kitchen circuits 15 amp vs 20 amp outlets
I am redoing my kitchen. All of the duplex outlets are on two 20 amp
12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR |
kitchen circuits 15 amp vs 20 amp outlets
tr wrote:
I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR Personally I would replace them with 20amp outlets, good ones, not the 37˘ contractor specials. Use the screw clamp terminals not the stab connects. I am really fuzzy about it, but as I recall it is OK to use the 15amp outlets, but I just would not do it so I am not really sure. -- Joseph Meehan Dia 's Muire duit |
kitchen circuits 15 amp vs 20 amp outlets
|
kitchen circuits 15 amp vs 20 amp outlets
If these are counter top or anywhere near sink, they should be 20A GFI. If for fridge or dishwasher, dedicated 20A. If you are redoing kitchen, you probably want to look at adding circuits/ receptacles. Think through what you want before you start, this is the time to upgrade elec circuits if needed. |
kitchen circuits 15 amp vs 20 amp outlets
"tr" wrote in message oups.com... I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? 15a outlets are fine, unless there is just one outlet on the circuit; then it has to be 20a. Only reason to have a 20a outlet is to fit a 20a plug. |
kitchen circuits 15 amp vs 20 amp outlets
A DUPLEX outlet ( the standard type) is 2 outlets, not one, and thus a 15
amp duplex can actually be used alone on a 20 amp circuit, though in a kitchen the more outlets the better so you might as well have more. When I did my kitchen I used the 20 amp ones though to be honest I have never even seen a 20 amp kitchen appliance, I just thought they 'might' be made a little heavier duty than a 15 amp ones..probably wishful thinking but the price difference wasn't much. -- Mike S. "Toller" wrote in message ... 15a outlets are fine, unless there is just one outlet on the circuit; then it has to be 20a. Only reason to have a 20a outlet is to fit a 20a plug. |
kitchen circuits 15 amp vs 20 amp outlets
FWIW: a couple of code books back, back stabbing of 12 gauge conductors
became illegal and outlet manufacturers reduced the size of the back stab holes so only 14 gauge will fit "Joseph Meehan" wrote in message . .. tr wrote: I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR Personally I would replace them with 20amp outlets, good ones, not the 37˘ contractor specials. Use the screw clamp terminals not the stab connects. I am really fuzzy about it, but as I recall it is OK to use the 15amp outlets, but I just would not do it so I am not really sure. -- Joseph Meehan Dia 's Muire duit |
kitchen circuits 15 amp vs 20 amp outlets
All the 15A outlets at the big stores are actually rated to 20A but
only have 15A plugs. That is required by code, from what I understand. Thus, you can use them on a 20A circuit. In fact, if you look at a 15A GFCI outlet, you'll see that they rate the secondary feed circuit (the tabs for more outlets) at 20A. Mikey S. states an interesting point about a duplex outlet being 2 devices. I wasn't sure how that works with code, so I just put in a real 20A GFCI duplex outlet on the dedicated circuit in my new bathroom. The uncertainty wasn't worth possibly failing an inspection. Now it's the only place in the house where I could plug in my arc welder! -rev tr wrote: I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR |
kitchen circuits 15 amp vs 20 amp outlets
In article .com,
"Sev" wrote: If for fridge or dishwasher, dedicated 20A. For fridge and other essentials, I prefer to put an often used light on the same circuit so I will be aware when the breaker trips before the frozen food thaws. -- Free men own guns - www.geocities/CapitolHill/5357/ |
kitchen circuits 15 amp vs 20 amp outlets
The NEC prohibits installing lights on kitchen outlet circuits, other than
ones plugged into the outlets "Nick Hull" wrote in message .. . In article .com, "Sev" wrote: If for fridge or dishwasher, dedicated 20A. For fridge and other essentials, I prefer to put an often used light on the same circuit so I will be aware when the breaker trips before the frozen food thaws. -- Free men own guns - www.geocities/CapitolHill/5357/ |
kitchen circuits 15 amp vs 20 amp outlets
On 15 Nov 2006 12:48:36 -0800, "The Reverend Natural Light"
wrote: All the 15A outlets at the big stores are actually rated to 20A but only have 15A plugs. That is required by code, from what I understand. Thus, you can use them on a 20A circuit. In fact, if you look at a 15A GFCI outlet, you'll see that they rate the secondary feed circuit (the tabs for more outlets) at 20A. I think they's call that a 20A GFCI. Mikey S. states an interesting point about a duplex outlet being 2 devices. I wasn't sure how that works with code, so I just put in a real 20A GFCI duplex outlet on the dedicated circuit in my new bathroom. The uncertainty wasn't worth possibly failing an inspection. Now it's the only place in the house where I could plug in my arc welder! -rev tr wrote: I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR -- 40 days until the winter solstice celebration Mark Lloyd http://notstupid.laughingsquid.com "All your western theologies, the whole mythology of them, are based on the concept of God as a senile delinquent." -- Tennessee Williams |
kitchen circuits 15 amp vs 20 amp outlets
On Wed, 15 Nov 2006 16:48:55 -0500, "RBM" rbm2(remove
wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets Isn't that just the countertop outlets? |
kitchen circuits 15 amp vs 20 amp outlets
I can't say exactly what you call them, but you can buy a GFCI with 15A
plugs that'll feed a 20A circuit or a GFCI with 20A plugs that'll also feed a 20A circuit. They're both the same internally, of course, but one has the different shaped plug and costs 3X as much. -rev Mark Lloyd wrote: I think they's call that a 20A GFCI. |
kitchen circuits 15 amp vs 20 amp outlets
Quite right Rev, it's called a 20 amp feed through
"The Reverend Natural Light" wrote in message oups.com... I can't say exactly what you call them, but you can buy a GFCI with 15A plugs that'll feed a 20A circuit or a GFCI with 20A plugs that'll also feed a 20A circuit. They're both the same internally, of course, but one has the different shaped plug and costs 3X as much. -rev Mark Lloyd wrote: I think they's call that a 20A GFCI. |
kitchen circuits 15 amp vs 20 amp outlets
No, it's any outlet connected to the two or more required small appliance
branch circuits. "Goedjn" wrote in message ... On Wed, 15 Nov 2006 16:48:55 -0500, "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets Isn't that just the countertop outlets? |
kitchen circuits 15 amp vs 20 amp outlets
In article , "RBM" rbm2(remove wrote:
The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
Here's all I could find . from the 2000 IRC
E3603.2 Kitchen and dining area receptacles.A minimum of two 20-ampere-rated branch circuits shall be provided to serve receptacles located in the kitchen, pantry, breakfast area and dining area. The kitchen countertop receptacles shall be served by a minimum of two 20-ampere-rated branch circuits, either or both of which shall also be permitted to supply other receptacle outlets in the kitchen, pantry, breakfast area and dining area. -- Steve Barker Paola, KS BNSF (BN) Fort Scott Sub MP 50 Nikon CP 995 www.barkerranch.net "Doug Miller" wrote in message et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
You don't consider lighting outlets as "other outlets"?
"Doug Miller" wrote in message et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
In article , "RBM" rbm2(remove wrote:
You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. "Doug Miller" wrote in message . net... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
RBM wrote:
The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets "Nick Hull" wrote in message .. . In article .com, "Sev" wrote: If for fridge or dishwasher, dedicated 20A. For fridge and other essentials, I prefer to put an often used light on the same circuit so I will be aware when the breaker trips before the frozen food thaws. -- Free men own guns - www.geocities/CapitolHill/5357/ The code only prohibits having lighting outlets on the counter top receptacle circuits and although it permits the refrigerator to be supplied from such a circuit it does not require that. So a receptacle placed behind a refrigerator so as to be inaccessible for counter top use could be supplied from a lighting circuit. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
kitchen circuits 15 amp vs 20 amp outlets
In article , on Thu, 16
Nov 2006 00:59:50 GMT, Doug Miller wrote: In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. PMFJI, but please see 2005 NEC 210.23(A) Quote:
Seth Goodman |
kitchen circuits 15 amp vs 20 amp outlets
The code only prohibits having lighting outlets on the counter top receptacle circuits and although it permits the refrigerator to be supplied from such a circuit it does not require that. So a receptacle placed behind a refrigerator so as to be inaccessible for counter top use could be supplied from a lighting circuit. -- Right... The refrigerator outlet in most dwellings is on a different circuit than the 2 required 20A countertop appliance outlets. These outlets are suppose to be for coffee pots, microwave ovens, broillers, blenders, can openers, etc. Two of them are needed because most of these kitchen appliances consume lots of power. Also note that the fridge outlet is one of the few exceptions that should not be on a GFCI outlet, lest it nuisance trip while you are out of town and spoil your food. The NEC recognizes this, even though the prevailing sentiment will be to require GFCI's on just about all outlet circuits in future codes. Beachcomber |
kitchen circuits 15 amp vs 20 amp outlets
In article , Seth Goodman wrote:
In article , on Thu, 16 Nov 2006 00:59:50 GMT, Doug Miller wrote: In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. PMFJI, but please see 2005 NEC 210.23(A) Quote:
Right... but since Code requires two small appliance circuits in a kitchen, a *third* outlet circuit could supply virtually any other loads as well, because that third circuit is not a "small appliance branch circuit ... required ... by 210.11(C) ..." and thus not subject to that restriction. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
Correct, the two OR MORE small appliance circuits can't serve any other
outlets except the "receptacle outlets" listed and you can add other outlets in these areas that are not part of the requirement. My reply was to a guy that wanted to add a lighting outlet to the SAME circuit as a small appliance receptacle is on "Doug Miller" wrote in message ... In article , Seth Goodman wrote: In article , on Thu, 16 Nov 2006 00:59:50 GMT, Doug Miller wrote: In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. PMFJI, but please see 2005 NEC 210.23(A) Quote:
Right... but since Code requires two small appliance circuits in a kitchen, a *third* outlet circuit could supply virtually any other loads as well, because that third circuit is not a "small appliance branch circuit ... required ... by 210.11(C) ..." and thus not subject to that restriction. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code I think if that were the case, they wouldn't use specific terms like "receptacle outlets" and "outlets" "Doug Miller" wrote in message m... In article , "RBM" rbm2(remove wrote: You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. "Doug Miller" wrote in message .net... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
In article , on Thu, 16
Nov 2006 11:33:21 GMT, Doug Miller wrote: In article , Seth Goodman wrote: In article , on Thu, 16 Nov 2006 00:59:50 GMT, Doug Miller wrote: In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. PMFJI, but please see 2005 NEC 210.23(A) Quote:
Right... but since Code requires two small appliance circuits in a kitchen, a *third* outlet circuit could supply virtually any other loads as well, because that third circuit is not a "small appliance branch circuit ... required ... by 210.11(C) ..." and thus not subject to that restriction. The code doesn't require *exactly* two. It requires at *least* two. See 210.52(B)(3) "Kitchen Receptacle Requirements", which says "not fewer than two small appliance branch circuits". Other sections use the term "at least two". You can have as many as you want = 2, but if they supply kitchen outlets, they are still small appliance branch circuits, and must obey code. There are some exceptions, but none that would allow supplying a light fixture on the same circuit as a refrigerator. As RBM suggested earlier, there's nothing to prevent one from plugging in a light (such as a night light) on the same circuit as the refrigerator (unless it's a dedicated refrigerator circuit). If you still disagree, please provide Code cites. If you don't own a copy of the NEC, you can read it on-line at: http://nfpa-acs-01.gvpi.net:8080/rrs...NFPASTD/7005SB You'll need to allow Java and pop-ups. -- Seth Goodman |
kitchen circuits 15 amp vs 20 amp outlets
In article , Seth Goodman wrote:
The code doesn't require *exactly* two. It requires at *least* two. See 210.52(B)(3) "Kitchen Receptacle Requirements", which says "not fewer than two small appliance branch circuits". Other sections use the term "at least two". You can have as many as you want = 2, but if they supply kitchen outlets, they are still small appliance branch circuits, and must obey code. There are some exceptions, but none that would allow supplying a light fixture on the same circuit as a refrigerator. As RBM suggested earlier, there's nothing to prevent one from plugging in a light (such as a night light) on the same circuit as the refrigerator (unless it's a dedicated refrigerator circuit). I stand corrected. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. |
kitchen circuits 15 amp vs 20 amp outlets
|
kitchen circuits 15 amp vs 20 amp outlets
See 210.52(B)(3) "Kitchen Receptacle Requirements", which says "not fewer than two small appliance branch circuits". Other sections use the term "at least two". You can have as many as you want = 2, but if they supply kitchen outlets, they are still small appliance branch circuits, and must obey code. There are some exceptions, but none that would allow supplying a light fixture on the same circuit as a refrigerator. As RBM suggested earlier, there's nothing to prevent one from plugging in a light (such as a night light) on the same circuit as the refrigerator (unless it's a dedicated refrigerator circuit). Just for clarification, you're asserting that any receptacle that is in a kitchen, reguardless of where in the kitchen it is, is therefore a small-appliance branch circut? (and thus must be 20 Amps, GFCI protected, and not connected to anything else?) (and excepting individual receptacles dedicated to single fixed devices, like a freezer, refer, or stove?) --Goedjn |
kitchen circuits 15 amp vs 20 amp outlets
"Doug Miller" wrote in message
et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. "Doug Miller" wrote in message m... In article , "RBM" rbm2(remove wrote: You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. RBM wrote: I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code I think if that were the case, they wouldn't use specific terms like "receptacle outlets" and "outlets" "Lighting Outlet. An outlet intended for the direct connection of a lamp-holder, a luminaire (lighting fixture), or a pendant cord terminating in a lamp-holder. Outlet. A point on the wiring system at which current is taken to supply utilization equipment. ["An example is a lighting outlet or a receptacle outlet." Handbook Commentary] Power Outlet. An enclosed assembly that may include receptacles, circuit breakers, fuse-holders, fused switches, buses, and watt-hour meter mounting means; intended to supply and control power to mobile homes, recreational vehicles, park trailers, or boats or to serve as a means for distributing power required to operate mobile or temporarily installed equipment. Receptacle Outlet. An outlet where one or more receptacles are installed." Copyright 2002 National Fire Protection Association The quoted material above is from the National Electric Code. Would you mind sharing which code you were referring to. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
kitchen circuits 15 amp vs 20 amp outlets
In article , on Thu, 16 Nov
2006 11:04:31 -0500, Goedjn wrote: Just for clarification, you're asserting that any receptacle that is in a kitchen, reguardless of where in the kitchen it is, is therefore a small-appliance branch circut? (and thus must be 20 Amps, GFCI protected, and not connected to anything else?) (and excepting individual receptacles dedicated to single fixed devices, like a freezer, refer, or stove?) Sounds like a trick question - all I was asserting was that you can't put a lighting fixture on the same circuit as a refrigerator. Your generalization may be true, but I'll leave the proof as an exercise for the reader. ;-) -- Seth Goodman |
kitchen circuits 15 amp vs 20 amp outlets
In article ,
"Joseph Meehan" wrote: Personally I would replace them with 20amp outlets, good ones, not the 37˘ contractor specials. Use the screw clamp terminals not the stab connects. I am really fuzzy about it, but as I recall it is OK to use the 15amp outlets, but I just would not do it so I am not really sure. Iıve seen, and have, the 20 amp outlets that are meant to accommodate a 20 amp plug. But, I have never seen or known of any appliance, perhaps with the exception of an air conditioner, that uses this plug. So why are these outlets needed in the kitchen? -- Larry Weil Lake Wobegone, NH |
kitchen circuits 15 amp vs 20 amp outlets
Joseph Meehan wrote:
tr wrote: I am redoing my kitchen. All of the duplex outlets are on two 20 amp 12 awg wire breakers. However...all of the old outlets are rated for 15 amp circuits ? I have come across this in kitchens many times before. Can you use duplexes rated for 15 amps in the kitchen with 20 amp breakers...fed by 12 awg wires ? Is this a common practice and OK via NEC...or should you use the 20 amp duplexes with the horizontal little plug fitting on the receptacles ? Thanks, TR Personally I would replace them with 20amp outlets, good ones, not the 37˘ contractor specials. Use the screw clamp terminals not the stab connects. I am really fuzzy about it, but as I recall it is OK to use the 15amp outlets, but I just would not do it so I am not really sure. -- Joseph Meehan Dia 's Muire duit A 20A circuits feeding the kitchen, yes, spending the extra $ for 20A outlets to put on that circuit when you will *never* find a kitchen appliance in any consumer store that actually has a 20A plug, no. I used 20A GFCIs and 20A spec grade outlets in my shop where they may actually see 20A plugs from time to time, but everything in the house is 15A GFCI where needed (they are rated 20A feed through) and 15A outlets where GFCIs are not needed. Everything is on 20A circuits though, not a single 15A circuit anywhere in the house and no 14ga wire anywhere either, not even lighting circuits. Pete C. |
kitchen circuits 15 amp vs 20 amp outlets
When the code states that the small appliance circuits can't be shared with
other "outlets", by the very definition, that you point out, if you read the commentary, "outlet" includes all types of outlets "Tom Horne, Electrician" wrote in message k.net... "Doug Miller" wrote in message et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. "Doug Miller" wrote in message m... In article , "RBM" rbm2(remove wrote: You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. RBM wrote: I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code I think if that were the case, they wouldn't use specific terms like "receptacle outlets" and "outlets" "Lighting Outlet. An outlet intended for the direct connection of a lamp-holder, a luminaire (lighting fixture), or a pendant cord terminating in a lamp-holder. Outlet. A point on the wiring system at which current is taken to supply utilization equipment. ["An example is a lighting outlet or a receptacle outlet." Handbook Commentary] Power Outlet. An enclosed assembly that may include receptacles, circuit breakers, fuse-holders, fused switches, buses, and watt-hour meter mounting means; intended to supply and control power to mobile homes, recreational vehicles, park trailers, or boats or to serve as a means for distributing power required to operate mobile or temporarily installed equipment. Receptacle Outlet. An outlet where one or more receptacles are installed." Copyright 2002 National Fire Protection Association The quoted material above is from the National Electric Code. Would you mind sharing which code you were referring to. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
kitchen circuits 15 amp vs 20 amp outlets
And the code still doesn't allow you to share the required small appliance
circuits with "other outlets" "Seth Goodman" wrote in message .net... In article , on Thu, 16 Nov 2006 11:33:21 GMT, Doug Miller wrote: In article , Seth Goodman wrote: In article , on Thu, 16 Nov 2006 00:59:50 GMT, Doug Miller wrote: In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. PMFJI, but please see 2005 NEC 210.23(A) Quote:
Right... but since Code requires two small appliance circuits in a kitchen, a *third* outlet circuit could supply virtually any other loads as well, because that third circuit is not a "small appliance branch circuit ... required ... by 210.11(C) ..." and thus not subject to that restriction. The code doesn't require *exactly* two. It requires at *least* two. See 210.52(B)(3) "Kitchen Receptacle Requirements", which says "not fewer than two small appliance branch circuits". Other sections use the term "at least two". You can have as many as you want = 2, but if they supply kitchen outlets, they are still small appliance branch circuits, and must obey code. There are some exceptions, but none that would allow supplying a light fixture on the same circuit as a refrigerator. As RBM suggested earlier, there's nothing to prevent one from plugging in a light (such as a night light) on the same circuit as the refrigerator (unless it's a dedicated refrigerator circuit). If you still disagree, please provide Code cites. If you don't own a copy of the NEC, you can read it on-line at: http://nfpa-acs-01.gvpi.net:8080/rrs...NFPASTD/7005SB You'll need to allow Java and pop-ups. -- Seth Goodman |
kitchen circuits 15 amp vs 20 amp outlets
RBM wrote:
When the code states that the small appliance circuits can't be shared with other "outlets", by the very definition, that you point out, if you read the commentary, "outlet" includes all types of outlets "Tom Horne, Electrician" wrote in message k.net... "Doug Miller" wrote in message et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. "Doug Miller" wrote in message m... In article , "RBM" rbm2(remove wrote: You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. RBM wrote: I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code I think if that were the case, they wouldn't use specific terms like "receptacle outlets" and "outlets" "Lighting Outlet. An outlet intended for the direct connection of a lamp-holder, a luminaire (lighting fixture), or a pendant cord terminating in a lamp-holder. Outlet. A point on the wiring system at which current is taken to supply utilization equipment. ["An example is a lighting outlet or a receptacle outlet." Handbook Commentary] Power Outlet. An enclosed assembly that may include receptacles, circuit breakers, fuse-holders, fused switches, buses, and watt-hour meter mounting means; intended to supply and control power to mobile homes, recreational vehicles, park trailers, or boats or to serve as a means for distributing power required to operate mobile or temporarily installed equipment. Receptacle Outlet. An outlet where one or more receptacles are installed." Copyright 2002 National Fire Protection Association The quoted material above is from the National Electric Code. Would you mind sharing which code you were referring to. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison Why do you assume that I'm arguing with you. Did I hit respond to the wrong posting? -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
kitchen circuits 15 amp vs 20 amp outlets
The quoted material above is from the National Electric Code. Would you
mind sharing which code you were referring to. -- Tom Horne I could be mistaken, but that sounds like an argument to me "Tom Horne, Electrician" wrote in message ink.net... RBM wrote: When the code states that the small appliance circuits can't be shared with other "outlets", by the very definition, that you point out, if you read the commentary, "outlet" includes all types of outlets "Tom Horne, Electrician" wrote in message k.net... "Doug Miller" wrote in message et... In article , "RBM" rbm2(remove wrote: The NEC prohibits installing lights on kitchen outlet circuits, other than ones plugged into the outlets I don't think that's correct -- do you have a Code cite for it? I see where the Code prohibits other *outlets* on those circuits (e.g. in other rooms), but I don't see a prohibition against lighting. -- Regards, Doug Miller (alphageek at milmac dot com) It's time to throw all their damned tea in the harbor again. "Doug Miller" wrote in message m... In article , "RBM" rbm2(remove wrote: You don't consider lighting outlets as "other outlets"? I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code. RBM wrote: I don't consider a light *fixture* (e.g. a ceiling light) as an outlet, and neither does the Code I think if that were the case, they wouldn't use specific terms like "receptacle outlets" and "outlets" "Lighting Outlet. An outlet intended for the direct connection of a lamp-holder, a luminaire (lighting fixture), or a pendant cord terminating in a lamp-holder. Outlet. A point on the wiring system at which current is taken to supply utilization equipment. ["An example is a lighting outlet or a receptacle outlet." Handbook Commentary] Power Outlet. An enclosed assembly that may include receptacles, circuit breakers, fuse-holders, fused switches, buses, and watt-hour meter mounting means; intended to supply and control power to mobile homes, recreational vehicles, park trailers, or boats or to serve as a means for distributing power required to operate mobile or temporarily installed equipment. Receptacle Outlet. An outlet where one or more receptacles are installed." Copyright 2002 National Fire Protection Association The quoted material above is from the National Electric Code. Would you mind sharing which code you were referring to. -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison Why do you assume that I'm arguing with you. Did I hit respond to the wrong posting? -- Tom Horne "This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison |
All times are GMT +1. The time now is 07:11 PM. |
Powered by vBulletin® Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.