  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Generac Troubleshooting

Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.
  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 74
Default Generac Troubleshooting

Dave wrote:
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Anyone who tries to answer this question with the information given is
bound to be wrong or really lucky. Is the installation equipped with an
automatic transfer switch?
--
Tom Horne
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 5,040
Default Generac Troubleshooting

In article 1_z9j.79$8y4.75@trnddc07,
Tom Horne wrote:

Dave wrote:
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Anyone who tries to answer this question with the information given is
bound to be wrong or really lucky. Is the installation equipped with an
automatic transfer switch?
--
Tom Horne


Nah. The OP just used the phrase "automatic transfer switch" twice in
his post to try to throw potential responders off track.
  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Generac Troubleshooting

Tom Horne wrote:

Dave wrote:
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Anyone who tries to answer this question with the information given is
bound to be wrong or really lucky. Is the installation equipped with an
automatic transfer switch?
--
Tom Horne


The OP referenced an automatic transfer switch twice. While I didn't
find the part number the OP listed, presumably he's referring to a
package of the 005253 genset and an RTS transfer switch.

The transfer switch manual:
http://www.generac.com/PublicPDFs/0171320SBY.pdf

The genset manual: http://www.generac.com/PublicPDFs/0172890SBY.pdf

The installation and owner's manual:
http://www.generac.com/PublicPDFs/0G0492.pdf

The OP didn't provide a lot of details, but some items to review
(besides the manuals) would be:

- Was the system tested after installation by simulating a power failure
via the utility disconnect breaker feeding the transfer switch?

- Was the 7 day exerciser function operating properly prior to the power
failure?

- Was the genset switch in the auto position when the power failure
occurred?

- Did anyone check the genset during the power failure to ensure it was
in auto and no fault indications were present?
  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Generac Troubleshooting

On Dec 17, 1:12 pm, "Stormin Mormon"
wrote:
Mental note to Dave: Do not start generator while under load. Make a sign,
and tape it to the generator.

--

Christopher A. Young;
.
.

"Dave" wrote in message

...
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Ah, I see, transfer switch allows the machine to start under no load,
then subsequently transfers load...


  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 3
Default Generac Troubleshooting

On Dec 17, 3:59 pm, Dave wrote:
On Dec 17, 1:12 pm, "Stormin Mormon"
wrote:





Mental note to Dave: Do not start generator while under load. Make a sign,
and tape it to the generator.


--


Christopher A. Young;
.
.


"Dave" wrote in message


...
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Ah, I see, transfer switch allows the machine to start under no load,
then subsequently transfers load...- Hide quoted text -

- Show quoted text -


Thanks for the replies - some comments will be answered next time when/
if this failure repeats itself.

Regarding feedback, is it possible to start the generator under load
with an automatic transfer switch in the circuit - isn't this one of
the preventative features of an automatic transfer switch?

Other thoughts/questions regarding the system test sequence:
1. 200-amp breaker upstream of the automatic transfer switch: Use to
simulate loss of offsite power
2. Main house panel service disconnect breaker (downstream of the
auto transfer switch): If the auto transfer switch is working
properly is it necessary to exercise this breaker in testing the
system?
3. Generator control panel breaker: Should this breaker be included
in the system test sequence and if so how?

  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 625
Default Generac Troubleshooting

Dave,

Since the generator starts as expected when the breaker is manually
switched, but fails to start when a power outage occurs, I would suspect the
transfer switch controller board is behaving intermittently. This board
controls the automatic transfer using a very simple method based on the
amount and duration of power outage to turn on / switch the generator, and
does the same in the reverse sequence as well when utility power returns.

Two suggestions:

1. Download the extensive (several hundred page) repair guide available at
the Generac / Guardian web site which has complete diagnostics, flow charts,
schematics, parts listings, drawings, and narrative. It is truly excellent,
and is offered in a pdf file at no charge. It explains all of the Generac in
great detail.

2. If the unit is still under the 2 year manufacturer's warranty, contact
your local dealer and document the problem, and have them look at it. Even
if it is an intermittent problem, you definitely WANT GENERAC to replace the
defective part if and when it fails completely. The board itself is probably
a few hundred bucks if you had to buy one yourself, and a new transfer
switch is well over $1000.

You might also note that there are two cartridge fuses protecting the 24
volt relay on the transfer switch, and one or both of these can, if not
snugly installed, cause switching problems. I suggest buying a couple spares
just in case one or both blow in a true emergency.

Hope this helps,

Smarty


"Dave" wrote in message
...
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.



  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,746
Default Generac Troubleshooting

Dave wrote:

On Dec 17, 3:59 pm, Dave wrote:
On Dec 17, 1:12 pm, "Stormin Mormon"
wrote:





Mental note to Dave: Do not start generator while under load. Make a sign,
and tape it to the generator.


--


Christopher A. Young;
.
.


"Dave" wrote in message


...
Utility power outage and the Generac 04390-2 (13kW NG) did not start
in 50F weather. Assuming for now the problem is not with the
generator because when the 200-amp breaker installed between the
utility meter and the automatic transfer switch was moved to the off
position, the Generac started as expected. Does this description
sound like a relay or other automatic transfer switch component
waiting to fail more permanently? Replies appreciated.


Ah, I see, transfer switch allows the machine to start under no load,
then subsequently transfers load...- Hide quoted text -

- Show quoted text -


Thanks for the replies - some comments will be answered next time when/
if this failure repeats itself.

Regarding feedback, is it possible to start the generator under load
with an automatic transfer switch in the circuit - isn't this one of
the preventative features of an automatic transfer switch?

Other thoughts/questions regarding the system test sequence:
1. 200-amp breaker upstream of the automatic transfer switch: Use to
simulate loss of offsite power
2. Main house panel service disconnect breaker (downstream of the
auto transfer switch): If the auto transfer switch is working
properly is it necessary to exercise this breaker in testing the
system?
3. Generator control panel breaker: Should this breaker be included
in the system test sequence and if so how?


The installation and owners manual I referenced in my other post has the
detailed procedures for all tests.
Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generac 7550 Generator The Fisherman Home Repair 16 May 9th 07 07:27 PM
Generac 7500 [email protected] Electronics Repair 22 December 24th 06 08:47 PM
Generac 5244 DOA [email protected] Home Repair 1 June 1st 06 02:56 AM
Help needed with Generac Generator Lloyd Cimprich Home Repair 2 April 12th 06 05:10 AM
Generac Oil Pressure Switch boden Home Repair 9 October 11th 05 04:08 AM


All times are GMT +1. The time now is 07:53 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"