I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!


  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

"Snuffy "Hub Cap" McKinney" wrote in message news I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!

PS -- The duct is well over the minimum size, clean, straight and clear all the way to the roof vent, about 8 feet. No back pressure.


  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,378
Default Broan Range Hood Venting into Room

On Sun, 13 Sep 2015 19:17:15 -0700, "Snuffy \"Hub Cap\" McKinney"
wrote:

I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!


I bought a new vent hood and it came set up to do up the vent and out
the front. It came with a plastic insert that you put over the front
exit if you wanted it to go up the roof vent. As this was an existing
house with a roof vent I hooked it to the vent tube and installed the
plastic cover. I could still feel air coming out thru the plastic
cover area. I suspect you are missing whatever sort of cover it came
with originally to cover up the inside vent area OR it's already
installed and just leaks some air like mine did. How strong is the
air flow out the inside part? I just left mine with the leakage since
it's in a rental. If it had been in my house I'd have figured how to
put metal duct tape over it on the inside to really seal it up.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 352
Default Broan Range Hood Venting into Room


"Snuffy "Hub Cap" McKinney" wrote in
message news I need to convert a range hood that is venting both up the vertical duct and
into the room, to just venting up to the duct. In the photo, the room vent
is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty
strong enough to vent only up the duct. There is an assembly connected
between the outlet of the fan to the top of the hood that directs some flow
through the vent in the top of the hood into the room. But I don't see any
way to close it - at least without taking things apart. No manual and
searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup
before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!

---------------


http://www.broan.com/common/productD...f-146a1bd37777

This is a link to one of their installation manuals, for one of their hoods
which can be EITHER ducted or non-ducted. It looks like whoever installed
didn't skip the steps pertaining to non-ducted installation AND did the
steps pertaining to ducted installastion to boot.

With any luck you can get in there and slide the recircultion slide plate
back in the closed position.

Good luck!



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

"taxed and spent" wrote in message ...

"Snuffy "Hub Cap" McKinney" wrote in
message news I need to convert a range hood that is venting both up the vertical duct and
into the room, to just venting up to the duct. In the photo, the room vent
is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty
strong enough to vent only up the duct. There is an assembly connected
between the outlet of the fan to the top of the hood that directs some flow
through the vent in the top of the hood into the room. But I don't see any
way to close it - at least without taking things apart. No manual and
searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup
before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!

---------------


http://www.broan.com/common/productD...f-146a1bd37777

This is a link to one of their installation manuals, for one of their hoods
which can be EITHER ducted or non-ducted. It looks like whoever installed
didn't skip the steps pertaining to non-ducted installation AND did the
steps pertaining to ducted installastion to boot.

With any luck you can get in there and slide the recircultion slide plate
back in the closed position.

Good luck!


Thanks AC & TS. I checked it out and that's exactly what happened. I can see something halfway diverting the exhaust out into the room. I bought it and the cabinet contractor installed it. Big mistake not reading the instructions first. The duct was already there from previous hood. Evidently people don't read the instructions.



  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 420
Default Broan Range Hood Venting into Room

Metal duct tape is your friend.
  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

wrote in message ...
Metal duct tape is your friend.


Yep, I always keep it handy. Still need to know if there's a plate blocking something before jumping into this. I'm hoping to get the manual or drawing from the Broan folks tomorrow.

Here's a poor sketch of the fan. Fan has a cylinder fastened to it and both turn together. The cylinder has a lip at the bottom that directs some of the exhaust away from the fan inlet and back out toward the range top. I put some metal tape around the housing which directs it back into the fan. Mickey Mouse I know, but it works in keeping the exhaust from spilling back outside the duct.

http://i58.tinypic.com/2588512.gif
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM
Found the manual for this unit online... Page 3 shows the steps that were skipped during installtion....

http://www.homedepot.com/catalog/pdf...6d0924c77a.pdf





"Snuffy "Hub Cap" McKinney" wrote in message news I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 352
Default Broan Range Hood Venting into Room


"Snuffy "Hub Cap" McKinney" wrote in
message ...
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM
Found the manual for this unit online... Page 3 shows the steps that were
skipped during installtion....

http://www.homedepot.com/catalog/pdf...6d0924c77a.pdf



----------

Isn't it page 4 that shows the steps that WERE NOT skipped (but should have
been)?


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 352
Default Broan Range Hood Venting into Room


"taxed and spent" wrote in message
...

"Snuffy "Hub Cap" McKinney" wrote
in message ...
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM
Found the manual for this unit online... Page 3 shows the steps that were
skipped during installtion....

http://www.homedepot.com/catalog/pdf...6d0924c77a.pdf



----------

Isn't it page 4 that shows the steps that WERE NOT skipped (but should
have been)?


er, you are right.




  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

"Snuffy "Hub Cap" McKinney" wrote in message news I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!

===

I just got around to fixing this hood. After getting the manual, it was 5 screws to remove the access panel holding the lights and one screw to remove the "air chute" (exhaust diverter). Inside the diverter the baffle had been inserted to blow air out into the room thru a vent in the top of the hood. It was simple to pull the baffle piece out, flip in around and keep the exhaust inside the duct.

I thought about just putting a piece of sheet metal over the opening in the duct, but didn't want to spend the time if it worked.

Reassembled and there is still a slight flow out of the vent into the room, and also some air flowing out around the lights, although both are lower than before. Still I don't want ANY exhaust coming out in the room. That defeats the whole purpose of having a vent fan.

I strated looking at where the air was coming from. The fan is fixed to a rotating housing, and the housing has a lip -- hard to describe -- on the bottom. So that when the exhaust starts to back up, it can flow back around the outside of the fan housing and down toward the stove top. The way the lip is curved, it forces the back pressure out away from the fan blade and it comes out back down thru the filters and toward the stove top. It also flows up and out the openings for the lights.

I looked up thru the fan and it looks pretty clear all the way to the top.

Now I'm starting to get ****ed. Seems to me the outlet of the van should be sealed so that any back pressure will not come back down into the kitchen. If that's a safety issue, they could have put a spring loaded relief vent instead of leaving that path completely clear.

I know there is always going to be exh leaking back around the blades, but I think this might be a bad design in this case.


Any comments about this?

  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 461
Default Broan Range Hood Venting into Room

"Snuffy "Hub Cap" McKinney" wrote in message ...
"Snuffy "Hub Cap" McKinney" wrote in message news I need to convert a range hood that is venting both up the vertical duct and into the room, to just venting up to the duct. In the photo, the room vent is seen on top of the hood.

http://www.nutone.com/common/seriesi...b-9600eae64e73

I have looked inside at all angles, and the squirrel cage fan is plenty strong enough to vent only up the duct. There is an assembly connected between the outlet of the fan to the top of the hood that directs some flow through the vent in the top of the hood into the room. But I don't see any way to close it - at least without taking things apart. No manual and searching the series number turned up nothing at www.broan.com.

Seems odd to me, but in any case, anyone ever seen this type of setup before?

Info from mfr plate:
Broan Allur Model QS1 Rev E, Mfd 2006, 1.8A, Hi/Low 110/220 CFM

Thanks buddies!

===

I just got around to fixing this hood. After getting the manual, it was 5 screws to remove the access panel holding the lights and one screw to remove the "air chute" (exhaust diverter). Inside the diverter the baffle had been inserted to blow air out into the room thru a vent in the top of the hood. It was simple to pull the baffle piece out, flip in around and keep the exhaust inside the duct.

I thought about just putting a piece of sheet metal over the opening in the duct, but didn't want to spend the time if it worked.

Reassembled and there is still a slight flow out of the vent into the room, and also some air flowing out around the lights, although both are lower than before. Still I don't want ANY exhaust coming out in the room. That defeats the whole purpose of having a vent fan.

I strated looking at where the air was coming from. The fan is fixed to a rotating housing, and the housing has a lip -- hard to describe -- on the bottom. So that when the exhaust starts to back up, it can flow back around the outside of the fan housing and down toward the stove top. The way the lip is curved, it forces the back pressure out away from the fan blade and it comes out back down thru the filters and toward the stove top. It also flows up and out the openings for the lights.

I looked up thru the fan and it looks pretty clear all the way to the top.

Now I'm starting to get ****ed. Seems to me the outlet of the van should be sealed so that any back pressure will not come back down into the kitchen. If that's a safety issue, they could have put a spring loaded relief vent instead of leaving that path completely clear.

I know there is always going to be exh leaking back around the blades, but I think this might be a bad design in this case.

Any comments about this?

****

The other comment is that instead of the lip on that fan housing being outward, if it were straight, any back pressure exhaust would flow straight down and be pulled back into the fan.



Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Range hood vent options/ self venting or vent through roof ? Mikepier Home Repair 3 September 3rd 07 06:48 AM
Broan Quiet Hood QT20000 steveseap Home Repair 1 June 25th 07 12:59 PM
Cooker hood extractor venting Pufter UK diy 0 May 17th 05 03:33 PM
Range hood vs. over-the-range microwave - which vent is better? Stan Home Repair 6 January 15th 05 02:45 AM
Broan Hood with RM325H 600CFM interior Blower: Anyone? Adam Finkelstein Home Ownership 4 February 16th 04 03:15 PM


All times are GMT +1. The time now is 12:04 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"