Default gas hob pressure

I have just installed a replacement hob which will be checked by a
corgi man.
But I have a problem. I have 20mb at burner jet but this drops
drmatically when I turn another burner on. With the gas lit you can see
the flames reduce in size when more than 1 burner is on at a time. This
happened with our old hob but I put it down to the age of the thing.

I did an extension some years ago and then about 5 years ago moved my
boiler to the garage.This was checked by a corgi man, he actulaly made
the final gas connections. I think the gas hob problem coincided with
boiler move but as I say, i put it down to the age of hob.


Here is a diagram of the pipes (approx including allowance for elbows)

2mtrs @ 22mm 10mtrs @ 22mm
Meter-------------------------TEE----------------------------------------------------------------------BOILER
1.6m3/hr
|
| 12mtrs @ 22mm
14mtrs @ 15mm

|---------------------------------REDUCER--------------------------------HOB
1m3/hr


I used the following link and calculations for pipe sizes all look ok?
Any ideas what the problem may be? I'd like to know whether Corgi man
will need to lay new pipes etc.

  #2   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 1,982
Default gas hob pressure

On Thu, 31 Aug 2006 15:38:48 -0700, dme wrote:

I have just installed a replacement hob which will be checked by a
corgi man.
But I have a problem. I have 20mb at burner jet but this drops
drmatically when I turn another burner on. With the gas lit you can see
the flames reduce in size when more than 1 burner is on at a time. This
happened with our old hob but I put it down to the age of the thing.

I did an extension some years ago and then about 5 years ago moved my
boiler to the garage.This was checked by a corgi man, he actulaly made
the final gas connections. I think the gas hob problem coincided with
boiler move but as I say, i put it down to the age of hob.


Here is a diagram of the pipes (approx including allowance for elbows)

2mtrs @ 22mm 10mtrs @ 22mm
Meter-------------------------TEE----------------------------------------------------------------------BOILER
1.6m3/hr
|
| 12mtrs @ 22mm
14mtrs @ 15mm

|---------------------------------REDUCER--------------------------------HOB
1m3/hr


I used the following link and calculations for pipe sizes all look ok?


The 15mm pipe from your Tee (I think - the formatting doesn't work as
ASCII art for me) will drop all your allowed 1mbar on its own if the hob
is taking 1m3/h (that's a big hob, isn't it?). Thus, taken with the 12m of
22mm and shared 2m of 22mm to the meter your pressure drop will be more
than what it should be. Even so you shouldn't be getting a radical drop in
flame size at the other burners. What does the pressure at the hob drop
to? (Stick your manometer hoze onto the burner jet of the smallest ring
if there isn't a test nipple anywhere, which there usually isn't on hobs.
Oh and mind out for the spark ignition as you're holding the tube in place!)

If you're getting more than say 2mb drop I'd suspect a blockage somewhere.

How much do the burner flames drop by when another burner is lit? Is
it enough for a burner set low to go right out? And do the burner flames
drop when the boiler fires up?

Any ideas what the problem may be? I'd like to know

whether Corgi man
will need to lay new pipes etc.


By the book, yes, and if one were commissioning the new appliance that's
the way to do it. If it's an existing appliance one might raise a 'not to
current standards' warning notice to cover one's backside if the
appliance wasn't showing any problems with the pressure. However the
problem you describe would definitely have to be addressed.

BTW you will shortly be receiving advice from a regular on this group to
re-do your pipework right the way back to the North Sea (or maybe Russia)
to avoid this problem. :-)

  #3   Report Post  
Posted to uk.d-i-y
external usenet poster
 
Posts: 22
Default gas hob pressure


"dme" wrote in message
oups.com...
I have just installed a replacement hob which will be checked by a
corgi man.
But I have a problem. I have 20mb at burner jet but this drops
drmatically when I turn another burner on. With the gas lit you can see
the flames reduce in size when more than 1 burner is on at a time. This
happened with our old hob but I put it down to the age of the thing.

I did an extension some years ago and then about 5 years ago moved my
boiler to the garage.This was checked by a corgi man, he actulaly made
the final gas connections. I think the gas hob problem coincided with
boiler move but as I say, i put it down to the age of hob.


Here is a diagram of the pipes (approx including allowance for elbows)

2mtrs @ 22mm 10mtrs @ 22mm

Meter-------------------------TEE-------------------------------------------
---------------------------BOILER
1.6m3/hr
|
| 12mtrs @ 22mm
14mtrs @ 15mm


|---------------------------------REDUCER--------------------------------HOB
1m3/hr


I used the following link and calculations for pipe sizes all look ok?
Any ideas what the problem may be? I'd like to know whether Corgi man
will need to lay new pipes etc.


I think you should re-do your pipework right the way back to the North Sea
(or maybe Russia)
to avoid this problem.

woodglass :-)


  #4   Report Post  
Posted to uk.d-i-y
Gav Gav is offline
external usenet poster
 
Posts: 50
Default gas hob pressure

John Stumbles wrote:
On Thu, 31 Aug 2006 15:38:48 -0700, dme wrote:

I have just installed a replacement hob which will be checked by a
corgi man.
But I have a problem. I have 20mb at burner jet but this drops
drmatically when I turn another burner on. With the gas lit you can see
the flames reduce in size when more than 1 burner is on at a time. This
happened with our old hob but I put it down to the age of the thing.

I did an extension some years ago and then about 5 years ago moved my
boiler to the garage.This was checked by a corgi man, he actulaly made
the final gas connections. I think the gas hob problem coincided with
boiler move but as I say, i put it down to the age of hob.


Here is a diagram of the pipes (approx including allowance for elbows)

2mtrs @ 22mm 10mtrs @ 22mm
Meter-------------------------TEE----------------------------------------------------------------------BOILER
1.6m3/hr
|
| 12mtrs @ 22mm
14mtrs @ 15mm

|---------------------------------REDUCER--------------------------------HOB
1m3/hr


I used the following link and calculations for pipe sizes all look ok?


The 15mm pipe from your Tee (I think - the formatting doesn't work as
ASCII art for me) will drop all your allowed 1mbar on its own if the hob
is taking 1m3/h (that's a big hob, isn't it?). Thus, taken with the 12m of
22mm and shared 2m of 22mm to the meter your pressure drop will be more
than what it should be. Even so you shouldn't be getting a radical drop in
flame size at the other burners. What does the pressure at the hob drop
to? (Stick your manometer hoze onto the burner jet of the smallest ring
if there isn't a test nipple anywhere, which there usually isn't on hobs.
Oh and mind out for the spark ignition as you're holding the tube in place!)

If you're getting more than say 2mb drop I'd suspect a blockage somewhere.

How much do the burner flames drop by when another burner is lit? Is
it enough for a burner set low to go right out? And do the burner flames
drop when the boiler fires up?

Any ideas what the problem may be? I'd like to know

whether Corgi man
will need to lay new pipes etc.


By the book, yes, and if one were commissioning the new appliance that's
the way to do it. If it's an existing appliance one might raise a 'not to
current standards' warning notice to cover one's backside if the
appliance wasn't showing any problems with the pressure. However the
problem you describe would definitely have to be addressed.

BTW you will shortly be receiving advice from a regular on this group to
re-do your pipework right the way back to the North Sea (or maybe Russia)
to avoid this problem. :-)

has anyone bothered to check the gas rate of the appliance to see if it
is burning correctly???
  #5   Report Post  
Posted to uk.d-i-y
Gav Gav is offline
external usenet poster
 
Posts: 50
Default gas hob pressure

John Stumbles wrote:
On Thu, 31 Aug 2006 15:38:48 -0700, dme wrote:

I have just installed a replacement hob which will be checked by a
corgi man.
But I have a problem. I have 20mb at burner jet but this drops
drmatically when I turn another burner on. With the gas lit you can see
the flames reduce in size when more than 1 burner is on at a time. This
happened with our old hob but I put it down to the age of the thing.

I did an extension some years ago and then about 5 years ago moved my
boiler to the garage.This was checked by a corgi man, he actulaly made
the final gas connections. I think the gas hob problem coincided with
boiler move but as I say, i put it down to the age of hob.


Here is a diagram of the pipes (approx including allowance for elbows)

2mtrs @ 22mm 10mtrs @ 22mm
Meter-------------------------TEE----------------------------------------------------------------------BOILER
1.6m3/hr
|
| 12mtrs @ 22mm
14mtrs @ 15mm

|---------------------------------REDUCER--------------------------------HOB
1m3/hr


I used the following link and calculations for pipe sizes all look ok?


The 15mm pipe from your Tee (I think - the formatting doesn't work as
ASCII art for me) will drop all your allowed 1mbar on its own if the hob
is taking 1m3/h (that's a big hob, isn't it?). Thus, taken with the 12m of
22mm and shared 2m of 22mm to the meter your pressure drop will be more
than what it should be. Even so you shouldn't be getting a radical drop in
flame size at the other burners. What does the pressure at the hob drop
to? (Stick your manometer hoze onto the burner jet of the smallest ring
if there isn't a test nipple anywhere, which there usually isn't on hobs.
Oh and mind out for the spark ignition as you're holding the tube in place!)

If you're getting more than say 2mb drop I'd suspect a blockage somewhere.

How much do the burner flames drop by when another burner is lit? Is
it enough for a burner set low to go right out? And do the burner flames
drop when the boiler fires up?

Any ideas what the problem may be? I'd like to know

whether Corgi man
will need to lay new pipes etc.


By the book, yes, and if one were commissioning the new appliance that's
the way to do it. If it's an existing appliance one might raise a 'not to
current standards' warning notice to cover one's backside if the
appliance wasn't showing any problems with the pressure. However the
problem you describe would definitely have to be addressed.

BTW you will shortly be receiving advice from a regular on this group to
re-do your pipework right the way back to the North Sea (or maybe Russia)
to avoid this problem. :-)

oh and i think you might need 99 mm gas pipe for this hob!!!!(that was a
joke before you start)
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Well pressure tank leaking..... Nozaki Home Repair 2 April 17th 06 07:03 AM
Boiler low pressure problems Milleniumaire UK diy 14 April 4th 06 07:31 PM
Low water pressure or low water flow? Chris Lewis Home Repair 0 March 28th 06 05:21 PM
trenching and other uses of a high pressure washer Jer Home Repair 5 November 18th 04 08:59 PM
Slightly OT "pressure" Ivan Vegvary Metalworking 2 August 6th 03 05:49 AM


All times are GMT +1. The time now is 02:03 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"