Home |
Search |
Today's Posts |
|
Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems. |
Reply |
|
|
LinkBack | Thread Tools | Display Modes |
#1
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
I just noticed that all the residential transformers on the poles on
my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. |
#2
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
|
#3
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
|
#4
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 10:28*am, George wrote:
On 2/24/2012 10:14 AM, wrote: I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. Think about it. Only one (of the two) wires feeding the primary of a typical single phase distribution transformer needs to be insulated. The 3 wires you see running down the road on poles are each one phase of a 3 phase distribution system. They are 120deg out of phase with each other. For larger industrial loads, like motors, they use all 3 phases and step it down. For light loads, residential, they use any one of the three phases and run it into a center tap transformer. The center tap becomes your neutral and each of the ends becomes one of the hots, giving you 240V between them, 120V between each of them and neutral. |
#5
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 10:28*am, George wrote:
On 2/24/2012 10:14 AM, wrote: How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. Think about it. Only one (of the two) wires feeding the primary of a typical single phase distribution transformer needs to be insulated. The problem is, there is only ONE wire. |
#6
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 10:14*am, wrote:
I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... ~~ Evan |
#7
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
wrote in message
The problem is, there is only ONE wire. The 2nd wire is the neutral down below. Notice this will run from pole to pole in-between where there are not 3 wires. The following is not exactly your transformer, but same thing... "If a primary neutral wire is available, a 'wye' or 'phase to neutral' transformer can be used. This usually has only one bushing on top, connected to one of the primary phases. The other end of the primary winding is 'grounded' to the transformer's case, which is connected to the neutral wire"... http://en.wikipedia.org/wiki/Distribution_transformer |
#8
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 10:45*am, Evan wrote:
Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. |
#9
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 10:31*am, bud-- wrote:
On 2/24/2012 9:14 AM, wrote: I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. In the alley behind my house the poles have one high voltage wire (8000V) and 3 low voltage wires (H-N-H). The low voltage H-H wires break between transformers but the neutral is continuous. The high voltage return must be on the secondary neutral. -- bud-- I think the return path for the other side of the primary transformer is the earth. Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. I see what the OP and you are talking about all over here in rural NJ. You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. I believe the other side is connected to earth ground. That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. |
#10
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
Google "Single-wire earth return" (SWER) for a diagram and explanation - as
others have said, it uses earth grounding for the return path. http://en.wikipedia.org/wiki/Single-wire_earth_return wrote in message ... On Feb 24, 10:45 am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. |
#11
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
SRN wrote: Google "Single-wire earth return" (SWER) for a diagram and explanation - as others have said, it uses earth grounding for the return path. http://en.wikipedia.org/wiki/Single-wire_earth_return wrote in message ... On Feb 24, 10:45 am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. The norm is one to three phase conductors at the top of the pole or on the cross arm at the top of the pole, with the neutral for those on the pole a few feet down, and the low voltage secondaries if present a few feet below that. The neutral is grounded at least every few poles with a small uninsulated wire down the side of the pole that connects to a plate at the bottom of the pole underground. The SWER or delta (two phase conductors, no neutral) configurations are obsolete and only found in areas with old infrastructure. |
#12
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 3:14*pm, wrote:
I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. The neutral and the ground may be one and the same. Common thing is Australia for example. But only in rural areas. So the "return" current goes through the ground. A cheap system, not without it's dangers. |
#13
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 12:14 PM, harry wrote:
On Feb 24, 3:14 pm, wrote: I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. The neutral and the ground may be one and the same. Common thing is Australia for example. But only in rural areas. So the "return" current goes through the ground. A cheap system, not without it's dangers. Some years back, I called the power company when I noticed that the metal thieves had cut and removed the copper ground/earth wires from all the power poles up and down the streets in my area. The wire was cut at the point as high as a man could reach. None of the power was of the single high voltage hot wire types. If that had been the case, there would have been a number of two legged crispy critters littering the downtown landscape. ^_^ TDD |
#14
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote:
On Feb 24, 10:45*am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGB I used 8000 for the primary from someone's earlier post. No clue what it really is. |
#15
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 11:52*am, "SRN" wrote:
The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. For purposes of this discussion, you are correct. These IS another wire somewhere. It may be running down the pole to the ground (using the earth as most of the "wire") and may look like a steel support cable... |
#16
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 2:01 PM, Larry Fishel wrote:
On Feb 24, 11:52 am, wrote: The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. For purposes of this discussion, you are correct. These IS another wire somewhere. It may be running down the pole to the ground (using the earth as most of the "wire") and may look like a steel support cable... In the US in a residential area, indeed. In some (very) rural areas of Sask, CA, I saw one-line w/ earth return as recently as roughly 20-yr ago yet... -- |
#17
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
harry wrote:
On Feb 24, 3:14 pm, wrote: I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. The neutral and the ground may be one and the same. Common thing is Australia for example. But only in rural areas. So the "return" current goes through the ground. A cheap system, not without it's dangers. I was looking outside one snowy day, and I saw a tree branch fall in my front yard with the end on fire. The branch had hit the single top wire connecting ground. Greg |
#18
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGB I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. |
#20
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
"Pete C." wrote:
Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGB I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg |
#21
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 6:52 PM, gregz wrote:
"Pete wrote: Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGBr I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg It could have been a static discharge from your antenna if you had an external antenna. Or it could have been a static electricity discharge from another source, even atmospheric. Another source may have been power company or an industrial site switching high voltage power at certain times every day. I can remember listening to distant stations on an AM radio in different bands and hearing a "zip..zip..zip" sound at regular intervals. TDD |
#22
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
I think the return path for the other side of the primary
transformer is the earth. *Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. *I see what the OP and you are talking about all over here in rural NJ. *You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. *I believe the other side is connected to earth ground. *That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. Yes there are exceptions but they are not in common use. The reason that system is used is because it saves a lot of money while still providing reliable service. The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. There is only one insulated connection to the primary winding and that is the other end from the neutral connection. The grounded stud on the case is connected to the neutral and to ground. Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. The reason that all of those currents do not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is rather small. The earth carrying current seldom causes any problems in systems that are maintained to the National Electrical Safety Code standard. The biggest exception is in the animal husbandry industries were the four footed critters that spend much of their day standing or lying in their own rather conductive waste do often suffer ill effects from event the small stray currents that are flowing across the ground. When some defect in the distribution neutral raises that current a little higher the animals suffer greatly and even die from the effects. In dairy cows for instance it will cause a drastic reduction in production and radical changes in the cows behavior and temperament because the animals are in nearly constant pain. Utilities in areas with large dairying industry. Have developed transformers with high impedance connections to ground in order to limit the stray current to levels that are imperceptible to the livestock. One of the utilities in Wisconsin painted these special transformers to look like the coloration of the locally dominant type of dairy cow. I hope that is helpful. -- Tom Horne |
#23
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Fri, 24 Feb 2012 17:36:07 -0800 (PST), Tom Horne
wrote: I think the return path for the other side of the primary transformer is the earth. *Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. *I see what the OP and you are talking about all over here in rural NJ. *You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. *I believe the other side is connected to earth ground. *That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. Yes there are exceptions but they are not in common use. The reason that system is used is because it saves a lot of money while still providing reliable service. The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. There is only one insulated connection to the primary winding and that is the other end from the neutral connection. The grounded stud on the case is connected to the neutral and to ground. Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. The reason that all of those currents do not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is Wouldn't the situation where the primary is feed by a single conductor have the same amperage returning through the earth as supplied by the phase conductor? I wouldn't consider that "rather small" rather small. The earth carrying current seldom causes any problems in systems that are maintained to the National Electrical Safety Code standard. The biggest exception is in the animal husbandry industries were the four footed critters that spend much of their day standing or lying in their own rather conductive waste do often suffer ill effects from event the small stray currents that are flowing across the ground. When some defect in the distribution neutral raises that current a little higher the animals suffer greatly and even die from the effects. In dairy cows for instance it will cause a drastic reduction in production and radical changes in the cows behavior and temperament because the animals are in nearly constant pain. Utilities in areas with large dairying industry. Have developed transformers with high impedance connections to ground in order to limit the stray current to levels that are imperceptible to the livestock. One of the utilities in Wisconsin painted these special transformers to look like the coloration of the locally dominant type of dairy cow. I hope that is helpful. |
#24
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
Metspitzer wrote: On Fri, 24 Feb 2012 17:36:07 -0800 (PST), Tom Horne wrote: I think the return path for the other side of the primary transformer is the earth. Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. I see what the OP and you are talking about all over here in rural NJ. You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. I believe the other side is connected to earth ground. That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. Yes there are exceptions but they are not in common use. The reason that system is used is because it saves a lot of money while still providing reliable service. The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. There is only one insulated connection to the primary winding and that is the other end from the neutral connection. The grounded stud on the case is connected to the neutral and to ground. Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. The reason that all of those currents do not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is Wouldn't the situation where the primary is feed by a single conductor have the same amperage returning through the earth as supplied by the phase conductor? I wouldn't consider that "rather small" Do you know what the currents are at primary voltages? Your 240V 100A residential service is some 3.3A at the lowest 7,200V primary voltage and something like 680mA at 35kV distribution, and that's only if it's running at the full 100A load which it isn't ever supposed to do for more than a few seconds. |
#25
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
The Daring Dufas wrote: On 2/24/2012 6:52 PM, gregz wrote: "Pete wrote: Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGBr I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg It could have been a static discharge from your antenna if you had an external antenna. Or it could have been a static electricity discharge from another source, even atmospheric. Another source may have been power company or an industrial site switching high voltage power at certain times every day. I can remember listening to distant stations on an AM radio in different bands and hearing a "zip..zip..zip" sound at regular intervals. TDD HID Street light ballast igniters are known to produce a lot of RFI when they come on at night, and if they have a bad lamp attached they cycle endlessly producing interference. With the switch to LED street lights and even parking lot lights that problem should gradually become a thing of the past. |
#26
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 8:52*pm, Metspitzer wrote:
On Fri, 24 Feb 2012 17:36:07 -0800 (PST), Tom Horne wrote: I think the return path for the other side of the primary transformer is the earth. *Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. *I see what the OP and you are talking about all over here in rural NJ. *You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. *I believe the other side is connected to earth ground. *That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). *That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. *Yes there are exceptions but they are not in common use. The reason that system is used is because it saves a lot of money while still providing reliable service. *The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. *There is only one insulated connection to the primary winding and that is the other end from the neutral connection. *The grounded stud on the case is connected to the neutral and to ground. *Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. *The reason that all of those currents do *not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. *If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. *Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is Wouldn't the situation where the primary is feed by a single conductor have the same amperage returning through the earth as supplied by the phase conductor? * *I wouldn't consider that "rather small" rather small. *The earth carrying current seldom causes any problems in systems that are maintained to the National Electrical Safety Code standard. *The biggest exception is in the animal husbandry industries were the four footed critters that spend much of their day standing or lying in their own rather conductive waste do often suffer ill effects from event the small stray currents that are flowing across the ground. *When some defect in the distribution neutral raises that current a little higher the animals suffer greatly and even die from the effects. *In dairy cows for instance it will cause a drastic reduction in production and radical changes in the cows behavior and temperament because the animals are in nearly constant pain. Utilities in areas with large dairying industry. *Have developed transformers with high impedance connections to ground in order to limit the stray current to levels that are imperceptible to the livestock. *One of the utilities in Wisconsin painted these special transformers to look like the coloration of *the locally dominant type of dairy cow. I hope that is helpful. No. Because the primary is supplied from two conductors. In a Multi Grounded Neutral (MGM) distribution system there is a continuous neutral conductor. It is the same neutral conductor that is part of the low lines; that is the lines below the transformer; that supply the individual premise wiring systems. That one conductor is serving as the neutral for both the distribution system and the premises wiring systems served by the transformers that are connected in succession to each phase of the distribution. That uninsulated conductor is grounded at intervals along it's route from the substation transformer were the distribution current originated. In normal operation it carries comparatively little current because of the cancellation that occurs in the common connections. The only current flowing on the neutral is the total difference between the current flowing on the three phases. Not the sum mind you just the difference. So if phase A is carrying one hundred, phase B one hundred five, and phase C one hundred three amperes the maximum current flowing in the neutral conductor at any given instant is five amperes. The actual purpose that the neutral current serves is to provide a larger number of common neutral connections in which the currents from the three phases can cancel each other out. In any portion of a three phase distribution system were all three phases are not present the neutral will carry the same current as the highest current on the one or two phases that are still present. It is only in the three phase portion of the network that the current will cancel out to a very small value. Once that portion of the system ties back into the three phase portion of the network then the current averaged from all such single phased stubs will again cancel out and the neutral current will again be a rather small value. -- Tom Horne |
#27
Posted to alt.home.repair
|
|||
|
|||
Example of earth ground
I got to admit, there is clueless, and there is clueless. This was to the
extreme. Christopher A. Young Learn more about Jesus www.lds.org .. "HeyBub" wrote in message m... pic http://thereifixedit.files.wordpress...t-to-earth.jpg |
#28
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 8:24*pm, Tom Horne wrote:
On Feb 24, 8:52*pm, Metspitzer wrote: On Fri, 24 Feb 2012 17:36:07 -0800 (PST), Tom Horne wrote: I think the return path for the other side of the primary transformer is the earth. *Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. *I see what the OP and you are talking about all over here in rural NJ. *You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. *I believe the other side is connected to earth ground. *That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). *That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. *Yes there are exceptions but they are not in common use.. The reason that system is used is because it saves a lot of money while still providing reliable service. *The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. *There is only one insulated connection to the primary winding and that is the other end from the neutral connection. *The grounded stud on the case is connected to the neutral and to ground. *Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. *The reason that all of those currents do *not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. *If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. *Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is Wouldn't the situation where the primary is feed by a single conductor have the same amperage returning through the earth as supplied by the phase conductor? * *I wouldn't consider that "rather small" rather small. *The earth carrying current seldom causes any problems in systems that are maintained to the National Electrical Safety Code standard. *The biggest exception is in the animal husbandry industries were the four footed critters that spend much of their day standing or lying in their own rather conductive waste do often suffer ill effects from event the small stray currents that are flowing across the ground. *When some defect in the distribution neutral raises that current a little higher the animals suffer greatly and even die from the effects. *In dairy cows for instance it will cause a drastic reduction in production and radical changes in the cows behavior and temperament because the animals are in nearly constant pain. Utilities in areas with large dairying industry. *Have developed transformers with high impedance connections to ground in order to limit the stray current to levels that are imperceptible to the livestock. *One of the utilities in Wisconsin painted these special transformers to look like the coloration of *the locally dominant type of dairy cow. I hope that is helpful. No. *Because the primary is supplied from two conductors. * In a Multi Grounded Neutral (MGM) distribution system there is a continuous neutral conductor. *It is the same neutral conductor that is part of the low lines; that is the lines below the transformer; that supply the individual premise wiring systems. *That one conductor is serving as the neutral for both the distribution system and the premises wiring systems served by the transformers that are connected in succession to each phase of the distribution. *That uninsulated conductor is grounded at intervals along it's route from the substation transformer were the distribution current originated. *In normal operation it carries comparatively little current because of the cancellation that occurs in the common connections. *The only current flowing on the neutral is the total difference between the current flowing on the three phases. *Not the sum mind you just the difference. *So if phase A is carrying one hundred, phase B one hundred five, and phase C one hundred three amperes the maximum current flowing in the neutral conductor at any given instant is five amperes. *The actual purpose that the neutral current serves is to provide a larger number of common neutral connections in which the currents from the three phases can cancel each other out. *In any portion of a three phase distribution system were all three phases are not present the neutral will carry the same current as the highest current on the one or two phases that are still present. *It is only in the three phase portion of the network that the current will cancel out to a very small value. *Once that portion of the system ties back into the three phase portion of the network then the current averaged from all such single phased stubs will again cancel out and the neutral current will again be a rather small value. -- Tom Horne- Hide quoted text - - Show quoted text - Tom is correct, we have had that sort of a system here in Illinois for at least 50 years. |
#29
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 8:14 PM, Pete C. wrote:
The Daring Dufas wrote: On 2/24/2012 6:52 PM, gregz wrote: "Pete wrote: Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGBr I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg It could have been a static discharge from your antenna if you had an external antenna. Or it could have been a static electricity discharge from another source, even atmospheric. Another source may have been power company or an industrial site switching high voltage power at certain times every day. I can remember listening to distant stations on an AM radio in different bands and hearing a "zip..zip..zip" sound at regular intervals. TDD HID Street light ballast igniters are known to produce a lot of RFI when they come on at night, and if they have a bad lamp attached they cycle endlessly producing interference. With the switch to LED street lights and even parking lot lights that problem should gradually become a thing of the past. A electrical engineer friend of mine was once the head of a power company communications division and he told me that many complaints of radio interference his department investigated turned out to be caused by defective doorbell transformers. TDD |
#30
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 25, 2:24*am, Tom Horne wrote:
On Feb 24, 8:52*pm, Metspitzer wrote: *The only current flowing on the neutral is the total difference between the current flowing on the three phases. *Not the sum mind you just the difference. *So if phase A is carrying one hundred, phase B one hundred five, and phase C one hundred three amperes the maximum current flowing in the neutral conductor at any given instant is five amperes. *The actual purpose that the neutral current serves is to provide a larger number of common neutral connections in which the currents from the three phases can cancel each other out. *In any portion of a three phase distribution system were all three phases are not present the neutral will carry the same current as the highest current on the one or two phases that are still present. *It is only in the three phase portion of the network that the current will cancel out to a very small value. *Once that portion of the system ties back into the three phase portion of the network then the current averaged from all such single phased stubs will again cancel out and the neutral current will again be a rather small value. -- Tom Horne- Hide quoted text - - Show quoted text - That is not true. The neutral current is the vector sum of the phase currents, not the numerical difference. |
#31
Posted to alt.home.repair
|
|||
|
|||
Example of earth ground
"HeyBub" wrote in
m: wrote: I think the return path for the other side of the primary transformer is the earth. Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. I see what the OP and you are talking about all over here in rural NJ. You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. I believe the other side is connected to earth ground. That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. pic http://thereifixedit.files.wordpress...ash-repairs-wh at-i-grounded-it-to-earth.jpg Thaks for that safety tip. I need to upgrade to the pic level. |
#32
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On Feb 24, 9:24*pm, Tom Horne wrote:
On Feb 24, 8:52*pm, Metspitzer wrote: On Fri, 24 Feb 2012 17:36:07 -0800 (PST), Tom Horne wrote: I think the return path for the other side of the primary transformer is the earth. *Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. *I see what the OP and you are talking about all over here in rural NJ. *You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. *I believe the other side is connected to earth ground. *That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. In most of North America we use a Multi Grounded Neutral (MGM). *That means that there is a neutral conductor that goes back to the source transformer's neutral point that is grounded at multiple points along it's route. *Yes there are exceptions but they are not in common use.. The reason that system is used is because it saves a lot of money while still providing reliable service. *The neutral in most utility distribution systems is common to both windings of the transformer. It connects to the uninsulated stud on the transformers case which is internally bonded to one end of the primary winding and the center of the secondary winding. *There is only one insulated connection to the primary winding and that is the other end from the neutral connection. *The grounded stud on the case is connected to the neutral and to ground. *Since the current will flow in all pathways available to it in proportion to the total impedance of the pathway some current will flow via the earth on the order of a few amperes per grounding electrode. Here is where it gets confusing. *The reason that all of those currents do *not add up to some phenomenal current flow through the earth is that the flows from the three phases cancel each other out in all of the common connections to the degree that the current being drawn from the system is equal. *If you ran impossibly long leads from a three phase power analyzer what you would see across any three consecutive transformers grounds would approach zero current. *Since no system is perfectly balanced across all three phases the current in the neutral and the earth is never zero but if you check the current flow in the source transformers neutral and it's grounding electrode conductor back at the power substation you would find that it is rather low. So while it is true that in an MGM distribution system some of the current is flowing through the earth the actual amperage doing that is Wouldn't the situation where the primary is feed by a single conductor have the same amperage returning through the earth as supplied by the phase conductor? * *I wouldn't consider that "rather small" rather small. *The earth carrying current seldom causes any problems in systems that are maintained to the National Electrical Safety Code standard. *The biggest exception is in the animal husbandry industries were the four footed critters that spend much of their day standing or lying in their own rather conductive waste do often suffer ill effects from event the small stray currents that are flowing across the ground. *When some defect in the distribution neutral raises that current a little higher the animals suffer greatly and even die from the effects. *In dairy cows for instance it will cause a drastic reduction in production and radical changes in the cows behavior and temperament because the animals are in nearly constant pain. Utilities in areas with large dairying industry. *Have developed transformers with high impedance connections to ground in order to limit the stray current to levels that are imperceptible to the livestock. *One of the utilities in Wisconsin painted these special transformers to look like the coloration of *the locally dominant type of dairy cow. I hope that is helpful. No. *Because the primary is supplied from two conductors. * In a Multi Grounded Neutral (MGM) distribution system there is a continuous neutral conductor. *It is the same neutral conductor that is part of the low lines; that is the lines below the transformer; that supply the individual premise wiring systems. *That one conductor is serving as the neutral for both the distribution system and the premises wiring systems served by the transformers that are connected in succession to each phase of the distribution. *That uninsulated conductor is grounded at intervals along it's route from the substation transformer were the distribution current originated. *In normal operation it carries comparatively little current because of the cancellation that occurs in the common connections. *The only current flowing on the neutral is the total difference between the current flowing on the three phases. *Not the sum mind you just the difference. *So if phase A is carrying one hundred, phase B one hundred five, and phase C one hundred three amperes the maximum current flowing in the neutral conductor at any given instant is five amperes. *The actual purpose that the neutral current serves is to provide a larger number of common neutral connections in which the currents from the three phases can cancel each other out. *In any portion of a three phase distribution system were all three phases are not present the neutral will carry the same current as the highest current on the one or two phases that are still present. *It is only in the three phase portion of the network that the current will cancel out to a very small value. *Once that portion of the system ties back into the three phase portion of the network then the current averaged from all such single phased stubs will again cancel out and the neutral current will again be a rather small value. -- Tom Horne- Hide quoted text - - Show quoted text - I'm with you on the essence of what you are saying regarding how the power is distributed. Where I still have questions is back to the original observation. Out on country roads, you have 3 high voltage wires, one for each phase. Then you'll have a group of houses. There is a transformer for those houses and it's connected to one phase. Since there are only 3 primary high voltage wires, are you saying the other side of the transformer is connected to the same neutral as the 240V services of the houses? I can see that working, as then you have multiple connections to earth ground for return on the primary side. But then there is also clearly substantial current flowing through earth ground back to the substation or more likely I guess to other earth ground points with other nearby pole transformers that are on different phases. If it's not done that way, then I don't understand the return path from that pole transformer. All I see are the 3 high voltage wires and then below it the 3 240V service wires, 2 hots, one neutral, going down the road. In other words, there is no neutral return path that I can see other than the 240V, secondary one. So, is it shared? I think that is what Bud said he thought might be going on too. And that seems to be the essence of the OP's question that has him stumped. |
#33
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 9:45 AM, Evan wrote:
On Feb 24, 10:14 am, wrote: I just noticed that all the residential transformers on the poles on my street only have one wire feeding them. There are three wires on top of the pole. One wire in, and three wires out to the triplex feeding my house. There are no other visible connections on the transformer. Heck, the next street over only has ONE wire at the top of the pole... I thought the three wires on the pole corresponded to each leg on my breaker panel, and a ground wire. How is the transformer creating two 110V legs and a ground from one feed wire? This just goes against everything I learned in school about electricity. Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... ~~ Evan Totally irrelevant to what dennis asked. In the urban area here the primary return is by the continuous secondary neutral, which attaches to the primary neutral at the feed point. It is multi-grounded, but the wire is lower resistance than the earth (or at least lower resistance than the earth connection). In rural areas I don't remember anywhere there wasn't another wire on the pole in addition to 1 or 3 distribution wires. Transmission wires don't necessarily have a neutral because it can be created at a substation. There may be solely earth return somewhere in the state, but I don't remember seeing it. -- bud-- |
#34
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/25/2012 1:56 AM, The Daring Dufas wrote:
On 2/24/2012 8:14 PM, Pete C. wrote: The Daring Dufas wrote: On 2/24/2012 6:52 PM, gregz wrote: "Pete wrote: Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGBr I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg It could have been a static discharge from your antenna if you had an external antenna. Or it could have been a static electricity discharge from another source, even atmospheric. Another source may have been power company or an industrial site switching high voltage power at certain times every day. I can remember listening to distant stations on an AM radio in different bands and hearing a "zip..zip..zip" sound at regular intervals. TDD HID Street light ballast igniters are known to produce a lot of RFI when they come on at night, and if they have a bad lamp attached they cycle endlessly producing interference. With the switch to LED street lights and even parking lot lights that problem should gradually become a thing of the past. A electrical engineer friend of mine was once the head of a power company communications division and he told me that many complaints of radio interference his department investigated turned out to be caused by defective doorbell transformers. TDD Sounded pretty crazy the first time I saw you post it. Jeff Wisnia came up with an FCC interference handbook http://tinyurl.com/63ob78 or http://transition.fcc.gov/ftp/Bureau...ceHandbook.pdf that gives details. Some doorbell transformers have a thermal protector on the primary that opens (and closes) if the transformer overheats. (It may be part of the limitation on current/power for a class 2 transformer.) It can wind up cycling maybe 7 times a second. My guess is that doorbell transformers have not been made that way for quite a while. -- bud-- |
#35
Posted to alt.home.repair
|
|||
|
|||
Example of earth ground
On 2/24/2012 6:25 PM, HeyBub wrote:
wrote: I think the return path for the other side of the primary transformer is the earth. Earth is used as a return in many distribution systems and while it saves money, it leads to some problems. I see what the OP and you are talking about all over here in rural NJ. You have 3 wires on top of the poles, which are the 3 phases. If you look at where you have houses, a single wire leads from one of those to the transformer. I believe the other side is connected to earth ground. That arragement then serves a small group of houses. With a larger commercial/industiral user you see 3 transfomers, one connected to each of the 3 phases. pic http://thereifixedit.files.wordpress...t-to-earth.jpg Ahhhh-haaaaa! So that's how they ground the Space Station and other satellites! |
#36
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
|
#37
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 2/24/2012 3:12 PM, Pete C. wrote:
Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGB I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. They are both. The pretty much standard system is a Y derived HV primary ~ 12kv phase to phase or ~ 7.2kv phase to neutral. |
#38
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
bud-- wrote:
On 2/25/2012 1:56 AM, The Daring Dufas wrote: On 2/24/2012 8:14 PM, Pete C. wrote: The Daring Dufas wrote: On 2/24/2012 6:52 PM, gregz wrote: "Pete wrote: Metspitzer wrote: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45 am, wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGBr I used 8000 for the primary from someone's earlier post. No clue what it really is. I believe 7,200V is about the lowest you will find anywhere and most are 13,200V or more. I was lying in bed one day watching guys adding a new transformer outside the window. When trying to clip the wire onto the hv wire I saw a pretty good arc. Probably at least 3 inches. A transformer feeding the house burnt out, so they replaced that, and added another transformer in addition to original. Result our house had less voltage fluctuations. When young, I used to use the shortwave radio, and ever so often, maybe twice a ay, a horrendous arching- buzzing sound would build up and quickly stop. Lasting 3-4 seconds. I never found the source of that. Didn't sound like anything that would be consumer generated. Greg It could have been a static discharge from your antenna if you had an external antenna. Or it could have been a static electricity discharge from another source, even atmospheric. Another source may have been power company or an industrial site switching high voltage power at certain times every day. I can remember listening to distant stations on an AM radio in different bands and hearing a "zip..zip..zip" sound at regular intervals. TDD HID Street light ballast igniters are known to produce a lot of RFI when they come on at night, and if they have a bad lamp attached they cycle endlessly producing interference. With the switch to LED street lights and even parking lot lights that problem should gradually become a thing of the past. A electrical engineer friend of mine was once the head of a power company communications division and he told me that many complaints of radio interference his department investigated turned out to be caused by defective doorbell transformers. TDD Sounded pretty crazy the first time I saw you post it. Jeff Wisnia came up with an FCC interference handbook http://tinyurl.com/63ob78 or http://transition.fcc.gov/ftp/Bureau...ceHandbook.pdf that gives details. Some doorbell transformers have a thermal protector on the primary that opens (and closes) if the transformer overheats. (It may be part of the limitation on current/power for a class 2 transformer.) It can wind up cycling maybe 7 times a second. My guess is that doorbell transformers have not been made that way for quite a while. I had two houses but never heard of that. Perhaps I did and forgot. Years ago our ham club had an interference expert from PG&E, come in to our meeting. The way he tracked down that type of interference was use am radios. You start at the broadcast band then work your way up in frequency, narrowing down the location. Like, am broadcast, cb, aircraft band, etc. The transformers I see know have a thermal break, for good. Greg |
#39
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
On 02/25/2012 11:30 AM, George wrote:
[snip] I have been on a lot of country roads and have never seen what you described. Typically there are the Y derived phase conductors on a crossarm or bracket with three insulators and an uninsulated neutral below. As density gets lower they will only carry one of the primary conductors and the neutral. The one here appears to have the neutral on top. See the picture at http://notstupid.us/pix/IMG_3427.JPG [snip] -- Mark Lloyd http://notstupid.us "A fanatic is one who can't change his mind and won't change the subject." -- Winston Churchill |
#40
Posted to alt.home.repair
|
|||
|
|||
one-wire pole transformers
Metspitzer wrote in
: On Fri, 24 Feb 2012 08:30:26 -0800 (PST), wrote: On Feb 24, 10:45*am, Evan wrote: Read up more on transformers... Residential power is typically single phase (although there are some exceptions to this) with a center tapped secondary winding on the transformer... The thing is, everything I know about electricity says that you need TWO wires to make a complete circuit. AC or DC, doesn't matter. Most streets have two overhead wires, with two wires going to the transformer. http://imgur.com/gFrGB I used 8000 for the primary from someone's earlier post. No clue what it really is. talking to the utility guy replacing the power transformer on the ground outside my apartment(after it blew),it was fed by 7200 volts,coming from a nearby pole. -- Jim Yanik jyanik at localnet dot com |
Reply |
|
Thread Tools | Search this Thread |
Display Modes | |
|
|
Similar Threads | ||||
Thread | Forum | |||
LV downlighters. Wire-wound or electronic transformers? | UK diy | |||
soldering enameled wire; repairing 110 to lower transformers | Electronics Repair | |||
soldering enameled wire; repairing 110 to lower transformers | Home Repair | |||
AC shaded pole single phase induction pole motor | Electronics Repair |