#41
|
|||
|
|||
"AlexW" wrote in message ... Rob Morley wrote: In article , says... snip My original response was to Bob Eager's point blank "no it doesn't" which is not specific at all as to why it "doesn't". I inadvertantly accused Bob Mannix snipping here and lack of clarity ... apologies, I mis-read the sender in the thread. Ah full circle. Apology accepted ). My comment about the trap was because I guessed Bob Eager put what he did (out of devilment) to see how long people argued about the reversing direction bit before realising it was the 50 that was wrong (which, if I may say, you weren't clear about realising/accepting, hence my other comments). Of course it may not have been like that at all, only he can say. -- Bob Mannix (anti-spam is as easy as 1-2-3 - not) |
#42
|
|||
|
|||
I dont want to be pedantic but AC current is just swapping the positive
and negative electrodes around 50 or 100 times a second, so positive and negative are switched around by AC current, http://www.tpub.com/neets/book2/1.htm AC AND DC Alternating current is current which constantly changes in amplitude, and which reverses direction at regular intervals. You learned previously that direct current flows only in one direction, and that the amplitude of current is determined by the number of electrons flowing past a point in a circuit in one second. If, for example, a coulomb of electrons moves past a point in a wire in one second and all of the electrons are moving in the same direction, the amplitude of direct current in the wire is one ampere. Similarly, if half a coulomb of electrons moves in one direction past a point in the wire in half a second, then reverses direction and moves past the same point in the opposite direction during the next half-second, a total of one coulomb of electrons passes the point in one second. The amplitude of the alternating current is one ampere. The preceding comparison of dc and ac as illustrated. Notice that one white arrow plus one striped arrow comprise one coulomb. |
#43
|
|||
|
|||
blackboab wrote: The LIVE and NEUTRAL wires are both passing current and the current is reversing at 50 times a second so that they swap over the roles of positive and negative. can i get electrocuted by holding the NEUTRAL ? a circuit only needs two wires to be complete. so how does the third wire - ground - fit in the circuit ? See http://amasci.com/amateur/whygnd.html MBQ |
#44
|
|||
|
|||
great article. the current goes from live to neutral and back again 50
times a second as explained here @@@@@@@@@@@@@@@@@@@@@@' But still, every once in a while a Customer will get a really nasty shock from a cheap plastic appliance that's wet. Or perhaps an electric hair dryer will fall into the bathtub, but the short-circuit current in the water won't be enough to blow the fuses in the house, and the bathtub water will become lethal. In theory there is a way to prevent this. These Customer shocks are happening because the customers' bodies offer a path for current between the appliance and the lightning-safety earth grounds. During the shocking event, some of the flowing charge is going in (and out) of the "hot" wire, but it is NOT going back into (and out of) the "neutral" wire as it's supposed to. Instead, it's going through the human, and also going into the grounded pipes of the plumbing. If we could measure the current that's taking the "wrong" path, maybe we could detect the problem and turn off the power before anyone dies. We can't measure the current in the plumbing, but we can measure it in the "hot" wire, measure the current in the "neutral" wire, then subtract them. This tells us what level of current was escaping via the "illegal" path through the human to ground. The subtraction should normally give a zero result, since there never should be a current path to ground that isn't using the neutral wire. If we amplify the subtraction's result and use it to trip a circuit breaker, we'll have a new type of appliance which turns itself off immediately when a human gets into the electrical path. These devices are now required in wet areas of homes (bathrooms.) They're called Ground Fault Interrupters. And so we've finally entered modern times, the "Age of the Electric Outlet with the Little Red Button Which Pops Out!" |
#45
|
|||
|
|||
On Wed, 5 Oct 2005 15:37:09 UTC, "Bob Mannix"
wrote: "AlexW" wrote in message ... My original response was to Bob Eager's point blank "no it doesn't" which is not specific at all as to why it "doesn't". I inadvertantly accused Bob Mannix snipping here and lack of clarity ... apologies, I mis-read the sender in the thread. Ah full circle. Apology accepted ). My comment about the trap was because I guessed Bob Eager put what he did (out of devilment) to see how long people argued about the reversing direction bit before realising it was the 50 that was wrong (which, if I may say, you weren't clear about realising/accepting, hence my other comments). Of course it may not have been like that at all, only he can say. You're absolutely right! Although I'm surprised that Alex didn't just put his hand up and admit he was wrong...! I snipped because I wasn't answering the other part... -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by Avenue Supplies, http://avenuesupplies.co.uk |
#46
|
|||
|
|||
On 5 Oct 2005 09:16:56 -0700, "blackboab"
scrawled: These devices are now required in wet areas of homes (bathrooms.) They're called Ground Fault Interrupters. And so we've finally entered modern times, the "Age of the Electric Outlet with the Little Red Button Which Pops Out!" Er, this is uk.d-i-y, note the UK bit. -- Stuart @ SJW Electrical Please Reply to group |
#47
|
|||
|
|||
Bob Mannix wrote:
Well I would make the assumption (for my own safety) that given a 240V supply might generate stray neutral voltages of up to 30V Higher voltages are not unknown on isolated overhead LV supplies in the sticks (cue "Wanderer"). a 330kv one *might* generate neutral voltages of up to 30kv. Of course it might not, as such supplies would be three phase and arranged differently, but I wouldn't take the chance myself! An HV supply won't usually have a distributed neutral conductor (just 3-phase, 3-wire). There'll be a neutral point at the transformer or generator, earthed via a known impedance, but only the 3 phase conductors head off outwards. -- Andy |
#48
|
|||
|
|||
i know.
but most of the information is still relevant. say what you want about the yanks being imperialist , war-mongering *******s but their technical knowledge is pretty impressive, at least they make good websites, |
#49
|
|||
|
|||
Bob Eager wrote:
On Wed, 5 Oct 2005 15:37:09 UTC, "Bob Mannix" wrote: "AlexW" wrote in message .. . My original response was to Bob Eager's point blank "no it doesn't" which is not specific at all as to why it "doesn't". I inadvertantly accused Bob Mannix snipping here and lack of clarity ... apologies, I mis-read the sender in the thread. Ah full circle. Apology accepted ). My comment about the trap was because I guessed Bob Eager put what he did (out of devilment) to see how long people argued about the reversing direction bit before realising it was the 50 that was wrong (which, if I may say, you weren't clear about realising/accepting, hence my other comments). Of course it may not have been like that at all, only he can say. You're absolutely right! Although I'm surprised that Alex didn't just put his hand up and admit he was wrong...! Oh you would say that ;-) Why be surprised? To be honest shortly after sending my first reply the sinusoid entered my head and I realised exactly 50 changes = 25 Hz but did not consider it was a trick question ... and my attention was elsewhere for a while .... After Bob M's post and decided if trick questions were the name of the game then actually I was not wrong in the strictest sense. Rob was right about wriggling ... but hey why not if you've been set up. I snipped because I wasn't answering the other part... |
#50
|
|||
|
|||
AlexW wrote:
I thought it did actually as Electrons flow from -ve to +ve IIRC, or the current flows from +ve to -ve in conventional notation. The live is always energised though with either a +ve or -ve potential wrt the neutral. Alex. That's an approximation. If the frequency is high enough, and/or the distance is long enough, a lot of the power gets carried as an electromagentic wave around the conductor. I'm used to seeing this at MHz and GHz ranges in short conductors, but I'm pretty sure this is why HT pylons have 4 wires with airgaps for each conductor. Andy |
#51
|
|||
|
|||
Bob Mannix wrote:
"AlexW" wrote in message ... Bob Mannix wrote: "AlexW" wrote in message . .. Bob Eager wrote: On Wed, 5 Oct 2005 08:53:23 UTC, "blackboab" wrote: AC current changes direction 50 times a second No, it doesn't. I thought it did actually as Electrons flow from -ve to +ve IIRC, or the current flows from +ve to -ve in conventional notation. The live is always energised though with either a +ve or -ve potential wrt the neutral. You fell into his little trap! It changes direction 100 times per second, having a burst in both directions 50 times a second. Trap? It still changes 50 times second though for the UK supply, the limits would be a minimum of 99 to 101 times. So that would be 100, not 50 AC current could actually change at any frequency. Well so it could but it *could* also be a 330,000 V AC supply, in which case I wouldn't touch the neutral! If the conditions were right, I'd touch the Phase. Since 33kV is probably going to be 3 phase, I'd say any one of them... |
#52
|
|||
|
|||
"Bob Mannix" wrote:
Well so it could but it *could* also be a 330,000 V AC supply, in which case I wouldn't touch the neutral! Not in the UK it couldn't (330kV that is) -- |
#53
|
|||
|
|||
On Wed, 05 Oct 2005 20:41:54 +0000, Andy Champ wrote:
I'm pretty sure this is why HT pylons have 4 wires with airgaps for each conductor. They always seem to have cables in multiples of 3 whenever I look. One group for each phase. -- Gooooooood Morning Cyberspace |
#54
|
|||
|
|||
In article ,
John Laird writes: On Wed, 05 Oct 2005 20:41:54 +0000, Andy Champ wrote: I'm pretty sure this is why HT pylons have 4 wires with airgaps for each conductor. They always seem to have cables in multiples of 3 whenever I look. One group for each phase. 275,000V is a bundle of two, and 400,000V is a bundle of four. This is to reduce the electric field strength which in turn reduces the corona discharge. Or maybe you are referring to the 3 or 6 lines carried, which will be for one or two 3-phase circuits? -- Andrew Gabriel |
#55
|
|||
|
|||
Simon wrote:
Everyone seems to be saying tripping out the lights is a bad Idea as you may fall over in the dark, so why not have two RCDs, one for lights and one for everything else. I must admit ours is old and protects everything. I have Nothing wrong with multiple RCDs. If you are on a TT install then that is the way to go anyway. The ultimate solution you could argue would be a RCBO for each circuit that needs one. The argument against RCDs, is the problems of unwanted trips as a result of "normal" leakage (some types of appliance are prone to it because they have mineral insulated heating elements, or capacitive filters on their mains inputs). For circuits that present very little real risk of electrocution the negatives may outweigh the positives. never found it turning the lights off a problem. I have only ever tripped it by accidentally touching the neutral, I never had the nerve to touch the live to see if it hurt. I have always liked the idea that everything in the house was protected so that I have to do something very foolish before I can electrocute myself. Just wish that there was one light in the garage that came on so that I could climb across all the junk in the garage to reset it. Why not add a non maintained emergency light then? About £20 from TLC. Wire it to a feed on the lighting circuit in there. That will keep it charged. When the power goes off it lights up. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#56
|
|||
|
|||
blackboab wrote:
but most of the information is still relevant. Apart from the bit about having sockets allowed in bathrooms... say what you want about the yanks being imperialist , war-mongering *******s but their technical knowledge is pretty impressive, at least they make good websites, Alas their electrical installations are of state of the ark in comparison to ours. So of very limited use as a source of reference material. -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#57
|
|||
|
|||
really ? how do they manage to do things like the space shuttle ?
then again two of those crashed and they lost 2 space probes they sent to Mars. Perhaps they arent as great as they like to think. what is the worst thing about their electrical systems ? |
#58
|
|||
|
|||
On 5 Oct 2005 23:24:42 -0700, blackboab wrote:
really ? how do they manage to do things like the space shuttle ? then again two of those crashed and they lost 2 space probes they sent to Mars. Perhaps they arent as great as they like to think. what is the worst thing about their electrical systems ? Err, how about twisted joints? -- the dot wanderer at tesco dot net |
#59
|
|||
|
|||
"Matt" wrote in message ... "Bob Mannix" wrote: Well so it could but it *could* also be a 330,000 V AC supply, in which case I wouldn't touch the neutral! Not in the UK it couldn't (330kV that is) OK, OK everyone! I accept that such systems are 3-phase without a neutral return. I thought 330kv was one of the standards (it clearly isn't). I was making a general point about the context of the original question determining the supply details - of course I realised almost immediately there would be nationalgridophiles who would descend on me ).. Actually it struck me there is an interesting psychological point - the overhead supplies in our street are 240V 3phase with neutral (every house is connected to the neutral and they are spread across the phases). While I am happy to touch the neutral in the house, I would be less happy to touch the neutral on the pole, but they are connected together so that's illogical but there you go. -- Bob Mannix (anti-spam is as easy as 1-2-3 - not) |
#60
|
|||
|
|||
Andrew Gabriel wrote:
275,000V is a bundle of two, and 400,000V is a bundle of four. This is to reduce the electric field strength which in turn reduces the corona discharge. There are two other benefits to bundling: - it significantly reduces the inductance (and hence the voltage drop), - it improves cooling of the conductors. At full winter load those 400 kV lines are carrying about 3,000 amps per bundle, so they do tend to get a bit warm. -- Andy |
#61
|
|||
|
|||
care to elaborate ?
you arent talking about their use of torture at Abu Ghraib and Guantanamo are you ? |
#62
|
|||
|
|||
blackboab wrote:
really ? how do they manage to do things like the space shuttle ? Don't see the connection to domestic electrics... hardly rocket science is it? ;-) then again two of those crashed and they lost 2 space probes they sent to Mars. Perhaps they arent as great as they like to think. Even monkeys fall out of trees... what is the worst thing about their electrical systems ? Hard to choose one really... we had a long thread on this a while back. In general they seem to have a lower level of "respect" for the electrical systems in houses - possibly due to lower perceived risk from the 110V supply they mostly use. However the lower supply voltage (hence higher current and heating effect) combined with the permitted use of poor wire jointing technique (twist on "wire nuts") and extensive use of aliminuim cable seems to result in far more electrical fire risks. AAUI the quality of their switch gear and accessories is lower (paper used as insulators etc). They often don't have RCDs. Their circuit breakers often lack the "magnetic" response facility that is standard on ours, and ensure that high overcurrents are cleared very quickly. They are also pretty poor on earthing systems (like not even having one on some socket circuits!), and equipotential bonding. The lower voltage and poorer MCBs makes earth fault loop impedances far more critical, and it can be very difficult or impossible to achieve rapid disconnect times. Try this thread for mo http://groups.google.com/group/uk.d-...1e8279a6609a36 http://tinyurl.com/7h7kr -- Cheers, John. /================================================== ===============\ | Internode Ltd - http://www.internode.co.uk | |-----------------------------------------------------------------| | John Rumm - john(at)internode(dot)co(dot)uk | \================================================= ================/ |
#63
|
|||
|
|||
|
#64
|
|||
|
|||
On 6 Oct 2005 02:46:30 -0700, blackboab wrote:
care to elaborate ? you arent talking about their use of torture at Abu Ghraib and Guantanamo are you ? Twisted joints, held together by some sort of ceramic or plastic thimble. -- the dot wanderer at tesco dot net |
#66
|
|||
|
|||
"blackboab" wrote in message oups.com... really ? how do they manage to do things like the space shuttle ? then again two of those crashed and they lost 2 space probes they sent to Mars. Perhaps they arent as great as they like to think. what is the worst thing about their electrical systems ? It isn't long since this topic became a long running argument in the newsgroup. Lets not go down that road AGAIN. |
#67
|
|||
|
|||
On Thu, 6 Oct 2005 12:42:08 +0100,it is alleged that The Wanderer
spake thusly in uk.d-i-y: On 6 Oct 2005 02:46:30 -0700, blackboab wrote: care to elaborate ? you arent talking about their use of torture at Abu Ghraib and Guantanamo are you ? Twisted joints, held together by some sort of ceramic or plastic thimble. Sprung steel coil actually, and they burn up significantly less often than strip connector. -- There is no reason anyone would want a computer in their home. - Ken Olson, President of DEC, 1977 |
#68
|
|||
|
|||
On Thu, 6 Oct 2005 17:57:00 UTC, Chip wrote:
On Thu, 6 Oct 2005 12:42:08 +0100,it is alleged that The Wanderer spake thusly in uk.d-i-y: On 6 Oct 2005 02:46:30 -0700, blackboab wrote: care to elaborate ? you arent talking about their use of torture at Abu Ghraib and Guantanamo are you ? Twisted joints, held together by some sort of ceramic or plastic thimble. Sprung steel coil actually, and they burn up significantly less often than strip connector. I've also seen plain ceramic thimbles with nothing else in them....Scruits they used to be called. -- The information contained in this post is copyright the poster, and specifically may not be published in, or used by Avenue Supplies, http://avenuesupplies.co.uk |
#69
|
|||
|
|||
On 6 Oct 2005 18:27:19 GMT,it is alleged that "Bob Eager"
spake thusly in uk.d-i-y: On Thu, 6 Oct 2005 17:57:00 UTC, Chip wrote: On Thu, 6 Oct 2005 12:42:08 +0100,it is alleged that The Wanderer spake thusly in uk.d-i-y: On 6 Oct 2005 02:46:30 -0700, blackboab wrote: care to elaborate ? you arent talking about their use of torture at Abu Ghraib and Guantanamo are you ? Twisted joints, held together by some sort of ceramic or plastic thimble. Sprung steel coil actually, and they burn up significantly less often than strip connector. I've also seen plain ceramic thimbles with nothing else in them....Scruits they used to be called. Yes, nasty things they were too. US Lighting manufacturers still produce a plastic equivalent that isn't UL Listed for anything at all (not that the dang things actually fit the wires either). Admittedly the old versions without the steel spring were a little 'pointless'. The modern ones are the result of years of development, and counterintuitively provide a very good joint with copper-copper. With alumin(i)um wiring, all bets are off, most US electricians suck air in through their teeth and start mentally making out a replacement bill when they find it. -- There is no reason anyone would want a computer in their home. - Ken Olson, President of DEC, 1977 |
#70
|
|||
|
|||
In article .com,
blackboab wrote: The LIVE and NEUTRAL wires are both passing current and the current is reversing at 50 times a second so that they swap over the roles of positive and negative. It's actually 100 times a second. The 50 Hz refers to a full cycle - from zero to + then zero to - and back to zero. Relative to *both* conductors. can i get electrocuted by holding the NEUTRAL ? What causes harm is potential difference. You could have a million volt supply, and if one side is earthed you should be able to touch that conductor safely. But not the other one...;-) a circuit only needs two wires to be complete. so how does the third wire - ground - fit in the circuit ? In an ideal world both neutral and earth are at the same potential. -- *A fool and his money can throw one hell of a party. Dave Plowman London SW To e-mail, change noise into sound. |
#71
|
|||
|
|||
John Laird wrote:
How is the field strength diminished by having multiple conductors in close proximity ? (My AC knowledge is very sketchy.) It's voltage-determined, is it not ? This is basic electrostatics and is the same at DC. Field strength is potential gradient. The field close to the surface of a round wire carrying a given charge per unit length is inversely proportional to the radius of the wire. Thus field concentration and the risk of breakdown always occurs near sharp edges or points. A rough engineering approximation for more complicated structures is to think of the field as proportional to one over the radius of curvature of a structure component. That's why much of the metalwork of high voltage equipment has smooth rounded edges. You can visualise it in terms of field lines (lines of flux) being more crowded together near a feature of small radius. High electric flux density implies high field strength since the two are proportional to each other, the constant of proportionality being called permittivity. -- Andy |
#72
|
|||
|
|||
"Andy Wade" wrote in message ... John Laird wrote: How is the field strength diminished by having multiple conductors in close proximity ? (My AC knowledge is very sketchy.) It's voltage-determined, is it not ? This is basic electrostatics and is the same at DC. Field strength is potential gradient. The field close to the surface of a round wire carrying a given charge per unit length is inversely proportional to the radius of the wire. Thus field concentration and the risk of breakdown always occurs near sharp edges or points. A rough engineering approximation for more complicated structures is to think of the field as proportional to one over the radius of curvature of a structure component. That's why much of the metalwork of high voltage equipment has smooth rounded edges. You can visualise it in terms of field lines (lines of flux) being more crowded together near a feature of small radius. High electric flux density implies high field strength since the two are proportional to each other, the constant of proportionality being called permittivity. Its years since I studied this aspect but from memory the bundle of conductors "looks like" a single larger conductor with an effectively larger diameter and thus a reduction in stress/corona is achieved. Someone else might be able to recall better from less aged studies? The 4 conductor bundles associated with 400kV are relatively easy to visualise this but 275 kX with 2 conductors must "look like" an oval I suppose. As a matter of interest I had a tour round Drax power station about thirty years ago and the primary connections between the station and the grid switching breaker farm were run in single heavy bars for a short distance. The noise of frying air molecules was astounding. |
#73
|
|||
|
|||
On Fri, 7 Oct 2005 08:06:43 +0000 (UTC), "John"
wrote: "Andy Wade" wrote in message ... John Laird wrote: How is the field strength diminished by having multiple conductors in close proximity ? (My AC knowledge is very sketchy.) It's voltage-determined, is it not ? This is basic electrostatics and is the same at DC. Field strength is potential gradient. The field close to the surface of a round wire carrying a given charge per unit length is inversely proportional to the radius of the wire. Thus field concentration and the risk of breakdown always occurs near sharp edges or points. A rough engineering approximation for more complicated structures is to think of the field as proportional to one over the radius of curvature of a structure component. That's why much of the metalwork of high voltage equipment has smooth rounded edges. You can visualise it in terms of field lines (lines of flux) being more crowded together near a feature of small radius. High electric flux density implies high field strength since the two are proportional to each other, the constant of proportionality being called permittivity. Its years since I studied this aspect but from memory the bundle of conductors "looks like" a single larger conductor with an effectively larger diameter and thus a reduction in stress/corona is achieved. Someone else might be able to recall better from less aged studies? The 4 conductor bundles associated with 400kV are relatively easy to visualise this but 275 kX with 2 conductors must "look like" an oval I suppose. As a matter of interest I had a tour round Drax power station about thirty years ago and the primary connections between the station and the grid switching breaker farm were run in single heavy bars for a short distance. The noise of frying air molecules was astounding. Thanks John. Your explanation was better in helping me understand why separating the conductors would have an effect. I had a staff tour around Fawley many years ago. We didn't go out to the transformer room as the guide said he didn't like being out there ! We did get to open up one of the furnace inspection windows to feel the heat coming off it (did you know furnaces are hung from the roof to allow expansion downwards and outwards?). I've also worked for a few days in a coal station in Notts. The noise around the ball mills can only be described as mind-numbing. -- NOBODY expects the Spanish Inquisition! |
#74
|
|||
|
|||
On Fri, 7 Oct 2005 08:06:43 +0000 (UTC), John wrote:
snip Its years since I studied this aspect but from memory the bundle of conductors "looks like" a single larger conductor with an effectively larger diameter and thus a reduction in stress/corona is achieved. Someone else might be able to recall better from less aged studies? The 4 conductor bundles associated with 400kV are relatively easy to visualise this but 275 kX with 2 conductors must "look like" an oval I suppose. As a matter of interest I had a tour round Drax power station about thirty years ago and the primary connections between the station and the grid switching breaker farm were run in single heavy bars for a short distance. Quite possibly relatively thin-wall hollow bus-bar sections. Nobody has yet mentioned skin effect (until now)..... -- the dot wanderer at tesco dot net |
#75
|
|||
|
|||
The Wanderer wrote:
On Fri, 7 Oct 2005 08:06:43 +0000 (UTC), John wrote: snip Its years since I studied this aspect but from memory the bundle of conductors "looks like" a single larger conductor with an effectively larger diameter and thus a reduction in stress/corona is achieved. Someone else might be able to recall better from less aged studies? The 4 conductor bundles associated with 400kV are relatively easy to visualise this but 275 kX with 2 conductors must "look like" an oval I suppose. As a matter of interest I had a tour round Drax power station about thirty years ago and the primary connections between the station and the grid switching breaker farm were run in single heavy bars for a short distance. Quite possibly relatively thin-wall hollow bus-bar sections. Nobody has yet mentioned skin effect (until now)..... They are solid copper running at around 22kV from the generator to the generator transformer but these are totally out of sight in normal operation. On the HV substation itself they use hollow copper or more usually nowadays aluminium - but I'm not sure if you can really call 100mm diameter and 20mm wall thickness tubing "thin wall" Occasionally on 132kV sites overhead line cable was also used as a flexible busbar. Most new switchgear (and busbar) installations are metalclad using sulphur hexafluoride gas as insulation. They occupy a fraction of the land area of an air insulated site. -- |
#76
|
|||
|
|||
On Fri, 07 Oct 2005 18:22:50 +0100, Matt wrote:
The Wanderer wrote: snip Quite possibly relatively thin-wall hollow bus-bar sections. Nobody has yet mentioned skin effect (until now)..... They are solid copper running at around 22kV from the generator to the generator transformer but these are totally out of sight in normal operation. On the HV substation itself they use hollow copper or more usually nowadays aluminium - but I'm not sure if you can really call 100mm diameter and 20mm wall thickness tubing "thin wall" Occasionally on 132kV sites overhead line cable was also used as a flexible busbar. Most new switchgear (and busbar) installations are metalclad using sulphur hexafluoride gas as insulation. They occupy a fraction of the land area of an air insulated site. Ah! I guessed someone would be along to air their knowledge! Hmm, let's see, fault levels should be worth a bit of discussion.... :-) -- the dot wanderer at tesco dot net |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
Snowbirds: House plant maint. question | Home Repair | |||
gas fireplace - wiring question | Home Repair | |||
Programmable Thermostat wiring question -rth7500 | Home Repair | |||
Generator standby wiring question (again) | UK diy | |||
Question about wiring lights | UK diy |