UK diy (uk.d-i-y) For the discussion of all topics related to diy (do-it-yourself) in the UK. All levels of experience and proficency are welcome to join in to ask questions or offer solutions.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Clive M
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

Does anyone have a diagram of how a system with 2 pumps and no valves is
wired together to give interlock? Secondly how does pump overrun work if 2
pumps are used (i assume you have to dump into the CH cylinder)


  #2   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

Does anyone have a diagram of how a system with 2 pumps and no valves is
wired together to give interlock?


Very simple. Wire the programmer output through the appropriate room or
cylinder thermostat to the pump. The same connections should also be made to
a relay. The Normally Open outputs of the relay should be connected together
in parallel and be used to run the boiler interlock.

Secondly how does pump overrun work if 2 pumps are used (i assume you
have to dump into the CH cylinder)


This gets a little more complicated. You basically need the pump overrun
output of the boiler to run the hot water pump. However, it is essential
that this doesn't end up as a call for heat back at the interlock, or it
will never switch off. You also don't want the HWC pump to run when the CH
pump is running, or the HWC will overheat.

Let's draw a logic diagram:

Inputs:
HWC = hot water call for heat (from thermostat/programmer)
CHC = central heating call for heat (from thermostat/programmer)
POR = pump overrun from boiler

Output:
HWP = Hot water pump
CHP = CH pump
BIL = boiler interlock
(T) = should be impossible or transient condition only


HWC CHC POR | HWP CHP BIL
0 0 0 | 0 0 0
0 0 1 | 1 0 0
0 1 0 | 0 1 1 (T)
0 1 1 | 0 1 1
1 0 0 | 1 0 1 (T)
1 0 1 | 1 0 1
1 1 0 | 1 1 1 (T)
1 1 1 | 1 1 1

(Alternative for DHW priority)
1 1 0 | 1 0 1 (T)
1 1 1 | 1 0 1

This gives

HWP = HWC OR ( POR AND NOT CHC)
CHP = CHC
BIL = HWC OR CHC

So, connect CHC directly to the CHP pump.
BIL is run by paralleled relays from HWC and CHC.
HWP is harder, but can be done with a few relays.

To be honest, I'd be inclined the run the whole control system in low
voltage logic (i.e. 5V 74LS/74HC) and end up in a nice relay for the boiler.
But then, it would be simple for someone like me to throw together something
on a bit of stripboard with a 7805, a wallwart and a handful of SSI logic
chips.

Christian.


  #3   Report Post  
Set Square
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In an earlier contribution to this discussion,
Clive M wrote:

Does anyone have a diagram of how a system with 2 pumps and no valves
is wired together to give interlock? Secondly how does pump overrun
work if 2 pumps are used (i assume you have to dump into the CH
cylinder)


I don't have an official diagram, but I've just drawn one on the back of an
envelope which I think will work. If I describe it, you should be able to
replicate it. I will deal with only the live connections, leaving you to put
in all the neutrals and earths.

On the left is the programmer, with feeds for HW and CH
To the right, one above the other, are the cylinder stat and room stat. Both
are normally closed switches, opening when the set temperature is reached
To the right of these is a mains changeover relay
To the far right is the boiler

Take a wire from the programmer's HW feed to one side of the cyl stat
Connect the other side of the cyl stat to the HW pump and to the NC contact
of the relay
Take a wire from the programmer's CH feed to one side of the room stat
Connect the other side of the room stat to the CH pump, the relay coil, and
the NO contact of the relay
Connect the relay's Common terminal to the Boiler switched live
Connect a permanently live feed to the Boiler permanent live
Connect the Boiler Pump terminal to the NC relay contact (and hence to the
HW pump)

If I am right, this will fire the boiler - plus the appropriate pump
whenever either the CH or HW or both are demanding heat, and will shut down
when neither is.
If the boiler's pump over-run stat operates, the HW pump will run until
things cool down.

I can see one potential problem with this, which may require a mod to the
boiler's internal wiring. On my boiler, the pump outlet is connected to
switched live below the boiler stat temp, and to permanent live above the
stat temp. My diagram, as it stands, would result in the HW pump running
whenever the boiler was on - even if the HW demand was satisfied. Severing t
he internal link between switched live and pump would do the trick - only
allowing the *boiler* to switch the pump on *above* the stat temp.

HTH.

--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #4   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

"Clive M" wrote in
:

Does anyone have a diagram of how a system with 2 pumps and no valves
is wired together to give interlock? Secondly how does pump overrun
work if 2 pumps are used (i assume you have to dump into the CH
cylinder)

I've considered the Grundfos Pump Plan - seems very advantageously priced
at plumbworld ATM, and came up with this doc

UPP_Pump_Plan_05_03.pdf

but I don't know where from.

It contains a wiring diagram.

I think they also sell a complete control pack, which I would be tempted to
use if I were installing it.

I really like the idea, but it's a bit bleeding edge for me...., what
happens if one pump fails in a cold snap?

mike
  #5   Report Post  
IMM
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring


"mike ring" wrote in message
52.50...
"Clive M" wrote in
:

Does anyone have a diagram of how a system with 2 pumps and no valves
is wired together to give interlock? Secondly how does pump overrun
work if 2 pumps are used (i assume you have to dump into the CH
cylinder)

I've considered the Grundfos Pump Plan - seems very advantageously priced
at plumbworld ATM, and came up with this doc

UPP_Pump_Plan_05_03.pdf

but I don't know where from.

It contains a wiring diagram.

I think they also sell a complete control pack, which I would be tempted

to
use if I were installing it.

I really like the idea, but it's a bit bleeding edge for me...., what
happens if one pump fails in a cold snap?


What happens if a zone valve packs up?




  #6   Report Post  
raden
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In message , Christian
McArdle writes
Does anyone have a diagram of how a system with 2 pumps and no valves is
wired together to give interlock?


Very simple. Wire the programmer output through the appropriate room or
cylinder thermostat to the pump. The same connections should also be made to
a relay. The Normally Open outputs of the relay should be connected together
in parallel and be used to run the boiler interlock.

Secondly how does pump overrun work if 2 pumps are used (i assume you
have to dump into the CH cylinder)


This gets a little more complicated. You basically need the pump overrun
output of the boiler to run the hot water pump.


So where does the heat go if the taps are turned off?

Didn't you mean the central heating pump ?

--
geoff
  #7   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

This gets a little more complicated. You basically need the pump overrun
output of the boiler to run the hot water pump.


So where does the heat go if the taps are turned off?

Didn't you mean the central heating pump ?


No, the pump for the hot water primary circuit is more suitable for pump
overrun than the central heating circuit. Don't get confused with the DHW
secondary, which is isolated from the primary system.

Christian.


  #8   Report Post  
Set Square
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In an earlier contribution to this discussion, mike ring
wrote:

I've considered the Grundfos Pump Plan - seems very advantageously
priced at plumbworld ATM, and came up with this doc

UPP_Pump_Plan_05_03.pdf

but I don't know where from.

It contains a wiring diagram.


A URL would be *awfully* useful!



I really like the idea, but it's a bit bleeding edge for me...., what
happens if one pump fails in a cold snap?

You lose *either* the HW *or* the CH - as opposed to losing *both* with a
conventional one-pump setup!
--
Cheers,
Set Square


  #9   Report Post  
Mike
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

It can actually all be done with a single relay (with Double pole change
over contacts). I have been working this out over the past few days.

Relay coil goes across the CH Pump.


Boiler overrun contacts.
Boiler overrun live goes to NC contact.
Heating Demand Live geos to NO contact.
HW Pump Live goes to Common.

Boiler control Contacts.
Heating Demand Live geos to NC contact.
Unswitched Live goes to the NO Contact.
Boiler switched Live goes to common.

Someone may be able to do an ASCII art version of this, It's beyond me.

Christian McArdle wrote:
Secondly how does pump overrun work if 2 pumps are used (i assume you
have to dump into the CH cylinder)



This gets a little more complicated. You basically need the pump overrun
output of the boiler to run the hot water pump. However, it is essential
that this doesn't end up as a call for heat back at the interlock, or it
will never switch off. You also don't want the HWC pump to run when the CH
pump is running, or the HWC will overheat.


  #10   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

Boiler overrun contacts.
Boiler overrun live goes to NC contact.
Heating Demand Live geos to NO contact.
HW Pump Live goes to Common.

Boiler control Contacts.
Heating Demand Live geos to NC contact.
Unswitched Live goes to the NO Contact.
Boiler switched Live goes to common.

Someone may be able to do an ASCII art version of this, It's beyond me.


Yes, I think that works!

Inputs to system:
CH On = Central heating on (at programmer)
HW On = Hot water on (at programmer)
POR = Pump output (from boiler)
N = Neutral
L = Permanent Live

Output from system:
BCFH = boiler call for heat

Pumps:
CHP = central heating pump
HWP = hot water pump

Switchgear:
rts = room thermostat
cts = cylinder thermostat
NO = normally open terminal
NC = normally closed terminal
C = common terminal
/\/\ = relay coil

/
CH On O---o o-------+--CHP---+---O N
rts | |
+--/\/\--+


  #11   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

"Set Square" wrote in :


I've considered the Grundfos Pump Plan - seems very advantageously
priced at plumbworld ATM, and came up with this doc

UPP_Pump_Plan_05_03.pdf

but I don't know where from.

It contains a wiring diagram.


A URL would be *awfully* useful!


http://www.centralheating.co.uk/inde...ewFile&id=6551

I hope it works, took ages to find again,


I can't find any reference to prevention of flow if only one service is
required - if the CH is on ISTM that the pump will pull water through the
boiler, but also tend to pull it back through the HW circuit.

Otherwise I'm very rempted, the price isn't too outrageous against one pump
and a 3port or two two port valves, and it seems more direct.

I realise 2 pumps in one casing means quite a lot of replacement for one
failure, but I haven't found grundfos pumps bad

mike
  #12   Report Post  
Set Square
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In an earlier contribution to this discussion,
mike ring wrote:

"Set Square" wrote in
:


I've considered the Grundfos Pump Plan - seems very advantageously
priced at plumbworld ATM, and came up with this doc

UPP_Pump_Plan_05_03.pdf

but I don't know where from.

It contains a wiring diagram.


A URL would be *awfully* useful!


http://www.centralheating.co.uk/inde...ewFile&id=6551

I hope it works, took ages to find again,


I can't find any reference to prevention of flow if only one service
is required - if the CH is on ISTM that the pump will pull water
through the boiler, but also tend to pull it back through the HW
circuit.

Otherwise I'm very rempted, the price isn't too outrageous against
one pump and a 3port or two two port valves, and it seems more direct.

I realise 2 pumps in one casing means quite a lot of replacement for
one failure, but I haven't found grundfos pumps bad

mike


Thanks for the link. Looks interesting! May not be too easy for diy-ers to
diagnose if the integrated logic goes wrong.

As far as I can see, you still have two water circuits with a common feed
from the boiler. I can't see any reason why either pump should induce any
flow in the other circuit. However, there is nothing to stop gravity
circulation if either circuit decides to do its own thing.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #13   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

"Set Square" wrote in
:


Thanks for the link. Looks interesting! May not be too easy for
diy-ers to diagnose if the integrated logic goes wrong.

As far as I can see, you still have two water circuits with a common
feed from the boiler. I can't see any reason why either pump should
induce any flow in the other circuit. However, there is nothing to
stop gravity circulation if either circuit decides to do its own
thing.


But one pump is fed not only from the boiler but from the other circuit,
unless there's something to prevent backward flow, as the are common at the
input of both pumps, and at the boiler return which would be at a higher
pressure.

I admit I don't know for sure, but having sketched it out, I'm more
convinced;

The gravity bit is the other thing; in the absence of any forced flow,
would the hot water cylinder cause a flow through the rads and cool itself
down?

Of course the maker prolly knows what he's up to - I just wish I knew more
before taking the plunge

mike
  #14   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

mike ring wrote in
52.50:

Further to that, I've jusst found this


http://www.grundfos.com/web/homeUK.n...8C904125681D00
3DFC03

(bit of a wrap)

which has more info - in particular what I've just seen is there's a spring
assisted nonreturn valve in each branch.

mike
  #15   Report Post  
Set Square
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In an earlier contribution to this discussion,
mike ring wrote:


But one pump is fed not only from the boiler but from the other
circuit, unless there's something to prevent backward flow, as the
are common at the input of both pumps, and at the boiler return which
would be at a higher pressure.


The boiler input and output will be at virtually the same pressure. The
output of a pump will be at a higher pressure than the input - and this
pressure will be dissipated by the resistance of the particular circuit. If
only one pump is running, all points on the other circuit are going to be at
the same pressure (ignoring static pressure differencers due to height
differences) - so there's nothing to induce any flow.


The gravity bit is the other thing; in the absence of any forced flow,
would the hot water cylinder cause a flow through the rads and cool
itself down?

What I was referring to here was gravity (sometimes called thermo-syphon or
convection) flow. Some (mainly older) systems were designed to have the HW
circuit operate by gravity flow without needing a pump - and used a pump
only for the CH side. In this dual pump setup, if the HW circuit took it
upon itself to start circulating by gravity when the boiler was on for the
benefit of the CH but when the HW pump wasn't running because the HW demand
was satisfied, there's nothing inherent in the design of this system to stop
it from doing so. A system using zone valves would physically stop the flow
by closing the valve under these circumstances. There's no danger of heat
being transferred from the hot water to the radiators. There *may* be a
danger of the hot water getting too hot when the CH is on, or of the
radiators getting warm in the summer when the HW is being heated.
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.




  #16   Report Post  
raden
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In message , Christian McArdle
writes
This gets a little more complicated. You basically need the pump overrun
output of the boiler to run the hot water pump.


So where does the heat go if the taps are turned off?

Didn't you mean the central heating pump ?


No, the pump for the hot water primary circuit is more suitable for pump
overrun than the central heating circuit. Don't get confused with the DHW
secondary, which is isolated from the primary system.

So where are you dumping the heat to if there is no DHW flow ?

--
geoff
  #17   Report Post  
Christian McArdle
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

So where are you dumping the heat to if there is no DHW flow ?

The cylinder itself. Although already at a high temperature (i.e. 60C), it
still acts as a nice energy dump, especially as the flow temperature rises.
Even if the flow temperature rises to 90C (unlikely), thats a nice 30C
difference across the heat exchanger and the cylinder won't get appreciably
hotter because of 30 seconds of overrun with the burners turned off.

Christian.


  #18   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

"Set Square" wrote in
:


The boiler input and output will be at virtually the same pressure.
The output of a pump will be at a higher pressure than the input - and
this pressure will be dissipated by the resistance of the particular
circuit. If only one pump is running, all points on the other circuit
are going to be at the same pressure (ignoring static pressure
differencers due to height differences) - so there's nothing to induce
any flow.

It's that "virtually" the same pressure that was worrying me - the circuit
looked so much like an electrical network I nearly started using Kirchoff
and Thevenin on it! I was certainly taken back to backdoor circuits and
steering diodes - and it _does_ have nonreturn valves.

Seriously, do you have any thoughts about the system; It doesn't seem all
that dear at the moment, comes with the wiring centre, and in priciple
looks better to me.

But I'm extremely inexperienced, in faact, when iit comes to upgradeing
cylinders and CH - none at all

mike
  #19   Report Post  
Set Square
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

In an earlier contribution to this discussion,
mike ring wrote:

"Set Square" wrote in
:


The boiler input and output will be at virtually the same pressure.
The output of a pump will be at a higher pressure than the input -
and this pressure will be dissipated by the resistance of the
particular circuit. If only one pump is running, all points on the
other circuit are going to be at the same pressure (ignoring static
pressure differencers due to height differences) - so there's
nothing to induce any flow.

It's that "virtually" the same pressure that was worrying me - the
circuit looked so much like an electrical network I nearly started
using Kirchoff and Thevenin on it! I was certainly taken back to
backdoor circuits and steering diodes - and it _does_ have nonreturn
valves.

Seriously, do you have any thoughts about the system; It doesn't seem
all that dear at the moment, comes with the wiring centre, and in
priciple looks better to me.

But I'm extremely inexperienced, in faact, when iit comes to
upgradeing cylinders and CH - none at all

mike


You really don't need to worry about cross-talk between the circuits - it
ain't going to happen. If it really does have valves to prevent gravity
circulation, these will prevent anything moving in the circuit whose pump
isn't running, and it should do exactly the same job as an S-plan system.
Ignoring costs, I would see the pros and cons relative to S-Plan as:

PROS
* Less individual components to accommodate and install - since it doesn't
need zone valves or a by-pass loop - (but it *does* need the anti-gravity
valves)
* Failure of one half of the pump would still enable the other circuit to
operate (but there would be no pump-over-run if the HW pump failed)

CONS
* The pump and control centre are proprietary, and cannot be replaced by
generic components in the way that S-Plan components can
* You have to have precisely two circuits as opposed to S-Plan, which can
(in its S-Plan-Plus form) accommodate unlimited circuits by the addition of
more zone valves - enabling (for example) separate control of upstairs and
downstairs radiators

You pays your money . . .
--
Cheers,
Set Square
______
Please reply to newsgroup. Reply address is invalid.


  #20   Report Post  
mike ring
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

"Set Square" wrote in
:


PROS
* Less individual components to accommodate and install - since it
doesn't need zone valves or a by-pass loop - (but it *does* need the
anti-gravity valves)
* Failure of one half of the pump would still enable the other circuit
to operate (but there would be no pump-over-run if the HW pump failed)

CONS
* The pump and control centre are proprietary, and cannot be replaced
by generic components in the way that S-Plan components can
* You have to have precisely two circuits as opposed to S-Plan, which
can (in its S-Plan-Plus form) accommodate unlimited circuits by the
addition of more zone valves - enabling (for example) separate control
of upstairs and downstairs radiators

You pays your money . . .


I think you're right - last winter my 3port valve failed, and after advice
from hereabouts I was able to replace it pronto, even though it needed the
wet bit replacing.

I was shopping today in a shed, and loadsa pumps and valves were available
- I could replace them as soon as the shops opened.

Ta

mike


  #21   Report Post  
Mike
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

Thanks Christian

I realised after I'd posted that I left out some detail but you have
added it.


This is slightly different from my previous "ideal" (number in bracket is
the difference), but should still work perfectly. The effect is not to start
the hot water pump directly in response to a hot water heating demand.
Instead, the system waits until the boiler's pump output is activated, which
should happen as the BIL input to the boiler has activated.


However the conventional single pump system does that anyway!

I bet someone comes up with a system that doesn't use a relay at all, but
just changeover thermostat terminals...


I think you need a doupble pole switch somewhere to make it work. Can
be either thermostat though.


  #22   Report Post  
Mike
 
Posts: n/a
Default Central Heating. 2 pumps no valves wiring

mike ring wrote:


I can't find any reference to prevention of flow if only one service is
required - if the CH is on ISTM that the pump will pull water through the
boiler, but also tend to pull it back through the HW circuit.


The pump plan pump has the anti backflow valves built into it.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Central Heating : Wiring Query John Pearson UK diy 6 January 13th 04 10:30 AM
Tower Wiring Centre for domestic central heating Jimmy UK diy 4 December 12th 03 05:07 PM
Central Heating - Problem with 3 way valve wiring. John UK diy 1 October 3rd 03 06:28 PM
Best Isolating valves for Central Heating Pumps?? Frank Sweeting UK diy 9 October 3rd 03 08:45 AM
2 port Vs 3 port central heating valves EMC UK diy 16 July 31st 03 08:09 PM


All times are GMT +1. The time now is 04:02 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"