Larry Jaques[_4_] May 28th 18 06:24 AM

Generator wiring question
 
On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .


The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .


That's what it takes to have a neutral and a safety ground.


I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)

--
If we can ever make red tape nutritional, we can feed the world.
--Robert Schaeberle

Clare Snyder May 28th 18 04:28 PM

Generator wiring question
 
On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .


The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .


That's what it takes to have a neutral and a safety ground.


I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)



Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA

Gunner Asch[_6_] May 28th 18 04:34 PM

Generator wiring question
 
On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.


I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)



Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA


New construction/retrofits must have that safety ground and the
neutral, bonded inside the breaker box. Some locales are stricter
than others about what a "retrofit" is.

Most...most "backwaters" have it on the books..but really dont care.
as long as its safe.


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


Larry Jaques[_4_] May 29th 18 01:19 AM

Generator wiring question
 
On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.


I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)



Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA


"Whatever for?" he queried, from said backwater.

--
If we can ever make red tape nutritional, we can feed the world.
--Robert Schaeberle

Clare Snyder May 29th 18 02:08 AM

Generator wiring question
 
On Mon, 28 May 2018 17:19:25 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.

I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)



Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA


"Whatever for?" he queried, from said backwater.



So you can use 120 volt lightbulbs and timers and primaries on control
circuit transformers, and fan motors. and all kinds of other low power
devices without (illegally) using the safety ground as a neutral,
potentially making the chassis "live" - as has been done,
unofficially, for decades - on both dryers and ranges.

It's a "safety" thing.
They initially allowed the use of the safety ground as a neutral as a
matter of expediency due to the high price of copper

Pete Keillor[_2_] May 29th 18 12:00 PM

Generator wiring question
 
On Mon, 28 May 2018 21:08:33 -0400, Clare Snyder
wrote:

On Mon, 28 May 2018 17:19:25 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.

I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)


Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA


"Whatever for?" he queried, from said backwater.



So you can use 120 volt lightbulbs and timers and primaries on control
circuit transformers, and fan motors. and all kinds of other low power
devices without (illegally) using the safety ground as a neutral,
potentially making the chassis "live" - as has been done,
unofficially, for decades - on both dryers and ranges.

It's a "safety" thing.
They initially allowed the use of the safety ground as a neutral as a
matter of expediency due to the high price of copper


I got used to having the neutral when I was designing lab carts with
240 V DC motors. It was very handy to have 120 V outlets out in the
middle of the lab for various tasks. My last set of carts were 440V
explosion proof in a classified area, so no outlets on those anyway.

I continued the practice when I built my shop, had the electricians
pull 4 wire for all my 240 V. circuits. But I haven't had the need
since distances are short to plenty of 120 V outlets in the shop.

I will probably relocate nearer the coast in the near future. I may
end up adding 120 V outlets to the welding cart if needed at the new
place.

Pete Keillor

Jim Wilkins[_2_] May 29th 18 01:28 PM

Generator wiring question
 
"Pete Keillor" wrote in message
...
On Mon, 28 May 2018 21:08:33 -0400, Clare Snyder

wrote:

On Mon, 28 May 2018 17:19:25 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder

wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John
wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs

wrote:


I think you'll find that those 3 pins are neutral and 220 on
the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral
and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.

I think the NEC demands those only in hospitals. Everyone else
has 2
hots and a not. (safety ground w/ no current)


Required for ranges and driers for at least the last 10 years
here in
Canada - don't know abiout the backwaters of the USA

"Whatever for?" he queried, from said backwater.



So you can use 120 volt lightbulbs and timers and primaries on
control
circuit transformers, and fan motors. and all kinds of other low
power
devices without (illegally) using the safety ground as a neutral,
potentially making the chassis "live" - as has been done,
unofficially, for decades - on both dryers and ranges.

It's a "safety" thing.
They initially allowed the use of the safety ground as a neutral as
a
matter of expediency due to the high price of copper


I got used to having the neutral when I was designing lab carts with
240 V DC motors. It was very handy to have 120 V outlets out in the
middle of the lab for various tasks. My last set of carts were 440V
explosion proof in a classified area, so no outlets on those anyway.

I continued the practice when I built my shop, had the electricians
pull 4 wire for all my 240 V. circuits. But I haven't had the need
since distances are short to plenty of 120 V outlets in the shop.

I will probably relocate nearer the coast in the near future. I may
end up adding 120 V outlets to the welding cart if needed at the new
place.

Pete Keillor


I was only a few feet away from another tech when he tried to measure
an SCR trigger circuit floating on 120V with a grounded scope. When he
flipped the power switch the entire probe exploded from the enormous
current in the braid, sending him to the hospital. I was facing away
and didn't see but I think his body shielded me from the fireball.

-jsw



Bob Engelhardt May 29th 18 05:46 PM

Generator wiring question
 
On 5/29/2018 8:28 AM, Jim Wilkins wrote:
I was only a few feet away from another tech when he tried to measure
an SCR trigger circuit floating on 120V with a grounded scope. When he
flipped the power switch the entire probe exploded from the enormous
current in the braid, sending him to the hospital. I was facing away
and didn't see but I think his body shielded me from the fireball.


Defective breaker?

Jim Wilkins[_2_] May 29th 18 06:11 PM

Generator wiring question
 
"Bob Engelhardt" wrote in message
...
On 5/29/2018 8:28 AM, Jim Wilkins wrote:
I was only a few feet away from another tech when he tried to
measure
an SCR trigger circuit floating on 120V with a grounded scope. When
he
flipped the power switch the entire probe exploded from the
enormous
current in the braid, sending him to the hospital. I was facing
away
and didn't see but I think his body shielded me from the fireball.


Defective breaker?


Parts of the probe remained attached. He had connected the probe
ground to the SCR cathode (hot line) so he could observe the optically
isolated SCR gate trigger pulse without interference from the 120V
sine wave it was riding on. It was a 240V power supply so both sides
of the SCRs were Hot.



Larry Jaques[_4_] May 30th 18 05:00 AM

Generator wiring question
 
On Mon, 28 May 2018 21:08:33 -0400, Clare Snyder
wrote:

On Mon, 28 May 2018 17:19:25 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.

I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)


Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA


"Whatever for?" he queried, from said backwater.



So you can use 120 volt lightbulbs and timers and primaries on control
circuit transformers, and fan motors. and all kinds of other low power
devices without (illegally) using the safety ground as a neutral,
potentially making the chassis "live" - as has been done,
unofficially, for decades - on both dryers and ranges.

It's a "safety" thing.
They initially allowed the use of the safety ground as a neutral as a
matter of expediency due to the high price of copper


OK, politics, like belt+suspenders. Got it. I'm going to have to ask
who plugs those things into dryer outlets, too, I'm afraid.

--
If we can ever make red tape nutritional, we can feed the world.
--Robert Schaeberle

Bob La Londe[_7_] May 30th 18 05:58 PM

Generator wiring question
 
On 5/25/2018 8:40 AM, Dave, I can't do that wrote:
Hi,

I have a 1-1/2HP, 220v motor running from the dryer socket, all good.

I was thinking of putting in a change over switch to run the motor from the generator when the power goes out as it does regularly out here.

https://www.amazon.com/Baomain-Unive.../dp/B01IZ5ZFYC

To save me dragging the gen-set out and starting it to find out what is coming out of the 240-socket, thought I'd ask here.

The house wiring uses the 3-wire 110-0-110 for the 220/240 but the gen has three pins for the 240-out. I am guessing one is Ground and the others are Neutral and 240v.

How do I go about wiring that to run the motor? An ASCII diagram would be good.

Thanks



Break out your meter and find out. There are 3 pin twist lock 110V
plugs. I have a few.

Gunner Asch[_6_] May 30th 18 06:55 PM

Generator wiring question
 
On Wed, 30 May 2018 09:58:38 -0700, Bob La Londe
wrote:

On 5/25/2018 8:40 AM, Dave, I can't do that wrote:
Hi,

I have a 1-1/2HP, 220v motor running from the dryer socket, all good.

I was thinking of putting in a change over switch to run the motor from the generator when the power goes out as it does regularly out here.

https://www.amazon.com/Baomain-Unive.../dp/B01IZ5ZFYC

To save me dragging the gen-set out and starting it to find out what is coming out of the 240-socket, thought I'd ask here.

The house wiring uses the 3-wire 110-0-110 for the 220/240 but the gen has three pins for the 240-out. I am guessing one is Ground and the others are Neutral and 240v.

How do I go about wiring that to run the motor? An ASCII diagram would be good.

Thanks



Break out your meter and find out. There are 3 pin twist lock 110V
plugs. I have a few.



Virtually ALL gensets that use a 3 wire twist lock and claim to put
out 240 volts...will have 240 across (2) of the connector pins and a
ground. The odd shaped pin will be the ground. Least..its supposed to
be.

Period.
Full stop
End Program.

Measure from 240 pin to ground. You may..may get 120 volts if the
genset is worth a ****.

I have several gensets..and they include a genset that claims to be
240..but isnt.

Gunner



---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus


Doug Miller[_4_] May 30th 18 09:10 PM

Generator wiring question
 
"Jim Wilkins" wrote in :

The neutral carries the difference between the hot leg currents. If
the load current is 100A on one leg and 0A on the other the neutral
will carry 100A. Increasing the load on the other leg decreases the
current in the neutral, so with 100A through both hot legs the neutral
carries 0A, not 200A, and it can be the same size cable as the two
hots.

Actually, if the load on the two 120V legs of the 240/120 service is reasonably well
balanced, the neutral cable can be substantially *smaller* than the two hots. For example, I
just helped my son install a new service panel in his house, upgrading from 100A to 200A
service, and he just passed his final electrical inspection last week -- with two 3/0 copper
cables for the hots, and 1/0 copper for the neutral. It actually would have passed with the
neutral as small as AWG 4, but I happened to have enough 1/0 on hand already, left over
from a long-ago project, and neither one of us had any 4.

Conceptually you get the right answer if you treat both loops of the
circuit as separate and then add the currents,


*subtract the currents

If the neutral has 100A
flowing in from one hot leg and simultaneously 100A out to the other
they will sum to 0


Correct.

Further example, in case it's unclear to anyone: 75A on one leg and 90A on the other leaves
15A on the neutral.


Clare Snyder May 30th 18 10:44 PM

Generator wiring question
 
On Tue, 29 May 2018 21:00:02 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 21:08:33 -0400, Clare Snyder
wrote:

On Mon, 28 May 2018 17:19:25 -0700, Larry Jaques
wrote:

On Mon, 28 May 2018 11:28:19 -0400, Clare Snyder
wrote:

On Sun, 27 May 2018 22:24:04 -0700, Larry Jaques
wrote:

On Sat, 26 May 2018 19:58:13 -0400, Neon John wrote:

On Fri, 25 May 2018 11:31:59 -0500, Terry Coombs
wrote:


* I think you'll find that those 3 pins are neutral and 220 on the
other 2 , with either hot to the neutral at 110 .

The 3 conductor 240 volt cable is 2 hots and ground. No neutral and
thus no 120 volts.
Mine has a 4 wire
socket , with 2 hots a neutral and a ground .

That's what it takes to have a neutral and a safety ground.

I think the NEC demands those only in hospitals. Everyone else has 2
hots and a not. (safety ground w/ no current)


Required for ranges and driers for at least the last 10 years here in
Canada - don't know abiout the backwaters of the USA

"Whatever for?" he queried, from said backwater.



So you can use 120 volt lightbulbs and timers and primaries on control
circuit transformers, and fan motors. and all kinds of other low power
devices without (illegally) using the safety ground as a neutral,
potentially making the chassis "live" - as has been done,
unofficially, for decades - on both dryers and ranges.

It's a "safety" thing.
They initially allowed the use of the safety ground as a neutral as a
matter of expediency due to the high price of copper


OK, politics, like belt+suspenders. Got it. I'm going to have to ask
who plugs those things into dryer outlets, too, I'm afraid.

A welder I had used a 120 volt fan. 240 volt welder.

Jim Wilkins[_2_] May 30th 18 11:44 PM

Generator wiring question
 
"Doug Miller" wrote in message
. ..
"Jim Wilkins" wrote in
:


Conceptually you get the right answer if you treat both loops of
the
circuit as separate and then add the currents,


*subtract the currents


Adding works if the direction is considered. I would have written 'add
algebraically' to an audience of engineers.
https://www.conservapedia.com/Algebraic_addition



Doug Miller[_4_] June 1st 18 02:52 PM

Generator wiring question
 
"Jim Wilkins" wrote in :

"Doug Miller" wrote in message
. ..
"Jim Wilkins" wrote in
:


Conceptually you get the right answer if you treat both loops of
the
circuit as separate and then add the currents,


*subtract the currents


Adding works if the direction is considered. I would have written 'add
algebraically' to an audience of engineers.


And I would have understood what you meant. Best to assume, though, IMHO, that most of
the people reading this discussion aren't engineers, and would be confused by the
terminology.

Since one current is arriving, and the other leaving, at the same point, they perforce have
opposite signs -- but electricians and laymen don't think that way. They see 70A current on
one leg, minus 30A current on the other, equals 40A in the neutral. and don't really care
about the fine points of Kirchoff's Current Law.

Jim Wilkins[_2_] June 1st 18 04:10 PM

Generator wiring question
 
"Doug Miller" wrote in message
. ..
"Jim Wilkins" wrote in
:

"Doug Miller" wrote in message
. ..
"Jim Wilkins" wrote in
:


Conceptually you get the right answer if you treat both loops of
the
circuit as separate and then add the currents,

*subtract the currents


Adding works if the direction is considered. I would have written
'add
algebraically' to an audience of engineers.


And I would have understood what you meant. Best to assume, though,
IMHO, that most of
the people reading this discussion aren't engineers, and would be
confused by the
terminology.

Since one current is arriving, and the other leaving, at the same
point, they perforce have
opposite signs -- but electricians and laymen don't think that way.
They see 70A current on
one leg, minus 30A current on the other, equals 40A in the neutral.
and don't really care
about the fine points of Kirchoff's Current Law.


Agreed, as long as they stick to single phase. I didn't want to plant
an incorrect idea in case they move on to three phase.