Robert11 January 19th 05 07:54 PM

Meaning Of 150 amp Service: At 115 V, Or At 220 V ?
 
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or
150 amps at 220 V ?

Thanks,
Bob



jhill January 19th 05 08:30 PM

220
"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115

V,
or
150 amps at 220 V ?

Thanks,
Bob





TCS January 19th 05 08:34 PM

On Wed, 19 Jan 2005 14:54:30 -0500, Robert11 wrote:
Hello:


When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or
150 amps at 220 V ?


Yes. And by the way, it's the same thing. If you have two 115V lines
@ 150 amps, it's also 150 amps @ 220V.



Hello World January 19th 05 09:30 PM

TCS wrote:
On Wed, 19 Jan 2005 14:54:30 -0500, Robert11 wrote:

Hello:



When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or
150 amps at 220 V ?



Yes. And by the way, it's the same thing. If you have two 115V lines
@ 150 amps, it's also 150 amps @ 220V.



What are inside the feed wires? 2 hots @120V each, and a neutral?
The neutral and ground are usually connected at the panel. So
how the electricity figure which way to go, to the neutral, or to
the ground?

EL January 19th 05 09:32 PM

Short answer is "yes" ;^)

A home with reasonably modern wiring will have electric service with 3 wires: 2 hots and a neutral. You'll get 220 (or
thereabouts) across both hots, and 110 (or thereabouts) from either to the neutral. Both hot wires go thru the main breaker,
which is really two breakers connected together mechanically so if one trips the other does also.

Bottom line: if you're using 110V you can draw 150 amps off each leg (300 total if evenly distributed), if you're using 220
you can pull 150 amps total. In the real world you're probably using a mixture so it gets a little more complicated.

Eric Law

"Robert11" wrote in message ...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V, or
150 amps at 220 V ?

Thanks,
Bob




Matt January 19th 05 10:05 PM

It figures it out by asking the water. That's what the wire is for that
connects the panel to the water pipe - it's a communication link.


bill a January 19th 05 10:42 PM

is that way power is measured in watts?
because it goes thru watter?


"Matt" wrote in message
oups.com...
It figures it out by asking the water. That's what the wire is for that
connects the panel to the water pipe - it's a communication link.



Matt January 19th 05 10:49 PM

Yep! Thats it exactly!


Nehmo Sergheyev January 19th 05 11:35 PM

- Hello World -
What are inside the feed wires? 2 hots @120V each, and a neutral?
The neutral and ground are usually connected at the panel. So
how the electricity figure which way to go, to the neutral, or to
the ground?


- Nehmo -
For simplicity, let's only concern ourselves with _one_ hot (black), the
neutral (white), and the ground (bare or green). Also let's just
consider an instant in the changing Alternating Current (AC) cycle, when
the hot is conventionally-called positive. Electricity of the household
line-current type can only travel in a complete circuit – the circuit
has to form a loop. So if a load, a lamp (a lamp with a metal housing
that is grounded to the ground prong of a 3-prong plug) for example, is
placed between the hot and the neutral (the normal situation), the
electricity goes, from the panel, through the hot, through the lamp,
then back through the neutral back to the panel. The ground wire does
nothing because there is no complete circuit that includes the ground
wire.

But suppose something goes wrong: let's say an insulation-stripped hot
wire inside the lamp now touches the lamp housing, a short. Now when you
turn on the lamp, which allows current to the hot wire, the electricity
goes from the panel, through the hot, through the short to the lamp
housing, through the ground prong of the plug, through the ground wire,
and back to the panel where, since the resistance of the circuit is low
and the current is thus high, the breaker opens. The ground wire served
its purpose.

That's how the electricity knows where to go; it goes only where the
circuit is complete.


--
*********************
* Nehmo Sergheyev *
*********************


TURTLE January 20th 05 03:14 AM


"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or
150 amps at 220 V ?

Thanks,
Bob


This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp double
pole breakers at 220 volt service.

E-mail me if you want to discuss it.

TURTLE



Ross Mac January 20th 05 09:56 AM


"TURTLE" wrote in message
.. .

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115
V, or
150 amps at 220 V ?

Thanks,
Bob


This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


How do you figure???????.........Ross


You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp
double pole breakers at 220 volt service.

E-mail me if you want to discuss it.

TURTLE




Doug Miller January 20th 05 01:40 PM

In article , "TURTLE" wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp double
pole breakers at 220 volt service.


Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use, at
full capacity, at the same time.

E-mail me if you want to discuss it.


The OP would be better off posting his questions publicly so that others have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



willshak January 20th 05 02:47 PM

On 1/20/2005 8:40 AM US(ET), Doug Miller took fingers to keys, and typed
the following:

In article , "TURTLE" wrote:


"Robert11" wrote in message
...


Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or 150 amps at 220 V ?



This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.



WRONG. It means 150 amps at 220 volts.


You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp double
pole breakers at 220 volt service.



Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use, at
full capacity, at the same time.



I certainly hope so. I have a 200 amp panel, and if I add all the
breaker sizes up (including the double 220v ones), it comes to 660 amps.
Just the 20 amp breakers alone add up to 280.

E-mail me if you want to discuss it.



The OP would be better off posting his questions publicly so that others have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.






--
Bill

Lawrence Wasserman January 20th 05 06:54 PM

In article ,
Robert11 wrote:
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or
150 amps at 220 V ?

Thanks,
Bob



Yes.




That is, if you look at how 220 is wired in a (US) home, if 150 amps
is being supplied on one leg, then it can "return" so to speak, either
on the neutral for 110V, or on the other hot leg for 220. So the 150
amps is available at either voltage.


--

Larry Wasserman Baltimore, Maryland



Matt January 20th 05 06:59 PM

Give 'em hell, Doug!


Doug Miller January 20th 05 08:14 PM

In article , (Lawrence Wasserman) wrote:
In article ,
Robert11 wrote:
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115 V,
or 150 amps at 220 V ?


Yes.

No.

That is, if you look at how 220 is wired in a (US) home, if 150 amps
is being supplied on one leg, then it can "return" so to speak, either
on the neutral for 110V, or on the other hot leg for 220. So the 150
amps is available at either voltage.


WRONG. 150 amp service can supply 150 amps on *each* leg of the service. That
adds up to 300 amps at 110 V. Or 150A at 220V. Or any combination that adds up
to 33 kVA, provided that no more than 16.5 kVA flows through an individual
leg.

[email protected] January 20th 05 08:15 PM


A home with reasonably modern wiring will have electric service with 3 wires: 2 hots and a neutral. You'll get 220 (or
thereabouts) across both hots, and 110 (or thereabouts) from either to the neutral. Both hot wires go thru the main breaker,
which is really two breakers connected together mechanically so if one trips the other does also.

Bottom line: if you're using 110V you can draw 150 amps off each leg (300 total if evenly distributed), if you're using 220
you can pull 150 amps total. In the real world you're probably using a mixture so it gets a little more complicated.


This answer being for most of north america, assuming that you don't
specifically ask for something different, in areas where 208V
residential
service is also available, and assuming you're willing to tolerate a
little laxity of of terminology.

What you're actually getting is a nominal 33 Kilowatts, which can
manifest
as 150 amps at 220V, or 300 amps at 110V, or any pro-rated combination
between.

Ross Mac January 21st 05 03:12 AM


"Doug Miller" wrote in message
om...
In article , "TURTLE"
wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at
115 V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp
double
pole breakers at 220 volt service.


Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use,
at
full capacity, at the same time.

E-mail me if you want to discuss it.


The OP would be better off posting his questions publicly so that others
have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



Thanks Doug...thats why I posted the "How do you figure" comment...there was
a serious violation of ohms law in the Turtles comment....Ross



[email protected] January 21st 05 05:15 AM

Ah, a man that knows there is a difference between kVA and KW. You
ought to use a moniker of "Mr. Power Factor" and keep 'em guessing.
;-)

Best regards,
Bob


[email protected] January 21st 05 02:01 PM

Yes, but is he real or reactive?


TURTLE January 23rd 05 07:59 AM


"Ross Mac" wrote in message
...

"Doug Miller" wrote in message
om...
In article , "TURTLE"
wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115
V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp double
pole breakers at 220 volt service.


Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use, at
full capacity, at the same time.

E-mail me if you want to discuss it.


The OP would be better off posting his questions publicly so that others have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



Thanks Doug...thats why I posted the "How do you figure" comment...there was a
serious violation of ohms law in the Turtles comment....Ross


This is Turtle.

I have say I got it backwards to be completely saying the story. You can get 150
amps on each leg . Then you fill in the blanks as to using 220 volt sevice of
both legs. Then when you say the box is only good for 150 amps at 220 volt
service. Your saying your drawing 150 amps from each leg and that adds up to 300
amps you will really be drawing from the box with 150 amps from each leg. When
you say 220 service breaker in the 150 amp box they are drawing 300 amps in the
real world. You may try to explain it differently but it mounts up to 300 amps
by way of 120 volt draw.

The meaning of 220 volt service at 150 amps means you can pull 150 amps off each
leg by doing so. This amounts to 300 amps if I use single breakers. Now you &
Mr. Miller please explain what is wrong with this info ?

TURTLE



Doug Miller January 23rd 05 05:53 PM

In article , "TURTLE" wrote:

"Ross Mac" wrote in message
...

"Doug Miller" wrote in message
om...
In article , "TURTLE"
wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115
V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.

WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp

double
pole breakers at 220 volt service.

Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use, at
full capacity, at the same time.

E-mail me if you want to discuss it.

The OP would be better off posting his questions publicly so that others

have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



Thanks Doug...thats why I posted the "How do you figure" comment...there was

a
serious violation of ohms law in the Turtles comment....Ross


This is Turtle.

I have say I got it backwards to be completely saying the story. You can get
150
amps on each leg . Then you fill in the blanks as to using 220 volt sevice of
both legs. Then when you say the box is only good for 150 amps at 220 volt
service. Your saying your drawing 150 amps from each leg and that adds up to
300
amps you will really be drawing from the box with 150 amps from each leg. When
you say 220 service breaker in the 150 amp box they are drawing 300 amps in the

real world. You may try to explain it differently but it mounts up to 300 amps
by way of 120 volt draw.

The meaning of 220 volt service at 150 amps means you can pull 150 amps off
each
leg by doing so. This amounts to 300 amps if I use single breakers. Now you &
Mr. Miller please explain what is wrong with this info ?

Nothing at all wrong with that... but this is what you posted first:

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


And that's backward.

TURTLE January 24th 05 01:07 AM


"Doug Miller" wrote in message
.. .
In article , "TURTLE"
wrote:

"Ross Mac" wrote in message
...

"Doug Miller" wrote in message
om...
In article , "TURTLE"
wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps at 115
V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.

WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp

double
pole breakers at 220 volt service.

Wrong again. It's perfectly OK for the ratings of the individual branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in use,
at
full capacity, at the same time.

E-mail me if you want to discuss it.

The OP would be better off posting his questions publicly so that others

have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



Thanks Doug...thats why I posted the "How do you figure" comment...there was

a
serious violation of ohms law in the Turtles comment....Ross


This is Turtle.

I have say I got it backwards to be completely saying the story. You can get
150
amps on each leg . Then you fill in the blanks as to using 220 volt sevice of
both legs. Then when you say the box is only good for 150 amps at 220 volt
service. Your saying your drawing 150 amps from each leg and that adds up to
300
amps you will really be drawing from the box with 150 amps from each leg. When
you say 220 service breaker in the 150 amp box they are drawing 300 amps in
the

real world. You may try to explain it differently but it mounts up to 300 amps
by way of 120 volt draw.

The meaning of 220 volt service at 150 amps means you can pull 150 amps off
each
leg by doing so. This amounts to 300 amps if I use single breakers. Now you &
Mr. Miller please explain what is wrong with this info ?

Nothing at all wrong with that... but this is what you posted first:

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


And that's backward.


This is Turtle.

I have been working with 3 phase 480 volt systems for the last two weeks and I
seem to get everything assbackwards when I get off 3 phase and get back on
single phase stuff again. If your 3 phasing your thinking 1/3 and not 1/2 with
single phase.

So can you forgive me for being assbackwards one time ?

TURTLE



Ross Mac January 24th 05 08:21 PM


"TURTLE" wrote in message
...

"Doug Miller" wrote in message
.. .
In article , "TURTLE"
wrote:

"Ross Mac" wrote in message
...

"Doug Miller" wrote in message
om...
In article , "TURTLE"
wrote:

"Robert11" wrote in message
...
Hello:

When they say a house has, e.g., 150 amp service, is that 150 amps
at 115
V,
or 150 amps at 220 V ?

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.

WRONG. It means 150 amps at 220 volts.

You can have 15 --- 20 amp single 115 volt breakers or 7.5 --- 20 amp
double
pole breakers at 220 volt service.

Wrong again. It's perfectly OK for the ratings of the individual
branch
circuit breakers to add up to a *lot* more than the rating of the main
disconnect. This is because the branch circuits will not _all_ be in
use, at
full capacity, at the same time.

E-mail me if you want to discuss it.

The OP would be better off posting his questions publicly so that
others
have
the opportunity to correct your errors.

--
Regards,
Doug Miller (alphageek-at-milmac-dot-com)

Get a copy of my NEW AND IMPROVED TrollFilter for NewsProxy/Nfilter
by sending email to autoresponder at filterinfo-at-milmac-dot-com
You must use your REAL email address to get a response.



Thanks Doug...thats why I posted the "How do you figure"
comment...there was
a
serious violation of ohms law in the Turtles comment....Ross

This is Turtle.

I have say I got it backwards to be completely saying the story. You can
get
150
amps on each leg . Then you fill in the blanks as to using 220 volt
sevice of
both legs. Then when you say the box is only good for 150 amps at 220
volt
service. Your saying your drawing 150 amps from each leg and that adds up
to
300
amps you will really be drawing from the box with 150 amps from each leg.
When
you say 220 service breaker in the 150 amp box they are drawing 300 amps
in the

real world. You may try to explain it differently but it mounts up to 300
amps
by way of 120 volt draw.

The meaning of 220 volt service at 150 amps means you can pull 150 amps
off
each
leg by doing so. This amounts to 300 amps if I use single breakers. Now
you &
Mr. Miller please explain what is wrong with this info ?

Nothing at all wrong with that... but this is what you posted first:

This is Turtle.

150 amps in 115 volt service or 300 amps in a 220 volt service.


And that's backward.


This is Turtle.

I have been working with 3 phase 480 volt systems for the last two weeks
and I seem to get everything assbackwards when I get off 3 phase and get
back on single phase stuff again. If your 3 phasing your thinking 1/3 and
not 1/2 with single phase.

So can you forgive me for being assbackwards one time ?

TURTLE


But of course, none of us have ever done that!....yeah right....take care
Turtle....Ross