There are many cost effective ways to connect a generator that are safe
although they may still be a technical violation of the electric code
that is enforced in your area.

In some recreational vehicles the cord that is used to connect the
vehicles electrical panel to the park outlet at the site is plugged into
an outlet from the generator when running on the onboard power. Since
the cords male cap is dead when unplugged from either outlet and it
cannot be plugged into two receptacles at once there is no danger of
electric shock from contact with exposed energized plug blades and no
likelihood of a back feed or interconnection of the two power sources.
Mobile homes are sometimes equipped with a fifty ampere cord and plug
assembly to connect them to power. Mobile home park service pedestals
are often equipped with a NEMA 14-50R pattern receptacle for just that
reason. It is true that the code does not sanction connecting a sub
panel to it's supply feeder via a four wire ranch receptacle and a range
cord set but like a mobile home were the same code permits the practice
it can be done safely. The total cost of the additional parts is less
than forty dollars US. When the need for emergency power arises you
unplug the cord from the outlet and plug it into an appropriate
recreational vehicle extension cord from the generator.

For one hundred dollars worth of parts you can set up a small sub panel
with two mechanically interlocked breakers to control the power to it.

There is a kit available for most SquareD panels that will interlock the
main breaker and a breaker in positions 2/4. The breaker in 2/4 serves
as the generator disconnect and the interlock keeps it from being closed
at the same time as the main breaker. Total cost of parts is less than
$120 US including the cost of the inlet box into which the generator
cord gets plugged.

All of these have some things in common. You would have to modify any
of them in order to create a back feed hazard. They can be connected by
any healthy adult without special knowledge or skill. They cost less
that an equivalent ampacity transfer switch.
--
Tom

  #2   Report Post  
albown
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.


"Thomas D. Horne" wrote in message
link.net...
There are many cost effective ways to connect a generator that are safe
although they may still be a technical violation of the electric code
that is enforced in your area.

In some recreational vehicles the cord that is used to connect the
vehicles electrical panel to the park outlet at the site is plugged into
an outlet from the generator when running on the onboard power. Since
the cords male cap is dead when unplugged from either outlet and it
cannot be plugged into two receptacles at once there is no danger of
electric shock from contact with exposed energized plug blades and no
likelihood of a back feed or interconnection of the two power sources.
Mobile homes are sometimes equipped with a fifty ampere cord and plug
assembly to connect them to power. Mobile home park service pedestals
are often equipped with a NEMA 14-50R pattern receptacle for just that
reason. It is true that the code does not sanction connecting a sub
panel to it's supply feeder via a four wire ranch receptacle and a range
cord set but like a mobile home were the same code permits the practice
it can be done safely. The total cost of the additional parts is less
than forty dollars US. When the need for emergency power arises you
unplug the cord from the outlet and plug it into an appropriate
recreational vehicle extension cord from the generator.

For one hundred dollars worth of parts you can set up a small sub panel
with two mechanically interlocked breakers to control the power to it.

There is a kit available for most SquareD panels that will interlock the
main breaker and a breaker in positions 2/4. The breaker in 2/4 serves
as the generator disconnect and the interlock keeps it from being closed
at the same time as the main breaker. Total cost of parts is less than
$120 US including the cost of the inlet box into which the generator
cord gets plugged.

All of these have some things in common. You would have to modify any
of them in order to create a back feed hazard. They can be connected by
any healthy adult without special knowledge or skill. They cost less
that an equivalent ampacity transfer switch.
--
Tom


A word of caution.
The utility requirements for this in the Phoenix area state " visible blade
disconnect".
Check with the utility before making connections. They get powerfully ****ed
off if you backfeed the grid by mistake.



  #3   Report Post  
albown
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.


"Thomas D. Horne" wrote in message
link.net...
There are many cost effective ways to connect a generator that are safe
although they may still be a technical violation of the electric code
that is enforced in your area.

In some recreational vehicles the cord that is used to connect the
vehicles electrical panel to the park outlet at the site is plugged into
an outlet from the generator when running on the onboard power. Since
the cords male cap is dead when unplugged from either outlet and it
cannot be plugged into two receptacles at once there is no danger of
electric shock from contact with exposed energized plug blades and no
likelihood of a back feed or interconnection of the two power sources.
Mobile homes are sometimes equipped with a fifty ampere cord and plug
assembly to connect them to power. Mobile home park service pedestals
are often equipped with a NEMA 14-50R pattern receptacle for just that
reason. It is true that the code does not sanction connecting a sub
panel to it's supply feeder via a four wire ranch receptacle and a range
cord set but like a mobile home were the same code permits the practice
it can be done safely. The total cost of the additional parts is less
than forty dollars US. When the need for emergency power arises you
unplug the cord from the outlet and plug it into an appropriate
recreational vehicle extension cord from the generator.

For one hundred dollars worth of parts you can set up a small sub panel
with two mechanically interlocked breakers to control the power to it.

There is a kit available for most SquareD panels that will interlock the
main breaker and a breaker in positions 2/4. The breaker in 2/4 serves
as the generator disconnect and the interlock keeps it from being closed
at the same time as the main breaker. Total cost of parts is less than
$120 US including the cost of the inlet box into which the generator
cord gets plugged.

All of these have some things in common. You would have to modify any
of them in order to create a back feed hazard. They can be connected by
any healthy adult without special knowledge or skill. They cost less
that an equivalent ampacity transfer switch.
--
Tom


A word of caution.
The utility requirements for this in the Phoenix area state " visible blade
disconnect".
Check with the utility before making connections. They get powerfully ****ed
off if you backfeed the grid by mistake.



  #4   Report Post  
Spehro Pefhany
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.

On Sun, 17 Aug 2003 00:18:25 GMT, the renowned "Gerald Newton"
wrote:

Many home owners do it the simple and cheap way - use a male to male
extension cord. Plug one end into the generator and the other into a
household receptacle. This is dangerous and a violation of the code, but
they do it anyway.


Somebody in rec.crafts.metalworking suggested wiring a parallel set of
receptacles which can *only* be energized by the generator. Then you
manually transfer the fridge etc. from one plug to the other right
beside it. Simple, cheap and it I can't see how it would be unsafe if
it was done properly as there is no connection between the generator
and the mains at any time. In the above method, the home owner has to
remember to disconnect the main breaker or a dangerous (to a lineman)
situation could exist.

Best regards,
Spehro Pefhany
--
"it's the network..." "The Journey is the reward"
Info for manufacturers: http://www.trexon.com
Embedded software/hardware/analog Info for designers: http://www.speff.com
  #5   Report Post  
Spehro Pefhany
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.

On Sun, 17 Aug 2003 00:18:25 GMT, the renowned "Gerald Newton"
wrote:

Many home owners do it the simple and cheap way - use a male to male
extension cord. Plug one end into the generator and the other into a
household receptacle. This is dangerous and a violation of the code, but
they do it anyway.


Somebody in rec.crafts.metalworking suggested wiring a parallel set of
receptacles which can *only* be energized by the generator. Then you
manually transfer the fridge etc. from one plug to the other right
beside it. Simple, cheap and it I can't see how it would be unsafe if
it was done properly as there is no connection between the generator
and the mains at any time. In the above method, the home owner has to
remember to disconnect the main breaker or a dangerous (to a lineman)
situation could exist.

Best regards,
Spehro Pefhany
--
"it's the network..." "The Journey is the reward"
Info for manufacturers: http://www.trexon.com
Embedded software/hardware/analog Info for designers: http://www.speff.com


  #6   Report Post  
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.

Why all the possibly dangerious etc complex things. I have a
generator with sufficient capacity to run frig, room ac, av center.
The very few times I have used it I simply used my 12 gage power cords
from the generator to the applienane thenunplugged pluged the frig
etc. from wall and into the cord. Little extra work but safe and
seldom necessary. Is someone there on an ventilator or something.

Louis




On Sat, 16 Aug 2003 17:50:10 GMT, "Thomas D. Horne"
wrote:

There are many cost effective ways to connect a generator that are safe
although they may still be a technical violation of the electric code
that is enforced in your area.

In some recreational vehicles the cord that is used to connect the
vehicles electrical panel to the park outlet at the site is plugged into
an outlet from the generator when running on the onboard power. Since
the cords male cap is dead when unplugged from either outlet and it
cannot be plugged into two receptacles at once there is no danger of
electric shock from contact with exposed energized plug blades and no
likelihood of a back feed or interconnection of the two power sources.
Mobile homes are sometimes equipped with a fifty ampere cord and plug
assembly to connect them to power. Mobile home park service pedestals
are often equipped with a NEMA 14-50R pattern receptacle for just that
reason. It is true that the code does not sanction connecting a sub
panel to it's supply feeder via a four wire ranch receptacle and a range
cord set but like a mobile home were the same code permits the practice
it can be done safely. The total cost of the additional parts is less
than forty dollars US. When the need for emergency power arises you
unplug the cord from the outlet and plug it into an appropriate
recreational vehicle extension cord from the generator.

For one hundred dollars worth of parts you can set up a small sub panel
with two mechanically interlocked breakers to control the power to it.

There is a kit available for most SquareD panels that will interlock the
main breaker and a breaker in positions 2/4. The breaker in 2/4 serves
as the generator disconnect and the interlock keeps it from being closed
at the same time as the main breaker. Total cost of parts is less than
$120 US including the cost of the inlet box into which the generator
cord gets plugged.

All of these have some things in common. You would have to modify any
of them in order to create a back feed hazard. They can be connected by
any healthy adult without special knowledge or skill. They cost less
that an equivalent ampacity transfer switch.


  #7   Report Post  
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.

Why all the possibly dangerious etc complex things. I have a
generator with sufficient capacity to run frig, room ac, av center.
The very few times I have used it I simply used my 12 gage power cords
from the generator to the applienane thenunplugged pluged the frig
etc. from wall and into the cord. Little extra work but safe and
seldom necessary. Is someone there on an ventilator or something.

Louis




On Sat, 16 Aug 2003 17:50:10 GMT, "Thomas D. Horne"
wrote:

There are many cost effective ways to connect a generator that are safe
although they may still be a technical violation of the electric code
that is enforced in your area.

In some recreational vehicles the cord that is used to connect the
vehicles electrical panel to the park outlet at the site is plugged into
an outlet from the generator when running on the onboard power. Since
the cords male cap is dead when unplugged from either outlet and it
cannot be plugged into two receptacles at once there is no danger of
electric shock from contact with exposed energized plug blades and no
likelihood of a back feed or interconnection of the two power sources.
Mobile homes are sometimes equipped with a fifty ampere cord and plug
assembly to connect them to power. Mobile home park service pedestals
are often equipped with a NEMA 14-50R pattern receptacle for just that
reason. It is true that the code does not sanction connecting a sub
panel to it's supply feeder via a four wire ranch receptacle and a range
cord set but like a mobile home were the same code permits the practice
it can be done safely. The total cost of the additional parts is less
than forty dollars US. When the need for emergency power arises you
unplug the cord from the outlet and plug it into an appropriate
recreational vehicle extension cord from the generator.

For one hundred dollars worth of parts you can set up a small sub panel
with two mechanically interlocked breakers to control the power to it.

There is a kit available for most SquareD panels that will interlock the
main breaker and a breaker in positions 2/4. The breaker in 2/4 serves
as the generator disconnect and the interlock keeps it from being closed
at the same time as the main breaker. Total cost of parts is less than
$120 US including the cost of the inlet box into which the generator
cord gets plugged.

All of these have some things in common. You would have to modify any
of them in order to create a back feed hazard. They can be connected by
any healthy adult without special knowledge or skill. They cost less
that an equivalent ampacity transfer switch.


  #8   Report Post  
Tom J
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.


wrote in message
...
Why all the possibly dangerious etc complex things. I have a
generator with sufficient capacity to run frig, room ac, av center.
The very few times I have used it I simply used my 12 gage power cords
from the generator to the applienane thenunplugged pluged the frig
etc. from wall and into the cord. Little extra work but safe and
seldom necessary. Is someone there on an ventilator or something.

Louis


Some of us have refrigerators that are hooked to water lines making it harder
to move it from the wall to unplug and plug in extension cords. Some of us
have central air that is hard wired and nothing to unplug!! Having a little
trouble breathing, but so far no ventilator. ;-)

Tom J


  #9   Report Post  
Tom J
 
Posts: n/a
Default Safe and cost effective generator connections to household wiring.


wrote in message
...
Why all the possibly dangerious etc complex things. I have a
generator with sufficient capacity to run frig, room ac, av center.
The very few times I have used it I simply used my 12 gage power cords
from the generator to the applienane thenunplugged pluged the frig
etc. from wall and into the cord. Little extra work but safe and
seldom necessary. Is someone there on an ventilator or something.

Louis


Some of us have refrigerators that are hooked to water lines making it harder
to move it from the wall to unplug and plug in extension cords. Some of us
have central air that is hard wired and nothing to unplug!! Having a little
trouble breathing, but so far no ventilator. ;-)

Tom J


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator FAQ Gunner Metalworking 0 January 23rd 04 05:24 PM


All times are GMT +1. The time now is 05:23 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"