Hey all,

My furnace seems to be running all right, but, one thing has me
curious.
I've got a Honeywell stat that is supposed to have "smart recovery"
that learns the amount of time necessary to re heat in the morning.
It takes the furnace about an hr to get back up from 57 to the 69 I
ask for in the morning with the outside temp in the single to teen
digits (Michigan)

In the mornings the heat will turn on around 6 to have the house warm
by 7. The odd thing is that the furnace will run for about 30 minutes
or more, then it will then stop for about a minute or 2 then turn
back on continuing to heat. At the time the furnace turns off it
might have raised the temp from 57 to 65 or so, on its way to 69.

The stat has a "heat" indicator on the display and while it is
blinking "recovery" indicating that the system is trying to re heat
the house, the "heat" indicator will turn off.

The fan will run for a few minutes after the heat indicator turns
off, then the whole system will sit for a minute or too, then it will
turn back on, and work its way back up to the desired temp.

Is this normal? should the furnace not run straight thru up until it
reaches the desired temp?


I've got an older (17 yrs??) furnace Thermo Pride Furnace which I
believe has an 80% efficiency (based on btu IN/OUT calcs on the
stickers. The house is about 30 yrs old 2200 sq/ft.

Thanks for any and all comments / info


Dave

  #2   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 6,586
Default Furnace Stops prematurely while in recovery mode

Zephyr wrote:

Hey all,

My furnace seems to be running all right, but, one thing has me
curious.
I've got a Honeywell stat that is supposed to have "smart recovery"
that learns the amount of time necessary to re heat in the morning.
It takes the furnace about an hr to get back up from 57 to the 69 I
ask for in the morning with the outside temp in the single to teen
digits (Michigan)

In the mornings the heat will turn on around 6 to have the house warm
by 7. The odd thing is that the furnace will run for about 30 minutes
or more, then it will then stop for about a minute or 2 then turn
back on continuing to heat. At the time the furnace turns off it
might have raised the temp from 57 to 65 or so, on its way to 69.

The stat has a "heat" indicator on the display and while it is
blinking "recovery" indicating that the system is trying to re heat
the house, the "heat" indicator will turn off.

The fan will run for a few minutes after the heat indicator turns
off, then the whole system will sit for a minute or too, then it will
turn back on, and work its way back up to the desired temp.

Is this normal? should the furnace not run straight thru up until it
reaches the desired temp?


I've got an older (17 yrs??) furnace Thermo Pride Furnace which I
believe has an 80% efficiency (based on btu IN/OUT calcs on the
stickers. The house is about 30 yrs old 2200 sq/ft.

Thanks for any and all comments / info


Dave

Hi,
You can peruse service option menu relating to this.
  #3   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 64
Default Furnace Stops prematurely while in recovery mode


"Tony Hwang" wrote in message
news:kfcwh.834083$5R2.647573@pd7urf3no...
Hi,
You can peruse service option menu relating to this.



sorry, I don't follow. what service menu are you referring to?

Dave


  #4   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 766
Default Furnace Stops prematurely while in recovery mode

Zephyr wrote:
Hey all,

My furnace seems to be running all right, but, one thing has me
curious.
I've got a Honeywell stat that is supposed to have "smart recovery"
that learns the amount of time necessary to re heat in the morning.
It takes the furnace about an hr to get back up from 57 to the 69 I
ask for in the morning with the outside temp in the single to teen
digits (Michigan)

In the mornings the heat will turn on around 6 to have the house warm
by 7. The odd thing is that the furnace will run for about 30 minutes
or more, then it will then stop for about a minute or 2 then turn
back on continuing to heat. At the time the furnace turns off it
might have raised the temp from 57 to 65 or so, on its way to 69.

The stat has a "heat" indicator on the display and while it is
blinking "recovery" indicating that the system is trying to re heat
the house, the "heat" indicator will turn off.

The fan will run for a few minutes after the heat indicator turns
off, then the whole system will sit for a minute or too, then it will
turn back on, and work its way back up to the desired temp.

Is this normal? should the furnace not run straight thru up until it
reaches the desired temp?


I've got an older (17 yrs??) furnace Thermo Pride Furnace which I
believe has an 80% efficiency (based on btu IN/OUT calcs on the
stickers. The house is about 30 yrs old 2200 sq/ft.

Thanks for any and all comments / info


Dave



I would not call it normal (Maybe for a heat pump, they often have a few
special tricks to reduce heating cost).

There may be a problem with the furnace (sounds like a gas furnace).
Maybe it is detecting a overheat situation at the burner. That could be a
bad sensor.

In all fairness, I am making a lot of guesses here, but I suspect you
will need to have someone check out the furnace. If it needs repair, I
would consider a newer high efficiency furnace as it may not pay to repair
that lower efficiency one in the long run.

--
Joseph Meehan

Dia 's Muire duit



  #5   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Furnace Stops prematurely while in recovery mode

On Feb 1, 8:00 am, "Joseph Meehan" wrote:
Zephyr wrote:
Hey all,


My furnace seems to be running all right, but, one thing has me
curious.
I've got a Honeywell stat that is supposed to have "smart recovery"
that learns the amount of time necessary to re heat in the morning.
It takes the furnace about an hr to get back up from 57 to the 69 I
ask for in the morning with the outside temp in the single to teen
digits (Michigan)


In the mornings the heat will turn on around 6 to have the house warm
by 7. The odd thing is that the furnace will run for about 30 minutes
or more, then it will then stop for about a minute or 2 then turn
back on continuing to heat. At the time the furnace turns off it
might have raised the temp from 57 to 65 or so, on its way to 69.


The stat has a "heat" indicator on the display and while it is
blinking "recovery" indicating that the system is trying to re heat
the house, the "heat" indicator will turn off.


The fan will run for a few minutes after the heat indicator turns
off, then the whole system will sit for a minute or too, then it will
turn back on, and work its way back up to the desired temp.


Is this normal? should the furnace not run straight thru up until it
reaches the desired temp?


I've got an older (17 yrs??) furnace Thermo Pride Furnace which I
believe has an 80% efficiency (based on btu IN/OUT calcs on the
stickers. The house is about 30 yrs old 2200 sq/ft.


Thanks for any and all comments / info


Dave


I would not call it normal (Maybe for a heat pump, they often have a few
special tricks to reduce heating cost).

There may be a problem with the furnace (sounds like a gas furnace).
Maybe it is detecting a overheat situation at the burner. That could be a
bad sensor.


It isn't a problem with the furnace, because he said that when this
happens, the "heat" indicator on the thermostat goes out and the
recovery indicator stays on. If it were the furnace, the heat
indicator on the thermostat would not change.

I think the service menu that Tony is referring to is the advanced
settings menu in the thermostat. Some of the HW thermostats, like
the LCD touchscreeen (8600?) ones have a zillion settings. It's
possible something in there controls this. Like maybe it's set for
some dual fuel system option, where it uses one fuel to get most of
the way, then switches.

If you can't find a setting, I'd contact HW or look on their FAQ page,
etc. My vote is this isn't right, and it's either a setting or a
software bug, but it's not a failure in the thermostat.






In all fairness, I am making a lot of guesses here, but I suspect you
will need to have someone check out the furnace. If it needs repair, I
would consider a newer high efficiency furnace as it may not pay to repair
that lower efficiency one in the long run.

--
Joseph Meehan

Dia 's Muire duit- Hide quoted text -

- Show quoted text -





  #6   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 201
Default Furnace Stops prematurely while in recovery mode

Dave,

What you describe may be normal. My furnace comes on in the morning and
runs for about half an hour. This raises the air temp in the house to 68,
the setpoint. The furnace shuts off. The walls, floors, ceilings et c. are
still cold. The thermostat is mounted next to a wall. Until the wall is
heated up the furnace keeps cycling quickly. It seems to take slightly more
than an hour and a half to heat up the interior walls. So the furnace does
run a lot first thing in the morning

Dave M.


  #7   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 4,500
Default Furnace Stops prematurely while in recovery mode

On Feb 1, 8:54 am, "David Martel" wrote:
Dave,

What you describe may be normal. My furnace comes on in the morning and
runs for about half an hour. This raises the air temp in the house to 68,
the setpoint. The furnace shuts off. The walls, floors, ceilings et c. are
still cold. The thermostat is mounted next to a wall. Until the wall is
heated up the furnace keeps cycling quickly. It seems to take slightly more
than an hour and a half to heat up the interior walls. So the furnace does
run a lot first thing in the morning

Dave M.



His doesn;t get to the setpoint. It stops prematurely at 65, when
the setpoint is 69, waits a bit, then resumes. That is not normal.




  #8   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 467
Default Furnace Stops prematurely while in recovery mode

In your case I would also be suspicious of the thermostat. Having
said that, mine was doing the exact same thing and it turned out to be
the fan limit switch.

  #9   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 64
Default Furnace Stops prematurely while in recovery mode


snip

I should have provided some more info,

it is a gas furnace, I have a gas water heater, and gas stove. The
furnace had the exhaust fan and ignitor unit replaced earlier this year
under home warrenty. I have a few vents closed currently to prevent
heating of unused rooms.



It isn't a problem with the furnace, because he said that when this
happens, the "heat" indicator on the thermostat goes out and the
recovery indicator stays on. If it were the furnace, the heat
indicator on the thermostat would not change.



That was my thinking too, that if the heat indicator went off on the stat,
that it was not the furnace that was at fault, it was the stat. A friend
of mine (who had not looked at it) suggested that maybe the furnace was
overheating, but, given the situation with the stat, I was skeptical of
that possibility. Unless the funace had some overheating sensor that fed to
the stat that turned of the stat, instead of just stopping the furnace
leaving the stat still calling for heat.

That all said, I do have a few vents closed in spare bedrooms and all the
vents in the unfinished basement.

I think the service menu that Tony is referring to is the advanced
settings menu in the thermostat. Some of the HW thermostats, like
the LCD touchscreeen (8600?) ones have a zillion settings. It's
possible something in there controls this. Like maybe it's set for
some dual fuel system option, where it uses one fuel to get most of
the way, then switches.


I will look into the stats menu settings, it doesn't seem like there is a
lot there, this is a lower end model, it doesn't even record the run times
for the past day/week/period.


If you can't find a setting, I'd contact HW or look on their FAQ page,
etc. My vote is this isn't right, and it's either a setting or a
software bug, but it's not a failure in the thermostat.


In all fairness, I am making a lot of guesses here, but I suspect you
will need to have someone check out the furnace. If it needs repair, I
would consider a newer high efficiency furnace as it may not pay to
repair
that lower efficiency one in the long run.

--
Joseph Meehan

Dia 's Muire duit- Hide quoted text -

- Show quoted text -





Thanks for all your help

Dave


  #10   Report Post  
Posted to alt.home.repair
external usenet poster
 
Posts: 64
Default Furnace Stops prematurely while in recovery mode


"Zephyr" Someguy@an email address.com wrote in message
. ..

snip

I should have provided some more info,

it is a gas furnace, I have a gas water heater, and gas stove. The
furnace had the exhaust fan and ignitor unit replaced earlier this year
under home warrenty. I have a few vents closed currently to prevent
heating of unused rooms.


I should have also added that I never see this happening when the furnace is
just maintaining the temp,





It isn't a problem with the furnace, because he said that when this
happens, the "heat" indicator on the thermostat goes out and the
recovery indicator stays on. If it were the furnace, the heat
indicator on the thermostat would not change.



That was my thinking too, that if the heat indicator went off on the
stat, that it was not the furnace that was at fault, it was the stat.
A friend of mine (who had not looked at it) suggested that maybe the
furnace was overheating, but, given the situation with the stat, I was
skeptical of that possibility. Unless the funace had some overheating
sensor that fed to the stat that turned of the stat, instead of just
stopping the furnace leaving the stat still calling for heat.

That all said, I do have a few vents closed in spare bedrooms and all the
vents in the unfinished basement.

I think the service menu that Tony is referring to is the advanced
settings menu in the thermostat. Some of the HW thermostats, like
the LCD touchscreeen (8600?) ones have a zillion settings. It's
possible something in there controls this. Like maybe it's set for
some dual fuel system option, where it uses one fuel to get most of
the way, then switches.


I will look into the stats menu settings, it doesn't seem like there is a
lot there, this is a lower end model, it doesn't even record the run
times for the past day/week/period.


If you can't find a setting, I'd contact HW or look on their FAQ page,
etc. My vote is this isn't right, and it's either a setting or a
software bug, but it's not a failure in the thermostat.


In all fairness, I am making a lot of guesses here, but I suspect
you
will need to have someone check out the furnace. If it needs repair, I
would consider a newer high efficiency furnace as it may not pay to
repair
that lower efficiency one in the long run.

--
Joseph Meehan

Dia 's Muire duit- Hide quoted text -

- Show quoted text -





Thanks for all your help

Dave




Reply
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules

Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Camcorder: Works perfect in 0 LUX mode; Hazy in normal mode Raqueeb Hassan Electronics Repair 2 January 9th 07 05:18 PM
Furnace turns off prematurely new2059 Home Repair 9 January 24th 06 05:26 PM
Furnace shuts off prematurely Rod Dahl Home Repair 15 October 12th 05 04:03 AM
Dryer Stops Running Prematurely Vince Home Repair 6 December 10th 04 08:32 PM
Energy savings? heat-recovery Unit 4 a furnace. lbbs Home Ownership 2 January 7th 04 09:54 PM


All times are GMT +1. The time now is 07:20 AM.

Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Copyright ©2004-2024 DIYbanter.
The comments are property of their posters.
 

About Us

"It's about DIY & home improvement"