On 16 Sep 2003 21:35:53 -0700,
(Charlie) wrote:

Hello,

I have a Honeywell wiring box into which all the components of my CH
system are wired. In the last couple of days the 2A fuse in this box
has blown (twice) and a 3A one also blew - obviously I have a problem.

The pilot light is still on. There are no signs of leaks. Presumably
it could be any of the components but presumably likely to be the pump
or the motorised value.


Depending on what the boiler is, it could be a fault there as well -
you don't say what the boiler is. Often the pilot light does not
depend on an electrical supply to the boiler working.


I have tightened all the wiring connections in case there was any
loose connections - there weren't.


Th other thing to look for is whether there are any places (and it
could be anywhere on the system) where the insulation on a wire might
have been nicked or possibly chafed by it going through a hole in
metal without a rubber or plastic grommet. Boilers can be
favourites for this if the installer was lazy.

My problem is how do I check these components if I have no power to
test them?


The problem as well is that these are intermittent.

Could I put a 3 pin plug on them and plug them into the mains?


You could for the pump, quite easily, and the motorised valve less
easily. These have up to five wires connecting to the motor and an
auxiliiary switch inside. You need to pick the motor wires. Either
you can take the cover off of the valve head and trace the colours to
the motor or look at the manufacturer's data sheet. One thing to
watch with this is that you will be feeding the item under test from a
different power source and this means that it is not isolated at the
same time as the rest of the system if you switch that off.

I don't think that you would be able to diagnose much more than the
pump and possibly the motorised valve this way. The boiler will
typically have multiple connections and you really need to know what
you are doing and have the manufacturer's service information .

One candidate for the fault you are describing is failed insulation
and shorted turns on the motor of the pump or the valve. This can
manifest itself as intermittent - I had a pump that failed that way
once. FOr any of these tests, don't use more than a 3A fuse.


What could I put temporarily and safely across the fuse holder to keep
the system running for a while while I test it.


NOTHING other than the correctlhy rated fuse. The 2A and 3A fuses
are there to protect the system and you. The 6 inch nail approach
can result in more damage or even a fire so don't be tempted.



Email replies to my address without the hotmail extension and
replacing the underscores with common email characters.

If I got a circuit tester what checks could I carry out with or
without the power on?


On an intermittent fault, I don't think that you will see all that
much.


I do recall a plumber coming to my last house, putting a circuit
tester across the pump terminals and instantly telling me I needed a
new pump. But he of course had power.


It could have been a failure that was an open circuit, a short circuit
or even an insulation breakdown to earth.



Finally what would I expect an CH electrical engineer to charge me to
do the relevent checks (North London)?


You might want to look back through recent posts and find Ed Sirett.
His email address is in his signature and is in North London.


All help gratefully received.

Charlie


..andy

To email, substitute .nospam with .gl
  #2   Report Post  
Alan James
 
Posts: n/a
Default Central Heating problem - 2A fuse blowing in honeywell wiring box


"Charlie" wrote in message
om...
Hello,

I have a Honeywell wiring box into which all the components of my CH
system are wired. In the last couple of days the 2A fuse in this box
has blown (twice) and a 3A one also blew - obviously I have a problem.

The pilot light is still on. There are no signs of leaks. Presumably
it could be any of the components but presumably likely to be the pump
or the motorised value.


I've had this twice and both times it was a failing synchron motor (not yet
failed) in the zone valve. Might be an idea to get a spare synchron motor
if you havn't got one. Were fairly cheap from BES, now you have to pay
postage.

I would first check if you have separate mains feeds to boiler and wiring
box. If separate I would not suspect boiler or pump initially. The
intermittency may just be due to the actual current being drawn. Don't
have the tables to hand but depending on the actual current the fuse may
take some time to blow. If you are confident (and competent) I would
suggest inserting a test meter on ac Amps in series with each load (zone
valve(s), pump, boiler etc). Obligatory health warning - switch-off while
connecting. What I might do in this situation is to fit a 13A plug (3A fuse)
to the feed and plug into a 30mA RCD. Healthy readings should be nowhere
near 3A. OK, won't work if it is genuinely an intermittent, but I would
suspect not.

Cost of Plumber? Sorry d-i-y here, you can buy a lot of pumps, zone valves,
test meters etc for the cost of a plumber.

Alan



  #3   Report Post  
PoP
 
Posts: n/a
Default Central Heating problem - 2A fuse blowing in honeywell wiring box

On Wed, 17 Sep 2003 22:00:23 +0100, "John Stumbles"
] wrote:

Anyone remember the old Hornby Dublo train set controller box which had some
special bulb in series with the transformer output, so that if you
overloaded or shorted it the bulb would light up but in normal operation the
bulb would quietly (or invisibly) pass current to the load?


You might need to post this in alt.geriatric.trainlovers

PoP

  #4   Report Post  
Charlie
 
Posts: n/a
Default Central Heating problem - 2A fuse blowing in honeywell wiring box

I would first check if you have separate mains feeds to boiler and wiring
box. If separate I would not suspect boiler or pump initially. The
intermittency may just be due to the actual current being drawn. Don't
have the tables to hand but depending on the actual current the fuse may
take some time to blow. If you are confident (and competent) I would
suggest inserting a test meter on ac Amps in series with each load (zone
valve(s), pump, boiler etc). Obligatory health warning - switch-off while
connecting. What I might do in this situation is to fit a 13A plug (3A fuse)
to the feed and plug into a 30mA RCD. Healthy readings should be nowhere
near 3A. OK, won't work if it is genuinely an intermittent, but I would
suspect not.


*********UPDATE*********

Had a bit of time today so this is what I did. Got a card of fuse wire
- cheaper than 50p a go fuses, even if a bit fiddly!! I turned off the
power and replaced the fuse.
I disconnected the red wire feed to the pump in the wiring box.
I set the programmer to off for both CH and HW and turned the power
back on. All ok so far.
I then switched the programmer to call for HW, still ok.
I then switched the programmer to also call for CH, still ok.

Eureka I'm thinking...it must be the pump - Grungfos 15-50. Based on a
previous post I tried to get hold of a replacement capacitor but no
luck. Decided I'll replace the pump, on the basis that even if it
isn't the pump this time at least I'll have a replacement next time.
I turned off the gate valves eitherside of the pump and tried to
remove the pump. Unfortunately I didn't have large enough spanners to
remove one side of the pump so reconnected to pipework again. What I
didn't realise was that whilst I had the gate values on either side of
the pump disconnected, the boiler couldn't come on. Presumably this
means I have a fully pumped system?

Anyway I decided to leave the pump disconnected this evening and try
again tomorrow. Bear in mind that at this time I'm still thinking its
the pump. The boiler was on and happily heating water and
approximately 40mins to an hour later the fuse went pop again.

When I was in the plumbers merchants he said if the pump was gone it
would smell of burning - it doesn't.

So now where do I stand? Have I confirmed it ISN'T the pump?
Does the fact that it took 40mins to an hour to blow indicate the
blowout happened when the motorised valve was moving to a different
position once the HW was heated?

Back to you boys ot there.

Charlie

And it was ok foabout 40minutes. The fuse then
  #5   Report Post  
Charlie
 
Posts: n/a
Default Central Heating problem - 2A fuse blowing in honeywell wiring box

When I opened the inspection at the front of the pump I got quite a
bit of water coming out of it, as opposed to a few drips. Is this
normal or does it indicate a knackered pump?

I put a screw driver in to try and turn it but nothing. Didn't have a
torch so unsure whether I was seating the screwdriver correctly.

Took the motorised valve apart - there is very little movement. when I
turn the valve but about the same as the amount of movement in the
motor. However when the motorised part was off and I slid the manual
overide lever across to manual, I got a consistent amount of
resistence and the lever comes back ALL the way to "Auto". But when
the motor and valve are back together the lever can be moved over and
back by about 1cm without any resistence. Is this normal?

And finally I opened the drain valve to drain the system and
"NOTHING". There doesn't appear to be any water in the system.
Presumably no water would cause overheating of the pump. Could this
blow the 2A fuse in the wiring box or could other parts overheat?

Cheers

Charlie


  #7   Report Post  
Charlie
 
Posts: n/a
Default Central Heating problem - 2A fuse blowing in honeywell wiring box

False alarm - there is water in the system - must be an old drain
cock.

Tried again today with the red wire feeding the pump switched out and
the valve manually turned on but it blew. Valve obviously kicked in
cos when I checked after the blow the vavle had retiurned to the auto
position. Tried with the valve feeds all out also also blew. Did
manage to get it going for a short while but then the boiler went out.
Managed to restart the pilot ok.

I've given up!!!

Charlie
  #8   Report Post  
Charlie
 
Posts: n/a
Default Pulling cabling through

Had the Electrician in. None of my components had gone!!! It turned
out there is a break in the cable running from under the stairs to the
kitchen. About 15 metres of cable nicely boxed and hidden. I did it
myself around 15 years ago so I can't complain too much!!

Now my problem is do I run a new cable in some sticky back trunking
along the skirting and behind the kitchen cupboards where it can be
seen (concrete floors unfortunately) or do I try and pull a new cable
thru the existing boxing which also contains the pipework? I
previously used twin and earth lighting cable. Electrician suggested I
use 4 core as a replacement as any future boiler is likely to have
live in addition to switched live. Will the new cable be up to being
pulled through about 15metres of boxing, 2 walls and 3 corners.

Cheers

Charlie
  #9   Report Post  
 
Posts: n/a
Default Pulling cabling through

In uk.d-i-y, Charlie wrote:

....................................... do I try and pull a new cable
thru the existing boxing which also contains the pipework?
.................................. Will the new cable be up to being
pulled through about 15metres of boxing, 2 walls and 3 corners.

No to both questions, I'm afraid! For the first, it's not accepted
practice to run mains-carrying cable in the same compartment as
pipework, on grounds both of heat (presumably the pipework includes
the boiler output - 70-80 degrees?) and of what-happens-if-there's-a-
fault-exposing-conductors (like, we're pretty sure the pipework's
earthed, but just *how* sure are we?)

For the second, pulling cable round three corners, expecially with
other pipework in their, is pretty much doomed to failure; and likely
even if you manage to damage the insulation.

But hey, maybe you can use this as an excuse to buy a nice new SDS drill
so you can channel the 4-core neatly ;-)

Stefek
  #10   Report Post  
Dave Liquorice
 
Posts: n/a
Default Pulling cabling through

On 30 Sep 2003 10:56:21 -0700, Charlie wrote:

Now my problem is do I run a new cable in some sticky back trunking
along the skirting and behind the kitchen cupboards where it can be
seen (concrete floors unfortunately) or do I try and pull a new
cable thru the existing boxing which also contains the pipework?


Pipework as in CH pipes to from boiler? Ordinary PVC cable doesn't
have a particulary high temperature rating. 80C+ from boiler pipework
probably exceeds it. I don't think we need be concerned about heating
from the load if you use 2.5mm.

Will the new cable be up to being pulled through about 15metres of
boxing, 2 walls and 3 corners.


If you can get clear straight runs you should be able to do it. No
chance around a corner, let alone 3.

--
Cheers
Dave. pam is missing e-mail



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pool water in central heating system Andy Hall UK diy 1 September 2nd 03 06:01 PM
Central heating wiring Paul Roman UK diy 10 August 30th 03 03:20 PM
Further to my last post entitled 'Flushing and treating central heating question' David W.E. Roberts UK diy 0 July 29th 03 08:15 PM
Immersion Heater Fuse Blowing MrCheerful UK diy 3 July 24th 03 03:15 PM
HONEYWELL CENTRAL HEATING VALVE V4043H tc3man1 UK diy 2 July 22nd 03 04:31 PM


All times are GMT +1. The time now is 02:17 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"