On 2008-08-25, wrote:

Sorry if this is a dumb question: if they are physically tied
together with a tie bar, and (somehow) a single breaker trips, will
the trip throw the switch hard enough to force the other breaker to
switch off together with it??


No, not always. There's a difference between a double pole breaker,
where the two sides are internally connected, and two single pole
breakers with a handle tie. In both cases, if you manually turn off
the breaker (you are using it as a disconnect), you will turn off both
sides. But as far as automatic operation (its job as an overcurrent
protection device), only the double pole breaker will reliably shut
off both sides.

For the OP, you need at a minimum to have the proper handle tie (no
nails!), and you may need to have a double pole breaker. I believe
that if the pump uses the neutral, you need a double pole breaker; if
it is a pure 240V load without using the neutral, then a handle tie is
sufficient. I've quoted the appropriate parts of the NEC below (2002
version). I'd just put in a double pole breaker, anyway, as it seems
safer.

Cheers, Wayne


240.20(B) "Circuit Breaker as Overcurrent Device." Circuit breakers
shall open all ungrounded conductors of the circuit unless otherwise
permitted in 240.20(B)(1), (B)(2), and (B)(3).

240.20(B)(2) "Grounded Single-Phase and 3-wire dc Circuits." In
grounded systems, individual single pole circuit breakers with
approved handle ties shall be permitted as the protection for each
ungrounded conductor for line-to-line connected loads for single-phase
circuits or 3-wire, direct current circuits.
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
220 house pump on two (2) SEPARATE breakers?? [email protected] Home Repair 18 August 26th 08 12:02 PM
One More Question Re House Circuit Breakers, Please ? Robert11 Home Repair 20 April 11th 08 10:20 PM
house wired without separate ground - problem? Nate Nagel Home Repair 41 October 27th 06 10:47 AM
Sump pump float switch: separate from pump? Marc_G Home Repair 4 January 15th 06 09:46 PM
Adding shower pump without a separate cold feed Vaci UK diy 7 February 25th 05 06:51 PM


All times are GMT +1. The time now is 11:33 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"