  #1   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as

http://aycu27.webshots.com/image/387...2625313_rs.jpg

work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.

Thanks for your speedy replies
  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Markt" wrote in message
...
Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as

http://aycu27.webshots.com/image/387...2625313_rs.jpg

work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.

Thanks for your speedy replies


More info. What DHW needs: showers, baths, etc? Heating? Other constraints?
You intent to build your own heat bank?

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default Heat bank & use of dual HW cylinders

OK - this is an idea - not based on practical experience.

Paralleling both cylinders sounds like a lot of extra pipework

What about putting the cylinders in series as far as the boiler goes?

So boiler hot feed enters near the top of the first cylinder, exits
from the normal boiler return point of the first cylinder, then feeds
into the entry point near the top of the second cylinder and finally
returns to the boiler from the lower exit point from the second
cylinder.

Hot water PHE is hooked to the first cylinder, and central heating
circuit(s) to the second cylinder. That may reduce hot water depletion
by space heating.

It might also be possible to configure valves so that an extra return
pipe from the first cylinder goes back directly to the boiler - for
summer use, when switched to "hw only".

Stats would be required on each cylinder, either able to call for heat
in winter, and reconfigurable for summer so that only the 1st is
active.

Is the above scheme workable?

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


wrote in message
...
OK - this is an idea - not based on practical experience.

Paralleling both cylinders sounds like a lot of extra pipework

What about putting the cylinders in series as far as the boiler goes?

So boiler hot feed enters near the top of the first cylinder, exits
from the normal boiler return point of the first cylinder, then feeds
into the entry point near the top of the second cylinder and finally
returns to the boiler from the lower exit point from the second
cylinder.

Hot water PHE is hooked to the first cylinder, and central heating
circuit(s) to the second cylinder. That may reduce hot water depletion
by space heating.

It might also be possible to configure valves so that an extra return
pipe from the first cylinder goes back directly to the boiler - for
summer use, when switched to "hw only".

Stats would be required on each cylinder, either able to call for heat
in winter, and reconfigurable for summer so that only the 1st is
active.

Is the above scheme workable?


Yep.

Points:

May as well keep them separate, one doing DHW, one CH (a CH buffer), with
DHW priority.
Hot water depletion by space heating can be prevented by a CH pump
interlock - DHW priority. That is the CH does not extract heat from the
cylinder while DHW is called and cylinder is below temperature. There again
the rads are in themselves a thermal store and the heat in them can be
usefully used to provide DHW. A good sized direct boiler will recover the
cylinder quickly. The great thing about using a heat bank/thermal store is
that a directly coupled boiler can be any size and will not cycle, with full
flow through the heat exchanger at all times.

  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message

...

Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers, baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.

Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.

Thanks all for the help


  #6   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Markt" wrote in message
...
On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message

...

Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.

Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?

The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the cylinder
and will take all its output. The F&E tank will only heat the cyoidner in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW priority
is ramping the DHW temp to maximum temperaure for a quick cylidner re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.

So, a:

- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)

Over to you....

  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Markt" wrote in message
...
On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message

...

Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.

Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?

The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the cylinder
and will take all its output. The F&E tank will only heat the cyoidner in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW priority
is ramping the DHW temp to maximum temperaure for a quick cylidner re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.

So, a:

- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- DHW blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)
- a blending valve (on the cylinder side of the boiler plate heat exchanger
to ensure only full temp water enters the cylinder).


Over to you....

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

On 15 Apr, 13:27, "Doctor Drivel" wrote:
"Markt" wrote in message

...



On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message


...


Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.


Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?

The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the cylinder
and will take all its output. The F&E tank will only heat the cyoidner in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW priority
is ramping the DHW temp to maximum temperaure for a quick cylidner re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.

So, a:

- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)

Over to you....


Hi boiler is existing (Vokera Mynute 28SE which is 28kW) Y connected
sealed primary. I'm not sure I follow your thinking on using a direct
cylinder with a PHE to isolate the boiler, why do this rather than
just use an indirect cylinder?

I started looking at two tanks as most web sites say I need 200 to
250L tank size for the size of house (its been extended). Which I
cannot fit into the existing space (which has a tank that is around
160L and seems to work fine - but we don't use the bath very often).
Do you think I could get away with a single indirect tank of 160L
with a fast coil and always have the boiler heat available?
  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Markt" wrote in message
...
On 15 Apr, 13:27, "Doctor Drivel" wrote:
"Markt" wrote in message

...



On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message


...


Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part
of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.


Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?

The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I
would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the
cylinder
and will take all its output. The F&E tank will only heat the cyoidner
in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW
priority
is ramping the DHW temp to maximum temperaure for a quick cylidner
re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.

So, a:

- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)

Over to you....


Hi boiler is existing (Vokera Mynute 28SE
which is 28kW) Y connected sealed primary.
I'm not sure I follow your thinking on using
a direct cylinder with a PHE to isolate the
boiler, why do this rather than
just use an indirect cylinder?


An indirect cylinder would need a fast recovery coil to take all the boilers
output. 28kW is a whack and few coils will take all that. These are not
cheap. Then you would use two. Double expense. Using a plate heat exchanger,
which is far more efficient than a coil, and will take all the boilers
output, means you can combine the heat output of the boiler and the
cylinder, which means you only need one direct cylinder of 150 litres. It
is cheaper and far more efficient and you will never run out of hot water as
when the cylinder is depleted you run off the boilers output - like a combi.

Do you think I could get away
with a single indirect tank of 160L
with a fast coil and always have
the boiler heat available?


Do you intend to keep the existing cylinder? In a hard water area if it is
oldish, it is best to get rid. If OK, you will get away with it using a
plate heat X that puts the boilers heat right at the top of the cylinder
where it is needed.

It will not be any more expensive having a direct cylinder, plate heat X and
pump, than a fast recovery coil cylinder.

I would have a 3-way "diverter" valve, the boiler set to maximum for fast
re-heat and a pipe stat, wired though the room stat circuit, on the CH flow
pipe to set the rads temperature. So when DHW full temp and when CH onto the
pipe stat. This boiler is not a condesning boiler and must be run at 80C
anyhow.

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

On Apr 15, 6:25 pm, "Doctor Drivel" wrote:
"Markt" wrote in message

...

On 15 Apr, 13:27, "Doctor Drivel" wrote:
"Markt" wrote in message


....


On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message


...


Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part
of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.


Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?


The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I
would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the
cylinder
and will take all its output. The F&E tank will only heat the cyoidner
in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW
priority
is ramping the DHW temp to maximum temperaure for a quick cylidner
re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.


So, a:


- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)


Over to you....


Hi boiler is existing (Vokera Mynute 28SE
which is 28kW) Y connected sealed primary.
I'm not sure I follow your thinking on using
a direct cylinder with a PHE to isolate the
boiler, why do this rather than
just use an indirect cylinder?


An indirect cylinder would need a fast recovery coil to take all the boilers
output. 28kW is a whack and few coils will take all that. These are not
cheap. Then you would use two. Double expense. Using a plate heat exchanger,
which is far more efficient than a coil, and will take all the boilers
output, means you can combine the heat output of the boiler and the
cylinder, which means you only need one direct cylinder of 150 litres. It
is cheaper and far more efficient and you will never run out of hot water as
when the cylinder is depleted you run off the boilers output - like a combi.

Do you think I could get away
with a single indirect tank of 160L
with a fast coil and always have
the boiler heat available?


Do you intend to keep the existing cylinder? In a hard water area if it is
oldish, it is best to get rid. If OK, you will get away with it using a
plate heat X that puts the boilers heat right at the top of the cylinder
where it is needed.

It will not be any more expensive having a direct cylinder, plate heat X and
pump, than a fast recovery coil cylinder.

I would have a 3-way "diverter" valve, the boiler set to maximum for fast
re-heat and a pipe stat, wired though the room stat circuit, on the CH flow
pipe to set the rads temperature. So when DHW full temp and when CH onto the
pipe stat. This boiler is not a condesning boiler and must be run at 80C
anyhow.


Hi Thanks for your help, I have drawn it up to help me understand.
Please could you let me know of any errors

http://image69.webshots.com/469/7/5/...4wqsWIa_fs.jpg

I'm taking advantage of the topology of the house which has a large sw
facing roof allowing the solar panels and cylinders to sit at
different ascending heights as illustrated in the diagram.

One cause for concern is the max temp that the solar panels might
achieve, (say if the system is unused for a few days in the summer)
could you suggest how to protect from this.

Markt

PS Screwfix have a 140L indirect cylinder which is a 20 minute re-heat
for £180 does this change the economics of using the PHE+Pump on a
direct cylinder?



  #11   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

On Apr 17, 5:18 pm, Markt wrote:
On Apr 15, 6:25 pm, "Doctor Drivel" wrote:



"Markt" wrote in message


...


On 15 Apr, 13:27, "Doctor Drivel" wrote:
"Markt" wrote in message


....


On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message


...


Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part
of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.


Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?


The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I
would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the
cylinder
and will take all its output. The F&E tank will only heat the cyoidner
in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW
priority
is ramping the DHW temp to maximum temperaure for a quick cylidner
re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.


So, a:


- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)


Over to you....


Hi boiler is existing (Vokera Mynute 28SE
which is 28kW) Y connected sealed primary.
I'm not sure I follow your thinking on using
a direct cylinder with a PHE to isolate the
boiler, why do this rather than
just use an indirect cylinder?


An indirect cylinder would need a fast recovery coil to take all the boilers
output. 28kW is a whack and few coils will take all that. These are not
cheap. Then you would use two. Double expense. Using a plate heat exchanger,
which is far more efficient than a coil, and will take all the boilers
output, means you can combine the heat output of the boiler and the
cylinder, which means you only need one direct cylinder of 150 litres. It
is cheaper and far more efficient and you will never run out of hot water as
when the cylinder is depleted you run off the boilers output - like a combi.


Do you think I could get away
with a single indirect tank of 160L
with a fast coil and always have
the boiler heat available?


Do you intend to keep the existing cylinder? In a hard water area if it is
oldish, it is best to get rid. If OK, you will get away with it using a
plate heat X that puts the boilers heat right at the top of the cylinder
where it is needed.


It will not be any more expensive having a direct cylinder, plate heat X and
pump, than a fast recovery coil cylinder.


I would have a 3-way "diverter" valve, the boiler set to maximum for fast
re-heat and a pipe stat, wired though the room stat circuit, on the CH flow
pipe to set the rads temperature. So when DHW full temp and when CH onto the
pipe stat. This boiler is not a condesning boiler and must be run at 80C
anyhow.


Hi Thanks for your help, I have drawn it up to help me understand.
Please could you let me know of any errors

http://image69.webshots.com/469/7/5/...4wqsWIa_fs.jpg

I'm taking advantage of the topology of the house which has a large sw
facing roof allowing the solar panels and cylinders to sit at
different ascending heights as illustrated in the diagram.

One cause for concern is the max temp that the solar panels might
achieve, (say if the system is unused for a few days in the summer)
could you suggest how to protect from this.

Markt

PS Screwfix have a 140L indirect cylinder which is a 20 minute re-heat
for £180 does this change the economics of using the PHE+Pump on a
direct cylinder?


Sorry link did not work, try this one

http://inlinethumb44.webshots.com/41...600x600Q85.jpg
  #12   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 8
Default Heat bank & use of dual HW cylinders

On 17 Apr, 17:24, Markt wrote:
On Apr 17, 5:18 pm, Markt wrote:



On Apr 15, 6:25 pm, "Doctor Drivel" wrote:


"Markt" wrote in message


....


On 15 Apr, 13:27, "Doctor Drivel" wrote:
"Markt" wrote in message


...


On 14 Apr, 19:59, "Doctor Drivel" wrote:
"Markt" wrote in message


...


Hi
I have been reading the excellent threads concerning heat banks on
here. I would like to move my HW tank into the roof space as part
of
the upgrade to a heat bank. However space is somewhat limited. Would
configurations such as


http://aycu27.webshots.com/image/387...2625313_rs.jpg


work with two separate HW tanks connected in parallel ? Thinking of
using 2x 130L cylinders, with the tallest aspect possible.


Thanks for your speedy replies


More info. What DHW needs: showers,
baths, etc? Heating? Other constraints?
You intent to build your own heat bank?


DHW needs are 1 bath + 2 showers, CH is for 4 bed house. I was
thinking about leaving the CH directly fed from the boiler, as it will
be difficult to retrofit the CH to run from the heat bank. Also want
to enable a solar option in the future as have a sw facing roof.


Yes looking to make my own heat bank with the external heat exchanger
as I'm worried about the all in one commercial solutions furring up in
our hard water area.


What sort of boiler? New boiler? Existing boiler?


The diagram is for the CH off the heat bank. The left hand side of the
cylinder is what you need. As you are doing a DHW only heat bank, I
would
have a one 140/150 litre "direct" cylinder heated via 100kW plate heat
exchanger. This isolates the boiler (which can be sealed) from the
cylinder
and will take all its output. The F&E tank will only heat the cyoidner
in
which its water always stays only in the cylinder - no sludge can
accumulate. Using a Keston Qudos boiler CH is modulating and DHW
priority
is ramping the DHW temp to maximum temperaure for a quick cylidner
re-heat.
This means, that when the cylinders heat partially depletes and the stats
switch in the boiler, the boiler and cylinder combine to give DHW, thus
extending the cylinders size.


So, a:


- Qudos boiler,
- 150 litre cylinder
- two 100kW plate heat exchangers
- two pumps
- cylinder stat (the Quodos stat/sensor)
- blending valve
- flow switch
- Surrey flange (if a shower connection on cylinder not needed)
- Magnaclean filter for CH return.
- two check valves
- enough full bore isolating valves
- a 3-way "diverting" valve for the boiler (DHW or CH)


Over to you....


Hi boiler is existing (Vokera Mynute 28SE
which is 28kW) Y connected sealed primary.
I'm not sure I follow your thinking on using
a direct cylinder with a PHE to isolate the
boiler, why do this rather than
just use an indirect cylinder?


An indirect cylinder would need a fast recovery coil to take all the boilers
output. 28kW is a whack and few coils will take all that. These are not
cheap. Then you would use two. Double expense. Using a plate heat exchanger,
which is far more efficient than a coil, and will take all the boilers
output, means you can combine the heat output of the boiler and the
cylinder, which means you only need one direct cylinder of 150 litres. It
is cheaper and far more efficient and you will never run out of hot water as
when the cylinder is depleted you run off the boilers output - like a combi.


Do you think I could get away
with a single indirect tank of 160L
with a fast coil and always have
the boiler heat available?


Do you intend to keep the existing cylinder? In a hard water area if it is
oldish, it is best to get rid. If OK, you will get away with it using a
plate heat X that puts the boilers heat right at the top of the cylinder
where it is needed.


It will not be any more expensive having a direct cylinder, plate heat X and
pump, than a fast recovery coil cylinder.


I would have a 3-way "diverter" valve, the boiler set to maximum for fast
re-heat and a pipe stat, wired though the room stat circuit, on the CH flow
pipe to set the rads temperature. So when DHW full temp and when CH onto the
pipe stat. This boiler is not a condesning boiler and must be run at 80C
anyhow.


Hi Thanks for your help, I have drawn it up to help me understand.
Please could you let me know of any errors


http://image69.webshots.com/469/7/5/...4wqsWIa_fs.jpg


I'm taking advantage of the topology of the house which has a large sw
facing roof allowing the solar panels and cylinders to sit at
different ascending heights as illustrated in the diagram.


One cause for concern is the max temp that the solar panels might
achieve, (say if the system is unused for a few days in the summer)
could you suggest how to protect from this.


Markt


PS Screwfix have a 140L indirect cylinder which is a 20 minute re-heat
for £180 does this change the economics of using the PHE+Pump on a
direct cylinder?


Sorry link did not work, try this one

http://inlinethumb44.webshots.com/41...8484S600x600Q8...


Had an idea regards the need for a solar heat dump. Could the PHE that
buffers heat from the boiler be reversed. Thinking was to change the 3
port Y valve to something more complex (two single valves, with a
complex control circuit) to allow heat from the thermal store through
the HPE and into the CH. Boiler pump and PHE pump both turned on.
Triggered by an Over temp stat on the heatbank. Its not failsafe -
would this matter?

Markt
  #13   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Markt" wrote in message
...

http://inlinethumb44.webshots.com/41...600x600Q85.jpg

Note on drawing: Have the flow from boiler (via plate) into the top of the
cylinder. This can be done via the shower port of the side (if one supplied)
by drilling out the pipe stop on a compression filling and feeding in a bent
piece of copper pipe that terminate just below the top the cylinder. Have
the cylinder stat one third up the cylinder. Have a thermostat probe in the
cylinder if possible.

I'm taking advantage of the topology of the house which has a large sw
facing roof allowing the solar panels and cylinders to sit at
different ascending heights as illustrated in the diagram.

One cause for concern is the max temp that the solar panels might
achieve, (say if the system is unused for a few days in the summer)
could you suggest how to protect from this.


Have high limit temperature stats on the solar cylinder "and" DHW heat
bank - I assume they are fitted as per drawing - set to 95C. When above 95C
the DHW pump runs to act as a shunt pump mixing the water in the two
cylinders. The DHW heating from the boiler is switched out when the shunt
pump runs - over 95C in any of the cylinders.

The heat from the solar cylinder will naturally rise into the heat bank,
although slowly as most heat will be rising via one pipe. Having water at
96C in the heat bank will do no harm as DHW is blended down.

Using the heat bank as a heat dump for the solar cylinder should be fine in
a UK climate. If both cylinders do get over 100C water will expand into the
F&E tank. If this does occur (climate change) the fit a radiator (bathroom)
off the heat bank and pump that to dissipate heat.

PS Screwfix have a 140L indirect cylinder
which is a 20 minute re-heat for £180 does
this change the economics of using the
PHE+Pump on a direct cylinder?


Is is only Part L. It will do 20 mins if 80C water is run through and at the
correct flow through the coil. It is not quick recovery and will not take
28kW. Fine for a solar cylinder. The plate will ensure the full output of
the boiler will go to the heat bank and the outputs of the heat bank and
boiler will combine to give a larger DHW output and make the boiler cast as
a combi (never run out of DHW) when the heat bank is depleted of heat.

Have a zone valve on the return to the solar panel, as in winter heat from
the solar cylinder will drop to the panel and you will be heating the sky.

  #14   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Doctor Drivel" wrote in message
...

"Markt" wrote in message
...

http://inlinethumb44.webshots.com/41...600x600Q85.jpg


Have a Reliance blending valve on the boiler set to 57C. This ensure there
will be no condensing in the boiler and only hot, not warm, water enters the
heat bank. This makes fast recovery and ensure the boiler and heat bank
combines outputs.

  #15   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Heat bank & use of dual HW cylinders


"Doctor Drivel" wrote in message
...

"Doctor Drivel" wrote in message
...

"Markt" wrote in message
...

http://inlinethumb44.webshots.com/41...600x600Q85.jpg


Have a Reliance blending valve on the boiler set to 57C. This ensure there
will be no condensing in the boiler and only hot, not warm, water enters
the heat bank. This makes fast recovery and ensure the boiler and heat
bank combines outputs.


Have a larger expansion vessel on the solar side. 16 litres, may be cheaper
to have two 8 litres.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
DIY Heat Bank: PHE specifications Mike Holmes UK diy 13 August 4th 07 10:34 PM
Home made Heat Bank robgraham UK diy 42 May 27th 07 04:06 PM
Heat bank and UFH Jeff Mowatt UK diy 33 February 19th 06 12:36 AM
Gravity circulation on a heat bank Davide UK diy 3 September 26th 05 12:09 AM
DPS Pandora heat bank Christian McArdle UK diy 12 November 2nd 03 12:10 AM


All times are GMT +1. The time now is 11:28 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"