Unvented hot water.
Hi All,
So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. We are going to investigate the price of having a high pressure hot water system fitted. Ive had a look at the heatweb website and am starting to educate myself into the benefits of heat banks and megaflows. In our house (4 bed) we have 3 bathrooms which consist of one bath, three showers and three sinks plus the kitchen hot water (also 15 radiators). Its quite a big system. Does anybody have any experience of fitting these type of systems into an existing Yplan gravity feed system and what size of unit would be required. I would like to be knowledgeable when the prospective plumbers turn up to give me a quote for obvious reasons. Is it a major job? BTW how would I know if the mains water was high enough in terms of pressure for use with such a system? Our mains riser in the kitchen comes in through a large bore pipe (70's house) and is stepped down straight away under the sink to 15mm for feeding the existing gravity system. Thanks for any advice, Matthew |
#2
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
BTW how would I know if the mains water was high enough in terms of
pressure for use with such a system? Our mains riser in the kitchen comes in through a large bore pipe (70's house) and is stepped down straight away under the sink to 15mm for feeding the existing gravity system. You need to measure the static pressure and the flow rate at the kitchen tap. Try it at several times of day, specifically including the morning "rush hour". You may have to contrive something to measure the pressure. In actuality, the flow rate is more important, although static pressure can be a good indicator of potential if you know the pipework to be well sized. If all is OK, you will need a 210L (or thereabouts) unvented cylinder or heatbank. If you live with greater than average numbers of teenage girls, consider a slight upgrade. Consider replacing the 15mm pipe with 22mm. Also consider running a dedicated 22mm line from the stop cock to the HWC/heat bank. The output from the heatbank should be in 15mm to reduce the hot water dead leg time and wastage, especially if your pressure is good. Christian. |
#3
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Christian McArdle wrote:
If all is OK, you will need a 210L (or thereabouts) unvented cylinder My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. |
#4
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
My bath is 500x1500x300mm deep. It takes 225 liters to fill it.
I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. Christian. |
#5
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Christian McArdle wrote:
My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. Christian. Especially considering that you would expect some cold to be added as well |
#6
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
"Richard Conway" wrote in message ... Christian McArdle wrote: My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. Christian. Especially considering that you would expect some cold to be added as well Perhaps he's a serial bather G AWEM |
#7
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
There is something wrong with your system if 700 litres won't
fill a 225 litre bath. Especially considering that you would expect some cold to be added as well Perhaps he's a serial bather G With a decent boiler, this wouldn't matter, as it should be capable of entirely regenerating the bath full of water in about 22 minutes. The 700 litre tank would provide about 1100 litres of bath water without any regeneration at all, which is almost 5 of his oversized bath loads. Christian. |
#8
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
In article .com,
Matthew wrote: So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. Chances are the hotel had a gravity fed system... We are going to investigate the price of having a high pressure hot water system fitted. Before that could you re-site the header tank up higher? You'd be amazed how little extra height effects pressure if you're starting from near zero head. -- *Snowmen fall from Heaven unassembled* Dave Plowman London SW To e-mail, change noise into sound. |
#9
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
On Mon, 21 Aug 2006 16:40:56 +0100, The Natural Philosopher wrote:
Christian McArdle wrote: If all is OK, you will need a 210L (or thereabouts) unvented cylinder My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. Something wrong here... 1)The water in the bath is not pure HW so it will only consume around half that quantity of HW. 2) Your bath is sized like most peoples however when you get in it, you only need the water around you (as you will displace anything from 50-100 litres). The received wisdom is that 70 litres of HW water needs to be stored per bathroom. (Obvious teenage mermaids and "celebs" taking "hollywood showers" make for a bit more still). -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards |
#10
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
"Dave Plowman (News)" wrote in message ... In article .com, Matthew wrote: So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. Chances are the hotel had a gravity fed system... Chances are it will not. We are going to investigate the price of having a high pressure hot water system fitted. Before that could Will you please eff off as you are an idiot. |
#11
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
"Christian McArdle" wrote in message ... BTW how would I know if the mains water was high enough in terms of pressure for use with such a system? Our mains riser in the kitchen comes in through a large bore pipe (70's house) and is stepped down straight away under the sink to 15mm for feeding the existing gravity system. You need to measure the static pressure and the flow rate at the kitchen tap. Try it at several times of day, specifically including the morning "rush hour". You may have to contrive something to measure the pressure. In actuality, the flow rate is more important, although static pressure can be a good indicator of potential if you know the pipework to be well sized. If all is OK, you will need a 210L (or thereabouts) unvented cylinder or heatbank. If you live with greater than average numbers of teenage girls, consider a slight upgrade. Consider replacing the 15mm pipe with 22mm. Also consider running a dedicated 22mm line from the stop cock to the HWC/heat bank. The output from the heatbank should be in 15mm to reduce the hot water dead leg time and wastage, especially if your pressure is good. Christian. Best go for a heat bank as unvented cylinders require an annual service of approx £100. Heat bank can operate at higher pressures, usually meaning good flows. If having 15mm on the draw-offs, have a manifold at the heat bank, which means all the DHW draw-offs go back to the one point |
#12
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Christian McArdle wrote:
My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. It will only fill three of them. Christian. |
#13
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Richard Conway wrote:
Christian McArdle wrote: My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. Christian. Especially considering that you would expect some cold to be added as well You don;t know much about my bathing habits so you? OR about ,y wifes habit of leaving the kitchen sink hot tap running while she wanders around thinking about something else entirely... |
#14
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Andrew Mawson wrote:
"Richard Conway" wrote in message ... Christian McArdle wrote: My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. There is something wrong with your system if 700 litres won't fill a 225 litre bath. Christian. Especially considering that you would expect some cold to be added as well Perhaps he's a serial bather G Indeed I am. AWEM |
#15
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Ed Sirett wrote:
On Mon, 21 Aug 2006 16:40:56 +0100, The Natural Philosopher wrote: Christian McArdle wrote: If all is OK, you will need a 210L (or thereabouts) unvented cylinder My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. Something wrong here... 1)The water in the bath is not pure HW so it will only consume around half that quantity of HW. 2) Your bath is sized like most peoples however when you get in it, you only need the water around you (as you will displace anything from 50-100 litres). The received wisdom is that 70 litres of HW water needs to be stored per bathroom. (Obvious teenage mermaids and "celebs" taking "hollywood showers" make for a bit more still). I never let received wisdom get in the way of personal experience. |
#16
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
There is something wrong with your system if 700 litres won't fill a 225
litre bath. It will only fill three of them. Wow, you like your baths at 60C? Even with a cold bit at the bottom of the cylinder, it should fill four. If the only reason you need it so big is because your wife leaves the tap on, I'd go for a much smaller tank, as it will waste less energy and regenerate from cold quicker. Christian. |
#17
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Doctor Drivel wrote: "Christian McArdle" wrote in message Best go for a heat bank as unvented cylinders require an annual service of approx £100. I used to have an unvented system and I was never required to have or to pay for a service. Heat bank can operate at higher pressures, usually meaning good flows. If having 15mm on the draw-offs, have a manifold at the heat bank, which means all the DHW draw-offs go back to the one point My unvented system was at 1bar pressure but it had a reasonable flow rate. My house now has a higher pressure but the flow is rubbish so that really needs to be checked before anyone starts fitting the mains fed systems. |
#18
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
wrote in message ps.com... Doctor Drivel wrote: "Christian McArdle" wrote in message Best go for a heat bank as unvented cylinders require an annual service of approx £100. I used to have an unvented system and I was never required to have or to pay for a service. "Every" maker stipulates an annual service. Heat bank can operate at higher pressures, usually meaning good flows. If having 15mm on the draw-offs, have a manifold at the heat bank, which means all the DHW draw-offs go back to the one point My unvented system was at 1bar pressure but it had a reasonable flow rate. My house now has a higher pressure but the flow is rubbish so that really needs to be checked before anyone starts fitting the mains fed systems. Yep. good pressure does not mean good flow. It can be improved greatly by installing an accumulator. |
#19
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Doctor Drivel wrote: I used to have an unvented system and I was never required to have or to pay for a service. "Every" maker stipulates an annual service. Yeah but it's usally refreshing the bubble or checking the pressure vessel, and a quick check of the safety valves all of which can be done whenever you like in a matter of minutes. I don't know though these days whether one still needs local council/water board approval to fit one. |
#20
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
wrote in message ups.com... Doctor Drivel wrote: I used to have an unvented system and I was never required to have or to pay for a service. "Every" maker stipulates an annual service. Yeah but it's usally refreshing the bubble or checking the pressure vessel, and a quick check of the safety valves all of which can be done whenever you like in a matter of minutes. The service "has" to undertaken by an "approved" unnted certificate installr. Thermal stores/heat banks can be DIYed and no annual service. Have a leak and if no service and proof of service then no insurance payout. I don't know though these days whether one still needs local council/water board approval to fit one. An unvented cylinder? Only an "approved" unvented certificate installer can install one. It is againt the law to fit one otherwise, unless signed off by a BCO. |
#21
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
On Tue, 22 Aug 2006 00:18:30 +0100, The Natural Philosopher wrote:
Ed Sirett wrote: On Mon, 21 Aug 2006 16:40:56 +0100, The Natural Philosopher wrote: Christian McArdle wrote: If all is OK, you will need a 210L (or thereabouts) unvented cylinder My bath is 500x1500x300mm deep. It takes 225 liters to fill it. I have a 700 liter tank, and sometimes that isn't enough.. Something wrong here... 1)The water in the bath is not pure HW so it will only consume around half that quantity of HW. 2) Your bath is sized like most peoples however when you get in it, you only need the water around you (as you will displace anything from 50-100 litres). The received wisdom is that 70 litres of HW water needs to be stored per bathroom. (Obvious teenage mermaids and "celebs" taking "hollywood showers" make for a bit more still). I never let received wisdom get in the way of personal experience. In which case something is not working aright. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards |
#22
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
On Mon, 21 Aug 2006 22:58:58 +0100, Doctor Drivel wrote:
"Dave Plowman (News)" wrote in message ... In article .com, Matthew wrote: So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. Chances are the hotel had a gravity fed system... Chances are it will not. For once, this once at least, I agree with you. -- Ed Sirett - Property maintainer and registered gas fitter. The FAQ for uk.diy is at http://www.diyfaq.org.uk Gas fitting FAQ http://www.makewrite.demon.co.uk/GasFitting.html Sealed CH FAQ http://www.makewrite.demon.co.uk/SealedCH.html Choosing a Boiler FAQ http://www.makewrite.demon.co.uk/BoilerChoice.html Gas Fitting Standards Docs he http://www.makewrite.demon.co.uk/GasFittingStandards |
#23
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
"Ed Sirett" wrote in message news On Mon, 21 Aug 2006 22:58:58 +0100, Doctor Drivel wrote: "Dave Plowman (News)" wrote in message ... In article .com, Matthew wrote: So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. Chances are the hotel had a gravity fed system... Chances are it will not. For once, this once at least, I agree with you. Best you always, as it will be much easier for you then. |
#24
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Ed Sirett wrote:
On Mon, 21 Aug 2006 22:58:58 +0100, Doctor Drivel wrote: "Dave Plowman (News)" wrote in message ... In article .com, Matthew wrote: So the time has finally come. Actually staying in hotel last week with a fantastic shower was the last nail in the coffin for our pathetic gravity feed system. Chances are the hotel had a gravity fed system... Chances are it will not. For once, this once at least, I agree with you. Thats the trouble with huge quantities of high pressure hot water. the temptation to stay luxuriating in it for hours... |
#25
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
Doctor Drivel wrote: The service "has" to undertaken by an "approved" unnted certificate installr. Thermal stores/heat banks can be DIYed and no annual service. Have a leak and if no service and proof of service then no insurance payout. Says who? An unvented cylinder? Only an "approved" unvented certificate installer can install one. It is againt the law to fit one otherwise, unless signed off by a BCO. ...but who-ever fits it also needs local approval. i.e the fitter still needs to get approval to fit one, even if they're registered. |
#26
Posted to uk.d-i-y
|
|||
|
|||
Unvented hot water.
wrote in message oups.com... Doctor Drivel wrote: The service "has" to undertaken by an "approved" unvented certificate installer. Thermal stores/heat banks can be DIYed and no annual service. Have a leak and if no service and proof of service then no insurance payout. Says who? The service? Having an unvented certificate? The government say that. Payout by insurance? The insurance companies. An unvented cylinder? Only an "approved" unvented certificate installer can install one. It is againt the law to fit one otherwise, unless signed off by a BCO. ..but who-ever fits it also needs local approval. i.e the fitter still needs to get approval to fit one, even if they're registered. He doesn't get approval. He fits it. He then registers the fitting with the LA. |
Reply |
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
AquaTherm Furnace - No Hot Water Issue | Home Repair | |||
The #1 rated home water filter in America Aquasana AQ-4000 | Home Ownership | |||
Detergents and cleaners FAQ | UK diy | |||
hot water recirculator, instant hot water but not a water heating unit, saves water, gas, time, money | Home Repair |