#1
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
I want to add a spur from a socket, but it already has a spur connected. So can I instead run 2 cables to the new 'spur', and connect one side of the ring with 30A connector block behind the original socket to one cable and the other to the original socket. Thus the new socket will be in the ring, and not a spur after all. The topology of this sounds fine to me, it's just the use of connector block behind the socket to extend one of the cables that i'm not sure about. cheers, rob. |
#2
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
cantalou wrote:
So can I instead run 2 cables to the new 'spur', and connect one side of the ring with 30A connector block behind the original socket to one cable and the other to the original socket. As long as it is electrically sound, and the connector block is in an accessible accessory box (ie, not wrapped in PVC tape and hidden under the floor). You might be squeezing it with the connector block in the same accessory box as the socket outlet. -- JGH |
#3
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
|
#4
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
On Fri, 7 Dec 2007 16:32:11 UTC, Roger
wrote: The message from contains these words: cantalou wrote: So can I instead run 2 cables to the new 'spur', and connect one side of the ring with 30A connector block behind the original socket to one cable and the other to the original socket. As long as it is electrically sound, and the connector block is in an accessible accessory box (ie, not wrapped in PVC tape and hidden under the floor). You might be squeezing it with the connector block in the same accessory box as the socket outlet. I could be misremembering but didn't someone say recently that the rule isn't that you can't have more than one spur off a socket but that you can't have more sockets on spurs than there are on the ring. Not something I would want to attempt though. I have enough trouble getting the wires into their holes in the first place even without a spur. :-) But he isn't prposing to do that. He's proposing to split the ring and then insert some more cable and the new socket. Hence the joints. The op could try what I have done in the past when extending ring mains. Repace the double socket with two single sockets in close proximity and wire the extension between them. Don't get the boxes too close together or the second socket will be an interference fit on the side of the first. You can always use a surface box that has space for two separate single sockets. Quite useful if you want extra wiring (and a possible, though arguably not very good way of housing the choc block in this case, by using a blanking plate on one side). -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#5
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
The message
from "Bob Eager" contains these words: I could be misremembering but didn't someone say recently that the rule isn't that you can't have more than one spur off a socket but that you can't have more sockets on spurs than there are on the ring. Not something I would want to attempt though. I have enough trouble getting the wires into their holes in the first place even without a spur. :-) But he isn't prposing to do that. He's proposing to split the ring and then insert some more cable and the new socket. Hence the joints. But his post started off with: "I want to add a spur from a socket, but it already has a spur connected." I read that as the op accepting that more than one spur from the same socket is forbidden. How do you see it? -- Roger Chapman |
#6
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
On Fri, 7 Dec 2007 17:45:54 UTC, Roger
wrote: The message from "Bob Eager" contains these words: I could be misremembering but didn't someone say recently that the rule isn't that you can't have more than one spur off a socket but that you can't have more sockets on spurs than there are on the ring. Not something I would want to attempt though. I have enough trouble getting the wires into their holes in the first place even without a spur. :-) But he isn't prposing to do that. He's proposing to split the ring and then insert some more cable and the new socket. Hence the joints. But his post started off with: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. So can I instead run 2 cables to the new 'spur', and connect one side of the ring with 30A connector block behind the original socket to one cable and the other to the original socket. Thus linking it into the ring. Thus the new socket will be in the ring, and not a spur after all. -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#7
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
"Bob Eager" wrote in message ... On Fri, 7 Dec 2007 17:45:54 UTC, Roger wrote: The message from "Bob Eager" contains these words: I could be misremembering but didn't someone say recently that the rule isn't that you can't have more than one spur off a socket but that you can't have more sockets on spurs than there are on the ring. Not something I would want to attempt though. I have enough trouble getting the wires into their holes in the first place even without a spur. :-) But he isn't prposing to do that. He's proposing to split the ring and then insert some more cable and the new socket. Hence the joints. But his post started off with: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. Why not? Two spurs from one point on the ring is acceptable (expected loading/balancing of the ring and the number of spurs already taken off the ring may come into play). A spur off a spur is not acceptable. Adam |
#8
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
On Fri, 7 Dec 2007 18:47:38 UTC, "ARWadsworth"
wrote: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. Why not? Two spurs from one point on the ring is acceptable (expected loading/balancing of the ring and the number of spurs already taken off the ring may come into play). A spur off a spur is not acceptable. Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#9
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
The message
from "Bob Eager" contains these words: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. Why not? Two spurs from one point on the ring is acceptable (expected loading/balancing of the ring and the number of spurs already taken off the ring may come into play). A spur off a spur is not acceptable. Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! The wording seemed clear enough to me, as did the problem of inserting all the wires. -- Roger Chapman |
#10
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
On Fri, 7 Dec 2007 20:37:56 UTC, Roger
wrote: The message from "Bob Eager" contains these words: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. Why not? Two spurs from one point on the ring is acceptable (expected loading/balancing of the ring and the number of spurs already taken off the ring may come into play). A spur off a spur is not acceptable. Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! The wording seemed clear enough to me, as did the problem of inserting all the wires. Good for you. -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by http://www.diybanter.com |
#11
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
The message
from "Bob Eager" contains these words: The wording seemed clear enough to me, as did the problem of inserting all the wires. Good for you. But not for you. :-) -- Roger Chapman |
#12
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Bob Eager wrote:
On Fri, 7 Dec 2007 18:47:38 UTC, "ARWadsworth" wrote: "I want to add a spur from a socket, but it already has a spur connected." That's what he wanted to do. But he knew he couldn't. Why not? Two spurs from one point on the ring is acceptable (expected loading/balancing of the ring and the number of spurs already taken off the ring may come into play). A spur off a spur is not acceptable. Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! It bloody well is! I found such a wiring nightmare whilst dry lining a kitchen once. Several junction boxes & bits of cable later I got it sorted. -- Dave - The Medway Handyman www.medwayhandyman.co.uk 01634 717930 07850 597257 |
#13
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Your proposed solution may be incorrect.
Regs limit the number of connections in a socket to 3 o 2 connections for the ring legs o 1 connection for 1 socket spur off the ring You propose a choc-block to keep to 3 connection limit o The choc block would need to be 30/32A ---- two spurs to 2x 1G sockets can draw 2x 13A = 26A ---- two spurs to 2x 2G sockets can draw 4x 13A = 52A* ---- * obviously limited in the latter by 32A ring CPD o The cables feeding the choc block must be 30/32A ---- a spur to 2x 1G sockets is 26A or 1x FTE-2.5mm ---- a spur to 2x 2G sockets is 32A or 2x FTE-2.5mm ---- so link the choc-bloc by FTE-4mm or reroute legs o The choc block & cables take up a lot of space ---- I doubt it would fit even in a 47mm depth box There are some alternatives. 1. If you only require 13A in total from "two spurs". a) If your existing socket is 1G (1-gang)... o Fit a Twin-1G metal backbox in place of the 1G socket ---- it is a single metal box with twin-1G fittings ---- separated by a metal plate which you push out o Fit a 1G Socket in the one side ---- into which your 2 ring legs connect o Fit a 1G Fused Outlet (FCU) into other side ---- run 3rd FTE-2.5mm to the socket next to it ---- run as many spurs as you want off this (13A fuse) o Maintains 3-wires into socket & good workmanship b) If your existing socket is 2G (2-gang)... o Fit a 1G metal backbox next to the socket o Fit a 1G Fused Outlet (FCU) into it ---- run 3rd FTE-2.5mm to the socket next to it ---- run as many spurs as you want off this (13A fuse) o Maintains 3-wires into socket & good workmanship 2. If you require 13A from each spur, 26A total. o Fit a Twin 1G metal backbox in place of the 1G socket ---- it is a single metal box with twin-1G fittings ---- separated by a metal plate which you push out o Fit a 1G Socket in EACH side of the fitting o Ring leg #1 goes to LH socket, leg #2 to RH socket ---- this separates the original ring o Link the two sockets by FTE-2.5mm ---- this rejoins the ring o Spur #1 off LH socket, Spur #2 off RH socket o Maintains 3-wires into socket & good workmanship However you may not have sufficient ring leg length. It can be done similarly with surface mount boxes, but that may be problematic re ring cable length. You CAN use a 30A junction box under floorboards: o The EXISTING socket become a spur o Your junction box then runs the 2 new spurs as a RING o You would need to link these 2 new spurs as a RING The problem is accessibility: o Accessibility means an area never subject to furniture o Eg, a landing area, access via hole/floorboard I would fit a twin-1G box in place of a 1G/2G socket, fit FCU in one side & 1G skt in other. Then run as many spurs as you like off the FCU subject to 13A load limit. Alternatively extend the ring properly - as a ring. I think I read your question correctly. -- DB. |
#14
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
In article ,
"The Medway Handyman" writes: Bob Eager wrote: Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! It bloody well is! I found such a wiring nightmare whilst dry lining a kitchen once. Several junction boxes & bits of cable later I got it sorted. Some socket makes have larger cable capacities than others. Depth of back box makes a big difference too when you have lots of cables or particularly thick cables. -- Andrew Gabriel [email address is not usable -- followup in the newsgroup] |
#15
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Dorothy Bradbury wrote:
Your proposed solution may be incorrect. Regs limit the number of connections in a socket to 3 o 2 connections for the ring legs o 1 connection for 1 socket spur off the ring SNIP Interesting. Could you cite the number(s), please? (I can't find it in my old (red-cover) version and I'm too mean to buy a new one until a couple of years after the 17th ed. has been released.) |
#16
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Dorothy Bradbury wrote:
Your proposed solution may be incorrect. Regs limit the number of connections in a socket to 3 o 2 connections for the ring legs o 1 connection for 1 socket spur off the ring Could you cite the number(s), please? 1stly, Implied... OSG 16th, p153, Appx8. "A non-fused spur feeds only 1 single/twin/multiple outlet or 1 permanently connected equipment. Such a spur is connected to a circuit at the terminals of a socket outlet or junction box or at the origin of the circuit in the DB". No regulation is cited, which suggests Guidance. In order to meet the Guidance meens 3 connections. 2ndly, Physically... o Skt terminals physically limited to 3x 4mm CSA conductors o Socket terminals may physically accept 4x 2.5mm CSA conductors The OSG guidance can be read as merely existing to prevent a chain of spurs off 1 socket fed by FTE-2.5mm with 32A CPD. It comes down to interpretation - by an Inspector on the day :-) Frankly, telephone the tech support of the socket maker. If they say it can physically accept the number of wires then you are complying with their instructions of acceptable usage. They will probably advise a 32-35mm depth backbox though. So the implementation may require physical change anyway. -- DB. |
#17
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Andrew Gabriel wrote:
In article , "The Medway Handyman" writes: Bob Eager wrote: Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! It bloody well is! I found such a wiring nightmare whilst dry lining a kitchen once. Several junction boxes & bits of cable later I got it sorted. Some socket makes have larger cable capacities than others. Depth of back box makes a big difference too when you have lots of cables or particularly thick cables. The TLC Ultimate range sockets have plenty of terminal space for 4 wires... The other trick to get more backbox depth is to use a spacer: http://cpc.farnell.com/jsp/Electrica...sp?sku=PL08925 (order codes PL08924 and PL08925) These surface mount over the sunken backbox and give you an extra 10mm of depth to play with, without changing the appearance of the socket in the way a complete surface mounting pattress would - it still looks flush mounted. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#18
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
Dorothy Bradbury wrote:
Dorothy Bradbury wrote: Your proposed solution may be incorrect. Regs limit the number of connections in a socket to 3 o 2 connections for the ring legs o 1 connection for 1 socket spur off the ring Could you cite the number(s), please? I don't believe there is one. You can have two spurs from the same location if required (point load and balance issues aside) 1stly, Implied... OSG 16th, p153, Appx8. "A non-fused spur feeds only 1 single/twin/multiple outlet or 1 permanently connected equipment. Such a spur is connected to a circuit at the terminals of a socket outlet or junction box or at the origin of the circuit in the DB". This does not really have anything to do with the number of spurs at a single connection point, only that a unfused spur should only feed a single socket of flex connection unit etc. No regulation is cited, which suggests Guidance. In order to meet the Guidance meens 3 connections. 2ndly, Physically... o Skt terminals physically limited to 3x 4mm CSA conductors o Socket terminals may physically accept 4x 2.5mm CSA conductors Given 2.5mm^2 is the normal cable of choice, 4 wires ought to be doable on most sockets. Some are very much better designed for this than others. You will note that most junction boxes also have 4 cable entry holes. They will probably advise a 32-35mm depth backbox though. So the implementation may require physical change anyway. or a spacer under the socket. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#19
Posted to uk.d-i-y
|
|||
|
|||
OK to extend ring with chocolate in socket box?
"Andrew Gabriel" andrew@a17 wrote in message ... In article , "The Medway Handyman" writes: Bob Eager wrote: Good point. I was assuming he'd be adding a spur to a spur. However, getting four cables in there might be 'challenging'! It bloody well is! I found such a wiring nightmare whilst dry lining a kitchen once. Several junction boxes & bits of cable later I got it sorted. Some socket makes have larger cable capacities than others. So you have met my girlfriend. Depth of back box makes a big difference too when you have lots of cables or particularly thick cables. I cannot comment about the depth of the backbox. Adam PS Sorry |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Extend 13A socket from cooker control unit? | UK diy | |||
Shaving socket from lighting ring | UK diy | |||
socket from the ring main | UK diy | |||
Is my main socket ring too big? | UK diy | |||
Extending socket circuit to a ring? | UK diy |