I have a 30 amp circiuit running to a high power outlet in my dining
room. I discovered if I flip one of the the 15 amp breakers on the
circuit in the breaker box, the power to the basement lights shuts
off.. How did they run at 15 amp line from the 30 amp circuit? there
is a junction box in the basement cieling with a line going to the
basement lights right were the 30 amp line runs up to the dining room.
  #2   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical geek question---

Chris wrote:
I have a 30 amp circiuit running to a high power outlet in my dining
room. I discovered if I flip one of the the 15 amp breakers on the
circuit in the breaker box, the power to the basement lights shuts
off.. How did they run at 15 amp line from the 30 amp circuit? there
is a junction box in the basement cieling with a line going to the
basement lights right were the 30 amp line runs up to the dining room.


One possibility not precluded by this description is there are two
separate circuits run physically parallel to that point where the
lighting circuit branches.

--
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 89
Default electrical geek question---


"Chris" wrote in message
...
I have a 30 amp circiuit running to a high power outlet in my dining
room. I discovered if I flip one of the the 15 amp breakers on the
circuit in the breaker box, the power to the basement lights shuts
off.. How did they run at 15 amp line from the 30 amp circuit? there
is a junction box in the basement cieling with a line going to the
basement lights right were the 30 amp line runs up to the dining room.




Two 15A breakers tied together does not make a 30A 110V branch circuit. In
most cases this is a 15A 220V branch. If that is the case, either hot black
wire plus a neutral white wire will make a 110V circuit.

The unanswered question is what is the true voltage and purpose of that
socket in the dining room. electric heat or dedicated window A/C perhaps.
Could be 110V x 2 plugs or a single 220V but 15A in every case. There is no
combination of 15A breakers that will get you a 30A circuit, they are never
run in parallel on the same phase to the same load. If it is 220V 15A then
you shold not be able to turn off the individual breakers, they should be
tied together with a bar and if that is broken you should replace it with a
new double slot breaker. If the basement light blows half the circuit, it
still may be energized in the dining room without you knowing it.

You should not have 110V lighting split off 220V service but it is
technically possible.


  #4   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical geek question---

dpb wrote:
Chris wrote:
I have a 30 amp circiuit running to a high power outlet in my dining
room. I discovered if I flip one of the the 15 amp breakers on the
circuit in the breaker box, the power to the basement lights shuts
off.. How did they run at 15 amp line from the 30 amp circuit? there
is a junction box in the basement cieling with a line going to the
basement lights right were the 30 amp line runs up to the dining room.


One possibility not precluded by this description is there are two
separate circuits run physically parallel to that point where the
lighting circuit branches.


Actually, when I read other response and re-read OP's question, I see it
does seemingly preclude my earlier response. Agree it sounds like
240V/15A service w/ one side to the lights.

Physically not any problem to do, not certain about whether code would
have allowed it at some time in the past or not but agree breakers
_should_ be ganged.

--
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 77
Default electrical geek question---

so what that means is if I am running an airconditioner in the dining
room, and turn on the lights in the basement, I could trip the
circuit, then?


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 240
Default electrical geek question---


"Chris" wrote in message
...
I have a 30 amp circiuit running to a high power outlet in my dining
room. I discovered if I flip one of the the 15 amp breakers on the
circuit in the breaker box, the power to the basement lights shuts
off.. How did they run at 15 amp line from the 30 amp circuit? there
is a junction box in the basement cieling with a line going to the
basement lights right were the 30 amp line runs up to the dining room.


Probably a 15A "Edison" circuit.

  #7   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical geek question---

Chris wrote:
so what that means is if I am running an airconditioner in the dining
room, and turn on the lights in the basement, I could trip the
circuit, then?


If as described; possible, yes. Likelihood would depend on the size of
the A/C unit.

You could verify the way it's connected measuring the voltage between
the two "hots" of the 240V A/C outlet to each other and to ground then
after tripping the breaker w/ the lights and repeating. If it's as you
think, on the second measurement instead of 120V from each to ground and
240V between you'll get 120V between and 120V from one side to ground
and 0V on the other. The other breaker test would show the same values
on the other side, obviously.

--
  #8   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical geek question---

Chris wrote:
so what that means is if I am running an airconditioner ...


As adjunct to other comment, what does the outlet for the A/C look like?

--
  #9   Report Post  
Posted to alt.home.repair
dpb dpb is offline
external usenet poster
 
Posts: 12,595
Default electrical geek question---

Chris wrote:
it's a huge three pronged outlet that reads 250 V/ 30 amps on it..


OK...guess that's what they did.

--
  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 77
Default electrical geek question---

it's a huge three pronged outlet that reads 250 V/ 30 amps on it..
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GEEK TREBUCHET J T Woodworking 5 May 15th 07 10:17 AM
Drunk Soapy Geek Patriarch Woodworking 0 May 20th 06 12:02 AM
Best Buy and Geek Squad computer privacy issues kr0 Electronics Repair 18 November 10th 05 10:04 PM


All times are GMT +1. The time now is 03:11 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"