We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr or
144 kwh per month. Actually, add some because the power factor is not 1.0
but take away some because it was not running continuously. Anyway, that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?


  #2   Report Post  
John McGaw
 
Posts: n/a
Default Circulator pumps?

"William W. Plummer" wrote in message
news:c6qYb.343182$na.502861@attbi_s04...
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr

or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?

I installed a Grundfos circulator on my system in Alaska more to reduce
noise than any other reason. My recollection is that it consumed something
like 120W but at this late date I can't recall if this was a full speed or
at one of the two lower speeds. The pump was efficient enough that I never
had to run it at the full speed and the house stayed warm even at sub-zero
temps. Because of a peculiarity of the heating system, a hanging heater
added to the garage which had no zone valve, the pump ran 24 X 7 whenever I
had the boiler switched on and my electric bills weren't spectacularly high.
--
John McGaw
[Knoxville, TN, USA]

Return address will not work. Please
reply in group or through my website:
http://johnmcgaw.com


  #3   Report Post  
m Ransley
 
Posts: n/a
Default Circulator pumps?

What is your water temp set at, If its set low the pump can run 24 - 7.
Baseboard heat requires apx 185 , large wall radiators 140. But going to
a higher temp will help. For large wall radiators my system is set at
190.
I beleive the AC motors are all comparable in efficency .
Look into other areas, CFLs , Phantom loads, and doing your own energy
audit with a Kill-A-Watt.
Anything plugged in ex., cordless phone, TV , radio, microwave , vcr,
sattelite, each apliance can easily add 1-2 $ a month,
It all adds up fast.

  #4   Report Post  
Art Todesco
 
Posts: n/a
Default Circulator pumps?

We see the same thing when there is a particularly cold month
even with forced air heat from the furnace blower. December is
hard to tell due to added Christmas light load. The newer
furnaces claim to have lower power requirements on the blower.
My present furnace (15 years old now) is better on electricity,
however, I believe it's partly because the blower has higher
CFMs compared to the old one, so it probably runs a bit less.

BTW, doesn't the power factor actually decrease the measured
watt-hours? That's why the power company adds capacitors to
correct the power factor so they don't loose money on low
readings. It's been a long time since I studied these things,
so I may be totally wrong here.

William W. Plummer wrote:
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr or
144 kwh per month. Actually, add some because the power factor is not 1.0
but take away some because it was not running continuously. Anyway, that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?



  #5   Report Post  
William W. Plummer
 
Posts: n/a
Default Circulator pumps?

I believe it is the other way because the power company must ship more power
to get the same amount into the reactive (motor) load to do the actual work.
It's sort of an "efficiency" thing.

A crude audit showed the circulator was 1/3 of my use, the frige was 1/3 and
the rest of the house (computers, TV, clocks, electric blanket (left on),
etc were the final 1/3. I get concerned when they start reading my meter
in RPM. Cleaning the frige fins was hard to do and didn't seem to make any
difference.


"Art Todesco" wrote in message
news:12sYb.206718$U%5.1136792@attbi_s03...
We see the same thing when there is a particularly cold month
even with forced air heat from the furnace blower. December is
hard to tell due to added Christmas light load. The newer
furnaces claim to have lower power requirements on the blower.
My present furnace (15 years old now) is better on electricity,
however, I believe it's partly because the blower has higher
CFMs compared to the old one, so it probably runs a bit less.

BTW, doesn't the power factor actually decrease the measured
watt-hours? That's why the power company adds capacitors to
correct the power factor so they don't loose money on low
readings. It's been a long time since I studied these things,
so I may be totally wrong here.

William W. Plummer wrote:
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the

reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2

kwh/hr or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?







  #6   Report Post  
Greg O
 
Posts: n/a
Default Circulator pumps?


"William W. Plummer" wrote in message
news:c6qYb.343182$na.502861@attbi_s04...
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr

or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?



Is it worth the trouble?
Even at 10 cents per KW it works out to $14.40 per month, when in use. If
you drop it by 1/2 you save $7.20 per month, when in use. I assume that the
circulating pump only runs on a call for heat, so warmer months will be even
less. If you have connections you may be able to buy a pump for $60 for a
small one, larger pumps are more yet. If you pay retail, and have someone
install it, the return on investment is less yet. At $60 it probably will
take 2-3 years to break even.
Greg

  #7   Report Post  
RB
 
Posts: n/a
Default Circulator pumps?

I don't know about circulators, but Gould has a line of more efficient
motors for swimming pool pumps that really make a difference. I doubt
that the efficiency of small motors (probably 0.1 HP for a circulator)
warrants as much interest in improved efficiency as a 2 or 3 HP pool
pump motor though.

RB

William W. Plummer wrote:
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr or
144 kwh per month. Actually, add some because the power factor is not 1.0
but take away some because it was not running continuously. Anyway, that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?



  #8   Report Post  
RB
 
Posts: n/a
Default Circulator pumps?



Art Todesco wrote:
We see the same thing when there is a particularly cold month even with
forced air heat from the furnace blower. December is hard to tell due
to added Christmas light load. The newer furnaces claim to have lower
power requirements on the blower. My present furnace (15 years old now)
is better on electricity, however, I believe it's partly because the
blower has higher CFMs compared to the old one, so it probably runs a
bit less.

BTW, doesn't the power factor actually decrease the measured
watt-hours? That's why the power company adds capacitors to correct the
power factor so they don't loose money on low readings. It's been a
long time since I studied these things, so I may be totally wrong here.

You're correct.

RB

William W. Plummer wrote:

We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my
electric bill
went up, also. I suspect the circulator pump motor might be the
reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2
kwh/hr or
144 kwh per month. Actually, add some because the power factor is
not 1.0
but take away some because it was not running continuously. Anyway,
that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?




  #9   Report Post  
William W. Plummer
 
Posts: n/a
Default Circulator pumps?

My circulator motor says 1.7 amps. At 115 vac, that is 200 watts. 200 /
746 is a little more than 1/4 HP. However, I don't know if the motor is
fully loaded by loop of baseboard radiators, all on one floor. Another
poster pointed out that using higher temperature water will deliver the
required heat in a shorter time, minimizing the time the circulator is
running.



"RB" wrote in message
...
I don't know about circulators, but Gould has a line of more efficient
motors for swimming pool pumps that really make a difference. I doubt
that the efficiency of small motors (probably 0.1 HP for a circulator)
warrants as much interest in improved efficiency as a 2 or 3 HP pool
pump motor though.

RB

William W. Plummer wrote:
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the

reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2

kwh/hr or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?





  #10   Report Post  
Greg O
 
Posts: n/a
Default Circulator pumps?


"William W. Plummer" wrote in message
news:K5KYb.213803$U%5.1238186@attbi_s03...
Another
poster pointed out that using higher temperature water will deliver the
required heat in a shorter time, minimizing the time the circulator is
running.




Which would raise the amount of gas or oil one uses to heat the water.
Certainly would cost more than the $14 a month it costs to run the pump!
Greg



  #11   Report Post  
m Ransley
 
Posts: n/a
Default Circulator pumps?

But for most of us electricity is double the cost of gas per btu
extracted so raising water temp is overall cheaper than running a pump

  #12   Report Post  
William W. Plummer
 
Posts: n/a
Default Circulator pumps?


"m Ransley" wrote in message
...
But for most of us electricity is double the cost of gas per btu
extracted so raising water temp is overall cheaper than running a pump


I agree. The boiler will only be on during the time that the circulater is
running, i.e., when a zone thermostat is calling for heat. So shortening
the time the thermostat calls for heat shortens the circulator time and the
burner time. It's a super win to use higher water temp. Also, note that
heat flow (calories per hour) is proportional to the temperature difference
(water to room), so that's another reason to use high temp water.


  #13   Report Post  
Stormin Mormon
 
Posts: n/a
Default Circulator pumps?

Well, there's not a lot you can do about it. Except maybe a couple drops of
Bell and Gossett approved oil in the oil cups.

If I was a wise acre, I'd suggest that you could save a lot of money by
disconnecting the pump, but I won't go there.

If it really bothers you, maybe your heating guy can turn up the boiler temp
a couple degrees, so the pump doesn't run as often. But that would increase
the risk of burns on the radiators, and would likely cost more than the
electric savings.

I'd reccomend that you find something more signifigant to worry about.
That's not very high on my list of things to concern me.

--

Christopher A. Young
Join Alt-Hvac Moderated
A free, easy to use Yahoo! group



"William W. Plummer" wrote in message
news:c6qYb.343182$na.502861@attbi_s04...
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr

or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?




  #14   Report Post  
ftwhd
 
Posts: n/a
Default Circulator pumps?



--
..
"William W. Plummer" wrote in message
news:c6qYb.343182$na.502861@attbi_s04...
We had a very cold winter here in New England and my heating system was
running much of the time. So gas bills have been high, but my electric

bill
went up, also. I suspect the circulator pump motor might be the reason.
The label on it says 1.7 amps so that is close to 200 watts or 0.2 kwh/hr

or
144 kwh per month. Actually, add some because the power factor is not

1.0
but take away some because it was not running continuously. Anyway,

that's
about the increase I saw.

Are there more efficient circulator motor/pumps available these days?
Recommendations?


well, us union guys always use Bell and Gossett. If you don't like it, we
let you talk to Uncle Guido. Get the picture? Like your knees?



  #15   Report Post  
m Ransley
 
Posts: n/a
Default Circulator pumps?

There is an aquastat on your boiler , either on it or under the front
cover, it will have a dial or screw adjustment and temp numbers on the
wheel. Just read it and set it to 170 or 180. unless its set real low
your savings will be mimimal and other things should be looked into for
saving electricity.
An 9$ pack of 4 - 13 watt compact flourescent that equal 60 watt
incandesant at HD or Menards will pay for itself in in 2 weeks at ,125
KWH run 24 x 7 . Thats a good investment.
I wouldnt disconnect it as Wise Acre Stormin suggests it could be .
Only Stormin worries about burns on a radiator he probably uses them
as chairs to warm his hemroids.Stormys Roid warmers.
And yes everything you change will help electric bills , but why pay
a service call for it.
Putting my tv vcr sattelite , dvd , stereo, on a switch and turning it
off at night saved me 4 $ a month . I removed 4 cordless phones and
save another 6



  #16   Report Post  
Bob
 
Posts: n/a
Default Circulator pumps?


"William W. Plummer" wrote
in message news:N9UYb.216670$U%5.1268075@attbi_s03...

"m Ransley" wrote in message
...
But for most of us electricity is double the cost of gas

per btu
extracted so raising water temp is overall cheaper than

running a pump

I agree. The boiler will only be on during the time that the

circulater is
running, i.e., when a zone thermostat is calling for heat. So

shortening
the time the thermostat calls for heat shortens the circulator

time and the
burner time. It's a super win to use higher water temp.

Also, note that
heat flow (calories per hour) is proportional to the

temperature difference
(water to room), so that's another reason to use high temp

water.

So, by raising the water temp, you reduce the heat flow into the
water from the flame?

Bob


  #17   Report Post  
m Ransley
 
Posts: n/a
Default Circulator pumps?

by raising water temp your thermostat- temp will reach and maintain
desired temp longer without boiler or pump running, with low water temp
a pump can just run continously refiring off the aquastat. So with
longer boiler operation water reaches a higher temp.

  #18   Report Post  
Paul Franklin
 
Posts: n/a
Default Circulator pumps?

Good points all, but....

It's not so simple.

First, adjusting the aquastat to a higher temperature changes the high
limit, which is not the always the same as raising the actual
temperature of the water. Most boilers, during all but the coldest
weather, will not get the water temperature up to the high limit
setting very often. Remember, the burner only fires when a zone is
calling for heat (and the water temp is below high limit setting).
Since most boilers are selected to have sufficient capacity to heat
the house even when temperature is at the design low, when the outside
temp is warmer, the house reaches the thermostat setting and shuts
down the burner before the water temp reaches high limit. The only
time my boiler hits high limit is first thing in the morning in very
cold weather when the system is raising the house temp from the night
setback to normal temperature.

It takes the same number of btu's delivered to the radiators to
maintain your house at temperature whether the water is at 140 or 190.
It's true that at a lower water temperature, the circ will have to run
longer to deliver those btu's, and several have pointed out correctly
that this costs real money. But running the water temperature higher
increases the standby losses up the stack, which also costs real
money. If you have an automatic vent damper, this helps this
somewhat. Standby losses are also increased when the standby time is
increased. Running higher water temp means more and longer standby
periods compared to lower water temp. Comparing the cost of
electricity to gas is irrelevant; you are not comparing electric heat
to gas heat. In this case, gas is always heating the water,
electricity is pushing it around. You save electricity by running the
circ less, but you pay it back by making up for the standby losses
with gas. Which factor wins depends on average temperature, boiler
efficiency, presence of vent damper, how well the boiler is matched to
the house, and on and on.

While running at lower water temp means the circ will run more, this
actually tends to deliver more even and comfortable heat, with fewer
cold drafts during the off time of the circulator. Yes it costs more
to run the circ longer, but some are willing to pay for more even
heat and the comfort. Again, this is offset also by the reduced
standby losses.

As I said, it's not so simple.


Paul Franklin

  #19   Report Post  
m Ransley
 
Posts: n/a
Default Circulator pumps?

Yea paul but standby loss on any boiler is minimal compared to
radiator loss , so get an Auto vent as most New systems have
Even so a higher effeciency system is best

  #20   Report Post  
L. M. Rappaport
 
Posts: n/a
Default Circulator pumps?

On Thu, 19 Feb 2004 13:34:24 GMT, "William W. Plummer"
wrote (with possible editing):

The baseboard radiators replaced a radiant, in-the-slab-copper system which
had gotten very leaky. I understand it was standard to set the temp fairly
low on those systems. I will have it checked the next time I have it
serviced.


That is VERY significant. At my place, we have both radiant and
baseboard. The radiant all has mixing valves to mix some of the
return with the supply. I can't remember the exact details, but as I
recall, radiant under concrete topped with tile is set somewhere
around 110 deg F while radiant under carpet is set around 120 deg F.
This compares with the boiler output which is fed to hot water and
baseboard and is set around 180 deg F.

I'm not an expert, but I'd guess that's your problem.

--

Larry
Email to rapp at lmr dot com


  #21   Report Post  
L. M. Rappaport
 
Posts: n/a
Default Circulator pumps?

On Tue, 17 Feb 2004 10:14:07 -0500, "John McGaw"
wrote (with possible editing):

....snip

I installed a Grundfos circulator on my system in Alaska more to reduce
noise than any other reason.


John,

I have a similar problem. Did you find the Grundfos was
substantially quieter?

Thanks,
--

Larry
Email to rapp at lmr dot com
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT +1. The time now is 06:53 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"