When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.

--


  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default replacement wire size

On 6/21/2014 3:44 PM, kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.


Are you changing the stove/range as well? If so, size it based on what
it needs.

The wire sizing isn't based on the number of conductors so use the same
as is there if the requirements haven't changed.

In general rule of thumb, the range will be on a 50A breaker and 8 ga
copper wire.

So the real answer is "we don't know" w/o additional information on the
range and breaker/fuse on the circuit.

--



  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default replacement wire size

On Saturday, June 21, 2014 5:16:02 PM UTC-4, dpb wrote:
On 6/21/2014 3:44 PM, kathleen ellis wrote:

When replacing the wiring for a stove what size wire should be used? I am


replacing 3 wires with 4 wire.




Are you changing the stove/range as well? If so, size it based on what

it needs.



The wire sizing isn't based on the number of conductors so use the same

as is there if the requirements haven't changed.



In general rule of thumb, the range will be on a 50A breaker and 8 ga

copper wire.



So the real answer is "we don't know" w/o additional information on the

range and breaker/fuse on the circuit.



--


+1

The wire size and breaker are determined by the
appliance. You seldom replace or change the wiring without
replacing the appliance, so this is a bit strange. The
appliance install instructions should say what to use.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11,640
Default replacement wire size

On 6/21/2014 4:44 PM, kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.


Same size you have.
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default replacement wire size

On Sat, 21 Jun 2014 20:44:01 +0000, kathleen ellis
wrote:

When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.

What size is there now? If you are using a 50 amp outlet you need
#6. It will be 6-3 with ground. (red/white/black plus green or
bare)What you have now will most likely be 6-2 with ground (black and
white plus bare ground)


  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 2
Default replacement wire size

On 6/23/2014 3:08 PM, Scott Lurndal wrote:
Doesn't it also depend on the length of the run?


1. Determine the load in amps.
2. Select a cable to handle the amps.
3. Select a breaker to limit amperage and protect the cable.
4. Up-size the cable if the permissible voltage drop would be exceeded.

  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default replacement wire size

On Monday, June 23, 2014 8:55:13 PM UTC-4, Jack wrote:
On 6/23/2014 3:08 PM, Scott Lurndal wrote:

Doesn't it also depend on the length of the run?




1. Determine the load in amps.

2. Select a cable to handle the amps.

3. Select a breaker to limit amperage and protect the cable.

4. Up-size the cable if the permissible voltage drop would be exceeded.


You mean you want to do it the right way?


  #11   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default replacement wire size

kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.

Hi,
If it is brand new stove, there it should be mentioned in the manual.
4 wires what I'd get with proper wire gauge. It will meet code for sure.
  #12   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 14
Default replacement wire size

If it is a double oven stove or a stove with a warming drawer you need number 6 copper wire.

If it is a basic stove you can get by with #8 copper.

The best thing is to check the stove installation instructions or the nameplate.



When replacing the wiring for a stove what size wire should be used? I am

replacing 3 wires with 4 wire.



--


  #13   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default replacement wire size

On Thu, 26 Jun 2014 09:54:26 -0700 (PDT), John G
wrote:

If it is a double oven stove or a stove with a warming drawer you need number 6 copper wire.

If it is a basic stove you can get by with #8 copper.

The best thing is to check the stove installation instructions or the nameplate.



When replacing the wiring for a stove what size wire should be used? I am

replacing 3 wires with 4 wire.



--

Because you never know what the "next" stove might be, it is highly
recommended to put the #6 cable in when replacing old cable to upgrade
to "current code". It would be a pitty to have to do the job all over
again next time you buy a new stove just because you "cheaped out"
this time
  #14   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,526
Default replacement wire size

Everyone is assuming the OP needs to run a new circuit to the stove location.

It is also possible it is just a new cord and plug on the stove, in which case the answer is going to be different.
  #15   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 18,538
Default replacement wire size

On Fri, 27 Jun 2014 07:42:10 -0700 (PDT), TimR
wrote:

Everyone is assuming the OP needs to run a new circuit to the stove location.

It is also possible it is just a new cord and plug on the stove, in which case the answer is going to be different.

From what I remember it was pretty plain the OP needed to provide a
"4 wire circuit" for the stove. to replace the "3 wire circuit" that
was currently installed.


  #17   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3,644
Default replacement wire size

On Saturday, June 21, 2014 4:44:01 PM UTC-4, kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am

replacing 3 wires with 4 wire.



--


I prefer the 4 wire install, how many here would wire a outlet with the neutral being ground too?
  #18   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default replacement wire size

On Tuesday, July 1, 2014 10:32:36 AM UTC-4, bob haller wrote:
On Saturday, June 21, 2014 4:44:01 PM UTC-4, kathleen ellis wrote:

When replacing the wiring for a stove what size wire should be used? I am




replacing 3 wires with 4 wire.








--




I prefer the 4 wire install, how many here would wire a outlet with the neutral being ground too?


Would you prefer it if it costs $1000 extra to run a new 4 wire cable
back to the panel? The comparison with the outlet isn't a good comparison,
because it's never been code to wire an outlet with the neutral
and ground shared. In the case of existing oven circuits, it's permitted
and common. From a technical perspective, a general purpose
outlet is typically different than a dedicated hardwired oven or oven
receptacle. In the case of outlets, there are typically multiple
outlets, lights etc on a circuit, more places for connections to come loose or
other problems to crop up. In the case of an oven, the shared neutral/grd
is on a dedictaed 8 gauge or better cicuit from the panel to the appliance.

Is 4 wire better and required for new circuit runs? Yes. Would I
go changing an otherwise adequate 3 wire circuit to 4, just to replace
an oven? No. Apparently all the oven manufacturers agree, because every
oven install manual I've seen shows how to connect it to either a 3 wire
or 4 wire circuit.
  #19   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default replacement wire size

On 7/1/2014 9:32 AM, bob haller wrote:
On Saturday, June 21, 2014 4:44:01 PM UTC-4, kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.

....

I prefer the 4 wire install, how many here would wire a outlet with
the neutral being ground too?


I, for one...there's 75+ yr of existing practice that hasn't
demonstrated any real problem.

When had repair on the well a couple of summers ago, the well service
guys used section of 4-wire cable to replace the torn up section because
they said the current county Code req'd it as only they could run. Of
course, they then clipped the ground conductor on both ends since
there's nowhere for it to go, anyways. About as stupid as blindly
replacing a 3-wire for a 4-wire in a range/electric dryer app.

--
  #20   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default replacement wire size

On 7/1/2014 11:52 AM, dpb wrote:
....

When had repair on the well a couple of summers ago, the well service
guys used section of 4-wire cable to replace the torn up section because
they said the current county Code req'd it as only they could run. Of
course, they then clipped the ground conductor on both ends since
there's nowhere for it to go, anyways. About as stupid as blindly
replacing a 3-wire for a 4-wire in a range/electric dryer app.


ADDENDUM to this story...

I've not researched this point in detail but I think this is a place
where the requirement quoted above is, in fact, a case of
misinterpretation of the NEC requirements as there is for the well pump
nothing but a single 240V load; there is no neutral current return from
a 120V circuit as is the situation trying to be avoided by the update to
the Code as there is in the case of the range or dryer.

Turns out we may be forced to drill a new well before long; I'm certain
to research this in depth (so to speak ) before spending an extra
third for 4-wire down a 300-ft hole when there's nothing for that fourth
conductor to do anyway except take up space and add to the expense.

If I'd been on the NFPA Code Committee when this came up I'd have voted
"no" simply on the cost/material basis of there being no demonstrable
real problem being solved that justified the added expense. "Parsimony"
is a virtue in engineering, too...

--



  #21   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 15,279
Default replacement wire size

On Wednesday, July 2, 2014 6:06:27 PM UTC-4, dpb wrote:
On 7/1/2014 11:52 AM, dpb wrote:

...



When had repair on the well a couple of summers ago, the well service


guys used section of 4-wire cable to replace the torn up section because


they said the current county Code req'd it as only they could run. Of


course, they then clipped the ground conductor on both ends since


there's nowhere for it to go, anyways. About as stupid as blindly


replacing a 3-wire for a 4-wire in a range/electric dryer app.




ADDENDUM to this story...



I've not researched this point in detail but I think this is a place

where the requirement quoted above is, in fact, a case of

misinterpretation of the NEC requirements as there is for the well pump

nothing but a single 240V load; there is no neutral current return from

a 120V circuit as is the situation trying to be avoided by the update to

the Code as there is in the case of the range or dryer.



I would agree that the well situation is a
misinterpretation of the code by someone. Even in cases where you
think the code section is excessive on some point, I've always
been able to see some point to doing it. To insert a section of 4 wire
cable in the middle of a 3 wire and leave the 4th unconnected,
obviously does nothing. Also, 240V loads are routinely connected
and are code compliant without a neutral all the time. That's how
wells are done here. So, I'd say either this is the well guys that
don't know what they are talking about, or else some local inspector
type that issued some edict either incorrectly or incorrectly interpreted,
etc.




Turns out we may be forced to drill a new well before long; I'm certain

to research this in depth (so to speak ) before spending an extra

third for 4-wire down a 300-ft hole when there's nothing for that fourth

conductor to do anyway except take up space and add to the expense.



I agree.




If I'd been on the NFPA Code Committee when this came up I'd have voted

"no" simply on the cost/material basis of there being no demonstrable

real problem being solved that justified the added expense. "Parsimony"

is a virtue in engineering, too...



--


Do you have any reason to believe it's part of the NEC?

A, as you say, it makes no sense at all from any physics

B, wells here are put in with 240V, 2 hots + ground all the time
and they pass electrical inspection.
  #22   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default replacement wire size

On 7/3/2014 6:37 AM, trader_4 wrote:
On Wednesday, July 2, 2014 6:06:27 PM UTC-4, dpb wrote:


....big snip...

If I'd been on the NFPA Code Committee when this came up I'd have voted
"no" simply on the cost/material basis of there being no demonstrable
real problem being solved that justified the added expense. "Parsimony"
is a virtue in engineering, too...

....

Do you have any reason to believe it's part of the NEC?

A, as you say, it makes no sense at all from any physics

B, wells here are put in with 240V, 2 hots + ground all the time
and they pass electrical inspection.


I was mixing both topics here and switched back once too quickly,
apparently...

No, I do _NOT_ think there's likely anything in NEC that justified the
4-wire cable in the well-hole; I have yet to discover from whence came
the supposed edict referred to by the well service guys...

What I was speaking of in the "voting against" comment is the new
section that requires the 4-wire for the grounding of the oven/dryer
branch circuit. There as you I do see there is at least an issue; I
just don't agree that the disease is worth the cost of the cure given
the history (or more correctly, the lack thereof) indicating it is a
safety issue of any magnitude at all.

I obviously wasn't in the room but I'd have had to seen an impressive
litany of cases where it had been the root cause of a problem and if
that were to have been demonstrated then I don't see how it could have
been justified to leave the exception standing. Making the change was,
imo, just bureaucracy doing what it does in this case. Most of the time
NFPA does a pretty good job but I think they misstepped on this one.

--
  #23   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default replacement wire size

On 7/1/2014 9:32 AM, bob haller wrote:
On Saturday, June 21, 2014 4:44:01 PM UTC-4, kathleen ellis wrote:
When replacing the wiring for a stove what size wire should be used? I am
replacing 3 wires with 4 wire.

....

I prefer the 4 wire install, how many here would wire a outlet with
the neutral being ground too?


Besides the aforementioned Code exception that doesn't require and
expressly permits the continued usage of 3-wire in existing
applications, there are a number of alternatives for rework/existing
work allowed by Code to add the ground if that is really, really, really
wanted besides running a new 4-wire cable the full distance.

These include pulling a separate ground and also exceptions that that
added ground doesn't necessarily have to follow the same path or even be
grounded at the same terminus. For the specifics see the Code or
consult local Code gurus.

--
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wire size Keith Nuttle Woodworking 41 June 7th 10 04:39 AM
wire size and amp rating Karl Townsend Metalworking 8 August 30th 07 02:18 PM
12 amp wire size Henry Home Repair 21 July 12th 07 07:07 PM
Wire size for 40A welder [email protected] Home Repair 8 December 18th 06 03:45 AM
Find the correct wire size for a load or the load for a selected wire size [email protected] Home Repair 5 December 13th 06 01:09 AM


All times are GMT +1. The time now is 12:29 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"