trip is acceptable, else use individual RCBOs. I then feed the cable at house end via a new sw fuse and 100mA RCD .. to provide fault current protection of the cable itself. 100mA with time delay... like: http://www.tlc-direct.co.uk/Products/MK6980.html Otherwise you won't be able to predict which will trip in the event of a genuine fault. or I could use an RCBO to combine fuse & RCD protection. http://tinyurl.com/5zd73z Yup When Leccy board do finally change me to PME proper, I am assuming I can leave the install as is ? You can. You would just have more earth fault protection on the submain than would actually be required. Just for a further option could I take the feed at house from a spare 30mA protected way in consumer unit .... and avoid need for the 100mA RCD. ... if this is OK (and can't see a reason why not) ... do I still need a separte RCD in outbuilding ? You could do this, and you would not need the separate RCD in the outbuilding. However you get no discrimination again, and this time you have to walk back to the house to reset it. I can live without the discrimination. http://tinyurl.com/5kcsjc ... on the this option I have drawn a DP sw ... this is to give me a place to easily isolate the 'cable' and also easily terminate the armour wires, I would use the suggested option of.... http://tinyurl.com/57jmud In both cases am I right that I still need the RCD in the outbuilding to provide local protection to sockets ? Not if the submain has 30mA RCD protection at the head end. Its the cheapest but least elegant way of doing it really. I had some problem with eSnips .. so also uploaded a combined sketch ... http://tinyurl.com/6ovfum Top piccie is ok, bottom one does not need the RCD in the garage. (if you put it in, no harm would come, but you could find the RCD at either end could trip (or both) on a fault) -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#25
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
On 20 Apr, 21:27, John Rumm wrote:
wrote: On Apr 19, 9:16 pm, John Rumm wrote: How about a waterproof gland onto a plastic CU in the garage, that way there is no way to make touch contact with the PME earthed armour of the cable? Comment about using non swa glands with swa. - NICEIC fail such installations (then or later PIR) - BCO visual inspection check for non swa glands (perhaps new spies :-) Argument being swa bs type approval requires bs type approved glands for swa. To clarify, I was not suggesting use of a non SWA gland - but use of an exterior "3 part" one one even though it would not be required for its waterproof characteristics. (having said that many interior ones come with the PVC boot anyway). For pme-to-tt swa perhaps consider swa glands into plastic box; type-approval of swa maintained, but house earth is not exported. However this does seem to be a case of being between a rock and a hard place... the brass gland will make the PME earth accessible in the outbuilding (albeit will very limited contact opportunity since I doubt many people spend much time fondling their glands in the garage). Is there a SWA type approval? -- Cheers, John. /================================================== ===============\ | * * * * *Internode Ltd - *http://www.internode.co.uk* * * * * *| |-----------------------------------------------------------------| | * * * *John Rumm - john(at)internode(dot)co(dot)uk * * * * * * *| \================================================= ================/ I haven't fondled my glands in the garage for a long time :-0 Thnaks for the help ... at least I can run the cable in now and close the trench. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
|
#27
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
On Apr 20, 10:43 pm, (Andrew Gabriel)
wrote: In article , writes: Argument being swa bs type approval requires bs type approved glands for swa. That's most likely to ensure a good connection to the armour, which is specifically not wanted in this case. Indeed - and agreed, however it is one nit-picked area. 1. swa armour cut outside enclosure, heatshrink armour, stuffing gland over bedding Favoured to stop PME earth appearing inside same enclosure as TT. arguments against... a) swa bedding not intended to be exposed outside enclosure (not sheath) b) swa bedding not intended to be clamped by stuffing gland (not sheath) c) swa must be terminated by swa gland at entry to enclosure citing a) b) d) use of non-swa gland exposes bedding to cut armour on cable movement/vibration Specific example of d) was 3-core 4mm - bedding is p*ss thin against cut armour. 2. swa armour cut inside enclosure, stuffing gland over sheath, heatshrink armour arguments against... a-d) deviations no longer apply, unfortunately PME earth now inside same enclosure as TT (same as proper swa gland) 3. swa into swa-gland on plastic box (PME termination box) with swa bedding routing on through box via male/bush into TT install box. arguments against... a-d) deviations no longer apply, PME & TT earths separated by enclosure. Unfortunately your swa-gland has a brass body at PME potential separated by the plastic gland shroud. Fine, until the event of host PME losing its neutral, whereupon that brass body becomes 240V. Hence the desire for plastic gland. Just a comment re some nit-pickers go ape seeing anything but swa- gland on swa. Aside, if TT end remotely wet use plastic rotary 1P/3P+N IP65 isolator (DIN cpd enclosure is high IP-rated until you open the door to isolate something or reset a CPD). Easily padlocked off if fixed rotary tools anywhere, kids about, sawing your sister in half gets messy. |
#28
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
|
#29
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
On Apr 22, 12:40 am, Andy Wade wrote:
wrote: 1. swa armour cut outside enclosure, heatshrink armour, stuffing gland over bedding FAOD I wasn't for a moment suggesting that. Of course, I used "1." to show how they suggested "2." & then "3.". 2. swa armour cut inside enclosure, stuffing gland over sheath, heatshrink armour That is what I was suggesting, and can't really see any problem with. Neither can I and it is common in industry. unfortunately PME earth now inside same enclosure as TT (same as proper swa gland) So what? Which regulation(s) in BS 7671 does that violate? None, I could not find anything either. That inspector insisted on swa gland for swa into plastic box. Other contractors insisted "rectifying" to swa gland into plastic box. The belief being that the plastic enclosure "stops PME contact". They did not consider the "shroud does not require tool for removal". 3. swa into swa-gland on plastic box (PME termination box) with swa bedding routing on through box via male/bush into TT install box. [...] Unfortunately your swa-gland has a brass body at PME potential separated by the plastic gland shroud. Fine, until the event of host PME losing its neutral, whereupon that brass body becomes 240V. Agreed: unsatisfactory, since the shroud can be removed without the use of a tool; also the creepage & clearance distance where the shroud abuts the box is inadequate. Exactly. Shroud removal exposes PME earth to anyone in the TT install. I suspect miss-application of 511-01-01 re intended purpose. Yes the intended purpose of an swa gland IS to terminate swa. However a more important need is preventing PME sitting on the outside of your enclosure in a TT install, which necessitates a plastic gland. Hence the desire for plastic gland. Just a comment re some nit-pickers go ape seeing anything but swa- gland on swa. I don't doubt that, but they must be able to justify their decisions by reference to BS 7671. What does the NICEIC technical manual have to say on the subject? Unknown, it would be interesting to find out. My suspicion is that they would say the plastic gland ("2.") complies. I hope they would also state that "3." fails for the reason given. A case of using a plastic gland, but if challenged cite the shroud. |
#30
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
wrote in message ... On Apr 22, 12:40 am, Andy Wade wrote: wrote: 1. swa armour cut outside enclosure, heatshrink armour, stuffing gland over bedding FAOD I wasn't for a moment suggesting that. Of course, I used "1." to show how they suggested "2." & then "3.". 2. swa armour cut inside enclosure, stuffing gland over sheath, heatshrink armour That is what I was suggesting, and can't really see any problem with. Neither can I and it is common in industry. unfortunately PME earth now inside same enclosure as TT (same as proper swa gland) So what? Which regulation(s) in BS 7671 does that violate? None, I could not find anything either. That inspector insisted on swa gland for swa into plastic box. Other contractors insisted "rectifying" to swa gland into plastic box. The belief being that the plastic enclosure "stops PME contact". They did not consider the "shroud does not require tool for removal". Just put the whole thing in a bigger box and screw the lid down.. then it needs a tool. ;-| |
#31
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
wrote in message ... I'm not really sure where this leaves me ...It seems I can't use a plastic gland as it will not meet BCO requirements .. if I use a brass gland it is potentially dangerous unless the connection is modified. a) Terminate using a brass gland .. and if I then heat shrink a full industrial sleeve over gland - is that 'acceptable' (better than push fit pvc sleeve) - and accept armour wires are within enclosure - but not terminated b)Terminate using brass gland .. but making connection on top bedding not the wires - is that 'acceptable' - seems poor practice. b) Terminate with a plastic Gland Or perhaps a solution is terminate fully as normal but within a separate plastic box (that needs tools to open) and then take only L&N into the CU. Presumably this meets BCO requirements and is also safe ? |
#32
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Terminate as A.Wade suggests with a plastic gland (listed as "2." in
my comment). In the future if anyone says you should use a "proper SWA gland in plastic box" point out to them that doing so would leave a "non-tool removable shroud as the only separator between a TT install & PME brass gland underneath". Stick that on a bit of paper in the box - just something to know if someone demands an SWA gland :-) No chance of it, but at least you are prepared to send them away to actually think rather than kneejerk. Some installation comments... Leave a "repair loop" in your swa - that way you can redo terminations or gland without having to replace a cable Cable should be at a depth appropriate for ground usage - ploughed field 1.5m or more, typical domestic 0.45m Cable should be laid in a suitably prepared trench - trench free from large stones, cable laid on a bed of riverwashed sand - 150mm of riverwashed sand above, then yellow cable marking tape, then backfill Cable route should be documented somewhere Watch cutting bedding around insulation, 4mm 3-core is often very thin above the cores - easy to nick the insulation which will fail a visual inspection if not an insulation resistance test also - it is for this reason that repair loops are a very good idea Nuffin to it, its the digging that will hurt the following morning. |
#33
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
Rick Hughes wrote:
Or perhaps a solution is terminate fully as normal but within a separate plastic box (that needs tools to open) and then take only L&N into the CU. Presumably this meets BCO requirements and is also safe ? Note that "BCO requirements" will vary with the BCO. So you may as well do it according to BS7671 and worry about what any BCO might say later (and if they want to argue, ask for supporting paragraphs from 7671). -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#34
Posted to uk.d-i-y
|
|||
|
|||
Electrical Installation Q
"John Rumm" wrote in message news:hvidnbOA7JgpPZLVnZ2dneKdnZydnZ2d@plusnet... Note that "BCO requirements" will vary with the BCO. So you may as well do it according to BS7671 and worry about what any BCO might say later (and if they want to argue, ask for supporting paragraphs from 7671). -- Cheers, John. which is what ? .... terminate is plastic gland or metal ? .... not being facetious, just want to get it right. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Electrical installation questions | UK diy | |||
Electrical installation tubes | Home Repair | |||
Electrical installation in a cloakroom | UK diy | |||
New Electrical installation help | UK diy | |||
Improving an old electrical installation | UK diy |