Can I cut out channels for cable on the underside of a beam (i.e. in the
ceiling downstairs)
for wiring purposes?
or can you only cut out sections on the top of the beam?
Weakening the beam is my worry
ta
--
Vass


  #2   Report Post  
Posted to uk.d-i-y
Tim S
 
Posts: n/a
Default wood beams and electrics

On Wed, 04 Jan 2006 08:57:17 +0000, Vass wrote:

Can I cut out channels for cable on the underside of a beam (i.e. in the
ceiling downstairs)
for wiring purposes?
or can you only cut out sections on the top of the beam?
Weakening the beam is my worry
ta


In the case of regular joists:

Hole through the centre neutral axis are preferred as these have little
effect on the strength.

The top is in max compression and the bottom is in max tension so notching
out top or bottom does weaken the beam.

Having said that, the beam *may* be so over specified as to not care.
Distance from the end of the beam is a factor too.

The real downside with this is tendency to put nails through cables later,
which is another reason why the centre is preferred.

Is it a joist (8x2, 4x2 etc) or a big heavy beam a la period cottage that
you have?

Tim
  #3   Report Post  
Posted to uk.d-i-y
Vass
 
Posts: n/a
Default wood beams and electrics


"Tim S" wrote in message
news
On Wed, 04 Jan 2006 08:57:17 +0000, Vass wrote:
In the case of regular joists:

Hole through the centre neutral axis are preferred as these have little
effect on the strength.

The top is in max compression and the bottom is in max tension so notching
out top or bottom does weaken the beam.

Having said that, the beam *may* be so over specified as to not care.
Distance from the end of the beam is a factor too.

The real downside with this is tendency to put nails through cables later,
which is another reason why the centre is preferred.

Is it a joist (8x2, 4x2 etc) or a big heavy beam a la period cottage that
you have?


1961 Semi - 8 x 2 joists
--
Vass


  #4   Report Post  
Posted to uk.d-i-y
Vass
 
Posts: n/a
Default wood beams and electrics


"John Rumm" wrote in message
...
There are two issues to factor he structural integrity of the beam, and
safety of the wiring.

The preferred solution is to drill through the middle of the beam since
this has least impact on it structurally, and also keeps the wires well
out of reach of damage. Even then there are guidelines in the building
regs about the maximum size of hole, and also where in the span it is best
placed (span/4 at each end being best IIRC).

Electrically, if you place wires into a ceiling notched into the bottom of
a joist, they are out of the expected "zones" for wiring runs and not at
sufficient depth (50mm) to be protected. Hence they will need additional
mechanical protection to make sure they can't be screwed or nailed into.
The same issues need to be considered if the wires are supported directly
below a floor covering.


OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart (approx)?
ta
--
Vass


  #5   Report Post  
Posted to uk.d-i-y
Rick
 
Posts: n/a
Default wood beams and electrics

On Wed, 4 Jan 2006 08:57:17 -0000, "Vass"
wrote:

Can I cut out channels for cable on the underside of a beam (i.e. in the
ceiling downstairs)
for wiring purposes?
or can you only cut out sections on the top of the beam?
Weakening the beam is my worry
ta


Only in the top, and only in certan zones, and certan max sizes,
according to my book on building regs.

Rick



  #6   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Vass wrote:

Can I cut out channels for cable on the underside of a beam (i.e. in the
ceiling downstairs)
for wiring purposes?


yes, but best you don't

or can you only cut out sections on the top of the beam?


not ideal there either! ;-)

Weakening the beam is my worry


There are two issues to factor he structural integrity of the beam,
and safety of the wiring.

The preferred solution is to drill through the middle of the beam since
this has least impact on it structurally, and also keeps the wires well
out of reach of damage. Even then there are guidelines in the building
regs about the maximum size of hole, and also where in the span it is
best placed (span/4 at each end being best IIRC).

Electrically, if you place wires into a ceiling notched into the bottom
of a joist, they are out of the expected "zones" for wiring runs and not
at sufficient depth (50mm) to be protected. Hence they will need
additional mechanical protection to make sure they can't be screwed or
nailed into. The same issues need to be considered if the wires are
supported directly below a floor covering.


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #7   Report Post  
Posted to uk.d-i-y
Brian
 
Posts: n/a
Default wood beams and electrics


"John Rumm" wrote in message
...
Vass wrote:

Can I cut out channels for cable on the underside of a beam (i.e. in the
ceiling downstairs)
for wiring purposes?


yes, but best you don't

or can you only cut out sections on the top of the beam?


I have never been in a house that doesn't have sections cut out of the tops
of beams! They had been wired when the 15th edition regs were about. All
done by professionals! It doesn't do any harm unless you go wild and hack
away half the beam.


  #8   Report Post  
Posted to uk.d-i-y
Alan
 
Posts: n/a
Default wood beams and electrics


"Vass" wrote in message
...

"John Rumm" wrote in message
...
There are two issues to factor he structural integrity of the beam,
and safety of the wiring.

The preferred solution is to drill through the middle of the beam since
this has least impact on it structurally, and also keeps the wires well
out of reach of damage. Even then there are guidelines in the building
regs about the maximum size of hole, and also where in the span it is
best placed (span/4 at each end being best IIRC).

Electrically, if you place wires into a ceiling notched into the bottom
of a joist, they are out of the expected "zones" for wiring runs and not
at sufficient depth (50mm) to be protected. Hence they will need
additional mechanical protection to make sure they can't be screwed or
nailed into. The same issues need to be considered if the wires are
supported directly below a floor covering.


OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart
(approx)?
ta
--
Vass


I find that a long (12" long or more) spade bit works well for this,
allowing you to drill at an angle with just the shaft of the bit rubbing on
the adjacent beam while drilling, keeping the drill itself out of the way.
You'll end up with angled holes however.

An alternative is to hire a R/A drill and use a short spade bit or hole
cutter.

Alan.



  #9   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Vass wrote:

OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart (approx)?


Hacksaw the end off a spade bit - leaving enough shank such that when
inserted into a drill there is about a joists thickness left sticking
out. Obviously opt for a short drill as well. I find a spade bit in my
18V cordless combi just fits between 3" wide joists on 400mm spacings. A
small corded power drill will also probably fit - the bottom of the
range elcheapo shed specials without any gearbox etc are often quite short.

Failing that you can get a right angle drilling adaptor for under £20.
These are not ideal however and best avoided if you can find another way
of doing it.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #10   Report Post  
Posted to uk.d-i-y
Lobster
 
Posts: n/a
Default wood beams and electrics

Tim S wrote:
On Wed, 04 Jan 2006 08:57:17 +0000, Vass wrote:


Can I cut out channels for cable on the underside of a beam (i.e.
in the ceiling downstairs) for wiring purposes? or can you only cut
out sections on the top of the beam? Weakening the beam is my worry


The real downside with this is tendency to put nails through cables
later, which is another reason why the centre is preferred.


These things are just the job for protecting cables in notches (top or
bottom of joists):
http://www.screwfix.com/app/sfd/cat/pro.jsp?cId=101228&ts=68294&id=30038

David


  #11   Report Post  
Posted to uk.d-i-y
Douglas de Lacey
 
Posts: n/a
Default wood beams and electrics

John Rumm wrote:
Vass wrote:

OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart
(approx)?



Hacksaw the end off a spade bit - leaving enough shank such that when
inserted into a drill there is about a joists thickness left sticking
out. Obviously opt for a short drill as well. I find a spade bit in my
18V cordless combi just fits between 3" wide joists on 400mm spacings. A
small corded power drill will also probably fit - the bottom of the
range elcheapo shed specials without any gearbox etc are often quite short.

Failing that you can get a right angle drilling adaptor for under £20.
These are not ideal however and best avoided if you can find another way
of doing it.


Brace and bit?

Douglas de Lacey
  #12   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Brian wrote:

I have never been in a house that doesn't have sections cut out of the tops


no, me neither!

of beams! They had been wired when the 15th edition regs were about. All
done by professionals! It doesn't do any harm unless you go wild and hack
away half the beam.


Plumbers and CH fitters tend to do far worse the electricians as well it
seems ;-)

It is one of those things that probably does not matter in most cases if
you are sensible. So think where you are in the span of long beams and
avoid the high stress sections, only notch in the centre of floor boards
so there is less chance of the board being nailed back through the wires
etc. Ceilings are a bit more dodgy since you less expect wires just
under the surface there.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #13   Report Post  
Posted to uk.d-i-y
Cicero
 
Posts: n/a
Default wood beams and electrics


"Brian" wrote in message
...

"John Rumm" wrote in message
...
Vass wrote:

Can I cut out channels for cable on the underside of a beam (i.e. in
the ceiling downstairs)
for wiring purposes?


yes, but best you don't

or can you only cut out sections on the top of the beam?


I have never been in a house that doesn't have sections cut out of the
tops of beams! They had been wired when the 15th edition regs were

about.
All done by professionals! It doesn't do any harm unless you go wild

and
hack away half the beam.


=================
See here for the general idea:

http://www.tlc-direct.co.uk/Main_Ind...essities~Cable
_Protection/index.html

Focus currently have a right angle drill attachment for about £8-00.

Cic.



  #14   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Douglas de Lacey wrote:

Brace and bit?


Can work, but these tend to be quite long, so you either have to drill
your hole at an angle (less of a problem with wires but a pain for
pipes), or sometimes you may get lucky and find the offset bit of the
brace lines up with the next joist and you can get a half rotation out
of it!

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #15   Report Post  
Posted to uk.d-i-y
Cicero
 
Posts: n/a
Default wood beams and electrics


"John Rumm" wrote in message
...
Douglas de Lacey wrote:

Brace and bit?


Can work, but these tend to be quite long, so you either have to drill
your hole at an angle (less of a problem with wires but a pain for

pipes),
or sometimes you may get lucky and find the offset bit of the brace

lines
up with the next joist and you can get a half rotation out of it!

--
Cheers,

John.

========================
Screwfix do these:
http://www.screwfix.com/app/sfd/cat/...73211&id=12082

They will fit an electric drill as well as the conventional brace.

There used to be a brace similar to a socket set ratchet which was
excellent
for getting into tight spaces. Unfortunately, it appears to have
disappeared
from the market. Maybe somebody will know if they're still available.

Cic.






  #16   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Cicero wrote:

Screwfix do these:
http://www.screwfix.com/app/sfd/cat/...73211&id=12082


Still a bit long at 4" though... and you can't cut them down like one of
these:

http://www.screwfix.com/app/sfd/cat/...75084&id=16901

They will fit an electric drill as well as the conventional brace.

There used to be a brace similar to a socket set ratchet which was
excellent
for getting into tight spaces. Unfortunately, it appears to have
disappeared
from the market. Maybe somebody will know if they're still available.


You might find if they have a hex end that an ordinary socket will fit.

--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #17   Report Post  
Posted to uk.d-i-y
Mike Barnes
 
Posts: n/a
Default wood beams and electrics

In uk.d-i-y, Cicero wrote:
Screwfix do these:
http://www.screwfix.com/app/sfd/cat/...73211&id=12082

They will fit an electric drill as well as the conventional brace.


If you use one of those in an electric drill, be *very* careful. It can
screw itself down a hole faster than a ferret after a rabbit.

--
Mike Barnes
  #18   Report Post  
Posted to uk.d-i-y
Cicero
 
Posts: n/a
Default wood beams and electrics

wrote in message
...
Cicero wrote:

Screwfix do these:
http://www.screwfix.com/app/sfd/cat/...73211&id=12082


Still a bit long at 4" though... and you can't cut them down like one of
these:

http://www.screwfix.com/app/sfd/cat/...75084&id=16901

They will fit an electric drill as well as the conventional brace.

There used to be a brace similar to a socket set ratchet which was
excellent
for getting into tight spaces. Unfortunately, it appears to have
disappeared
from the market. Maybe somebody will know if they're still available.


You might find if they have a hex end that an ordinary socket will fit.

--
Cheers,

John.

===============
They do have a hex end and they do fit a in a small socket. As far as
cutting a spade bit to length is concerned, you couldn't cut it much shorter
(if at all) than the auger bit so there's no real difference between the
two. However as another poster points out the auger bit can be rather fierce
in a power drill so it pays to use the slowest practical speed.

Cic.


  #19   Report Post  
Posted to uk.d-i-y
Vass
 
Posts: n/a
Default wood beams and electrics


"Vass" wrote in message
...

thanks for all advice
--
Vass


  #20   Report Post  
Senior Member
 
Posts: 242
Talking

Quote:
Originally Posted by Douglas de Lacey
John Rumm wrote:
Vass wrote:

OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart
(approx)?



Hacksaw the end off a spade bit - leaving enough shank such that when
inserted into a drill there is about a joists thickness left sticking
out. Obviously opt for a short drill as well. I find a spade bit in my
18V cordless combi just fits between 3" wide joists on 400mm spacings. A
small corded power drill will also probably fit - the bottom of the
range elcheapo shed specials without any gearbox etc are often quite short.

Failing that you can get a right angle drilling adaptor for under £20.
These are not ideal however and best avoided if you can find another way
of doing it.


Brace and bit?

Douglas de Lacey
How will a pair of tits help you?!?


  #21   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Cicero wrote:

They do have a hex end and they do fit a in a small socket. As far as
cutting a spade bit to length is concerned, you couldn't cut it much shorter
(if at all) than the auger bit so there's no real difference between the


You can cut a spade to have only 2" projecting from the end of the drill
if required - not sure you could do that with an auger.

(also less sure I would want to go trashing a good auger bit in the
first place!)




--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #22   Report Post  
Posted to uk.d-i-y
Cicero
 
Posts: n/a
Default wood beams and electrics


"John Rumm" wrote in message
...
Cicero wrote:

They do have a hex end and they do fit a in a small socket. As far as
cutting a spade bit to length is concerned, you couldn't cut it much
shorter (if at all) than the auger bit so there's no real difference
between the


You can cut a spade to have only 2" projecting from the end of the drill
if required - not sure you could do that with an auger.

(also less sure I would want to go trashing a good auger bit in the

first
place!)




--
Cheers,

John.

=====================
My 25mm (95mm long) auger bit (Screwfix) projects 2.75" (70mm) from the
drill chuck. Cutting a 25mm spade bit to the shortest feasible length
would
leave a minimum projection of 2.625" (67mm) - a difference of only 1/8"
(3mm).

Lengths are proportionately less for smaller sizes of auger / spade bits,
so
there's not much to be gained by cutting a spade bit.

Cic.



  #23   Report Post  
Posted to uk.d-i-y
Andy Wade
 
Posts: n/a
Default wood beams and electrics

John Rumm wrote:

Douglas de Lacey wrote:
Brace and bit?


Can work, but these tend to be quite long, so you either have to drill
your hole at an angle (less of a problem with wires but a pain for
pipes), or sometimes you may get lucky and find the offset bit of the
brace lines up with the next joist and you can get a half rotation out
of it!


You'll be wanting a joist brace...
e.g. http://www.antiquetools.co.uk/1291.html

--
Andy
  #24   Report Post  
Posted to uk.d-i-y
John Rumm
 
Posts: n/a
Default wood beams and electrics

Andy Wade wrote:

You'll be wanting a joist brace...
e.g. http://www.antiquetools.co.uk/1291.html


Nice looking bit of kit....

Don't fancy the price much though!


--
Cheers,

John.

/================================================== ===============\
| Internode Ltd - http://www.internode.co.uk |
|-----------------------------------------------------------------|
| John Rumm - john(at)internode(dot)co(dot)uk |
\================================================= ================/
  #25   Report Post  
Posted to uk.d-i-y
Rob Morley
 
Posts: n/a
Default wood beams and electrics

In article
Vass wrote:
snip

OK great thanks for the advice, but not having seen a right angled drill
how do I get a hole in the centre with joists just 12 inches apart (approx)?

lawson-his.co.uk/scripts/details.php?cat=Rotary%20Drills&product=27147
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 03:30 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"