The wiki article
http://wiki.diyfaq.org.uk/index.php?...and_Heat_Banks
says:

Assume (for the sake of illustration) that
the water in the store reaches 70C when fully heated
the incoming cold water is at 10C
the hot water must be at least 40C to be acceptable
the heat exchanger is perfect, i.e. there is no temperature drop across
it.

As DHW is heated it will rise to 70C (when the store is fully heated)
and will cool the water in the store to 10C. If the cooled water is
thoroughly mixed with the hot water the whole store will progressively
cool until it reaches 40C after which the temperature of the DHW
becomes unacceptable. However if the water cooled to 10C is kept
separate and only the water at 70C is fed to the heat exchanger then
the DHW will continue to produce acceptable water until the whole store
contains only water at 10C. In the first scenario the amount of heat
available by cooling the store from 70C to 40C is available for heating
DHW, while in the second the amount of heat available is that of
cooling the store from 70C to 10C. This gives much more DHW for a given
volume of store at a given temperature. Stratification, where the cool
water at the bottom of the store remains relatively separate from the
hotter water further up, provides a means of approaching this goal.

========

Comments here concern the thermal store.

I'd like to suggest that with stratified water, at end of useful hot
water output one has a situation where the water at the top of the heat
exchanger is 40C, and water below graduates down to 10C, rather than
all water being at 10C. There isnt any way you could get hot water at
40C from a tank thats all at 10C, or 20 or 30. This still gives much
more output than with a no-stratified tank.


Second I have a question related to the thermal store diagram and how
it might perhaps operate more effectively. I think we can accept that
the water in teh cylinder will vary from bottom to top in a continous
temperature progresion, ie 10,11,12,13,14 etc all the way to perhaps
65C or thereabouts. And we're assuming the water enters e heat
exchanger at 10C for this example.

The thermal store diagram is shown with the exchanger in the top half
of the cylinder only. The water here would mostly be well above 10C.

Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.

OTOH if one were to use a full height heat exchnager, with the cold fed
to the heat exchange pipe at the bottom of the tank, not half way up,
that bottom half of tank water prewarms the HW before it reaches the
half way up the tank level in the heat exchange pipe. This means the
top half of tank water has to do less work, and the heat, or just
warmth, is being drawn out of the colder water in the bottom half. IOW
you'll get more total volume of HW out, and the tank will end up with
colder water in the bottom half than if it used a top section only heat
exhanger.

I'm not sure if I've explained it too good!


NT

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 464
Default Thermal Stores and Heat Banks Question


wrote in message
ps.com...
The wiki article
http://wiki.diyfaq.org.uk/index.php?...and_Heat_Banks
says:

Assume (for the sake of illustration) that
the water in the store reaches 70C when fully heated
the incoming cold water is at 10C
the hot water must be at least 40C to be acceptable
the heat exchanger is perfect, i.e. there is no temperature drop across
it.

As DHW is heated it will rise to 70C (when the store is fully heated)
and will cool the water in the store to 10C. If the cooled water is
thoroughly mixed with the hot water the whole store will progressively
cool until it reaches 40C after which the temperature of the DHW
becomes unacceptable. However if the water cooled to 10C is kept
separate and only the water at 70C is fed to the heat exchanger then
the DHW will continue to produce acceptable water until the whole store
contains only water at 10C. In the first scenario the amount of heat
available by cooling the store from 70C to 40C is available for heating
DHW, while in the second the amount of heat available is that of
cooling the store from 70C to 10C. This gives much more DHW for a given
volume of store at a given temperature. Stratification, where the cool
water at the bottom of the store remains relatively separate from the
hotter water further up, provides a means of approaching this goal.

========

Comments here concern the thermal store.

I'd like to suggest that with stratified water, at end of useful hot
water output one has a situation where the water at the top of the heat
exchanger is 40C, and water below graduates down to 10C, rather than
all water being at 10C. There isnt any way you could get hot water at
40C from a tank thats all at 10C, or 20 or 30. This still gives much
more output than with a no-stratified tank.


Second I have a question related to the thermal store diagram and how
it might perhaps operate more effectively. I think we can accept that
the water in teh cylinder will vary from bottom to top in a continous
temperature progresion, ie 10,11,12,13,14 etc all the way to perhaps
65C or thereabouts. And we're assuming the water enters e heat
exchanger at 10C for this example.

I only have perssonal experience of the Heatbank installed in my house
(others may vary) but IMHO your suggestion doesn't track with actuality ....
I cannot "accept that the water in teh cylinder will vary from bottom to
top in a continous temperature progresion, ie 10,11,12,13,14 etc all the way
to perhaps 65C or thereabouts"
Experience, and judicous prodding of the pipes with a digital thermomer,
leads me to conclude that hot water 'floats' on top of colder water. {BTW; I
have a _personal_ dislike of the term 'water' used when describing Heatbank
operation - I prefer to use the term _fluid_ (albeit it water) to
differentiate between 'water' that becomes DHW and 'fluid' that lives within
the boiler, heatbank and radiator circuits ~ I trust you'll bear with this
foilble}.
On the heatbank I've installed 'fluid' is drawn off the top of the cylinder
(where it's hottest} and enters the Heat Plate Exchanger{HPE) surrendering
some of its heat. This fluid is injected back into the cylinder at the
bottom. Thus the hottest fluid is always at the top. {This situation
continues until there's no more 70deg 'fluid' at the upper surface. IMHO,
the continuos gradient you/'ve surmised doesn't arise.


The thermal store diagram is shown with the exchanger in the top half
of the cylinder only. The water here would mostly be well above 10C.


My actual installation has the HPE more-or-less in the middle BUT it's fed
off two aperture locateted 'very close' to the top of the cyclinder (Hot)
and 'very close' to the bottom of the cylinder for 'cooled' return.


Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.

Dubious conslusion: the HPE accepts fluid from the very top of the
cylinder -
it's physical location is irrelevant. For practical purposes it's apposite
to install it onto the cylinder removed from the penetrations -hence 'mine'
is mounted about 'half-way-up' ... but it's fed off apertures at the top and
bottom. Your other surmises are premised on a dodgy conclusion.

OTOH if one were to use a full height heat exchnager,


the 'height ' of a HPE is once again irrelevant ... the area of the HPE is
scaled to transfer heat from the fluid to the rising main transforming it
from water @ 10 deg C to water @ 40 deg C [your figures re-quoted). The
fuild is circulated through the HPE by a pump while cold mains water is
blended with the heated water emenating from the HPE to maintain a
demanded temperature [ ... my setting is to provide Hot water (at mains
pressure) @ 55 deg C ... ]



with the cold fed
to the heat exchange pipe at the bottom of the tank, not half way up,
that bottom half of tank water prewarms the HW before it reaches the
half way up the tank level in the heat exchange pipe. This means the
top half of tank water has to do less work, and the heat, or just
warmth, is being drawn out of the colder water in the bottom half. IOW
you'll get more total volume of HW out, and the tank will end up with
colder water in the bottom half than if it used a top section only heat
exhanger.

I'm not sure if I've explained it too good!


NT


Me too; I hope I've explained it as well.

--

Brian


  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 9,560
Default Thermal Stores and Heat Banks Question

Brian Sharrock wrote:
wrote in message


Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.


Dubious conslusion: the HPE accepts fluid from the very top of the
cylinder -
it's physical location is irrelevant. For practical purposes it's apposite
to install it onto the cylinder removed from the penetrations -hence 'mine'
is mounted about 'half-way-up' ... but it's fed off apertures at the top and
bottom. Your other surmises are premised on a dodgy conclusion.


Only trouble is, I think we're talking about 2 different things there.
I was specifically talking about the other type of system, where the
water runs through a heat exchanger located inside the tank. Things
will be a bit different with your external exchanger setup.


I'm not sure if I've explained it too good!


Me too; I hope I've explained it as well.


Well, at least the fluid vs water terms help.


NT

  #4   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 464
Default Thermal Stores and Heat Banks Question


wrote in message
ups.com...
Brian Sharrock wrote:
wrote in message


Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.


Dubious conslusion: the HPE accepts fluid from the very top of the
cylinder -
it's physical location is irrelevant. For practical purposes it's
apposite
to install it onto the cylinder removed from the penetrations -hence
'mine'
is mounted about 'half-way-up' ... but it's fed off apertures at the top
and
bottom. Your other surmises are premised on a dodgy conclusion.


Only trouble is, I think we're talking about 2 different things there.
I was specifically talking about the other type of system, where the
water runs through a heat exchanger located inside the tank. Things
will be a bit different with your external exchanger setup.


OK! From your usage of the phrase "the heat exchanger, which is halfway up
the tank"
as opposed to 'immersed heating coil', I inferred you were referring to an
external plate heat exchanger. BTW; your observations was one ot the reasons
why I 'rejected' that design in my 'procurement' policy.

I'm not sure if I've explained it too good!


Me too; I hope I've explained it as well.


Well, at least the fluid vs water terms help.


OK ! I personally found the hot water here- cold water there- _very_
confusing, particularly trying to determine where the water in the boiler
versus the water in the bath were ... so I instructed myself to cite one as
a fluid ( system, heat transfer, ...water) and the other as water (potable,
warm or cold). With these differentiated the penny dropped .... and I
purchased a vented, heatbank which operates the CH and DHW .... and clears
the loft of a cold water storage tank.

--

BRian


NT



  #5   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 2,379
Default Thermal Stores and Heat Banks Question

Very interested in this debate - particularly good thermal store/heat
bank design - what is the best "professional" source of design info?
Book? Online?



  #7   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Thermal Stores and Heat Banks Question


"Brian Sharrock" wrote in message
...

wrote in message
ps.com...
The wiki article
http://wiki.diyfaq.org.uk/index.php?...and_Heat_Banks
says:

Assume (for the sake of illustration) that
the water in the store reaches 70C when fully heated
the incoming cold water is at 10C
the hot water must be at least 40C to be acceptable
the heat exchanger is perfect, i.e. there is no temperature drop across
it.

As DHW is heated it will rise to 70C (when the store is fully heated)
and will cool the water in the store to 10C. If the cooled water is
thoroughly mixed with the hot water the whole store will progressively
cool until it reaches 40C after which the temperature of the DHW
becomes unacceptable. However if the water cooled to 10C is kept
separate and only the water at 70C is fed to the heat exchanger then
the DHW will continue to produce acceptable water until the whole store
contains only water at 10C. In the first scenario the amount of heat
available by cooling the store from 70C to 40C is available for heating
DHW, while in the second the amount of heat available is that of
cooling the store from 70C to 10C. This gives much more DHW for a given
volume of store at a given temperature. Stratification, where the cool
water at the bottom of the store remains relatively separate from the
hotter water further up, provides a means of approaching this goal.

========

Comments here concern the thermal store.

I'd like to suggest that with stratified water, at end of useful hot
water output one has a situation where the water at the top of the heat
exchanger is 40C, and water below graduates down to 10C, rather than
all water being at 10C. There isnt any way you could get hot water at
40C from a tank thats all at 10C, or 20 or 30. This still gives much
more output than with a no-stratified tank.


Second I have a question related to the thermal store diagram and how
it might perhaps operate more effectively. I think we can accept that
the water in teh cylinder will vary from bottom to top in a continous
temperature progresion, ie 10,11,12,13,14 etc all the way to perhaps
65C or thereabouts. And we're assuming the water enters e heat
exchanger at 10C for this example.

I only have perssonal experience of the Heatbank installed in my house
(others may vary) but IMHO your suggestion doesn't track with actuality
....
I cannot "accept that the water in teh cylinder will vary from bottom to
top in a continous temperature progresion, ie 10,11,12,13,14 etc all the
way to perhaps 65C or thereabouts"
Experience, and judicous prodding of the pipes with a digital thermomer,
leads me to conclude that hot water 'floats' on top of colder water. {BTW;
I have a _personal_ dislike of the term 'water' used when describing
Heatbank operation - I prefer to use the term _fluid_ (albeit it water) to
differentiate between 'water' that becomes DHW and 'fluid' that lives
within the boiler, heatbank and radiator circuits ~ I trust you'll bear
with this foilble}.
On the heatbank I've installed 'fluid' is drawn off the top of the
cylinder (where it's hottest} and enters the Heat Plate Exchanger{HPE)
surrendering some of its heat. This fluid is injected back into the
cylinder at the bottom. Thus the hottest fluid is always at the top. {This
situation continues until there's no more 70deg 'fluid' at the upper
surface. IMHO, the continuos gradient you/'ve surmised doesn't arise.


The thermal store diagram is shown with the exchanger in the top half
of the cylinder only. The water here would mostly be well above 10C.


My actual installation has the HPE more-or-less in the middle BUT it's fed
off two aperture locateted 'very close' to the top of the cyclinder (Hot)
and 'very close' to the bottom of the cylinder for 'cooled' return.


What make of heat bank?

People are confused and the Wiki is not that good. A thermal store
(immersed coil) and a heat bank (using plate heat exchanger) operate on the
same "principle" and are of the same family. However in detail they are very
different with the heat bank far more efficient. Manufacturers don't help
with come calling heat banks thermal stores. I have heat transfer fluid
(water) from the store enter the plate heat exchanger at over 70C and the
amount of heat it transfers to the incoming mains water drops the heat
transfer fluid to below 20C. I can wrap my hand around the pipe and it feels
quite cool.

Plate heat exchangers are far more efficient than an immersed coil.

ACV have a hybrid thermal store/tank-in-tank unvented cylinder. They claim
the boiler will always condense. They so this by having a DHW coil at the
very bottom of the cylinder. Fresh cold water enters the coil cooling the
bottom of the cylinder greatly. Then the water rises through a pipe into an
immersed tan-in-tank further up the store. The coil lower down pre-heats the
DHW and cool the bottom to endure condensing operation at all time.

Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.


The coil is in the top half because the bottom half is reserved for CH. The
great thing about heat banks. If designed correctly they can combine the
energy output of the stored transfer fluid (water) and the boiler. This
means the store can be downsized.

  #8   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Thermal Stores and Heat Banks Question


wrote in message
ups.com...
Brian Sharrock wrote:
wrote in message


Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end of
useful hot output, the water below the heat exchnager will be about the
same temp as it was before HW was drawn off, namely a gradient from 10C
to 40C.


Dubious conslusion: the HPE accepts fluid from the very top of the
cylinder -
it's physical location is irrelevant. For practical purposes it's
apposite
to install it onto the cylinder removed from the penetrations -hence
'mine'
is mounted about 'half-way-up' ... but it's fed off apertures at the top
and
bottom. Your other surmises are premised on a dodgy conclusion.


Only trouble is, I think we're talking about 2 different things there.
I was specifically talking about the other type of system, where the
water runs through a heat exchanger located inside the tank. Things
will be a bit different with your external exchanger setup.


Yep. They are different. So talk about one or the other.

  #9   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Thermal Stores and Heat Banks Question


"Brian Sharrock" wrote in message
...

wrote in message
ups.com...
Brian Sharrock wrote:
wrote in message


Now, if the exchanger is in the top part of the cylinder, the mains
pressure cold water comes into the bottom of the heat exchanger, which
is halfway up the tank, and will meet tank water temp of somewhere
between 10 and 65C, lets say maybe 35-40C. What this means is at end
of
useful hot output, the water below the heat exchnager will be about
the
same temp as it was before HW was drawn off, namely a gradient from
10C
to 40C.


Dubious conslusion: the HPE accepts fluid from the very top of the
cylinder -
it's physical location is irrelevant. For practical purposes it's
apposite
to install it onto the cylinder removed from the penetrations -hence
'mine'
is mounted about 'half-way-up' ... but it's fed off apertures at the top
and
bottom. Your other surmises are premised on a dodgy conclusion.


Only trouble is, I think we're talking about 2 different things there.
I was specifically talking about the other type of system, where the
water runs through a heat exchanger located inside the tank. Things
will be a bit different with your external exchanger setup.


OK! From your usage of the phrase "the heat exchanger, which is halfway
up the tank"
as opposed to 'immersed heating coil', I inferred you were referring to an
external plate heat exchanger. BTW; your observations was one ot the
reasons why I 'rejected' that design in my 'procurement' policy.

I'm not sure if I've explained it too good!


Me too; I hope I've explained it as well.


Well, at least the fluid vs water terms help.


OK ! I personally found the hot water here- cold water there- _very_
confusing, particularly trying to determine where the water in the boiler
versus the water in the bath were ... so I instructed myself to cite one
as a fluid ( system, heat transfer, ...water) and the other as water
(potable, warm or cold). With these differentiated the penny dropped ....
and I purchased a vented, heatbank which operates the CH and DHW .... and
clears the loft of a cold water storage tank.


The terms are usually primary water (transfer fluid) and secondary water
(potable) . Many can't grasp this either.

  #10   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 4,046
Default Thermal Stores and Heat Banks Question


wrote in message
ups.com...
Very interested in this debate - particularly good thermal store/heat
bank design - what is the best "professional" source of design info?
Book? Online?


The best ask me, after reading http://www.heatweb,com They explain it quite
well.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
new-fangled "thermal stores" [email protected] UK diy 3 September 16th 06 04:38 PM
Open vented mains pressure thermal stores Rich UK diy 6 November 22nd 05 02:23 PM
Direct Heat Banks - why no zone valves (and other questions) Dave UK diy 32 October 10th 04 04:58 PM
What I have learnt about geo thermal heat pumps George Eberhardt Home Repair 11 September 9th 04 08:56 PM
Heat banks (again!) Dave UK diy 148 September 6th 04 08:45 PM


All times are GMT +1. The time now is 03:32 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"