I'm wiring up some outlets in my garage. I have a receptacle, wire going in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?



[email protected] December 24th 06 02:08 AM

House wiring question.
 
I usually wrap the two grounds together and then attach one of the
ground wires to the screw, cutting the other one a little shorter.

(I am NOT an electrician)


[email protected] December 24th 06 02:22 AM

House wiring question.
 

Ook wrote:
I'm wiring up some outlets in my garage. I have a receptacle, wire going in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?


Take a look at the diagram at:

http://img.timeinc.net/toh/images/el...outlets01t.jpg

In other words, connect the ground wire with a pig tail to the screw on
top of the outlet. I wouldn't use the same screw. Home Depot, actually
has some pre-made pig tails, but using those only make sense if you are
going to do a lot of them.


Gary KW4Z December 24th 06 02:23 AM

House wiring question.
 
Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to see
because some codes require a GFCI circuit in the garage area. You can wrap
take a bare copper (ground) wire and run to the ground connection, of the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut it
and make your splices there. The important thing, again, is maintaining the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and maintain
that throughout each outlet or you risk electrocution. Each outlet has a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me any
freakin' spam at zootal dot com delete the Don't send me any freakin' spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire going in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?




John Gilmer December 24th 06 02:44 AM

House wiring question.
 

wrote in message
ps.com...
I usually wrap the two grounds together and then attach one of the
ground wires to the screw, cutting the other one a little shorter.


I don't trust just wrapping two grounds together.

If it's "new work" I use one of those wirenuts with a hole in the end and
leave the longer of the two ground wires uncut. Slip the wirenut over the
long wire and slide it down to where the second ground can be laid
alongside. Twist both wires together. If the ground wires have already
been but short, you just add a third through the hole.

I picked up some "pigtail" wirenuts (12 each in white, black, red, and
green) and they are useful when you have only a single device.


(I am NOT an electrician)




Ook December 24th 06 02:49 AM

House wiring question.
 
I have the hot/neutral stuff down :). I've probably forgotten more about
electricity then most electricians will ever know. However, having said
that, I know squat about building codes. I decided to run a short wire from
the ground screw of the receptacle and use a wirenut to bind that to the two
ground wires running through the box. I gather that doing it that way meets
code, and it will probably work almost as well though I'll be the first to
admit I don't like using wire nuts, even if it is the time honored way to
wire houses. I've seen too many get hot because the connection wasn't as
good as it should/could have been.


----- Original Message -----
From: "Gary KW4Z"
Newsgroups: alt.home.repair
Sent: Saturday, December 23, 2006 6:23 PM
Subject: House wiring question.


Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and maintain
that throughout each outlet or you risk electrocution. Each outlet has a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?



"Gary KW4Z" wrote in message
...
Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and maintain
that throughout each outlet or you risk electrocution. Each outlet has a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?






Ook December 24th 06 02:50 AM

House wiring question.
 



Ook wrote:
I'm wiring up some outlets in my garage. I have a receptacle, wire going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?


Take a look at the diagram at:

http://img.timeinc.net/toh/images/el...outlets01t.jpg

In other words, connect the ground wire with a pig tail to the screw on
top of the outlet. I wouldn't use the same screw. Home Depot, actually
has some pre-made pig tails, but using those only make sense if you are
going to do a lot of them.


This is how I ended up doing it. I wasn't sure if code allowed two wires to
be attached to one screw or not, so I redid it like the picture shows.



John Grabowski December 24th 06 03:24 AM

House wiring question.
 

"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I have the hot/neutral stuff down :). I've probably forgotten more about
electricity then most electricians will ever know. However, having said
that, I know squat about building codes. I decided to run a short wire

from
the ground screw of the receptacle and use a wirenut to bind that to the

two
ground wires running through the box. I gather that doing it that way

meets
code, and it will probably work almost as well though I'll be the first to
admit I don't like using wire nuts, even if it is the time honored way to
wire houses. I've seen too many get hot because the connection wasn't as
good as it should/could have been.



Twist the wires together tightly with pliers and then twist on the wire
connector. You won't have a heat problem that way. Too often inexperienced
DIYers will just insert the wires into the wire connector and twist it on.
I think that the Scotchloks are the only brand that are approved for
non-twisted mechanical connection.



Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of

the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut

it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and

maintain
that throughout each outlet or you risk electrocution. Each outlet has

a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire

going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two

screws
for
the hot wire, but only one screw for the ground wire. I hook the hot

and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw?

It
seems to be secure, but it is it the correct way to do this?



"Gary KW4Z" wrote in message
...
Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of

the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut

it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and

maintain
that throughout each outlet or you risk electrocution. Each outlet has

a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire

going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two

screws
for
the hot wire, but only one screw for the ground wire. I hook the hot

and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw?

It
seems to be secure, but it is it the correct way to do this?







Steve Barker LT December 24th 06 03:43 AM

House wiring question.
 
Twist the two ground wires together tightly with a pair of square nosed
pliers, then cut one off. Put the other on the outlet.

--
Steve Barker


"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I'm wiring up some outlets in my garage. I have a receptacle, wire going
in the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for the hot wire, but only one screw for the ground wire. I hook the hot
and neutral wires to the respective screws, works fine.What is the correct
way to wire up the ground wire? Can I put both of them on the same screw?
It seems to be secure, but it is it the correct way to do this?




Steve Barker LT December 24th 06 03:44 AM

House wiring question.
 
Twisting the grounds together is perfectly acceptable and works fine.

--
Steve Barker




"John Gilmer" wrote in message
...

wrote in message
ps.com...
I usually wrap the two grounds together and then attach one of the
ground wires to the screw, cutting the other one a little shorter.


I don't trust just wrapping two grounds together.

If it's "new work" I use one of those wirenuts with a hole in the end and
leave the longer of the two ground wires uncut. Slip the wirenut over
the
long wire and slide it down to where the second ground can be laid
alongside. Twist both wires together. If the ground wires have already
been but short, you just add a third through the hole.

I picked up some "pigtail" wirenuts (12 each in white, black, red, and
green) and they are useful when you have only a single device.


(I am NOT an electrician)






Steve Barker LT December 24th 06 03:46 AM

House wiring question.
 
It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.

--
Steve Barker

"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I have the hot/neutral stuff down :). I've probably forgotten more about
electricity then most electricians will ever know. However, having said
that, I know squat about building codes. I decided to run a short wire from
the ground screw of the receptacle and use a wirenut to bind that to the
two ground wires running through the box. I gather that doing it that way
meets code, and it will probably work almost as well though I'll be the
first to admit I don't like using wire nuts, even if it is the time honored
way to wire houses. I've seen too many get hot because the connection
wasn't as good as it should/could have been.


----- Original Message -----
From: "Gary KW4Z"
Newsgroups: alt.home.repair
Sent: Saturday, December 23, 2006 6:23 PM
Subject: House wiring question.


Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut
it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and maintain
that throughout each outlet or you risk electrocution. Each outlet has a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?



"Gary KW4Z" wrote in message
...
Depending on who you ask the important thing is secure a good continuous
mechanical connection through the circuit. Being in the garage check to
see
because some codes require a GFCI circuit in the garage area. You can
wrap
take a bare copper (ground) wire and run to the ground connection, of the
outlet, then secure it to the remaining wire runs with a lug nut or most
just pull enough wire out of the outlet and loop the connections or cut
it
and make your splices there. The important thing, again, is maintaining
the
integrity of the ground through your outlets. Make sure that your HOT
(Black) wire goes into the proper position on the receptacle and maintain
that throughout each outlet or you risk electrocution. Each outlet has a
HOT side and a Neutral side but sounds like you already have that down.


On 12/23/06 8:50 PM, in article
, "Ook" Ook Don't send me
any
freakin' spam at zootal dot com delete the Don't send me any freakin'
spam
wrote:

I'm wiring up some outlets in my garage. I have a receptacle, wire going
in
the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for
the hot wire, but only one screw for the ground wire. I hook the hot and
neutral wires to the respective screws, works fine.What is the correct
way
to wire up the ground wire? Can I put both of them on the same screw? It
seems to be secure, but it is it the correct way to do this?








Tom The Great December 24th 06 04:13 AM

House wiring question.
 
On 23 Dec 2006 18:08:41 -0800, wrote:

I usually wrap the two grounds together and then attach one of the
ground wires to the screw, cutting the other one a little shorter.

(I am NOT an electrician)


IMHO:

If you toss on a "greenie" on what you did, it would sound ok.
"Greenies" are green wire nuts with a hole in it to allow a single
wire to pass through.

later,

tom @
www.MedJobSite.com



Toller December 24th 06 04:37 AM

House wiring question.
 

"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I'm wiring up some outlets in my garage. I have a receptacle, wire going
in the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for the hot wire, but only one screw for the ground wire. I hook the hot
and neutral wires to the respective screws, works fine.What is the correct
way to wire up the ground wire? Can I put both of them on the same screw?
It seems to be secure, but it is it the correct way to do this?

Around here grounds are required to be crimped. I crimp them and put the
longer one on the outlet.



[email protected] December 24th 06 04:58 AM

House wiring question.
 

John Grabowski wrote:

Twist the wires together tightly with pliers and then twist on the wire
connector. You won't have a heat problem that way. Too often inexperienced
DIYers will just insert the wires into the wire connector and twist it on.
I think that the Scotchloks are the only brand that are approved for
non-twisted mechanical connection.


Ye Gads! I guess you learn something every day. I'm not an electrician
and I've always just worked on my own house, but I've never twisted the
wires first. However, I have always made sure that the wires are
securely fastened in the connector. The good news is that 20-years
later, I haven't had any problems. The bad news is that you've given me
yet another thing to worry about, but thanks anyway.


Chris Friesen December 24th 06 06:12 AM

House wiring question.
 
Steve Barker LT wrote:
It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.


Which is a nuisance, but easily diagnosed and fixed. Losing your safety
ground is a potentially serious problem.

Chris

[email protected] December 24th 06 12:31 PM

House wiring question.
 

Toller wrote:
"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I'm wiring up some outlets in my garage. I have a receptacle, wire going
in the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for the hot wire, but only one screw for the ground wire. I hook the hot
and neutral wires to the respective screws, works fine.What is the correct
way to wire up the ground wire? Can I put both of them on the same screw?
It seems to be secure, but it is it the correct way to do this?

Around here grounds are required to be crimped. I crimp them and put the
longer one on the outlet.


That's what I use too. They have the little metal crimp widgets that
look like a small barrel. I leave one ground a lot longer, twist them
all together, slide the crimp barrel thing over them and crimp.


[email protected] December 24th 06 12:50 PM

House wiring question.
 

wrote:
On 23 Dec 2006 20:58:50 -0800,
wrote:

I think that the Scotchloks are the only brand that are approved for
non-twisted mechanical connection.


Ye Gads! I guess you learn something every day. I'm not an electrician
and I've always just worked on my own house, but I've never twisted the
wires first. However, I have always made sure that the wires are
securely fastened in the connector. The good news is that 20-years
later, I haven't had any problems. The bad news is that you've given me
yet another thing to worry about, but thanks anyway.



I would suggest you read the box before you believe this. All major
brands say twisting is NOT necessary.


I have a DIY home wiring book that says all you need to do is push the
wires in the nut and twist. But, I prefer to twist the wires before
putting the nut on. The nut seems to grab better and I know if the nut
were to somehow come off that I would still have a good solid
connection. Plus I find the wires are easier to work with when they're
twisted. Just a personal preference of mine.

-Felder


RBM December 24th 06 08:04 PM

House wiring question.
 
You can't put them on the same screw, you can attach both wires to the box,
then use a self grounding outlet, or you can splice the two wires together,
using an approved method, then attach one to the receptacle. You can not
just twist the two wires together, cut one short and attach it to the
outlet, some mechanical means must be used to maintain continuity between
the ground wires



"Ook" Ook Don't send me any freakin' spam at zootal dot com delete the
Don't send me any freakin' spam wrote in message
...
I'm wiring up some outlets in my garage. I have a receptacle, wire going
in the box, wire coming out and going to the next box. The receptacle is a
standard receptacls, and has two screws for the neutral wire, two screws
for the hot wire, but only one screw for the ground wire. I hook the hot
and neutral wires to the respective screws, works fine.What is the correct
way to wire up the ground wire? Can I put both of them on the same screw?
It seems to be secure, but it is it the correct way to do this?




Terry December 25th 06 06:45 PM

House wiring question.
 
On Sun, 24 Dec 2006 01:12:15 -0500, wrote:

On 23 Dec 2006 20:58:50 -0800,
wrote:

I think that the Scotchloks are the only brand that are approved for
non-twisted mechanical connection.


Ye Gads! I guess you learn something every day. I'm not an electrician
and I've always just worked on my own house, but I've never twisted the
wires first. However, I have always made sure that the wires are
securely fastened in the connector. The good news is that 20-years
later, I haven't had any problems. The bad news is that you've given me
yet another thing to worry about, but thanks anyway.



I would suggest you read the box before you believe this. All major
brands say twisting is NOT necessary.



Because it is not necessary does not mean it is not better.

Twisting them is better.

Pop` December 26th 06 12:29 AM

House wiring question.
 
Terry wrote:
On Sun, 24 Dec 2006 01:12:15 -0500, wrote:

On 23 Dec 2006 20:58:50 -0800,
wrote:

I think that the Scotchloks are the only brand that are approved
for non-twisted mechanical connection.

Ye Gads! I guess you learn something every day. I'm not an
electrician and I've always just worked on my own house, but I've
never twisted the wires first. However, I have always made sure
that the wires are securely fastened in the connector. The good
news is that 20-years later, I haven't had any problems. The bad
news is that you've given me yet another thing to worry about, but
thanks anyway.



I would suggest you read the box before you believe this. All major
brands say twisting is NOT necessary.



Just happen to have a few boxes nearby:
Gee, I thought Leviton and CH were major brands; both of the boxes say the
wires need to end up twisted and even show pictures. Someone's BS ing here;
wonder if it's me or you? g I'm sure those guys will be disappointed to
see that they're not major brands, poor guys.

What you guys are missing is exactly WHEN the twisting occurs!

Pop`



Mark Lloyd December 26th 06 07:04 PM

House wiring question.
 
On Mon, 25 Dec 2006 13:45:02 -0500, Terry
wrote:

On Sun, 24 Dec 2006 01:12:15 -0500, wrote:

On 23 Dec 2006 20:58:50 -0800,
wrote:

I think that the Scotchloks are the only brand that are approved for
non-twisted mechanical connection.

Ye Gads! I guess you learn something every day. I'm not an electrician
and I've always just worked on my own house, but I've never twisted the
wires first. However, I have always made sure that the wires are
securely fastened in the connector. The good news is that 20-years
later, I haven't had any problems. The bad news is that you've given me
yet another thing to worry about, but thanks anyway.



I would suggest you read the box before you believe this. All major
brands say twisting is NOT necessary.



Because it is not necessary does not mean it is not better.

Twisting them is better.


For some reason, people usually leave that bit out. They seem to
consider "you don't have to" to mean "DON'T".
Mark Lloyd
http://notstupid.laughingsquid.com

"The government of the United States is not, in
any sense, founded on the Christian religion."
-- George Washington

[email protected] December 27th 06 06:39 PM

House wiring question.
 

Steve Barker LT wrote:
It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.


I think the regulations restrict the number of "devices" in a box, but
I don't know if wire nuts are considered to be a "device".


Doug Miller December 27th 06 06:40 PM

House wiring question.
 
In article . com, wrote:

I don't know if wire nuts are considered to be a "device".

No.

--
Regards,
Doug Miller (alphageek at milmac dot com)

It's time to throw all their damned tea in the harbor again.

Terry December 27th 06 10:59 PM

House wiring question.
 
On 27 Dec 2006 10:39:16 -0800, wrote:


Steve Barker LT wrote:
It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.


I think the regulations restrict the number of "devices" in a box, but
I don't know if wire nuts are considered to be a "device".


You are talking about number of conductors. No?
Wire nuts don't count. It is based on the volume of the box.

Nate Nagel December 28th 06 01:02 AM

House wiring question.
 
Terry wrote:
On 27 Dec 2006 10:39:16 -0800, wrote:


Steve Barker LT wrote:

It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.


I think the regulations restrict the number of "devices" in a box, but
I don't know if wire nuts are considered to be a "device".



You are talking about number of conductors. No?
Wire nuts don't count. It is based on the volume of the box.


But they do take up space. "Spec Grade" receptacles with the
screw-tightened back wire ports are your friends.

going off on a tangent, does anyone make "spec grade" Decora style
receps in the 15A flavor? Only ones I've seen are 20A, which is nice
for the kitchen, laundry, etc. but that doesn't help elsewhere...

Left to my own devices (heh) I would have just bought spec grade regular
stuff in plain old ivory, but the home decor dept. has mandated white
Decora devices.

nate

--
replace "fly" with "com" to reply.
http://home.comcast.net/~njnagel

Tom Horne, Electrician December 28th 06 03:27 AM

House wiring question.
 
Nate Nagel wrote:
Terry wrote:
On 27 Dec 2006 10:39:16 -0800, wrote:


Steve Barker LT wrote:

It actually would have been more important to pigtail the hots and
neutrals.
Putting one on each screw creates a situation where if one
connection goes
bad, then you lose all your downstream current.

I think the regulations restrict the number of "devices" in a box, but
I don't know if wire nuts are considered to be a "device".



You are talking about number of conductors. No?
Wire nuts don't count. It is based on the volume of the box.


But they do take up space. "Spec Grade" receptacles with the
screw-tightened back wire ports are your friends.

going off on a tangent, does anyone make "spec grade" Decora style
receps in the 15A flavor? Only ones I've seen are 20A, which is nice
for the kitchen, laundry, etc. but that doesn't help elsewhere...

Left to my own devices (heh) I would have just bought spec grade regular
stuff in plain old ivory, but the home decor dept. has mandated white
Decora devices.

nate


You can get the specification grade Decora devices at an electrical
supply house. Call and ask if they stock Leviton Catalog #: 16252-W.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous
for general use." Thomas Alva Edison

Mark Lloyd December 28th 06 08:49 PM

House wiring question.
 
On Wed, 27 Dec 2006 20:02:32 -0500, Nate Nagel
wrote:

Terry wrote:
On 27 Dec 2006 10:39:16 -0800, wrote:


Steve Barker LT wrote:

It actually would have been more important to pigtail the hots and neutrals.
Putting one on each screw creates a situation where if one connection goes
bad, then you lose all your downstream current.

I think the regulations restrict the number of "devices" in a box, but
I don't know if wire nuts are considered to be a "device".



You are talking about number of conductors. No?
Wire nuts don't count. It is based on the volume of the box.


But they do take up space. "Spec Grade" receptacles with the
screw-tightened back wire ports are your friends.

going off on a tangent, does anyone make "spec grade" Decora style
receps in the 15A flavor? Only ones I've seen are 20A, which is nice
for the kitchen, laundry, etc. but that doesn't help elsewhere...

Left to my own devices (heh) I would have just bought spec grade regular
stuff in plain old ivory, but the home decor dept. has mandated white
Decora devices.

nate


I prefer white. That "ivory" appears perpetually dirty, since that's
the color of dirt.
--