DIYbanter

DIYbanter (https://www.diybanter.com/)
-   Home Repair (https://www.diybanter.com/home-repair/)
-   -   110V and water (https://www.diybanter.com/home-repair/273433-110v-water.html)

Charles Bishop[_2_] March 15th 09 01:46 AM

110V and water
 
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles

RBM[_2_] March 15th 09 02:31 AM

110V and water
 

"Charles Bishop" wrote in message
...
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles


Not unless it is a GFCI breaker. Outdoor splice boxes and underground
splices are always wet, from condensation if not direct water entry. If the
type of box you have has threaded knockouts, try putting silicone around the
threads.



Steve Barker[_2_] March 15th 09 03:28 AM

110V and water
 
Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.

Davej March 15th 09 03:32 AM

110V and water
 
On Mar 14, 7:46 pm, (Charles Bishop) wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


How did the water get in?

Because if it had, the breaker would have tripped, right?


Only if it had a GFCI and the water caused current flow in the ground
wire.

Tony Hwang March 15th 09 04:44 AM

110V and water
 
Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

Hi,
If it is not GFCI, and pure water is not a good conductor. You should
have drain holes on the box and liberal use of silicon sealant to
minimize water/moisture build up.

Ralph Mowery March 15th 09 04:55 AM

110V and water
 

"Charles Bishop" wrote in message
...
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles


It may or may not trip the breaker. Water is not a very good conductor and
small ammounts can just cause a small current flow. It may even heat up the
water. Had a water heater that the element cracked and was causing the
water to heat up way too much. That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.



John Gilmer[_3_] March 15th 09 05:11 AM

110V and water
 

"RBM" wrote in message
...

"Charles Bishop" wrote in message
...
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles


Not unless it is a GFCI breaker. Outdoor splice boxes and underground
splices are always wet, from condensation if not direct water entry. If
the type of box you have has threaded knockouts, try putting silicone
around the threads.


When underground wiring insulation fails the failure in manifested by a
chemical reaction between the conductor and the surrounding earth. With Al
wire, this happens quickly. With Cu it's relatively slow. Basically
speaking the cable is eaten away and fails "open." In proportion to the
current the wire normally delivers to the load, the earth leakage is minor
so it will not trip a breaker (except for ground fault, of course.).




CJT March 15th 09 05:35 AM

110V and water
 
Steve Barker wrote:

Charles Bishop wrote:

I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.


pure water isn't conductive, but when was the last time you saw any pure
water?

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .

mm March 15th 09 06:04 AM

110V and water
 
On Sat, 14 Mar 2009 22:44:46 -0600, Tony Hwang
wrote:

Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

Hi,
If it is not GFCI, and pure water is not a good conductor. You should
have drain holes on the box and liberal use of silicon sealant to
minimize water/moisture build up.


Should he seal the drain holes, or use drain-only holes?

[email protected] March 15th 09 01:43 PM

110V and water
 
On Mar 14, 11:32*pm, Davej wrote:
On Mar 14, 7:46 pm, (Charles Bishop) wrote:

I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


How did the water get in?

Because if it had, the breaker would have tripped, right?


Only if it had a GFCI and the water caused current flow in the ground
wire.


The current flow does not have to be in the ground wire. In fact, a
GFCI doesn't need a ground wire at all to work. The GFCI trips when
it senses an imbalance between the currents in the hot and neutral,
meaning some current is going somewhere else. In this case, it would
trip if current was flowing from a wet connection to earth.

[email protected] March 15th 09 01:45 PM

110V and water
 
On Mar 15, 12:55*am, "Ralph Mowery"
wrote:
"Charles Bishop" wrote in message

...

I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. *Water is not a very good conductor and
small ammounts can just cause a small current flow. *It may even heat up the
water. *Had a water heater that the element cracked *and was causing the
water to heat up way too much. *That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.

John Grabowski March 15th 09 02:09 PM

110V and water
 

"Ralph Mowery" wrote in message
m...

"Charles Bishop" wrote in message
...
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles


It may or may not trip the breaker. Water is not a very good conductor
and small ammounts can just cause a small current flow. It may even heat
up the water. Had a water heater that the element cracked and was
causing the water to heat up way too much. That was casude by some of the
current bypassing the thermostat and directly heating the water. Still did
not trip the breaker.




*You reminded me of a commercial kitchen that I serviced many years ago.
One time the manager complained that it was taking a long time for the
coffee urn to heat the water. No problem with the temperature, but it took
a few hours to get hot. I knew that there was a 2000 watt element in the
urn so it should have heated up faster. I took the unit apart and found
that the element had practically disintegrated. The water was being heated
by the current flowing through it.


Pat March 15th 09 02:58 PM

110V and water
 
On Mar 15, 9:45*am, wrote:
On Mar 15, 12:55*am, "Ralph Mowery"
wrote:



"Charles Bishop" wrote in message


...


I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. *Water is not a very good conductor and
small ammounts can just cause a small current flow. *It may even heat up the
water. *Had a water heater that the element cracked *and was causing the
water to heat up way too much. *That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. *They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


.... of SALT water. You need to add salt or they don't work. Don't
you have kids?

[email protected] March 15th 09 03:24 PM

110V and water
 
On Mar 15, 10:58*am, Pat wrote:
On Mar 15, 9:45*am, wrote:





On Mar 15, 12:55*am, "Ralph Mowery"
wrote:


"Charles Bishop" wrote in message


...


I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. *Water is not a very good conductor and
small ammounts can just cause a small current flow. *It may even heat up the
water. *Had a water heater that the element cracked *and was causing the
water to heat up way too much. *That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. *They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


... of SALT water. *You need to add salt or they don't work. *Don't
you have kids?- Hide quoted text -



You only need to add salt if the water is low in minerals. Most tap
waters work fine. I've had various vaporizers of that type and never
had to add salt. In the directions, they talk about adding a small
amount of salt if it doesn't work without it.


TWayne March 15th 09 05:28 PM

110V and water
 
Steve Barker wrote:
Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover
off of the outdoor junction box, water came out. Don't know how much
was in there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the wiring connections, held together by wire nuts, or maybe
it did. Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.


Water itself isn't very conductive but it IS conductive; it's the
impurities (dirt, dissolved stuff, etc.) that makes water conductive so
it very well could have been. Even rainwater isn't normally pure enough
to not trip a GFCI, for example.



stan March 15th 09 06:41 PM

110V and water
 
On Mar 15, 10:43*am, wrote:
The current flow does not have to be in the ground wire. *In fact, a
GFCI doesn't need a ground wire at all to work. *The GFCI trips when
it senses an imbalance between the currents in the hot and neutral,
meaning some current is going somewhere else. * In this case, it would
trip if current was flowing from a wet connection to earth.



Glad someone pointed that out. A GFCI (so called "Ground
fault ...... ) operates when there is an imbalance between the current
flowing in the neutral and live wires; of say a 115 volt circuit.

If there IS an imbalance it does not have to be leakage to ground!
Although that is a main purpose to protect users of potentially faulty
apparatus.

Witnessed a situation where a neutral wire was inadvertently also
connected to another circuit in the adjacent living unit.

Every time they plugged into that circuit, next door, the currents
were imbalanced and 'this' GFCI tripped!

See another post about whether water conducts! Almost anything will
conduct (slightly).

stan March 15th 09 06:50 PM

110V and water
 
On Mar 15, 10:33*am, Van Chocstraw
wrote:

No? Well wet your fingers and stick them in a socket.

Van Chocstraw


Van.

Correct. If your wet fingers present a resistance of say 20,000 ohms a
'small' current WILL flow.

For example; 115 volts/20,000 ohms = 5.75 milliamps. Enough to stop
your heart in certain circumstance but not near enough to trip a 15
amp (that's 15,000 milliamps) circuit breaker!

At low voltage if I hold the two leads of a multimeter in my two hands
I get something of the order of 100,000 ohms.
If my hands were wet or I dig the points of the meter leads into the
skin it is possible to get it down to less than 50,000 ohms.

That's how some electricians, dangerously, will test for 115 volts by
brushing their fingers quickly across a live lead!

stan March 15th 09 06:54 PM

110V and water
 
On Mar 15, 2:28*pm, "Twayne" wrote:
Steve Barker wrote:
Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover
off of the outdoor junction box, water came out. Don't know how much
was in there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the wiring connections, held together by wire nuts, or maybe
it did. Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.


Water itself isn't very conductive but it IS conductive; it's the
impurities (dirt, dissolved stuff, etc.) that makes water conductive so
it very well could have been. *Even rainwater isn't normally pure enough
to not trip a GFCI, for example.


Well we get acid rain and there can also be condensation within boxes
and conduits etc.
Also variuos impurities/dirt etc. can be present that get dissolved
into moisture and conduct slightly.
It is true that 'distilled' very pure water only conducts slightly.

[email protected] March 15th 09 07:53 PM

110V and water
 
On Sat, 14 Mar 2009 22:28:53 -0500, Steve Barker
wrote:

Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.

That is

[email protected] March 15th 09 07:55 PM

110V and water
 
On Sat, 14 Mar 2009 22:28:53 -0500, Steve Barker
wrote:

Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.

That is not correct. Lots of hot vapour humidifiers work by running
the current through water between 110 volt AC electrodes. The water
conducts well enough to heat the water to boiling in the tube
surrounding the 2 electrodes - and yes, they DO work with distilled
and/or RO purified water.

[email protected] March 15th 09 08:02 PM

110V and water
 
On Sat, 14 Mar 2009 22:28:53 -0500, Steve Barker
wrote:

Charles Bishop wrote:
I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.


Di-inized water 5.5 × 10-6[1] changes to 1.2 × 10-4 in water with no
gas present[1]

Drinking water 0.0005 to 0.05 This value range is typical of high
quality drinking water and not an indicator of water quality

Water conductivity

Pure water is not a good conductor of electricity. Ordinary distilled
water in equilibrium with carbon dioxide of the air has a conductivity
of about 10 x 10-6 W-1*m-1 (20 dS/m). Because the electrical current
is transported by the ions in solution, the conductivity increases as
the concentration of ions increases.
Thus conductivity increases as water dissolved ionic species.

Typical conductivity of waters:
Ultra pure water 5.5 · 10-6 S/m
Drinking water 0.005 €“ 0.05 S/m
Sea water 5 S/m

So not HIGHLY conductive may be true, but nonconductive would be
false.

[email protected] March 15th 09 08:05 PM

110V and water
 
On Sun, 15 Mar 2009 07:58:33 -0700 (PDT), Pat
wrote:

On Mar 15, 9:45Â*am, wrote:
On Mar 15, 12:55Â*am, "Ralph Mowery"
wrote:



"Charles Bishop" wrote in message


...


I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. Â*Water is not a very good conductor and
small ammounts can just cause a small current flow. Â*It may even heat up the
water. Â*Had a water heater that the element cracked Â*and was causing the
water to heat up way too much. Â*That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. Â*They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


... of SALT water. You need to add salt or they don't work. Don't
you have kids?

NO they do not require salt, and Chalescraft, for one, distictly
cautions AGAINST adding salt. Apparently there is a chlorine danger
when NaCl is added to the water.

[email protected] March 15th 09 08:07 PM

110V and water
 
On Sun, 15 Mar 2009 08:24:48 -0700 (PDT), wrote:

On Mar 15, 10:58Â*am, Pat wrote:
On Mar 15, 9:45Â*am, wrote:





On Mar 15, 12:55Â*am, "Ralph Mowery"
wrote:


"Charles Bishop" wrote in message


...


I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. Â*Water is not a very good conductor and
small ammounts can just cause a small current flow. Â*It may even heat up the
water. Â*Had a water heater that the element cracked Â*and was causing the
water to heat up way too much. Â*That was casude by some of the current
bypassing the thermostat and directly heating the water. Still did not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. Â*They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


... of SALT water. Â*You need to add salt or they don't work. Â*Don't
you have kids?- Hide quoted text -



You only need to add salt if the water is low in minerals. Most tap
waters work fine. I've had various vaporizers of that type and never
had to add salt. In the directions, they talk about adding a small
amount of salt if it doesn't work without it.

When the kids were little we used one. My wife HATES deposit build-up
in kettles etc, so it was run on distilled water - and it worked.

Better than salt is a bit of washing soda or Borax.(if you need to add
anything)

CJT March 15th 09 09:10 PM

110V and water
 
wrote:
On Sat, 14 Mar 2009 22:28:53 -0500, Steve Barker
wrote:


Charles Bishop wrote:

I was repairing some landscaping lighting, and when I took the cover off
of the outdoor junction box, water came out. Don't know how much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?


not necessarily, water is not conductive.



Di-inized water 5.5 × 10-6[1] changes to 1.2 × 10-4 in water with no
gas present[1]

Drinking water 0.0005 to 0.05 This value range is typical of high
quality drinking water and not an indicator of water quality

Water conductivity

Pure water is not a good conductor of electricity. Ordinary distilled
water in equilibrium with carbon dioxide of the air has a conductivity
of about 10 x 10-6 W-1*m-1 (20 dS/m). Because the electrical current
is transported by the ions in solution, the conductivity increases as
the concentration of ions increases.
Thus conductivity increases as water dissolved ionic species.

Typical conductivity of waters:
Ultra pure water 5.5 · 10-6 S/m
Drinking water 0.005 €“ 0.05 S/m
Sea water 5 S/m

So not HIGHLY conductive may be true, but nonconductive would be
false.


http://en.wikipedia.org/wiki/Electrical_conductivity

--
The e-mail address in our reply-to line is reversed in an attempt to
minimize spam. Our true address is of the form .

TWayne March 18th 09 02:24 PM

110V and water
 

wrote in message
...
On Sun, 15 Mar 2009 07:58:33 -0700 (PDT), Pat
wrote:

On Mar 15, 9:45 am, wrote:
On Mar 15, 12:55 am, "Ralph Mowery"
wrote:



"Charles Bishop" wrote in message

...

I was repairing some landscaping lighting, and when I took the
cover off
of the outdoor junction box, water came out. Don't know how much
was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the
wiring connections, held together by wire nuts, or maybe it did.

Because if it had, the breaker would have tripped, right?

--
charles

It may or may not trip the breaker. Water is not a very good
conductor and
small ammounts can just cause a small current flow. It may even
heat up the
water. Had a water heater that the element cracked and was causing
the
water to heat up way too much. That was casude by some of the
current
bypassing the thermostat and directly heating the water. Still did
not trip
the breaker.

That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


... of SALT water. You need to add salt or they don't work. Don't
you have kids?


I have kids. And I also know how mistaken you are if you think only kids
can use such devices.

Adding salt to the water is not necessary and is specifically prohibited
for warranty purpose of any such device we've ever had.

The work fine without adding anything to the regular drinking water.

Considering this thread was started by a troll and taken on by a buncho
of egotists with nothing worthwhile to do, every single person so far
has missed the actual reason WHY they work as they do. No one has
mentioned the material used in the posts of these things, and althoug it
was obliquely referenced, no one pointed out that current flow will
depend on the distance between the two probes in the water and the
surface area of the probes at first. Once the process gets started,
it's self sustaining as long as any water is still touching both probes.
Me, I'm done with this thread; my only reason for reading it was to
see who the dummies might be. It's quicker than long lurks.


NO they do not require salt, and Chalescraft, for one, distictly
cautions AGAINST adding salt. Apparently there is a chlorine danger
when NaCl is added to the water.




TWayne March 18th 09 02:26 PM

110V and water
 

wrote in message
...
On Sun, 15 Mar 2009 08:24:48 -0700 (PDT), wrote:

On Mar 15, 10:58 am, Pat wrote:
On Mar 15, 9:45 am, wrote:





On Mar 15, 12:55 am, "Ralph Mowery"
wrote:

"Charles Bishop" wrote in message

...

I was repairing some landscaping lighting, and when I took the
cover off
of the outdoor junction box, water came out. Don't know how
much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the
wiring connections, held together by wire nuts, or maybe it
did.

Because if it had, the breaker would have tripped, right?

--
charles

It may or may not trip the breaker. Water is not a very good
conductor and
small ammounts can just cause a small current flow. It may even
heat up the
water. Had a water heater that the element cracked and was
causing the
water to heat up way too much. That was casude by some of the
current
bypassing the thermostat and directly heating the water. Still
did not trip
the breaker.

That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. They heat the water by
just
using 2 electrodes near each other submerged in a plastic tank of
water.

... of SALT water. You need to add salt or they don't work. Don't
you have kids?- Hide quoted text -



You only need to add salt if the water is low in minerals. Most tap
waters work fine. I've had various vaporizers of that type and never
had to add salt. In the directions, they talk about adding a small
amount of salt if it doesn't work without it.

When the kids were little we used one. My wife HATES deposit build-up
in kettles etc, so it was run on distilled water - and it worked.


And there was still some scale buildup, wasn't there? It's the
electro-chemical reactions. Now let's sit back and watch the egos take
off on that.


Better than salt is a bit of washing soda or Borax.(if you need to add
anything)




[email protected] March 18th 09 07:24 PM

110V and water
 
On Wed, 18 Mar 2009 10:26:30 -0400, "Twayne"
wrote:


wrote in message
.. .
On Sun, 15 Mar 2009 08:24:48 -0700 (PDT), wrote:

On Mar 15, 10:58 am, Pat wrote:
On Mar 15, 9:45 am, wrote:





On Mar 15, 12:55 am, "Ralph Mowery"
wrote:

"Charles Bishop" wrote in message

...

I was repairing some landscaping lighting, and when I took the
cover off
of the outdoor junction box, water came out. Don't know how
much was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the
wiring connections, held together by wire nuts, or maybe it
did.

Because if it had, the breaker would have tripped, right?

--
charles

It may or may not trip the breaker. Water is not a very good
conductor and
small ammounts can just cause a small current flow. It may even
heat up the
water. Had a water heater that the element cracked and was
causing the
water to heat up way too much. That was casude by some of the
current
bypassing the thermostat and directly heating the water. Still
did not trip
the breaker.

That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. They heat the water by
just
using 2 electrodes near each other submerged in a plastic tank of
water.

... of SALT water. You need to add salt or they don't work. Don't
you have kids?- Hide quoted text -



You only need to add salt if the water is low in minerals. Most tap
waters work fine. I've had various vaporizers of that type and never
had to add salt. In the directions, they talk about adding a small
amount of salt if it doesn't work without it.

When the kids were little we used one. My wife HATES deposit build-up
in kettles etc, so it was run on distilled water - and it worked.


And there was still some scale buildup, wasn't there? It's the
electro-chemical reactions. Now let's sit back and watch the egos take
off on that.


Actually with the distilled water, deposits were ALMOST non-existant.

Better than salt is a bit of washing soda or Borax.(if you need to add
anything)




[email protected] March 18th 09 09:19 PM

110V and water
 
On Mar 18, 10:24*am, "Twayne" wrote:
wrote in message

...





On Sun, 15 Mar 2009 07:58:33 -0700 (PDT), Pat
wrote:


On Mar 15, 9:45 am, wrote:
On Mar 15, 12:55 am, "Ralph Mowery"
wrote:


"Charles Bishop" wrote in message


...


I was repairing some landscaping lighting, and when I took the
cover off
of the outdoor junction box, water came out. Don't know how much
was in
there, maybe 1/4 to 1/2 cup. I'm guessing it wasn't enough to
reach the
wiring connections, held together by wire nuts, or maybe it did.


Because if it had, the breaker would have tripped, right?


--
charles


It may or may not trip the breaker. Water is not a very good
conductor and
small ammounts can just cause a small current flow. It may even
heat up the
water. Had a water heater that the element cracked and was causing
the
water to heat up way too much. That was casude by some of the
current
bypassing the thermostat and directly heating the water. Still did
not trip
the breaker.


That's also how some of the vaporizers that they sell in the drug
stores to use when you have a cold work. They heat the water by just
using 2 electrodes near each other submerged in a plastic tank of
water.


... of SALT water. *You need to add salt or they don't work. *Don't
you have kids?


I have kids. And I also know how mistaken you are if you think only kids
can use such devices.

Adding salt to the water is not necessary and is specifically prohibited
for warranty purpose of any such device we've ever had.

The work fine without adding anything to the regular drinking water.

Considering this thread was started by a troll and taken on by a buncho
of egotists with nothing worthwhile to do, every single person so far
has missed the actual reason WHY they work as they do. *No one has
mentioned the material used in the posts of these things, and althoug it
was obliquely referenced, no one pointed out that current flow will
depend on the distance between the two probes in the water and the
surface area of the probes at first. *Once the process gets started,
it's self sustaining as long as any water is still touching both probes.
* *Me, I'm done with this thread; my only reason for reading it was to
see who the dummies might be. *It's quicker than long lurks.



I diidn't see any problem with the thread and no one else seems
upset. Also, what makes you think that no one else here knows that
the current flow will depend on the surface area of the probes. Oh,
BTW genius, the current doesn't just depend on the surface area
initially, it depends on the surface area all the time.

Don't let the door hit you on the way out.

Charles Bishop[_2_] March 21st 09 02:32 PM

110V and water
 
In article ,
wrote:

On Sun, 15 Mar 2009 02:04:39 -0400, mm
wrote:

Should he seal the drain holes, or use drain-only holes?


The code says raceways and boxes "shall be arranged to drain".
They know "wet locations" will eventually accumulate water. You want
drain holes in boxes. I have found it is also good to point wirenuts
up and keep them in the top of the box.


The common "weatherproof" boxes don't have drain holes in them[1]. Should
drain holes be drilled before they are installed?

charles

[1] Mostly, I think because this would mean there would be only one way
the box could be installed and have the drain holes work.

Charles Bishop[_2_] March 21st 09 02:33 PM

110V and water
 
In article , "Twayne"
wrote:

[snip]

Considering this thread was started by a troll . . . [snip]


cite?

--
charles


All times are GMT +1. The time now is 07:01 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004 - 2014 DIYbanter