I need some help and advice on heating and cooling for a 2nd story
extension in Melbourne.
The existing house is brick veneer (built in the 60) has an old gas
ducted heating (~70 vintage) 1 ~5yr old 6.5kw reverse cycle ac for the
living room at the back. There are ceiling fans in the bedroom and
living room for cooling.
surface area is ~160 sq m.

The upstair extension is ~65 sq m. 2 bedroom, 1 study and 1 retreat
area.
The existing ducted heating to the back of the house is disconnected.
(where the old reverse cycle ac is...) to reduce clearence space.
There is no room to run ducts between 1st level and 2nd level.

There are 3 ideas:
a) install an evaporative cooling with vent on upstair only. Rely on
the stair well to let the moist air to vent out down stair, rely on
the stair well to let the heated air rise up to heat upstair.
(cost ~4K)

b) install 2 2.5kw cooling reverse cyclesplit system (inverter type)
in the bedroom upstair. 1 ~5kw split system in the study to blow out
to the retreat area.
cost ~7k

c) install a ducted reverse cycle, 5pts. 7.5kw plus machine (do you
need an inverter type)
cost ~7K-10K

Ceiling fan in living room and rooms. for b) and c)

Any good suggestions? Running cost for a) is lowest but would it be
ok?
The insulation upstair is max out except the window is not double
glazed.

Any suggestion on how you would approach the problem? The pro and con
on all 3 options?
  #2   Report Post  
 
Posts: n/a
Default

tony wrote:

I need some help and advice on heating and cooling for a 2nd story
extension in Melbourne...


There are 3 ideas:
a) install an evaporative cooling with vent on upstair only...


Does evaporative cooling work well in Melbourne? It looks like the
relative humidity is about 50% at 3 PM on an average summer day.

http://www.bom.gov.au/cgi-bin/climat...ript.cgi?86071

b) install 2 2.5kw cooling reverse cyclesplit system (inverter type)


Is that a heat pump? What's an "inverter type"? Variable speed drive?

Ceiling fan in living room and rooms. for b) and c)

Any good suggestions?


You might run a whole house window exhaust fan upstairs with a window
inlet downstairs (and also run the ceiling fans) at night when outdoor
air is cooler than indoor air, using a differential thermostat, and close
up the house during the day and let its thermal mass provide coolth.
The average daily min and max temps are 13 and 25 C (56 and 78 F.)

To prevent reverse airflow during the day, the inlet and outlet windows
might have one-way passive lightweight plastic film or motorized dampers.
With large enough windows, the dampers might keep the house cool without
the fan :-) With dew point control to avoid condensation, they could also
provide heat.

If there isn't much mass on the 2nd floor, you might bring up cool air
from the 1st with a fan and a 2nd floor thermostat and occupancy sensor.
You might bring down warm air in wintertime.

A 2500 cfm fan and a 500 Btu/h-F house with 20K Btu/F of thermal mass
might be modeled like this, viewed in a fixed font:

1/500
Ta (56 min, 78 max) -------www------------ Ti (59 min, 63 max)
| |
| / 1/2500 |
-- ---www----|
|
--- 20K Btu/F
---
|
-
10 PI=4*ATN(1)
20 G=500'house conductance (Btu/h-F)
30 C=20000'house capacitance (Btu/F)
40 CFM=2500'fan cfm
50 FOR DAY=1 TO 10'simulate 10 average days
60 TIMIN=100'initialize min temp
70 FOR HOUR=0 TO 23
80 FANMARK=0
90 TA=(78+56)/2+(78-56)/2*SIN(2*PI*HOUR/24)'outdoor temp (F)
100 IF TITA THEN Q=(TA-TI)*(G+CFM):FANMARK=1:ELSE Q=(TA-TI)*G
110 TI=TI+Q/C'new house temp (F)
120 IF DAY10 GOTO 170'stats for last day
130 IF TITIMIN THEN TIMIN=TI
140 TITOT=TITOT+TI'total for average
150 IF TITIMAX THEN TIMAX=TI
160 FANHOURS=FANHOURS+FANMARK
170 NEXT HOUR
180 NEXT DAY
190 PRINT TIMIN,TITOT/24,TIMAX,FANHOURS

Min house Avg house Max house Fan hours
temp (F) temp (F) temp (F) per day

59.30385 61.30324 63.40533 8

Nick

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
eScrew OWNS YOU!!! [email protected] Metalworking 7 December 22nd 04 09:47 PM
eScrew Dave Jackson Woodworking 1 December 21st 04 01:54 AM
Funny story about metal [email protected] Metalworking 10 December 20th 04 05:26 PM
Funny story about repair [email protected] Electronics Repair 0 December 20th 04 03:35 AM
Illegal house extension demolished Mr Justice S Tinks UK diy 88 September 16th 03 08:40 PM


All times are GMT +1. The time now is 04:46 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"