Water heater was not providing hot water. I replaced elements after
testing showed resistance was out of spec (6 ohms instead of 10-15).
Still no hot water. Check voltage coming into heater with Simpson
Analog meter. Reading is 0 volts between the two wires, but about 115V
from each wire to ground (the tank).

This seems like I must be getting the same (in phase) 120 V power to
each lead instead of the separate (180 degree out of phase) power
signal.

The wiring has not changed!

I do notice that the circuit breaker for the water heater is "soft".
It does not have the snap and spring tension of other similar breakers
in the box.

Is it possible for a breaker to fail in this way?


Thanks for any help.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Electric water heater getting 120V to ground on each feed but 0V between them. Bad breaker?

m_p_v_13 wrote:
Water heater was not providing hot water. I replaced elements after
testing showed resistance was out of spec (6 ohms instead of 10-15).
Still no hot water. Check voltage coming into heater with Simpson
Analog meter. Reading is 0 volts between the two wires, but about 115V
from each wire to ground (the tank).


Sounds like one leg is open, either in the wiring or in the breaker.
If you feel competent enough, pull the panel cover and measure
the two hot lines at the breaker. This should help you diagnose
it. Do NOT do this if you're not familar with the procedure and
are the least bit wary doing it.

Yes, a breaker can fail in this fashion, and if it has, the panel
cover will have to be removed to replace the breaker.

Leroy

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Electric water heater getting 120V to ground on each feed but 0Vbetween them. Bad breaker?

On Jan 12, 12:55 am, "Leroy" leroy@ addy.invalid wrote:
m_p_v_13 wrote:
Water heater was not providing hot water. I replaced elements after
testing showed resistance was out of spec (6 ohms instead of 10-15).
Still no hot water. Check voltage coming into heater with Simpson
Analog meter. Reading is 0 volts between the two wires, but about 115V
from each wire to ground (the tank).


Sounds like one leg is open, either in the wiring or in the breaker.
If you feel competent enough, pull the panel cover and measure
the two hot lines at the breaker. This should help you diagnose
it. Do NOT do this if you're not familar with the procedure and
are the least bit wary doing it.

Yes, a breaker can fail in this fashion, and if it has, the panel
cover will have to be removed to replace the breaker.

Leroy


Thanks Leroy.

If one leg were open, wouldn't I get a reading of 0V for that wire
versus ground?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Electric water heater getting 120V to ground on each feed but 0V between them. Bad breaker?

m_p_v_13 wrote:

If one leg were open, wouldn't I get a reading of 0V for that wire
versus ground?


No. The open line would 'float' to the voltage of the working
hot wire.






  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Electric water heater getting 120V to ground on each feed but 0V between them. Bad breaker?

m_p_v_13 wrote:

If one leg were open, wouldn't I get a reading of 0V for that wire
versus ground?


Think of it as a voltage divider circuit. you've got 115 volts
going into a 15 ohm resistor going to a 20 Kohm analog
meter to ground. voltage would barely drop aacross the
hw heater element.







  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 11
Default Electric water heater getting 120V to ground on each feed but 0V between them. Bad breaker?

BTW, did you check the thermostat(s)? go he

http://www.bobvila.com/HowTo_Library...ers-F2171.html


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Electric water heater getting 120V to ground on each feed but 0Vbetween them. Bad breaker?

On Jan 12, 1:35*am, "Leroy" leroy@ addy.invalid wrote:
m_p_v_13 wrote:

If one leg were open, wouldn't I get a reading of 0V for that wire
versus ground?


Think of it as a voltage divider circuit. *you've got 115 volts
going into a 15 ohm resistor going to a 20 Kohm analog
meter to ground. *voltage would barely drop aacross the
hw heater element.


That of course is assuming he's measuring it with the feed wires
connected to the heater, which seems reasonable, as it accounts for
the readings. Also, if he's measuring the resistance of the elements
without disconnecting, then he's probably reading both elements in
parallel which is why he's getting about half what he's expecting.
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Electric water heater getting 120V to ground on each feed but 0Vbetween them. Bad breaker?

I did not have the feed wires disconnected when checking voltage on
them. Duh.
I see how an open leg could cause my reading since (assuming the
thermostat was working) there would be a circuit (including the
element) between the feed leads.

I did however test the element resistance with one wire disconnected.

So I was getting the same phase 120, because it was from the same lead
by way of the circuit through the element (and not from the breaker).
I'm embarrassed that I missed this.

Thanks Leroy and trad.

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Hot Water Heater Scorched Black Feed Wire [email protected] Home Repair 2 March 2nd 07 08:11 PM
54 Amp Hot Water Heater - What breaker? [email protected] Home Repair 12 November 22nd 06 03:35 AM
New Water Heater Breaker Box herlihyboy Home Repair 14 January 1st 06 06:37 PM
Above ground pool heaters - Gas heater vs. Electric heat pump ack123 Home Ownership 1 June 15th 05 04:39 PM
electric shower cold water feed gary moore UK diy 2 August 5th 03 11:21 AM


All times are GMT +1. The time now is 07:05 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"