Home Repair (alt.home.repair) For all homeowners and DIYers with many experienced tradesmen. Solve your toughest home fix-it problems.

Reply
 
LinkBack Thread Tools Search this Thread Display Modes
  #1   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 135
Default Square D QO question

On Mar 29, 9:36 am, boden wrote:
I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.

Does Square D make a QO 20 amp breaker with a delay characteristic?
Perhaps a thermal breaker?

Although the circuit is dedicated, running 10AWG in order to put in a 30
amp breaker will not be fun.

Thanks,
Boden

Yes, I think they do, just for that reason.

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 300
Default Square D QO question

I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.

Does Square D make a QO 20 amp breaker with a delay characteristic?
Perhaps a thermal breaker?

Although the circuit is dedicated, running 10AWG in order to put in a 30
amp breaker will not be fun.

Thanks,
Boden

  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 1,934
Default Square D QO question


"boden" wrote in message
...
I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.

Does Square D make a QO 20 amp breaker with a delay characteristic?
Perhaps a thermal breaker?

Although the circuit is dedicated, running 10AWG in order to put in a 30
amp breaker will not be fun.

Thanks,
Boden


A standard QO circuit breaker is rated for that initial motor surge. The
easiest thing to do is replace the circuit breaker, however the fact that
your motor is drawing more than its nameplate rating is a concern. It's
possible that your motor is on its way out or something is causing it to
work harder then it should. Did you check the voltage under load?

  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 49
Default Square D QO question

Meter reading will varty depending on the type meter you have.

True rms?



On Thu, 29 Mar 2007 10:36:48 -0500, boden wrote:

I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.

Does Square D make a QO 20 amp breaker with a delay characteristic?
Perhaps a thermal breaker?

Although the circuit is dedicated, running 10AWG in order to put in a 30
amp breaker will not be fun.

Thanks,
Boden

  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 590
Default Square D QO question


"boden" wrote in message
...
I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the breaker
opens at least half the time at start-up.


How long has this been occurring? Perhaps something has changed? The three
easiest solutions a

1/ Tighten all the screws. The wires going to breakers in the panel often
get a little loose over time. Turn off the main power first!
2/ Does the Nutone have a capacitor type motor? It might be defective (the
capacitor).
3/ Try a new breaker.




  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 361
Default Square D QO question

boden writes:
I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.


Sounds like you have a weak breaker. A 20 amp breaker should take at
least 20 seconds or so to trip when the load is 40 amps. Your load is
apparently around 25 amps, and at that current it should take many
minutes to trip. Meanwhile, the central vac should be up to speed, and
the current down at 13.5 A, in less than 20 seconds.

Here's an example trip curve for one model of QO breaker. The same site
has many others if you know exactly which model of breaker you have.

http://ecatalog.squared.com/pubs/Cir.../QO/730-11.pdf

Dave
  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 303
Default Square D QO question

On Thu, 29 Mar 2007 10:36:48 -0500, boden wrote:

I have a Nutone central vacuum on a dedicated 20 amp, 120v circuit. The
vacuum is spec'd to draw 12.6 amps (I measure it at closer to 13.5 amps)
but the starting current is close to twice that. Consequently the
breaker opens at least half the time at start-up.

Does Square D make a QO 20 amp breaker with a delay characteristic?
Perhaps a thermal breaker?

Although the circuit is dedicated, running 10AWG in order to put in a 30
amp breaker will not be fun.

Thanks,
Boden



Seems strang, have you tried swapping another 20a breaker in?

tom @ www.Consolidated-Loans.info

Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
spokeshave question (how to drill a square hole) Andy Woodworking 9 July 9th 06 12:43 AM
2" square stock strength question Grant Erwin Metalworking 22 September 8th 05 09:10 PM
Engineering question about square steel tubing carl mciver Metalworking 17 August 15th 05 04:21 PM
Square tubing question SteveB Metalworking 2 March 15th 05 05:46 PM
Square d duplex breaker question gary Home Repair 9 March 7th 05 04:05 AM


All times are GMT +1. The time now is 02:34 PM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"