Does code require the receptacle for a over-the-range microwave to be GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is it
sufficient to depend on the microwave ground being intact at all times?)

Anyway the main question is, "Doec the code require a GFI here?"

Many thanks.
  #2   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Elec code question

No, only counter outlets in the kitchen


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is it
sufficient to depend on the microwave ground being intact at all times?)

Anyway the main question is, "Doec the code require a GFI here?"

Many thanks.



  #3   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Elec code question


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is it
sufficient to depend on the microwave ground being intact at all times?)

Anyway the main question is, "Doec the code require a GFI here?"



No


  #4   Report Post  
Posted to alt.home.repair
SRN SRN is offline
external usenet poster
 
Posts: 94
Default Elec code question


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be

GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is it
sufficient to depend on the microwave ground being intact at all times?)

Anyway the main question is, "Doec the code require a GFI here?"



No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Actually, assuming we are talking kitchens in dwelling units, the 2005 NEC,
Article 210.8(A)(6) only says that kitchens require GFCIs on receptacles
"where the receptacles are installed to serve the countertop surfaces".
Local codes may be more restrictive.


  #5   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Elec code question

For starters, they say something different then they say for outlets above
stoves for microwaves


"Clark" wrote in message
...
"SRN" wrote in
:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be
GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is
it sufficient to depend on the microwave ground being intact at all
times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Actually, assuming we are talking kitchens in dwelling units, the 2005
NEC, Article 210.8(A)(6) only says that kitchens require GFCIs on
receptacles "where the receptacles are installed to serve the countertop
surfaces". Local codes may be more restrictive.

Ok, I'll certainly go along with that, but what do they say about
receptacles near wet locations or exterior doors?

--
---
there should be a "sig" here





  #6   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Elec code question


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be

GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is it
sufficient to depend on the microwave ground being intact at all

times?)

Anyway the main question is, "Doec the code require a GFI here?"



No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.



Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.


  #7   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Elec code question

Regardless of what "an inspector" should require, the NEC doesn't



"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to be
GFI
protected? (Seems to me like it would be a good idea because one may
frequently be touching the microwave and the grounded range - or is

it
sufficient to depend on the microwave ground being intact at all

times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.



Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it within 6
feet of a wet location? If those conditions are met then an inspector
should require protection. Got it?

--
---
there should be a "sig" here



  #8   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Elec code question


"Clark" wrote in message
...
"RBM" rbm2(remove wrote in news:xFVIi.670$GW.238
@newsfe12.lga:

Regardless of what "an inspector" should require, the NEC doesn't


The NEC requires protection for outlets near wet locations. No one has
provided a cite for an exception to that requirement.


Sorry, wrong again. You need to invest in a code book. There is nothing in
the NEC that requires (generally) that GFCI protection is required for
outlets "near wet locations" It does require protection in specific wet
locations and other specific locations, but adjacent to an exist door on the
inside of a house, while "near" a wet location, is not required to be GFCI
protected


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to

be
GFI
protected? (Seems to me like it would be a good idea because one

may
frequently be touching the microwave and the grounded range - or is
it
sufficient to depend on the microwave ground being intact at all
times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it within

6
feet of a wet location? If those conditions are met then an inspector
should require protection. Got it?

--
---
there should be a "sig" here







--
---
there should be a "sig" here



  #9   Report Post  
Posted to alt.home.repair
RBM RBM is offline
external usenet poster
 
Posts: 1,690
Default Elec code question

Clark, you're reaching!!! Originally when GFCI protection was required at
kitchen counters, it was for any outlet within six feet of the sink. That's
changed and all kitchen counter outlets are required to be protected. GFCI
rules are pretty specific now, such as where an outdoor hot tub is
installed, a GFCI outlet is required to be installed between ten and twenty
feet from the tub. The only current six foot rule I know of is a counter top
at a wet bar, any outlet within six feet of the sink must be protected


"Clark" wrote in message
...
"RBM" rbm2(remove wrote in
:


"Clark" wrote in message
...
"RBM" rbm2(remove wrote in news:xFVIi.670$GW.238
@newsfe12.lga:

Regardless of what "an inspector" should require, the NEC doesn't


The NEC requires protection for outlets near wet locations. No one has
provided a cite for an exception to that requirement.


Sorry, wrong again. You need to invest in a code book. There is nothing
in the NEC that requires (generally) that GFCI protection is required
for outlets "near wet locations" It does require protection in specific
wet locations and other specific locations, but adjacent to an exist
door on the inside of a house, while "near" a wet location, is not
required to be GFCI protected


Ummm, what about the rule of being within six feet? That still holds does
it not?




"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave
to
be
GFI
protected? (Seems to me like it would be a good idea because
one
may
frequently be touching the microwave and the grounded range - or
is
it
sufficient to depend on the microwave ground being intact at all
times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it
within
6
feet of a wet location? If those conditions are met then an inspector
should require protection. Got it?

--
---
there should be a "sig" here






--
---
there should be a "sig" here






--
---
there should be a "sig" here



  #10   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Elec code question


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave to

be
GFI
protected? (Seems to me like it would be a good idea because one

may
frequently be touching the microwave and the grounded range - or is

it
sufficient to depend on the microwave ground being intact at all

times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.



Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it within 6
feet of a wet location? If those conditions are met then an inspector
should require protection. Got it?



I got the fact that you don't understand NEC codes.




  #11   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Elec code question


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d5c94$46f617a4$9440c41e$2024
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range microwave

to
be
GFI
protected? (Seems to me like it would be a good idea because one

may
frequently be touching the microwave and the grounded range - or

is
it
sufficient to depend on the microwave ground being intact at all
times?)

Anyway the main question is, "Doec the code require a GFI here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it

within
6
feet of a wet location? If those conditions are met then an inspector
should require protection. Got it?



I got the fact that you don't understand NEC codes.


Wrong again.



Yeah, right.
If you did, you wouldn't be asking your stupid ass questions.


  #12   Report Post  
Posted to alt.home.repair
No Name
 
Posts: n/a
Default Elec code question


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:3e33$46f7481b$9440c41e$12360
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d5c94$46f617a4$9440c41e$2024
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:d7073$46f3d805$9440c41e$30006
@STARBAND.NET:


"Clark" wrote in message
...
kjpro @ usenet.com wrote in news:14698$46f09249$9440c41e$8159
@STARBAND.NET:


wrote in message
...
Does code require the receptacle for a over-the-range

microwave
to
be
GFI
protected? (Seems to me like it would be a good idea because

one
may
frequently be touching the microwave and the grounded range -

or
is
it
sufficient to depend on the microwave ground being intact at

all
times?)

Anyway the main question is, "Doec the code require a GFI

here?"


No

It does is it is near the sink.

But you knew that. Right? I'm sure you'll say so anyway.


Once again, you show you're ignorance.
Try purchasing a NEC2005 and learn to read.



You're still wrong. Could the receptacle serve the counter? Is it

within
6
feet of a wet location? If those conditions are met then an

inspector
should require protection. Got it?


I got the fact that you don't understand NEC codes.


Wrong again.



Yeah, right.
If you did, you wouldn't be asking your stupid ass questions.

Wrong again. Read the questions and try to understand the point this time.



I got the point, you're a Putz.


Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Elec Shower Question . Stuart B UK diy 3 March 21st 07 01:06 PM
Elec Question Don Dando Woodworking 3 March 18th 06 04:10 PM
Elec. subpanel question Martin Home Repair 7 June 9th 05 08:26 PM
e-lectrical code question Borax Home Repair 6 June 3rd 05 04:22 AM
elec. code for heater in bathroom Michael Press Home Repair 7 January 6th 04 08:23 PM


All times are GMT +1. The time now is 12:56 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"