I'm adding a 60k btu unit heater (ceiling mount) to a detached
workshop (w/ permit). It will be nat. gas and is a 2 psi system. The
heater is the only gas appliance in the building. There will be a
regulator
(2psi to 7"wc) located about 2-3' from the heater (the regulator will
be in the attic). Total pipe from from the riser to the regulator in
the building is about 20 feet.

Should this regulator be a "line" or "appliance" type regulator, or
does it matter? I'm looking at using either a Maxitrol 325-3L or
325-3.

Thanks,
Rob

Joe Bobst November 3rd 04 03:34 PM

Why would you need a regulator since your NG company supplies one at the gas
meter? In my experience, Modine and other unit heater suppliers that I have
installed don't need extra gas regulation. Nor do gas furnaces. Maybe its the
type of heater gas valve or something? Please enlighten as I may be behind the
latest technology. ???

Joe


Greg O November 3rd 04 11:42 PM


"Joe Bobst" wrote in message
...
Why would you need a regulator since your NG company supplies one at the

gas
meter? In my experience, Modine and other unit heater suppliers that I

have
installed don't need extra gas regulation. Nor do gas furnaces. Maybe its

the
type of heater gas valve or something? Please enlighten as I may be behind

the
latest technology. ???

Joe


Re-read his post, gas pressure is 2 PSI.
He needs a regulator, a 325-3 should be fine.
Latest technology? Not really! Many utilities supply the natural gas at 6-7
inches of water column to the home, often a utility will supply at 2 PSI,
then regulators for the appliances are required.
The utility in our area typically provides 2 PSI NG.
Greg



Zypher November 4th 04 07:49 AM

The unit heater should come with an appliance regulator.? No?

--
Zyp
"Greg O" wrote in message
...

"Joe Bobst" wrote in message
...
Why would you need a regulator since your NG company supplies one at the

gas
meter? In my experience, Modine and other unit heater suppliers that I

have
installed don't need extra gas regulation. Nor do gas furnaces. Maybe

its
the
type of heater gas valve or something? Please enlighten as I may be

behind
the
latest technology. ???

Joe


Re-read his post, gas pressure is 2 PSI.
He needs a regulator, a 325-3 should be fine.
Latest technology? Not really! Many utilities supply the natural gas at

6-7
inches of water column to the home, often a utility will supply at 2 PSI,
then regulators for the appliances are required.
The utility in our area typically provides 2 PSI NG.
Greg





Speedy Jim November 4th 04 02:06 PM

Zypher wrote:

The unit heater should come with an appliance regulator.? No?

Modern gas valves come with an integral regulator.
However, typically the regulator has a maximum inlet
pressure rating of only 1/2 psi. In this case he
does need an upstream regulator.

Jim

Rob November 4th 04 02:41 PM

Re-read his post, gas pressure is 2 PSI.
He needs a regulator, a 325-3 should be fine.
Latest technology? Not really! Many utilities supply the natural gas at

6-7
inches of water column to the home, often a utility will supply at 2 PSI,
then regulators for the appliances are required.
The utility in our area typically provides 2 PSI NG.
Greg



Yes, there is a regulator at the gas meter, but that brings the
"street" pressure down to 2psi; from there it is distributed to the
various appliances and further regulated to 7"wc. In my situation, a
separate 2psi line (size 1") runs from the meter to the shop (about
100'). The heater needs an input of about 7"wc and thus the need for
a 2psi to 7" reg. The heater does have an internal regulator but it
only allows 7"wc input and brings the pressure down to about 3.5"wc
for the burner.